Current Transducer
CTSR 0.6-TP/SP2
PRN
600 mA
For the electronic measurement of current: DC, AC, pulsed..., with galvanic separation between
the primary circuit and the secondary circuit.
● Closed loop (compensated) current transducer
● Voltage output
● Single supply voltage
● PCB mounting
● Four integrated primary conductors.
● Residual current measurement
● Leakage current measurement in transformerless PV
inverters
● First human contact protection of PV arrays
● Failure detection in power sources
● Symmetrical fault detection (e.g. after motor inverter)
● Leakage current detection in stacked DC sources
● Single phase or three phase nominal current measurement
up to ± 30 A per wire (DC or AC).
Special feature
● No retention pin.
Advantages
High accuracy
● Very low offset drift over temperature
● High overload capability
● High insulation capability
● Reference pin with two modes, Ref In and Ref Out
● Degauss and test functions
● Possibility to add up to four primary wires (diam. 4.2 mm
Standards
● EN 50178: 1997
● IEC 61010-1: 2010
● UL 508: 2010.
Application Domain
● Industrial
max) in addition to the already integrated primary conductors. ● Suitable to fulfil VDE 0126-1-1, UL 1741.
N°97.H3.G6.002.0
28January2014/version 6
Page 1/10
LEM reserves the right to carry out modifications on its transducers, in order to improve them, without prior notice
www.lem.com
CTSR 0.6-TP/SP2
Absolute maximum ratings
Supply voltage
Primary conductor temperature
Overload capability (100 µs, 500 A/µs)
U
Î
Value
3300
Stresses above these ratings may cause permanent damage. Exposure to absolute maximum ratings for extended periods may
degrade reliability.
UL 508: Ratings and assumptions of certification
File # E189713 Volume: 2 Section: 3
Standards
● CSA C22.2 NO. 14-10 INDUSTRIAL CONTROL EQUIPMENT - Edition 11 - Revision Date 2011/08/01
● UL 508 STANDARD FOR INDUSTRIAL CONTROL EQUIPMENT - Edition 17 - Revision Date 2010/04/15
Ratings
Primary involved potential*
Max surrounding air temperature
Primary current
Secondary supply voltage
Output voltage
* Enviromental: For use in Pollution degree 3.
Conditions of acceptability
When installed in the end-use equipment, consideration shall be given to the following:
1 - A suitable enclosure shall be provided in the end-use application.
2 - The insulation between the primary and the secondary sensing circuits were evaluated with 4250 V AC for CTSR 0.6-TP/
SP and 2200 V AC for CTSR 0.6-P in dielectric voltage withstand test.
5 - CTSR series is intended to be mounted on the printed wiring board of the end-use equipment.
7 - The uninsulated live parts of primary feeder and secondary circuit clearance spacing of Model CTSR XX-P series shall
maintain at least 5.5 mm apart.
8 - Primary feeder of the devices shall be connected after an overvoltage device or system which has been evaluated by the
Standard for Transient Voltage Surge Suppressors, UL 1449.
Marking
Only those products bearing the UL or UR Mark should be considered to be Listed or Recognized and covered under UL's
Follow-Up Service. Always look for the Mark on the product.
U
out
V AC/DC
V DC
Value Version P
According to series primary currents
0 to 7
Value Version TP
Page 2/10
www.lem.com
CTSR 0.6-TP/SP2
Insulation coordination
Rms voltage for AC insulation test 50 Hz/1 min
Impulse withstand voltage 1.2/50 µs
Partial discharge extinction rms voltage @ 10 pC
Clearance (pri. - pri.)
Creepage distance (pri. - pri.)
Clearance (pri. - sec.)
Creepage distance (pri. - sec.)
U
d
Û
U
e
d
CI
d
Cp
d
CI
d
Cp
kV
kV
kV
mm
mm
mm
mm
Value
2.475
6.7
6.7
13.5
33.2
Comment
Shortest distance through
air
Shortest path along device
body
air
body
air
body
air
body
Reinforced insulation, CAT
III, PD2 non uniform field
according to EN 50178
III, PD3 non uniform field
according to EN 50178,
IEC 61010
When mounted on a PCB
(with recommended hole and pad diameters, see paragraph “PCB footprint”).
Comparative tracking index
Application example
d
CI
d
Cp
d
CI
d
Cp
CTI
mm
mm
mm
mm
5.6
12.5
12.5
Application example
Environmental and mechanical characteristics
Ambient operating temperature
Ambient storage temperature
Mass
m
g
Min
-40
-50
Typ
105
Comment
55
Page 3/10
www.lem.com
Electrical data
CTSR 0.6-TP/SP2
At
= 25 °C,
U
= + 5 V, output voltage referred to
ref
, unless otherwise noted (see Min., Max., typical definition paragraph) in
page 9.
Primary nominal residual rms current
Primary residual current, measuring range
Supply voltage
Current consumption
Output voltage referred to GND
(during Degauss cycle)
ref
(Test current)
Reference voltage @
= 0
External reference voltage
Electrical offset current
referred to primary (Note
2)
Temperature coefficient of
ref
OE
= 0
Theoretical sensitivity
Sensitivity error (Note
2)
Linearity error
Magnetic offset current (1000 x
PRN
referred to primary
Output rms noise voltage (1 Hz .. 10 kHz)
Reaction time @ 10 % of
PRN
Step response time to 90 % of
PN
Frequency bandwidth (- 1 dB)
Accuracy (Note
3)
Notes:
1)
2)
PRN
PRM
U
Min
-850
4.75
Typ
Comment
5.25
21.6
(mA)/N
With
= 1000 turns
- 40 .. 105 °C
1)
1)
Internal reference
Internal reference of
ref
input = 499 Ω
1)
out
out
ref
ref
OE
TCV
ref
TCV
OE
th
ε
TCG
ε
OM
no
ra
r
BW
2.495
2.3
0.3
0.75
2.505
ppm/K
ppm/K
V/A
ppm/K
% of
PRM
mV
µs
µs
kHz
-24
4.2
24
±50
±520
- 40 .. 105 °C
ppm/K of 2.5 V
- 40 .. 105 °C
> 500 kΩ
- 40 .. 105 °C
2.476
-0.7
0.3
0.4
17
> 500 kΩ
> 500 kΩ,
di/dt
> 5 A/µs
> 500 kΩ,
di/dt
> 5 A/µs
> 500 kΩ
= (ε
ε
L 2
1/2
0.7
±100
1.3
See “Application information” section.
Only with a primary nominal residual current, see paragraph “Primary nominal residual current and primary nominal
current”.
3)
Accuracy @
and
TA
= (X
+ (TCG•100•(T
+ (TCV
OE
•2.5•(T
- 25 )/G
th
•100/
Page 4/10
www.lem.com
CTSR 0.6-TP/SP2
Typical performance characteristics
Relative sensitivity (dB)
Frequency (Hz)
Noise voltage spectral density of V
Device: CTSR 0.6-P #05-61
Figure 1: Frequency response
Cumulated RMS noise voltage of V
-60
-65
-70
v
(dBVrms/rtHz)
e
no
(dBVrms/rtHz)
n
-75
-80
-85
-90
-95
-100
-105
-110
no
(V)
(V)
n
f
(Hz)
Phase (°)
f
c
(Hz)
Figure 2: Output noise voltage spectral density
Figure 3: Output noise, cumulated rms
Figure 4: Typical step response
Figure 5: Typical step response
Page 5/10
www.lem.com