3.0 KW
180-264VAC
ETN-HP
SERIES
Model
ETN24HP
ETN26HP
ETN28HP
ETN48HP
24V
26V
28V
48V
Output
125A
115A
107A
63A
Efficiency
85%
85%
85%
85%
The High Power PFC isolated Front Ends HOT-PLUG power
supply provide 24, 26, 28 and 48VDC single output. Complete
front-end solutions for driving high density DC to DC modules in
distributed Power Systems with (N+1) redundancy. Using Elcon
Top Drawer Connector, this ET series provides high reliable and
rugged compact power.
ELECTRICAL SPECIFICATIONS
INPUTS
RANGE: Full input Range 180 to 264 VAC. Single Phase
FREQUENCY: 43 to 63Hz.
INRUSH CURRENT: 25A averaged over ½ cycle
HARMONIC CURRENT: <5%
EFFICIENCY: 80% to 85% (Measured at full load and 208 VAC
Input)
Power Factor (>0.99)
0 C to +50 C at full load
Standard 5” X 5” X 11.25” envelope
Output Fully Floating
Overcurrent Protection
Overvoltage Protection
Remote Sense
Overtemperature Protection
Self-contained Forced Air Cooling
Meets UL, CSA and VDE Safety
Meets EMI EN88155 Level A
ISO9001
OUTPUTS
VOLTAGE: 24, 26, 28, and 48 VDC
CURRENT: See Tables
ADJUSTMENT RANGE: +5 to –10% of nominal output voltage.
POLARITY: Output is isolated. It may be referenced plus/minus as
required.
REMOTE SENSING: Compensates for up to 0.5V total loop drop
in the output line.
STATIC REGULATION: Line: +/- 0.25% over full line range.
Load: Option: =/-% zero load to full load. Droop IFE: Option:
the output sags from +5% when the load is increased from 10% to
100%.
VOLTAGE STABILITY: +/-0.1% FOR 24 hour period after 30
minute warm up.
OUTPUTS
TEMP COEFFICIENT: +/-0.02%/ C FROM 0 c TO +50 c.
P-P RIPPLE AND NOISE: 1% (20Hz to 50MHz Bandwidth).
MINIMUM LOAD: Not Required.
TURN ON DELAY: 1 sec. Max from application of AC line.
OVER VOLTAGE PROTECTION: 125% +/-5% of nominal. OVP
shutdown is latched until the input line is removed for 5 secs and
then reapplied. OVP sensing is don at the output terminals.
OVERCURRENT PROTECTION: Current l=Limit Point: 110% to
120% of full load.
OPTIONS
-6B CURRENT SHARING
-20c ISOLATION DIODE
-128l DC POWER GOOD
ETA-USA Tel:
408-778-2793 Fax: 408-779-2753 e-mail: sales@eta-usa.com
ETN-HP SERIES
ENVIRONMENTAL
OVERTEMPERATURE PROTECTION:
Automatically shuts down and latches the unit in the event of an over
temperature condition. After cool down, power must be recycled to
restart the unit.
AUDIBLE NOISE:
63 dBA max at 1 meter. 70 dBA for high speed
fans. (See Output Tables for units with high speed fan).
TEMPERATURE:
Standard: 0 C to +50 C at full load. Storage: -55 C
to +85 C.
HUMIDITY:
20% to 95% non-condensing.
ALTITUDE:
Operating: 8,000 Ft. Derates to 90% at 10,000 Ft. Non-
Operating at 30,000 feet.
VIBRATION:
Operating: From 5 to 27Hz, 0.02” double amplitude:
from 27 to 500Hz, 0.75G, 3 Axes, 5 min/octave sweep, dwell 1 min at
resonance.
Non-Operating:
From 5 to 17Hz, 0.01” double amplitude: from 17 to
500Hz, 1.5G peak: 3 axes, 5min/octave sweep, dwell 1 min at
resonance.
MTBF:
500,000 hours
SHOCK:
Operating: 5G, half sine, 11msec 3 axes. Non-Operating: 15G
half sine, 11 msec, 3 axes.
COOLING:
Forced air, internal fan Airflow normally exits at
connector.
EMI:
Conducted & Radiated EN55022 level A
SAFETY:
Meets UL1950 , CSA1950, and TUV t EN60950.
DIMENSIONS:
Elcon Lower Drawer Connector
Pin 1: AC Input (N)
Pin 21:
Pin 2: AC Input (L)
Pin 22:
Pin 3: Chassis Gnd
Pin 23:
Pin 4: Chassis Gnd
Pin 25:
Pin 5: Unit Present
Pin 26:
Pin 7: Unit Present
Pin 27:
Pin 17: Current Sharing Pin 28:
Pin 18: Current Monitor Pin 29:
Pin 19: Logic Return
Pin 20: Logic Inhibit
Pins 6, 8-16 and 24 Not Used.
Power Fail
Undervoltage Detect
Remote Sense +
Remote Sense -
Output +
Output -
Output +
Output -
ETA-USA Tel: