RSI-95
The Gamewell-FCI 600 Series analog addressable Fire
Alarm Control Panel (FACP) will provide all of the required
functions to control the releasing of bulk fire suppressant
materials. The Gamewell-FCI 600 Series analog address-
able FACPs are currently listed for NFPA 13 Sprinkler,
NFPA 15 Water Spray, NFPA 11 Low-Expansion Foam,
NFPA 16 Water Foam, NFPA 17 Dry Chemical, and NFPA
2001 Clean Agent types of suppressant. The Gamewell-
FCI Releasing Solenoid Interface (RSI-95) is an intelligent
addressable interface for the remote control and supervi-
sion of activation solenoids used in releasing applications.
The Releasing Solenoid Interface (RSI-95) is an address-
able Releasing Service Module, providing intelligent analog
addressable control functionality complete with full sole-
noid supervision and transient voltage suppression. Only
the RSI-95 can be used to actuate the releasing solenoid.
The RSI-95 is automatically bypassed during a Smart-
Start™ or circuit initialization to prevent accidental dis-
charge during the generic configuration, should inputs be
inadvertently activated.
The analog addressable RSI-95 solenoid control module is
designed for use with any 600 Series FACP. To avoid
unplanned fire suppressant release, the RSI-95 assembly
is the ONLY assembly to be used to provide remote releas-
ing solenoid control. The circuit can control up to two amps
of DC power to the solenoid. The RSI-95 is powered and
controlled via the analog addressable signaling line circuit
and the solenoid power is obtained from the control panel
or a UL-Listed fire protection 24 VDC power supply. The
RSI-95 fully supervises the releasing solenoid.
RSI-95
Compatible with the Gamewell-FCI 600 Series analog
addressable fire alarm control panels.
Provides full solenoid supervision.
Transient voltage suppression.
Mounts in its own unique base.
Automatic bypass at system start-up.
2.0 A of DC power for solenoid.
Types of Suppressants:
– NFPA 13 Sprinkler.
– NFPA 15 Water Spray.
– NFPA 11 Low Expansion.
– NFPA 16 Water Foam.
– NFPA 17 Dry Chemical.
– NFPA 2001 Clean Agent.
NOTE: Releasing systems must be designed by
properly qualified personnel.
Installation Guideline
Install the RSI-95 according to NFPA 70, NEC 760, and
any applicable local codes.
NOTE: Only one each RSI-95 and solenoid may be con-
nected together for each releasing circuit. The RSI-95 is
designed to fit on a 4.688" (11.908 cm) by 2.125" (5.397
cm) deep electrical box (user supplied).
SmartStart™ is a trademark of Honeywell International Inc.
An ISO 9000-2000 Company
SIGNALING
S521
GAMEWELL-FCI
Specifications are for information only, are not intended for installation purposes, and are subject to change without notice. No responsibility is assumed by Gamewell-FCI for their use.
©2007 Honeywell International Inc. All rights reserved.
www.gamewell-fci.com
CS-2046 Rev. A page 1 of 2
12 Clintonville Road, Northford, CT 06472-1610 USA • Tel: (203) 484-7161 • Fax: (203) 484-7118
CS-2064ph1.wmf
Installation Guideline (Continued)
The addition of the trim ring (P/N 70839) allows flush instal-
lation. The total voltage drop from the power supply to the
end of the solenoid circuit shall not exceed two volts. The
RSI-95 must have its address programmed before the sys-
tem will operate correctly.
Ordering Information
Model
RSI-95
RSI-95 assembly consists of an RSM-95
analog addressable Releasing Service
Module and integral SID Solenoid Interface
Device.
NOTE: RSM-95 and SID no longer available
separately.
Flush trim ring for RSM-95.
Installation
Connect the system wiring to the four-position terminal
block L1, L2, P1, P2 per wiring diagram A-W532-1. Con-
nect the solenoid device wiring to the four-position terminal
block per wiring diagram A-W572.
IMPORTANT! Maximum L1 – L2 loop resistance should not
be more than 25 ohms.
70839
CAUTION:
No wiring connections should be made while the system is
powered.
Temperature:
Humidity:
Power:
+P and –P, or
+24 and –24:
Normal Current:
Alarm Current:
Solenoid Circuit
Rating:
Mounting:
0°C to 49°C (32°F to 120°F)
85%, non-condensing
21 VDC from analog addressable
module.
24 VDC from UL-Listed power
source.
6.5 mA
6.5 mA + solenoid load
2.0 A power-limited steady
operation
4.0"
(10.16 cm),
4.688"
(11.908 cm),
double-gang electrical box
GAMEWELL-FCI
CS-2046 Rev. A page 2 of 2