SmartOnline 208/240&120V 10kVA 9kW Double-
Conversion UPS, 9U, Extended Run, Network
Card Slot, USB, DB9, Bypass,Hardwire
MODEL NUMBER:
SU10KRT3U
Highlights
q
10kVA / 10,000VA / 9000W on-
line double-conversion UPS; 0.9
power factor
q
208/120V or 240/120V 50/60Hz
output; Economy mode option
q
9U Rack / Tower compatible;
Hot-swappable power and
battery modules
q
USB, RS232 & EPO ports; Slot
for Network Management Card
options
q
Front panel LEDs with detailed
LCD monitoring and control
screen
q
Expandable runtime with
optional external battery packs
Tripp Lite SU10KRT3U 10,000VA / 10kVA / 9000 watt online, double-conversion UPS system offers
complete power protection for critical network applications. This system delivers online, double-conversion
UPS protection with zero transfer time, suitable for advanced networking applications. Fault-tolerant auto-
bypass prevents unexpected service interruptions during UPS overload or internal fault conditions.
Included stepdown transformer with manual bypass switch enables hot-swappable replacement of entire
UPS power module with no interruption to connected equipment. Enhanced availability, fault tolerance
and simple hot-swap replacement options make this UPS ideal for advanced networking applications in
data centers, computer rooms, network closets and rugged industrial locations.
q
Hardwire input (3 wire);
Hardwire output
Package Includes
q
SU10000RT3UPM 3U UPS
power module
q
BP240V10RT3U external
battery pack
q
Tripp Lite SU10KRT3U 10kVA / 10,000VA / 9000 watt on-line, double-conversion UPS system in 9U
total rack/tower configuration (3U UPS power module, 3U external battery pack and 3U step-down
transformer)
q
SU10KXFMRRT3U step down
switch
q
Included stepdown transformer with manual bypass switch enables hot-swappable UPS power module
replacement with no interruption in output power to connected networking equipment
q
Four post compatible rack rail kit
(3 sets)
q
Fault tolerant electronic bypass maintains utility output during a variety of UPS fault conditions
Hardwire input and output connections
Maximum installed rack depth of only 32.5 in. / 82.6cm
Full-time active power conditioning provides clean, continuous dual-conversion AC output free of
voltage fluctuations, power interruptions and line noise
q
Tower stands for upright tower
configuration
q
q
q
USB, DB9 and EPO cables
q
q
Double-conversion operation converts raw input from AC to DC, then resynthesizes output power back
to perfect sine wave AC with enhanced protection from harmonic distortion, fast electrical impulses and
other hard-to-solve power problems not addressed by other UPS types
q
Maintains full-time sine wave output within 2% of 208/240 and 120V nominal at 50/60Hz during
1/7
brownouts as low 100V and overvoltages as high as 300V
q
Expandable runtime is supported with optional BP240V10RT3U; BP240V787C-1PH external battery
packs
q
Some external battery configurations require the use of Tripp Lite's External Battery Configuration
Software (see manual)
q
Intelligent battery management system with temperature-compensated charging extends battery life
Highly efficient operation in optional economy mode significantly reduces BTU heat output and
operating energy costs
q
q
Battery independent restart ensures automatic UPS power-up without user interaction after lengthy
power outages, even when batteries are expired and require replacement
q
USB & Serial ports enable data-saving unattended shutdown when used with Tripp Lite's PowerAlert
software, available via FREE download from www.tripplite.com/poweralert
q
HID-compliant USB interface enables integration with built-in power management and auto shutdown
features of Windows and Mac OS X
q
Slot for network management card options
Compatible with Tripp Lite UPS management card options TLNETCARD, WEBCARDLX,
SNMPWEBCARD, MODBUSCARD and RELAYIOCARD
q
q
Optional RELAYIOMINI interface module offers three configurable hard contact closure outputs for
custom event notification (requires removal of USB interface module)
q
Supports Emergency Power Off (EPO) via built-in interface
Included rail kit supports 9U 19 inch rackmount installation in 4 post racks
Optional 2POSTRMKITHD supports installation in 2 post 19 inch racks
Front panel LEDs and LCD readout with scroll controls and password option supports visual monitoring
of all major UPS functions and advanced UPS settings for charge level, nominal voltage selection,
frequency conversion and other operational parameters
q
q
q
q
LED / LCD display panel rotates for viewing in rackmount or tower configurations
Network-grade AC surge and noise suppression
Industrial mode option (factory preset) enables supports high current startup loads by momentarily
switching to bypass mode in response to short duration overload conditions
q
q
q
Frequency conversion mode enables conversion of 60Hz to 50Hz or 50Hz to 60Hz (no de-rating)
External battery packs are field replaceable and hot swappable
q
OVERVIEW
UPC Code
037332121509
OUTPUT
2/7
Output Volt Amp Capacity (VA)
Output kVA Capacity (kVA)
Output Watt Capacity (Watts)
Output kW Capacity (kW)
Output Capacity Details
10000
9.0
Supports up to 105% load continuously in double conversion mode, 106 to 125% for 1 minute, 126% to 150% for 30
seconds; Loads over 150% trigger immediate bypass mode operation to support loads directly from mains power;
Double conversion mode is automatically restored as load levels are reduced to 95% or less
0.9
3:1
120V; 208V; 240V
Voltage selection via front panel LCD interface
50 / 60 Hz; Supports 50 to 60 Hz and 60 to 50 Hz conversion
Output frequency matches input nominal on startup; Frequency conversion mode enables conversion of 60Hz to
50Hz or 50Hz to 60Hz (no de-rating); Output frequency regulation +/- 0.05Hz (free running)
+/- 2%
+/- 10%
+/- 2%
Hardwire
Pure Sine wave
Pure Sine wave
No
Power Factor
Crest Factor
Nominal Output Voltage(s)
Supported
Nominal Voltage Details
Frequency Compatibility
Frequency Compatibility Details
Output Voltage Regulation (Line
Mode)
(Economy Line Mode)
Output Voltage Regulation (Battery
Mode)
Output Receptacles
Output AC Waveform (AC Mode)
Output AC Waveform (Battery
Mode)
Individually Controllable Load Banks
INPUT
Rated input current (Maximum Load)
Nominal Input Voltage(s) Supported
UPS Input Connection Type
UPS Input Connection Description
Recommended Electrical Service
Input Phase
54A (208V), 46.8A (240V)
208V AC; 240V AC
Hardwire
3 wire single phase input (L1, L2, G)
60A
Single-Phase
BATTERY
Full Load Runtime (min.)
Half Load Runtime (min.)
Expandable Battery Runtime
External Battery Pack Compatibility
4.3 min. (9000w)
12.5 min. (4500w)
Supports extended runtime with optional external battery packs
BP240V10RT3U; <a class="productLink" href="//www.tripplite.com/External-240V-Tower-Battery-Pack-for-
use-with-Select-Tripp-Lite-UPS-Systems-BP240V787C-1PH~BP240V787C-1PH">BP240V787C-1PH</a>
3/7
DC System Voltage (VDC)
Battery Recharge Rate (Included
Batteries)
Battery Replacement Description
Expandable Runtime
240
Less than 6 hours from 10% to 90% (typical, full load discharge)
Hot-swappable, user replaceable external battery packs
Yes
VOLTAGE REGULATION
Voltage Regulation Description
Overvoltage Correction
Undervoltage Correction
2% output voltage regulation in standard online, double-conversion mode
Corrects overvoltages up to 300V
Corrects undervoltages as low as 100V
USER INTERFACE, ALERTS & CONTROLS
Front Panel LCD Display
Selectable LCD display with scroll and selection buttons enables UPS control and detailed monitoring options;
LED/LCD panel rotates for viewing in rack/tower formats; LCD Display supports ENGLISH, FRENCH, GERMAN,
ITALIAN, SPANISH and PORTUGUESE (see manual)
2 Switches control off/on power status and alarm-cancel/self-test operation; 2 additional switches support set and
execute scrolling LCD functions; Bundled transformer module includes bypass switch to enable hot-swap UPS
power module replacement
Alarm cancel switch
Unique audible alarms for all major UPS, environmental and power conditions (see manual)
6 LEDs indicate line power, online mode, economy/bypass mode, on-battery, charger and AC output status; LCD
screen offers additional information and control options
Switches
Alarm Cancel Operation
Audible Alarm
LED Indicators
SURGE / NOISE SUPPRESSION
UPS AC Suppression Joule Rating
UPS AC Suppression Response
Time
EMI / RFI AC Noise Suppression
2565
Instantaneous
Yes
PHYSICAL
Included Mounting Accessory
Installation Form Factors Supported
with Optional Accessories
Optional Mounting Accessory Notes
3 sets of adjustable 4 post rack rails included; 2-9USTAND tower kit included
2 post rackmount (2POSTRMKITHD)
3 sets of <a class="productLink" href="//www.tripplite.com/2-Post-Rack-Mount-Installation-Kit-3U-Larger-UPS-
Transformer-Battery-Pack-Components~2POSTRMKITHD">2POSTRMKITHD</a> required for 2 post
rackmount installation of each included component
Rackmount
5.14 x 17.5 x 25.82
13.06 x 44.45 x 65.58
Primary Form Factor
UPS Power Module Dimensions
(hwd, in.)
(hwd, cm)
Rack Height (U Spaces)
Maximum Device Depth (in.)
4/7
Minimum Required Rack Depth
(inches)
Maximum Device Depth (cm)
Minimum Required Rack Depth (cm)
UPS Power Module Weight (lbs.)
UPS Power Module Weight (kg)
UPS Dimensions Details
Stepdown Transformer Dimensions
(hwd / in.)
(hwd / cm)
Stepdown Transformer Weight (lbs.)
Stepdown Transformer Weight (kg)
Included Battery Pack Dimensions
(hwd / in.)
Included Battery Pack Weight (lbs.)
Included Battery Pack Weight (kg)
Shipping Dimensions (hwd / in.)
Shipping Dimensions (hwd / cm)
Shipping Weight (lbs.)
Shipping Weight (kg)
Cooling Method
UPS Housing Material
Maximum Device Depth (mm)
Stepdown Transformer Height (mm)
Stepdown Transformer Width (mm)
Stepdown Transformer Depth (mm)
Primary UPS Height (mm)
Primary UPS Width (mm)
Primary UPS Depth (mm)
33
82.55
83.82
43
19.50
Includes 3U UPS/power module, 3U transformer module with bypass switch and 3U battery pack; MAXIMUM
DEVICE DEPTH specification refers to the whole UPS installed depth with hardwire PDU installed
5.25 x 17.5 x 26
13.34 x 44.45 x 66.04
102
46.27
5.25 x 17.5 x 25
158.7
71.99
40.00 x 25.50 x 41.00
101.60 x 64.77 x 104.14
469.00
212.73
Fan
Steel
826
133
445
660
131
445
656
ENVIRONMENTAL
Storage Temperature Range
Relative Humidity
AC Mode BTU / Hr. (Full Load)
AC Economy Mode BTU / Hr. (Full
Load)
+32 to +104 degrees Fahrenheit / 0 to +40 degrees Celsius
+5 to +122 degrees Fahrenheit / -15 to +50 degrees Celsius
0 to 95%, non-condensing
3415
1280
5/7