LDT2400 Series are high power multipurpose digital power supplies
with three phase input voltage 400 – 500 VAC, delivering 2400 W of
output power, covering output voltages from 24 to 170 V (model
dependent).
Their compact size, high efficiency and excellent reliability together
with easy installation make them fit demanding applications where
compactness and high power are needed.
LDT2400 Series are Class I isolation devices suitable for SELV and
PELV circuitry (up to 48 VDC models) and are designed to be mounted
on DIN rail and installed inside a protective enclosure.
3 phase AC input: 400 – 500 VAC
Overload 150% (3600 W peak)
Active PFC for optimal efficiency
Active input surge suppressor for improved reliability
CPU control allows flexibility and multiple programmable features
Battery charger function included
Thermally regulated fan optimal cooling in harsh operating conditions
Wide output voltages range
Two phase operation possible with power derating
Automation
Process Control
Communication
Instrumentation Equipment
LDT2400 Series
LDT2400-24
LDT2400-48
LDT2400-72
LDT2400-170
400 - 500 VAC / 520 - 725 VDC
24 VDC
48 VDC
72 VDC
170 VDC
100 A
50 A
33 A
14 A
Technical parameters are typical, measured in laboratory environment at 25°C and 400 VAC / 50 Hz, at nominal values, after
minimum 5 minutes of operation.
Input AC Voltage Range
Input DC Voltage Range
Input Frequency
Input AC Current
Input DC Current
Power Factor Correction
Inrush Peak Current
Touch (Leakage) Current
Internal Protection Fuse
Recommended External Protection
3 phase (UL certified)
Operating
400 – 500 VAC
340 – 550 VAC
520 – 725 VDC
47 - 63 Hz
Vin = 400 VAC
Vin = 500 VAC
Vin = 520 VDC
Vin = 725 VDC
4.5 A
3.5 A
5.2 A
3.8 A
> 0.9
10 A
0.6 mA
Active
Active Inrush current limiter
None, external fuse must be provided
It is strongly recommended to provide external surge
arresters (SPD) according to local regulations
Fuse 3x AT 10 A or 3x MCB 10 A C curve
In case of 2 phase operation, reduce the output load to 50% of the nominal value.
Output Power
Rated Voltage (Adjustable Voltage Range)
LDT2400-24
LDT2400-48
LDT2400-72
LDT2400-170
LDT2400-24
LDT2400-48
LDT2400-72
LDT2400-170
LDT2400-24
LDT2400-48
LDT2400-72
LDT2400-170
LDT2400-24
LDT2400-48
LDT2400-72
LDT2400-170
with Remote Sense active and at Vout nom
Continuous Current
Overload Limit (Constant Current Mode)
Overload Limit (Hiccup Mode) (max. 5s)
Load Regulation
Ripple & Noise
2400 W
24 VDC (11.9 - 29 VDC)
48 VDC (23 - 56 VDC)
72 VDC (50 – 87 VDC)
170 VDC (85 – 175 VDC)
100 A
50 A
33 A
14 A
150 A / 5 s
75 A / 5 s
50 A / 5 s
21 A / 5 s
150 A
75 A
50 A
21 A
1%
400 mVpp
tech.support@psbel.com
LDT2400 Series
Hold up Time
Output Protections
10 ms
Output Over Voltage Protection
Parallel Connection
Efficiency
Dissipated Power
Thermal protection
Output overvoltage
LDT2400-24
LDT2400-48
LDT2400-72
LDT2400-170
Possible for power or redundancy
(includes internal ORing circuit)
LDT2400-24 / LDT2400-48
LDT2400-72
LDT2400-170
LDT2400-72
LDT2400-170
33 VDC
68 VDC
100 VDC
200 VDC
> 92%
> 93%
> 92%
< 200 W
< 180 W
< 200 W
Ripple and Noise are measured with 20 MHz bandwidth, probe terminated with a 0.1μF MKP parallel capacitor.
Pay attention, set the current limitation mode jumper on C.C. mode when connecting more units in parallel.
NOTE:
Power rating, losses, efficiency, ripple, thermal behaviour and start-up may change outside of the nominal rated input range.
Contact factory for details.
Status Signals
User Interface
Operating Modes
DC OK / CHARGE - green LED
ALARM - red LED
Dry contact (SPDT, 24 VDC / 1 A)
Alphanumeric LCD display
LCD with 4 keys
0 – 10 V voltage and 4 - 20 mA current output for output current 0 - 100% IN
Auxiliary 12 V / 100 mA isolated power supply
Load voltage sense
Optoisolated remote shut down input
USB communication interface via communication module (COMM-BOX)
Optional: remote temperature sensor for battery charging (WNTC-2MT)
Overboost: allows 150% output power for 5 sec, then off for 10 sec
Constant current: adjustable 10 - 100% load
Storage Temperature
Derating
Humidity
Life time Expectancy
Overvoltage Category
Pollution Degree
Protection Class
Isolation Voltage
UL certified up to 50°C
(Start-up type tested: - 40°C)
- 40 to + 70°C
- 40 to + 80°C
Automatic power derating (1200 W) for 2 phase operation - 60 W/°C over 50°C
Non-condensing
At 25°C ambient full Load
5 - 95% RH
458253 h (52.3 years)
III (EN50178)
2 (IEC60664-1)
Class I
4.2 kVDC
2.2 kVDC
0.75 kVDC
Standards & Approvals
Input to Output
Input to Ground
Output to Ground
UL508 (certified)
EN60950 (reference)
EN50178 (reference)
Asia-Pacific
+86 755 298 85888
Europe, Middle East
+353 61 225 977
North America
+1 408 785 5200
BCD.00760_AB
© 2016 Bel Power Solutions & Protection
LDT2400 Series
EMC Emission
EN55011 (CISPR11)
EN55022 (CISPR22)
EN61000-3-2
EN61000-4-2
EN61000-4-3
EN61000-4-4
EN61000-4-5
EN61000-4-11
EN60529
IEC 60068-2-6
IEC 60068-2-27
For temperature < - 20°C the LCD is not operating, but the unit will operate correctly
Possible at nominal voltage with load derating.
Class A
Class A
Class A
Level 3
Level 3
Level 4
Level 4
Level 2
IP20
5-17.8 Hz: ±1.6 mm; 17.8-500 Hz: 2g 2Hours
/ axis (X,Y,Z)
30g 6 ms, 20 g 11 ms;
3 bumps / direction, 18 bumps total
EMC Standards
EMC Immunity
Protection Degree
Vibration sinusoidal
Shock
Display
Control Keys
Output Connector
Auxiliary Connector
Input Connector
DIN rail fixing Clamp
Communication Interface
Status LEDs
Buzzer (Internal)
Figure 1. Detail of Auxiliary Connector (4)
LDT2400 Series
INPUT CONNECTIONS
3 phase:
L1 = Phase 1
L2 = Phase 2
L3 = Phase 3
= earth ground
DC:
L1 = + Positive DC
L2 = - Negative DC
L3 = do not connect
= earth ground
OUTPUT CONNECTIONS
+ = Positive DC
- = Negative DC
AUXILIARY CONNECTION I/Os
TSENSE = Temperature Sensor
Shutdown = Remote Shutdown (+/-)
Dry contact = COM / NC / NO Contact
GND AUX = Auxiliary Supply GND
4-20 mA = Output Current Measurement 4-20 mA
0-10 V = Output Current Measurement 0-10 V
SHARE = Load Share BUS (+/-)
SENSE = Remote Voltage Sense (+/-)
+12 V AUX = Auxiliary +12Vdc/100mA
Weight
Dimensions
Rail Mounting
Connection Terminals
Case Material
Input
Output
Auxiliary
Aluminum
Screw type header (16 - 10 AWG)
Screw type header (2 AWG)
Screw type pluggable 16 pin (16 AWG)
2.8 kg
233 x 160 x 101 mm
IEC 60715/H15/TH35-7.5(-15)
1.5 – 6 mm²
Up to 35 mm
1.5 mm
Figure 2. Mechanical Drawing
NUCLEAR AND MEDICAL APPLICATIONS
- Products are not designed or intended for use as critical components in life support systems,
equipment used in hazardous environments, or nuclear control systems.
TECHNICAL REVISIONS
- The appearance of products, including safety agency certifications pictured on labels, may change depending on the
date manufactured. Specifications are subject to change without notice.
Asia-Pacific
+86 755 298 85888
Europe, Middle East
+353 61 225 977
North America
+1 408 785 5200
BCD.00760_AB