FETA7000T-144
产品描述开关电源 7488W 144V 52A
产品类别电源/电源管理    开关电源
文件大小854KB,共7页
制造商Cosel
下载文档 详细参数 选型对比 全文预览
FETA7000T-144在线购买
FETA7000T-144 - - 点击查看 点击购买
FETA7000T-144概述
开关电源 7488W 144V 52A
FETA7000T-144规格参数
厂商名称Cosel
产品种类开关电源
发货限制由于产品尺寸或重量的缘故,只可用美元购买才能运输到您所在的国家。
输出电压—通道1144 VDC
输出端数量1 Output
输出功率7.488 kW
开放式框架/封闭式Enclosed
输入电压170 VAC to 264 VAC
输出电流—通道152 A
工业Commercial
绝缘电压3 kV
安装风格Chassis
长度475 mm
宽度388 mm
高度43 mm
系列FETA
尺寸475 mm x 388 mm x43 mm
输入频率47 Hz to 63 Hz
负载调节Regulated
最大工作温度+ 60 C
最小工作温度- 10 C
工厂包装数量1
单位重量11 kg
FETA2500BA
AC-DC Power Supplies Enclosed Type
Ordering information
FET A 2500 B A -OO -O
Example recommended EMI/EMC filter
NAC-20-472
High voltage pulse noise type : NAP series
Low leakage current type : NAM series
Series name
Single output
Output wattage
200/230V input
Version
Output voltage
Optional
F2: Reverse air exhaust
R: with Remote ON/OFF
Positive logic control
A higher current rating EMI/EMC filter
may be recommended in view of the
other devices that could be connected
in parallel with the power supply.
*Make
sure necessary tests will be carried out on your end equipment with the power supply installed in accordance with any required EMC/EMI regulations.
MODEL
MAX OUTPUT WATTAGE[W]
DC OUTPUT
*1
FETA2500BA-36
1980
36V 55A
FETA2500BA-48
2496
48V 52A
FETA2500BA-36
FETA2500BA-48
AC170 - 264 1f (Output derating is required at AC170V - 180V. Refer to instruction manual 4.2)
ACIN 200V
11.3typ
13.8typ
50 / 60 (47 - 63)
80typ (Io=10%)
83typ (Io=10%)
87typ (Io=20%)
89typ (Io=20%)
INPUT
EFFICIENCY[%]
ACIN 230V
91typ (Io=50%)
92.5typ (Io=50%)
90typ (Io=100%)
91.5typ (Io=100%)
ACIN 230V
POWER FACTOR
0.98typ (Io=100%)
INRUSH CURRENT[A] ACIN 200V
*2
20max / 60max (Primary inrush current /Secondary inrush current) (More than 10 sec. to re-start)
LEAKAGE CURRENT[mA]
0.85max (ACIN 240V 60Hz, Io=100%, According to IEC60950-1)
VOLTAGE[V]
36
48
ACIN 170V-180V
Output derating is required at ACIN 180V or less (refer to instruction manual 4.2)
CURRENT[A]
ACIN 180V-264V
55
52
LINE REGULATION[mV]
144max
192max
LOAD REGULATION[mV]
360max
480max
0 to +50C
*3
300max
360max
RIPPLE[mVp-p]
-10 to 0C
*3
360max
480max
0 to +50C
*3
360max
480max
RIPPLE NOISE[mVp-p]
OUTPUT
-10 to 0C
*3
480max
600max
0 to +50C
360max
480max
TEMPERATURE REGULATION[mV]
-10 to +50C
440max
600max
*4
144max
DRIFT[mV]
192max
START-UP TIME[s]
1.7max (ACIN 200V, Io=100%)
10typ (Io=100%)
HOLD-UP TIME[ms]
ACIN 200V
20typ (Io=50%)
*5
28.80 - 39.60
OUTPUT VOLTAGE ADJUSTMENT RANGE[V]
38.40 - 52.80
*6
OUTPUT VOLTAGE SETTING[V]
36.00 - 37.44
48.00 - 49.92
Activate over 105% - 120% of rated current and recovers automatically.
OVERCURRENT PROTECTION
(Output voltage shuts down when the output voltage continuously drops due to overcurrent protection.)
PROTECTION
*7
42.00 - 45.00
OVERVOLTAGE PROTECTION[V]
56.00 - 60.00
CIRCUIT AND
DC_OK LAMP
LED (Green)
OTHERS
ALARM LAMP
LED (Amber)
REMOTE ON/OFF
Provided
INPUT-OUTPUT AUX RC WRN PG
AC3,000V 1minute, Cutoff current = 25mA, DC500V 50MW min (At room temperature)
INPUT-FG
AC2,000V 1minute, Cutoff current = 25mA, DC500V 50MW min (At room temperature)
ISOLATION
OUTPUT AUX RC WRN PG-FG
AC500V 1minute, Cutoff current = 100mA, DC500V 50MW min (At room temperature)
OUTPUT-AUX RC WRN PG
AC100V 1minute, Cutoff current = 100mA, DC100V 50MW min (At room temperature)
OPERATING TEMP.,HUMID.AND ALTITUDE
-10 to +70C (Output derating is required), 20 - 90%RH (Non condensing), 3,000m (10,000 feet) max
STORAGE TEMP.,HUMID.AND ALTITUDE
-20 to +85C, 20 - 90%RH (Non condensing), 9,000m (30,000 feet) max
ENVIRONMENT
VIBRATION
10 - 55Hz, 19.6m/s
(2G), 3minutes period, 60minutes each along X, Y and Z axis
IMPACT
196.1m/s
(20G), 11ms, once each along X, Y and Z axis
AGENCY APPROVALS
UL60950-1, C-UL (CSA60950-1), EN60950-1
SAFETY AND
CONDUCTED NOISE
Complies with FCC Part15-A, CISPR22-A, EN55011-A, EN55022-A, VCCI-A
NOISE REGULATIONS
HARMONIC ATTENUATOR
Complies with IEC61000-3-2 Class A
*8
*9
102X41X340mm [4.02X1.61X13.39 inches] (WXHXD) / 2.3kg max
CASE SIZE/WEIGHT
OTHERS
COOLING METHOD
Forced cooling (internal fan)
*1
*2
*3
AUX output power is not included.
The current of input surge to a built-in noise filter (0.2ms or less) is excluded.
Measured by 500MHz oscilloscope.
Ripple and ripple noise is measured on measuring board with capacitor of 22mF within
150mm from the output terminal.
Drift is the change in DC output for an eight hour period after a half-hour warm-up at 25C,
with the input voltage held constant at the rated input/output.
Can't be used above the rated output current and the rated output power.
When the output voltage is adjusted to higher than 49.92V and the load factor is over 70%
of the rated current, if the load current changes quickly (< 200msec), the output voltage
drops approximately 5V below the setting voltage.
*7
MODEL
VOLTAGE[V]
CURRENT[A]
FREQUENCY[Hz]
*7
*4
*5
*6
*8
*9
Output voltage recovers from protection by shutting down the input voltage and waiting
more than 10 seconds then turning on AC input again, or turning off the output voltage by
remote control.
Please contact us about another class.
Case size contains neither the terminal blocks, connector and screw.
To meet the specifications, do not operate over-loaded condition.
A sound may occur from power supply at peak loading.
FETA-2
FETA7000T-144相似产品对比
FETA7000T-144 FETA7000T-48 FETA2500BA-36 FETA2500BA-48
描述 开关电源 7488W 144V 52A 开关电源 7113W 48V 148.2A 开关电源 1980W 36V 55A 开关电源 2496W 48V 52A
厂商名称 Cosel Cosel Cosel Cosel
产品种类 开关电源 开关电源 开关电源 开关电源
输出电压—通道1 144 VDC 48 VDC 36 VDC 48 VDC
输出端数量 1 Output 1 Output 1 Output 1 Output
输出功率 7.488 kW 7.113 W 1.98 kW 2.496 kW
开放式框架/封闭式 Enclosed Enclosed Enclosed Enclosed
输入电压 170 VAC to 264 VAC 170 VAC to 264 VAC 170 VAC to 264 VAC 170 VAC to 264 VAC
输出电流—通道1 52 A 148.2 A 55 A 52 A
工业 Commercial Commercial Commercial Commercial
绝缘电压 3 kV 3 kV 3 kV 3 kV
安装风格 Chassis Chassis Chassis Chassis
长度 475 mm 475 mm 340 mm 340 mm
宽度 388 mm 388 mm 102 mm 102 mm
高度 43 mm 43 mm 41 mm 41 mm
系列 FETA FETA FETA FETA
尺寸 475 mm x 388 mm x43 mm 475 mm x 388 mm x43 mm 340 mm x 102 mm x 41 mm 340 mm x 102 mm x 41 mm
输入频率 47 Hz to 63 Hz 47 Hz to 63 Hz 47 Hz to 63 Hz 47 Hz to 63 Hz
负载调节 Regulated Regulated Regulated Regulated
最大工作温度 + 60 C + 60 C + 70 C + 70 C
最小工作温度 - 10 C - 10 C - 10 C - 10 C
工厂包装数量 1 1 1 1
单位重量 11 kg 11 kg 2.3 kg 2.3 kg
站点相关: 大学堂 TI培训 Datasheet 电子工程 索引文件: 240  176  472  95  265  5  4  10  2  6