WALL MOUNT
SELECT-A-STROBE/HORN
• UL and cUL listed
• 12 VDC with 15, 35 or 60 cd setting
• 24 VDC with 15, 35, 60, 75, 95 or 110 cd settings
• 6 distinct candela settings
• Candela selection view window
• 15/75 ADA compliant on 60cd setting
• 33 sound output settings
• Horn or chime sound output
• Pre-wire back plate
• Universal back plate mounting (single gang, double gang,
octagon, or 4” square)
• Single screw mounting
• Indoor only
• Low current draw
The SH-1224 Strobe/Horn Series provides a wide range of candela
light output options in a single device. The candela settings include a
12 or 24 volt DC operation for the 15, 35 and 60 (75 on axis) candela
settings and 24 volt DC operation for the 15, 35, 60, 75, 95 and 110
candela settings. The candela setting is displayed through the front
window and is selectable using a drum wheel.
The horn settings include Temporal, Non-Temporal, March Time
and a Chime sound. The horn also has Low, Mid and High volume
settings for each pattern and tone. The tones include 2400 Hz, Electro-
Mechanical, Broadband and Chime.
Installation
The voltage input can be either regulated DC or full wave rectified
(FWR) 12 volt or 24 volt operation with an operating range from 8 to
33 V DC. The strobes can be synchronized using a control panel with
the Potter (Amseco) sync protocol or a SMD10-3A sync module.
The SH-1224 utilizes a universal mounting plate that will mount on a
single gang, double gang, octagon and 4” square electrical boxes. The
back plate allows the installer to mount the plate and connect the wire
connections. The strobe attaches in a hinge fashion from the top and is
secured by a single mounting screw. The strobe completely covers the
mounting back plate, therefore it can be mounted before other trades
work is completed and not affect the final look.
SH-1224 SERIES
A jumper plug is provided to test for correct
wiring in the supervisory mode only. Do not
pass alarm current through the jumper.
Installation must comply in accordance with applicable standards.
Ordering Information
Stock Number
4560070
4560071
Model Number
SH-1224R
SH-1224W
Selectable strobe/horn/chime
Color
Red
White
Potter Electric Signal Co., LLC • St. Louis, MO • Cust Service: 866-240-1870 • Tech Support:866-956-1211• Canada 888-882-1833 • www.pottersignal.com
PRINTED IN USA
MKT. #8910004 - REV F
7/10
PAGE 1 OF 4
WALL MOUNT
Dimensions: inches (mm)
Light output in precentage when measured from the following
directions per UL 1971.
SH-1224 SERIES
6 5/64 (154.4)
5 (127)
2 5/16 (59)
High voltage may be present inside the light assembly even
though power is not connected. If access to teh coponent board
is required (removal or replacement), the capacitor must be
discarged by touching a wire to both ends of the flashtube.
DO NOT attempt to touch or move the assembly until the
capacitor has been discharged.
Strobe Current
Light
Output
15cd
35cd
60/75cd
75cd
95cd
110cd
UL Designation
Operating Voltage Range
Flash Rate
Sync Module (SMD10-3A)
Range
NA
8 - 17.5V
60 times/min.
Available
Max. RMS Operating Current (mA RMS)
Reg. 12 VDC
116
209
254
NA
NA
NA
Reg. 12 FWR
152
267
258
NA
NA
NA
Reg. 24 VDC
62
102
131
146
177
196
12/24V
Regulated 12 DC/FWR
Regulated 24 DC/FWR
16 - 33V
Reg. 24 FWR
99
152
190
208
243
268
Horn Dipswitch
Pattern
1 ON - Non-temporal
1 OFF - Temporal
Both 2 = OFF
1 and 2 ON = March Time
ON
Tone
3 and 4 ON = 2400Hz
3 ON and 4 OFF = Electromechanical
3 and 4 OFF = Chime
3 OFF and 4 ON = Broadband
Volume
5 and 6 ON = High
5 ON and 6 OFF = Mid
5 and 6 OFF = Low
7 and 8 ON = Horn/strobe on 2 wires
7 and 8 OFF = Horn and strobe on 4 wires
Indoor model: 32°F to 120°F (0°C to 49°C)
To determine total current draw, add desired strobe setting and horn
selection. Refer to the installation instructions for further information.
PRINTED IN USA
7/10
PAGE 2 OF 4
WALL MOUNT
Non-Temporal Horn Current
Pattern
Volume
Max. RMS Current
(mA RMS Current)
Reg 12 VDC
2400 Hz
High
Mid
Low
High
Electro-Mechanical
Mid
Low
High
Broadband
Mid
Low
High
Chime
Mid
Low
119
44
43
27
146
41
28
27
Reg 24 VDC
87
28
26
26
dBA Reverberant Ratings per
UL464 (dBA @ 10 ft.)
Reg 12 VDC
87
82
79
86
82
79
86
81
77
58
Reg 24 VDC
87
82
84
82
79
57
dBA Anechoic Ratings per
CAN/ULC S525 (dBA @ 10 ft.)
Reg 12 VDC
99
94
92
93
101
96
94
86
79
75
Reg 24 VDC
92
93
102
98
95
86
SH-1224 SERIES
Pattern
Volume
Max. RMS Current
(mA RMS Current)
Reg 12 VDC
2400 Hz
High
Mid
Low
High
Electro-Mechanical
Mid
Low
High
Broadband
Mid
Low
High
Chime
Mid
Low
124
46
42
28
151
45
Reg 24 VDC
87
Reg 12 VDC
82
77
74
83
78
75
82
77
75
68
61
55
Reg 24 VDC
82
79
75
82
82
78
76
55
Reg 12 VDC
92
93
101
97
94
86
79
75
Reg 24 VDC
92
101
96
93
102
98
95
86
79
76
March Time Horn Current
Pattern
Volume
Max. RMS Current
(mA RMS Current)
Reg 12 VDC
2400 Hz
High
Mid
Low
High
Electro-Mechanical
Mid
Low
High
Broadband
Mid
Low
121
47
36
114
42
42
29
Reg 24 VDC
92
31
19
86
27
19
77
28
Reg 12 VDC
83
79
76
83
83
79
76
Reg 24 VDC
84
81
77
83
81
77
84
Reg 12 VDC
99
95
92
92
101
97
94
Reg 24 VDC
92
93
102
98
95
PRINTED IN USA
7/10
PAGE 3 OF 4
WALL MOUNT
Wiring Diagram
SH-1224 SERIES
SH-24
SH-24
DWG# 8910004-1
Engineering Specifications
The installer shall provide and install the Potter SH-1224 selectable
strobe/horn. The strobe shall have six (6) candela settings. The
candela settings shall be selectable using a drum roller and shall
display the candela setting on the front of the device. The horn shall
have 33 selectable settings configurable by dip switches. The sounder
shall be capable of ANSI Temporal Code 3, March Time and produce
a chime output. The horn shall have three distinct volume levels.
The strobe/horn shall operate at 12 or 24 VDC regulated or full wave
rectified. The strobe/horn shall have an operating range between 8 and
33 VDC. the strobes an by synchronized using a control panel with
the Potter sync protocol or the SMD10-3A sync module. The strobe
shall utilize a mounting plate that allows the installer to pre-wire the
mounting plate. The mounting plate shall be universal and mount on a
single gang, double gang, octagon or 4 inch square box. The mounting
plate shall be completely covered by the strobe and shall be secured
by a single screw. The strobe shall be UL listed to standard 1638,
General Signaling, and standard 1971, Signaling Devices for the
Hearing Impaired. In addition, the strobes shall be cUL listed to CAN-
ULC S526. The horn shall be UL listed to standard 464, Audible
Signaling Devices.
PRINTED IN USA
7/10
PAGE 4 OF 4