SEC/S/ Stella TAO
SEC/S/Stella TAO
Approved
Ericsson Internal
PRODUCT SPECIFICATION
TABLE OF CONTENTS
No.
1 (1)
(3)
Prepared (also subject responsible if other)
1/1301-BMR6401401+ Uen
Specification
00152-EN/LZT146 302
Technical
Checked
Date
PKR
4000
TAO
SEC/S/ Stella
series
SEC/S/Stella TAO
Key Features
DC/DC converters,
Input
36-75
V, Output
up to 1.5
A/7 W
Industry standard MacroDens
TM
footprint
47.8 x 28.1 x max height 8.0 mm (1.88 x 1.11 x max
height 0.32 in.)
High efficiency, typ. 83 % at 5.0 Vout full load
1500 Vdc input to output isolation
Meets isolation requirements equivalent to basic
insulation according to IEC/EN/UL 60950
More than 7.2 million hours predicted MTBF at 40
o
ambient temperature
(MICJOHN)
2007-09-17
2007-8-23
EN/LZT 146
302
R6F
November
2007
R6G
November
2008
Rev
Reference
© Ericsson Power Modules AB
General Characteristics
Over current protection
Soft start
Remote control
Output voltage adjust function
Input voltage adjust function
Highly automated manufacturing to ensure highest
quality
ISO 9001/14001 certified supplier
Safety Approvals
Design for Environment
Meets requirements in high-
temperature lead-free soldering
processes.
Contents
General Information
Safety Specification
Absolute Maximum Ratings
Product Program
2.1V, 1.5A / 3.2W Electrical Specification PKR 4310 SI
3.3V, 1.5A / 5W Electrical Specification PKR 4510 SI
5.0V, 1.2A / 6W Electrical Specification PKR 4611 SI
12V, 0.6A / 7W Electrical Specification PKR 4713 SI
+12V, 0.25A / -12V, 0.25A / 6W Electrical Specification PKR 4621 SI
+5.0V, 0.6A / -5.0V, 0.6A / 6W Electrical Specification PKR 4622 SI
+5.0V, 0.6A / +3.3V, 0.9A / 6W Electrical Specification PKR 4628 SI
EMC Specification
Operating Information
Thermal Consideration
Connections
Mechanical Information
Soldering Information
Delivery Information
Product Qualification Specification
............................................................. 2
............................................................. 3
............................................................. 4
Ordering No.
............................................................. 5
............................................................. 7
........................................................... 11
........................................................... 14
........................................................... 17
........................................................... 20
........................................................... 23
........................................................... 26
........................................................... 27
........................................................... 28
........................................................... 29
........................................................... 30
........................................................... 33
........................................................... 35
........................................................... 36
SEC/S/ Stella TAO
Approved
Ericsson Internal
No.
2 (3)
Specification
Technical
Checked
Date
PKR
4000
TAO
SEC/S/ Stella
series
DC/DC converters,
Input
36-75
V, Output
up to 1.5
A/7 W
General Information
Ordering Information
See Contents for individual product ordering numbers.
Option
SMD, lead-free surface finish
SMD, leaded surface finish
Through hole pin
Suffix
SPB
Ordering No.
PKR 4310 SI
PKR 4310 SPBI
PKR 4310 PI
(MICJOHN)
2007-09-17
EN/LZT 146
302
R6F
November
2007
R6G
November
2008
Rev
Reference
Compatibility with RoHS requirements
The products are compatible with the relevant clauses and
requirements of the RoHS directive 2002/95/EC and have a
maximum concentration value of 0.1% by weight in
homogeneous materials for lead, mercury, hexavalent
chromium, PBB and PBDE and of 0.01% by weight in
homogeneous materials for cadmium.
Exemptions in the RoHS directive utilized in Ericsson
Power Modules products include:
Lead in high melting temperature type solder (used to
solder the die in semiconductor packages)
Lead in glass of electronics components and in
electronic ceramic parts (e.g. fill material in chip
resistors)
Lead as an alloying element in copper alloy containing
up to 4% lead by weight (used in connection pins
made of Brass)
The exemption for lead in solder for servers, storage and
storage array systems, network infrastructure equipment
for switching, signaling, transmission as well as network
management for telecommunication is only utilized in
surface mount products intended for end-users’ leaded
SnPb Eutectic soldering processes. (See ordering
information table).
Quality Statement
The products are designed and manufactured in an
industrial environment where quality systems and methods
like ISO 9000, 6σ (sigma), and SPC are intensively in use to
boost the continuous improvements strategy. Infant
mortality or early failures in the products are screened out
and they are subjected to an ATE-based final test.
Conservative design rules, design reviews and product
qualifications, plus the high competence of an engaged
work force, contribute to the high quality of our products.
Warranty
Warranty period and conditions are defined in Ericsson
Power Modules General Terms and Conditions of Sale.
Limitation of Liability
Ericsson Power Modules does not make any other
warranties, expressed or implied including any warranty of
merchantability or fitness for a particular purpose
(including, but not limited to, use in life support
applications, where malfunctions of product can cause
injury to a person’s health or life).
Reliability
The Mean Time Between Failure (MTBF) is calculated at full
output power and an operating ambient temperature (T
) of
+40°C, which is a typical condition in Information and
Communication Technology (ICT) equipment. Different
methods could be used to calculate the predicted MTBF
and failure rate which may give different results. Ericsson
Power Modules currently uses one method, Telcordia
SR332.
Predicted MTBF for the series is:
7.2 million hours according to Telcordia SR332, issue
1, Black box technique.
Telcordia SR332 is a commonly used standard method
intended for reliability calculations in ICT equipment. The
parts count procedure used in this method was originally
modelled on the methods from MIL-HDBK-217F, Reliability
Predictions of Electronic Equipment. It assumes that no
reliability data is available on the actual units and devices
for which the predictions are to be made, i.e. all predictions
are based on generic reliability parameters.
SEC/S/ Stella TAO
Approved
Ericsson Internal
No.
3 (3)
Specification
Technical
Checked
Date
PKR
4000
TAO
SEC/S/ Stella
series
DC/DC converters,
Input
36-75
V, Output
up to 1.5
A/7 W
General information
Ericsson Power Modules DC/DC converters and DC/DC
regulators are designed in accordance with safety
standards IEC/EN/UL60950,
Safety of Information
Technology Equipment.
IEC/EN/UL60950 contains requirements to prevent injury
or damage due to the following hazards:
Electrical shock
Energy hazards
Fire
Mechanical and heat hazards
Radiation hazards
Chemical hazards
(MICJOHN)
2007-09-17
EN/LZT 146
302
R6F
November
2007
R6G
November
2008
Rev
Reference
Isolated DC/DC converters
It is recommended that a slow blow fuse with a rating
twice the maximum input current per selected product be
used at the input of each DC/DC converter. If an input filter
is used in the circuit the fuse should be placed in front of
the input filter.
In the rare event of a component problem in the input filter
or in the DC/DC converter that imposes a short circuit on
the input source, this fuse will provide the following
functions:
Isolate the faulty DC/DC converter from the input
power source so as not to affect the operation of
other parts of the system.
Protect the distribution wiring from excessive
current and power loss thus preventing
hazardous overheating.
On-board DC-DC converters are defined as component
power supplies. As components they cannot fully comply
with the provisions of any Safety requirements without
“Conditions of Acceptability”. It is the responsibility of the
installer to ensure that the final product housing these
components complies with the requirements of all
applicable Safety standards and Directives for the final
product.
Component power supplies for general use should comply
with the requirements in IEC60950, EN60950 and
UL60950
“Safety of information technology equipment”.
There are other more product related standards, e.g.
IEEE802.3af “Ethernet LAN/MAN Data terminal equipment
power”, and ETS300132-2 “Power supply interface at the
input to telecommunications equipment; part 2: DC”, but
all of these standards are based on IEC/EN/UL60950 with
regards to safety.
regulators are UL60950 recognized and certified in
accordance with EN60950.
The flammability rating for all construction parts of the
products meets requirements for V-0 class material
according to IEC 60695-11-10.
The products should be installed in the end-use
equipment, in accordance with the requirements of the
ultimate application. Normally the output of the DC/DC
converter is considered as SELV (Safety Extra Low
Voltage) and the input source must be isolated by
minimum Double or Reinforced Insulation from the primary
circuit (AC mains) in accordance with IEC/EN/UL60950.
The galvanic isolation is verified in an electric strength test.
The test voltage (V
iso
) between input and output is
1500 Vdc or 2250 Vdc for 60 seconds (refer to product
specification).
Leakage current is less than 1
μA
at nominal input voltage.
24 V DC systems
The input voltage to the DC/DC converter is SELV (Safety
Extra Low Voltage) and the output remains SELV under
normal and abnormal operating conditions.
48 and 60 V DC systems
If the input voltage to Ericsson Power Modules DC/DC
converter is 75 Vdc or less, then the output remains SELV
(Safety Extra Low Voltage) under normal and abnormal
Single fault testing in the input power supply circuit should
be performed with the DC/DC converter connected to
demonstrate that the input voltage does not exceed
75 Vdc.
If the input power source circuit is a DC power system, the
source may be treated as a TNV2 circuit and testing has
demonstrated compliance with SELV limits and isolation
requirements equivalent to Basic Insulation in accordance
Non-isolated DC/DC regulators
The input voltage to the DC/DC regulator is SELV (Safety
ESKEVIN
Approved
Limited Internal
No.
Checked
Date
1 (23)
2/1301-BMR 640
Technical Specification
1401+ Uen
EN/LZT 146
302
R6E
November
2007
R6G
November
2007
R6F
September
2008
Rev
Reference
PKR
4000
series
SEC/D (Julia You)
DC/DC converters,
Input
36-75
V, Output
up to 1.5
A/7 W
EZYPING
2007-8-27
Characteristics
ref
iso
tr
RC
adj
Operating Temperature (see Thermal Consideration section)
Storage temperature
Input voltage
Isolation voltage (input to output test voltage)
Input voltage transient (Tp 100 ms)
Remote Control pin voltage
(see Operating Information section)
Adjust pin voltage (see Operating Information section)
Positive logic option
-5
-5
min
-45
-55
-0.5
typ
max
+110
+125
+75
1500
90
+40
+40
Vdc
Stress in excess of Absolute Maximum Ratings may cause permanent damage. Absolute Maximum Ratings, sometimes referred to as no destruction limits, are
normally tested with one parameter at a time exceeding the limits of Output data or Electrical Characteristics. If exposed to stress above these limits, function and
performance may degrade in an unspecified manner.
Fundamental Circuit Diagram
Single output
Vadj
NOR
Out1
+In
Rtn
TOA
RC
-In
Double output (positive output 2)
Vadj
Out1
NOR
+In
Rtn
Out2
TOA
RC
-In
Double output (negative output 2)
Vadj
Out1
NOR
Rtn
+In
Out2
TOA
RC
-In
ESKEVIN
Approved
Limited Internal
No.
Checked
Date
2 (23)
2/1301-BMR 640
1401+ Uen
EN/LZT 146
302
R6E
November
2007
R6G
November
2007
R6F
September
2008
Rev
Reference
PKR
4000
series
SEC/D (Julia You)
DC/DC converters,
Input
36-75
V, Output
up to 1.5
A/7 W
EZYPING
2007-8-27
ref
= -30 to +85ºC, V
= 38 to 72 V, pin 8 connected to pin 9 unless otherwise specified under Conditions.
Typical values given at: T
ref
= +25°C, V
= 53 V, max I
O
, unless otherwise specified under Conditions.
Characteristics
Conditions
min
typ
max
Ioff
Ion
O
SVR
Input voltage range
Turn-off input voltage
Turn-on input voltage
Internal input capacitance
Output power
Supply voltage rejection (ac)
Output voltage initial setting
f = 100 Hz sinewave, 1 Vp-p
50 % of max I
O
η
Efficiency
max I
O
50 % of max I
O
, V
= 48 V
max I
O
, V
= 48 V
d
li
RC
f
s
Power Dissipation
Input idling power
Input standby power
Switching frequency
max I
O
O
= 0, V
= 53 V
= 53 V (turned off with RC)
50-100% of max I
O
412
75
75
75
485
558
1.4
Decreasing input voltage
Increasing input voltage
38
33.4
34.8
72
36
38
PKR 4310 SI
μ
dB
mW
mW
kHz
Oi
Output voltage initial setting and
accuracy
ref
= +25°C, V
= 53 V, I
O
= 1.15A
Output adjust range
Output voltage tolerance band
10-100% of max I
O
O
= 0
max I
O
= 53 V, 10-100% of max I
O
= 53 V, Load step 25-75-25 % of
max I
O
, di/dt = 1 A/
μ
s,
see Note 1
Idling voltage
Line regulation
Load regulation
Load transient
voltage deviation
Load transient recovery time
Ramp-up time
(from 10−90 % of V
Oi
2.07
1.76
2.01
2.12
2.17
2.38
2.28
mV
mV
mV
us
O
2.5
-225
+90
0.7
2.8
3.0
28
185
tr
tr
r
s
O
lim
sc
Oac
0.9
ms
ms
mVp-p
Start-up time
(from V
connection to 90% of V
Oi
10-100% of max I
O
1.3
Vo = 1.9 V, T
ref
< max T
ref
ref
= 25ºC,
See ripple & noise section,
max I
O
, V
O
2.0
2.6
2.7
Output current
Current limit threshold
Short circuit current
Output ripple & noise
3.1
3.1
Note 1: Output filter according to Ripple & Noise section