BCM
Bus Converter
MBCM270x338M235A00
(Previous Part – VMB0004MFJ)
US
NRTL
US
Isolated Fixed Ratio DC-DC Converter
Features & Benefits
270V
DC
–33.75V
DC
235W Bus Converter
MIL-STD-704E/F Compliant
High efficiency (>95.0%) reduces
system power consumption
High power density (>796W/in
reduces power system footprint by >40%
Contains built-in protection features against:
n
Undervoltage
n
Overvoltage lockout
n
Overcurrent protection
n
Short Circuit protection
n
Overtemperature protection
Provides enable/disable control,
internal temperature monitoring
Can be paralleled to create multi-kW arrays
Product Ratings
IN
= 270V (240 – 330V)
OUT
= 33.75V (30 – 41.25V)
no load
OUT
= up to 235W
K = 1/8
The MIL-COTS VI Chip
bus converter is a high efficiency (>95.0%)
Sine Amplitude Converter™ (SAC™) operating from a 240 to 330V
primary bus to deliver an isolated 30 – 41.25V secondary voltage.
The MBCM270F338M235A00 is provided in a VI Chip package
compatible with standard pick-and-place and surface mount
assembly processes.
Part Numbering
Product Number
MBCM270x450M270A00
Package Style (x)
= J-Lead
= Through hole
Product Grade
= -55° to 125°C
Typical Applications
High Voltage 270V Aircraft Distributed Power
28V
DC
MIL-COTS PRM™ Interface (MP028F036M21AL)
High Density Power Supplies
Communications Systems
For Storage and Operating Temperatures see General Characteristics.
Typical Application
PR
enable / disable
switch
SW1
F1
IN
C1
1 µF
-IN
-OUT
-IN
+IN
PC
TM
PC
TM
IL
VC
SG
OS
CD
VC
PC
TM
BCM
+OUT
PRM
+OUT
+IN
VTM
+OUT
+IN
-OUT
-IN
-OUT
BCM
Bus Converter
Page 1 of 23
Rev 1.8
08/2016
vicorpower.com
800 927.9474
MBCM270x338M235A00
Pin Configuration
+OUT
+IN
-OUT
TM
RSV
PC
+OUT
-OUT
-IN
Bottom View
Pin Descriptions
Pin Number
A1-E1, A2-E2
L1-T1, L2-T2
H1, H2
J1, J2
K1, K2
A3-D3, A4-D4,
J3-M3, J4-M4
E3-H3, E4-H4,
N3-T3, N4-T4
Signal Name
+IN
–IN
TM
RSV
PC
+OUT
–OUT
INPUT POWER
INPUT POWER
RETURN
OUTPUT
NC
OUTPUT/INPUT
OUTPUT POWER
OUTPUT POWER
RETURN
Positive input power terminal
Negative input power terminal
Temperature monitor, input side referenced signal
No connect
Enable and disable control, input side referenced signal
Positive output power terminal
Negative output power terminal
Function
Control Pin Specifications
See Using the Control Signals PC, TM for more information.
PC (BCM Primary Control)
The PC pin can enable and disable the BCM module. When held
below V
PC_DIS
the BCM shall be disabled. When allowed to
float with an impedance to –IN of greater than 50kΩ the
module will start. When connected to another BCM PC pin
the BCM modules will start simultaneously when enabled. The PC
pin is capable of being driven high either by an external logic signal
or internal pull up to 5V (operating).
TM (BCM Temperature Monitor)
The TM pin monitors the internal temperature of the BCM module
within an accuracy of ±5°C. It has a room temperature setpoint of
~3.0V and an approximate gain of 10mV/°C. It can source up to
100µA and may also be used as a “Power Good” flag to verify that
the BCM module is operating.
BCM
Bus Converter
Page 2 of 23
Rev 1.8
08/2016
vicorpower.com
800 927.9474
MBCM270x338M235A00
Absolute Maximum Voltage Ratings
The absolute maximum ratings below are stress ratings only. Operation at or beyond these maximum ratings can cause permanent damage to the device.
+IN to –IN
PC to –IN
TM to –IN
+IN/–IN to +OUT/–OUT
+OUT to –OUT
Temperature during reflow
MSL 4 (Datecode 1528 and later)
Isolation voltage (hipot)
Working voltage (IN - OUT)
-1.0
Comments
Min
-1.0
-0.3
-0.3
DC
DC
DC
DC
BCM
Bus Converter
Page 3 of 23
Rev 1.8
08/2016
vicorpower.com
800 927.9474
MBCM270x338M235A00
Electrical Specifications
Specifications apply over all line and load conditions, unless otherwise noted;
boldface
specifications apply over the temperature range of
-55°C
125°C (M-Grade); all other specifications are at T
= 25ºC unless otherwise noted.
Attribute
Conditions / Notes
Min
Typ
Powertrain
Voltage range
dV/dt
Quiescent power
No load power dissipation
Inrush Current Peak
DC Input Current
K Factor
IN
dV
IN
/dt
NL
INR_P
IN_DC
IN
= 270V
DC
IN
= 240 – 330V
DC
IN
= 270 V
DC
, Average P
OUT
< = 235W, Tpeak < 5ms
No Load
OUT
< = 235W
IN
= 270V, P
OUT
= 235W
IN
= 240V to 330V, P
OUT
= 235W
IN
= 270V, T
= 100°C, P
OUT
= 235W
60W < P
OUT
< 235W Max
= 25°C
= 125°C
= -55°C
94.1
94
93.7
90
180
105
170
210
160
3.12
OUT
= 0µF, P
OUT
= 235W, V
IN
= 270V
IN
= 270V, C
PC
= 0
460
1.64
3.28
160
540
1.72
3.44
95.4
95.2
94.7
PC connected to -IN
IN
= 240 to 330V
IN
= 330V C
OUT
= 100µF, P
OUT
= 235W
OUT
= 235W
1/8
235
215
352.5
41.25
7.3
395
240
270
330
DC
V/µs
mW
OUT
IN
Output Power (Average)
Output Power (Peak)
Output Voltage
Output Current (Average)
Efficiency (Ambient)
Efficiency (Hot)
Minimum Efficiency
(Over Load Range)
Output Resistance (Ambient)
Output Resistance (Hot)
Output Resistance (Cold)
Load Capacitance
Switching Frequency
Ripple Frequency
Output Voltage Ripple
IN
to V
OUT
(Application of V
IN
OUT
OUT_P
OUT
OUT
h
h
h
OUT
OUT
OUT
OUT
SW
SW_RP
OUT_PP
ON1
mΩ
mΩ
mΩ
µF
MHz
MHz
mV
ms
BCM
Bus Converter
Page 4 of 23
Rev 1.8
08/2016
vicorpower.com
800 927.9474
MBCM270x338M235A00
boldface
-55°C
Attribute
Conditions / Notes
Min
Typ
Protection
Input overvoltage recovery threshold
Input overvoltage lockout threshold
Input undervoltage lockout
threshold
Input undervoltage recovery threshold
Output overcurrent trip
Short circuit protection trip threshold
Short circuit protection response time
constant
Thermal shutdown threshold
IN_OVLO-
IN_OVLO+
IN_UVLO-
IN_UVLO+
OCP
SCP
SCP
J_OTP
IN
= 270V, 25°C
350
355
90
125
1.2
135
365
372
115
125
385
125
135
µs
Output Power (W)
250
31.00
33.00
Steady State
35.00
37.00
5ms 352.5W Ave
39.00
41.00
Figure 1
— Safe operating area
BCM
Bus Converter
Page 5 of 23
Rev 1.8
08/2016
vicorpower.com
800 927.9474