Flex 402
Two-Zone Fire Alarm Control Panel
The Gamewell Flex 402 Fire Alarm
Control Panel brings the latest in mi-
croprocessor technology to conven-
tional fire controls. The Flex 402 is
compatible with the new
i³
™ smoke
detectors from System Sensor, and
provides advanced features including
drift compensation, maintenance alert,
and freeze warning. Automatic synchro-
nization of audio/visual devices is pro-
vided, selectable for three manufactur-
ers’ protocols. The NAC protocol in-
cludes the ability, using a single pair of wires, to silence audible devices while
strobes continue to flash.
The Flex 402 is also compatible with conventional input devices such as two-
and four-wire smoke detectors, pull stations, waterflow devices, tamper switches
and other normally-open contact devices.
Operation
The activation of a compatible smoke detector or any normally-open fire alarm
initiating device will: activate audible and visual signaling devices, illuminate an
indicating LED, sound the piezo sounder at the FACP, activate the FACP alarm
relay, and operate an optional module which notifies a remote station or initiates
an auxiliary control function.
i³™
Technology Features
• Drift compensation automatically adjusts detector sensitivity and increases
resistance to false alarms caused by dust accumulation.
• The maintenance alert LEDs (per zone) warn of excessive dirt accumulation,
preventing false alarms.
• Detector sensitivity is automatically measured. The twice-yearly test require-
ments of NFPA 72 (7-3.2.1) are met without using a ladder or test meter.
• The wireless handheld sensitivity meter eliminates the need for voltmeters,
magnets, or a physical connection to the detector. The reader displays sensi-
tivity in terms of percent-per-foot obscuration and provides text status indica-
tion.
• The supervisory LED (per zone) provides a warning if a detector senses tem-
peratures approaching freezing.
• Special test protocol and LED indication allow a quick test of all detectors —
without a ladder.
• Electronic heat-sensing element provides thermal detection in addition to pho-
toelectronic smoke detection.
Flex 402 Two-Zone FACP
CS-2402 09/01/06
Page 1 of 2
• Two Style B (Class B) Initiating Device
Circuits (IDCs).
• One Style Y (Class B) Notification Appliance
Circuit (NAC).
• 24 VDC.
NAC synchronization features:
– Provides synchronization of standard ANSI
audible signals as required by NFPA 72
(3-8.4.1.2.3).
– Provides synchronization of ADA compliant
strobes per NFPA 72 (4-4.4.1).
– Selectable for System Sensor, Wheelock,
and Gentex protocols.
– Selective Silence feature allows manual
silencing of horns while strobes continue to
flash on the same NAC.
• Silent or Audible Walk Test operation mode
commanded from the front keypad, with
automatic return to normal after one hour of
inactivity.
• Alarm verification selectable per zone.
• Each zone may be programmed for
supervisory or fire; each zone has separate
red and yellow LEDs.
• Disable switches provided for each zone.
NACs programmable for:
Silence Inhibit, Auto
Silence, Strobe Synchronization, Selective
Silence (horn/strobe mute), Temporal or
Steady signal, Silenceable or
Nonsilenceable.
• Form-C Alarm and Trouble relays.
• 3.0 amps total usable current.
• Optional dress panel (P/N
DP-FLEX).
• Piezo sounder for alarm, trouble, supervisory,
and maintenance.
Control buttons:
ACK (Acknowledge), Alarm
Silence, Reset, Walktest,
Zone Enable/Disable (one per zone).
LED indicators:
Fire Alarm (one per zone),
Supervisory (one per zone), Trouble (one
per zone), Maintenance (one per zone),
AC Power, NAC Disable, Zone Disable,
NAC Fault, System Trouble, Power Trouble,
Walktest, Alarm Silence, Earth Fault (on
circuit board), Battery Fault (on circuit board),
Charger Fault (on circuit board).
Listings
Listings and approvals below apply to the
basic Flex 402 panel. In some cases, certain
modules may not be listed by certain
approval agencies, or listing may be in
process. Consult factory for latest listing
status.
• UL Listed: file S521.
• CSFM approved: file 7165-1288-180.
• MEA approved: file 366-04-E.
Backbox Mounting
The cabinet can be surface-mounted. The door is removable during installa-
tion by opening and lifting it off the hinges. The cabinet mounts using two
key slots at the top of the backbox and two additional 0.250" diameter holes
at the bottom.
AC power, TB8
120 VAC, 50/60 Hz, 2.3 A.
Wire size:
minimum 14 AWG (2.0 mm²)
with 600 V insulation.
Battery (sealed lead-acid only), J8
Maximum charging circuit:
normal flat
charge 27.6 VDC @ 0.8 A.
Maximum battery charger capacity:
18 AH battery. Two 7 AH batteries can
be housed in the FACP cabinet. Larger
batteries require a separate battery
box such as the
BB-17F.
Initiating device circuits, TB3
Alarm zones 1&2. Power-limited circuitry.
Operation:
all zones Style B (Class B).
Normal operating voltage:
nominal 22
VDC.
Alarm current:
15 mA minimum.
Standby current:
4 mA.
Short circuit current:
40 mA maximum.
Maximum loop resistance:
100 ohms.
End-of-line resistor:
4.7K ohm, 1/2
watt (P/N
71252).
Notification appliance circuits, TB2
One NAC on Flex 402. Power-limited
circuitry.
nominal 24
VDC.
Maximum signaling current:
2.5 A total
with standard transform.
4.7K ohm, 1/2
watt (P/N
71252).
Form-C relays
Trouble relay TB5 (fail-safe). Alarm
relay TB6.
Contact ratings:
2.0 A @ 30 VAC
(resistive).
Auxiliary outputs
Resettable power, TB1
Power-limiting circuitry.
Operating voltage:
nominal 24 VDC.
Maximum available current:
500 mA,
appropriate for powering four-wire
smoke detectors.
Total current
for resettable power and one NAC
must not exceed 3 A for the Flex 402.
Cabinet dimensions
Door:
15.342" (38.97 cm) high x 14.677"
(37.28 cm) wide x 0.375" (0.95 cm)
deep.
Backbox:
15.0" (38.10 cm) high
x 14.5" (36.83 cm) wide x 3.0" (7.62 cm)
Ordering Information
F402
BB-17F
DP-FLEX
TR-1-R
52194
Two-zone conventional FACP.
Battery box, required to house two batteries greater than 7
AH, to a maximum of 18 AH.
Dress panel.
Trim ring for semi-flush mounting.
Flex 402 Installation and Maintenance Manual.
i³™
is a trademark and
Gamewell®
is a registered trademark of Honeywell International Inc.
Gamewell-FCI
12 Clintonville Road
Northford, CT 06472-1610
Phone: 203-484-7161
Fax: 203-484-7118
www.gamewell-fci.com
A Honeywell Company
© 2006 Gamewell-FCI
deep.
Specifications and wiring information are provided for information only and are
believed to be accurate. Gamewell-FCI assumes no responsibility for their use.
Data and design are subject to change without notice. Installation and wiring
instructions shipped with the product shall always be used for actual installation.
For more information, contact Gamewell-FCI.
Page 2 of 2
CS-2402 09/01/06