Solid-state Timers
H3DK
DIN Track-mounted, 22.5-mm-width
Standard Timer Series
• A wide AC/DC power supply range (24 to 240 VAC/DC).
*1
• All sub-series include models with 12-VDC power supply.
*1
• G-type Models (H3DK-G) now include model with 240 to 440-
VAC power supply.
• UL
*3
, CSA, and CCC
*2
certification and EN 61812-1 compliance.
CE Marking.
• EMC (EN 61812-1) compliance for application in heavy industri-
al, residential, commercial, or light industrial environments.
• Finger-safe terminal block and captive screws according to EN
50274.
*1. Except for the H3DK-H.
*2. Certification for the H3DK-GE is scheduled to be obtained in the near future.
*3. Except for the H3DK-GE.
LR
Model Number Structure
The Entire H3DK Series
H3DK Series
H3DK-M/-S Multi-range,
Multi-mode Timers
H3DK-F
Twin Timers
H3DK-G
Star-delta Timers
H3DK-H Power
OFF-delay Timers
Page 2
Eight-mode Timer
H3DK-M1/M2
Operating Modes
A: ON Delay
B: Flicker OFF Start
B2: Flicker ON Start
C: Signal ON/OFF Delay
D: Signal OFF Delay
E: Interval
G: Signal ON/OFF Delay
J: One-shot Output
Four-mode Timer
H3DK-S1/S2
Operating Modes
A: ON Delay
E: Interval
J: One-shot Output
Page 11
Operating Modes
Flicker-OFF Start/
Flicker-ON Start
Operating Modes
Star-delta Timer
Page 15
Operating Modes
Power OFF-delay
Timer
Page 21
Model Number Legend
(Not all models that can be represented with the model number legend can necessarily be produced.)
H3DK-@@@@
1 2 3 4
1. Type
Meaning
Eight-mode Timer
Four-mode Timer
Twin Timer
Star-delta Timer
Power OFF-delay Timer
2. Control Output
Meaning
SPDT
DPDT
3. Supply Voltage
Blank
12 VDC
24 to 48 VAC/DC
100 to 120 VAC
200 to 240 VAC
240 to 440 VAC *
Meaning
24 to 240 VAC/DC
4. Time Ranges (H-type
Models Only)
Meaning
0.1 to 1.2 s or 1 to 12 s
1 to 12 s or 10 to 120 s
* M- and S-type models only.
* G-type models only.
New Product News
Multi-range, Multi-mode Timer
H3DK-M/H3DK-S
• Multiple time ranges and operating modes let you cover a wide
range of applications.
• The time-limit DPDT output contacts can be changed to time-limit
SPDT and instantaneous SPDT output contacts using a switch.
• Sequence checks are easily performed by setting an instanta-
neous output to 0.
• Start signal control for the H3DK-M.
LR
Ordering Information
List of Models
Supply voltage
Control output
Contact output, DPDT (time-limit DPDT, or time-limit
SPDT + instantaneous SPDT)
Changed using a switch.
Contact output, SPDT (time-limit SPDT)
Model
Model
Model
Model
Eight-mode Timer
H3DK-M2
H3DK-M1
H3DK-M2A
H3DK-M1A
Four-mode Timer
H3DK-S2
H3DK-S1
H3DK-S2A
H3DK-S1A
24 to 240 VAC/DC
12 VDC
Accessories (Order Separately)
Item
Specification
50 cm (l) x 7.3 mm (t)
Mounting Track
1 m (l) x 7.3 mm (t)
1 m (l) x 16 mm (t)
End Plate
Spacer
Model
PFP-50N
PFP-100N
PFP-100N2
PFP-M
PFP-S
Model Structure
Model
H3DK-M2
Operating modes
A: ON Delay
B: Flicker OFF start
B2: Flicker ON start
D: Signal OFF Delay
E: Interval
J: One-shot Output
A: ON Delay
E: Interval
J: One-shot Output
Terminal block
Input type
Output type
Relay, DPDT
Voltage input
9 terminals
Relay, SPDT
cURus (UL 508
CSA C22.2 No. 14)
DIN Track mounting EN 61812-1
IEC 60664-1 4 kV/2
EN 50274
Mounting method
Safety standards
Accessories
H3DK-M1
User label
H3DK-S2
H3DK-S1
Relay, DPDT
6 terminals
Relay, SPDT
H3DK-M/H3DK-S
Time Ranges
Time range setting
Set time range
Scale numbers
0.1 s
0.1 to 1.2 s
1s
1 to 12 s
10 s
10 to 120 s
1 min
1 to 12 min
10 min
10 to 120 min
1h
1 to 12 h
10 h
10 to 120 h
100 h
100 to 1,200 h
Ratings
Power supply voltage
*1
Allowable voltage fluctuation
range
Power reset
Reset voltage
Voltage input
H3DK-M2/-S2
Power con-
sumption
*3 H3DK-M1/-S1
H3DK-M2A/-S2A
H3DK-M1A/-S1A
Control output
Ambient operating temperature
Storage temperature
Ambient operating humidity
• 24 to 240 VAC/DC, 50/60 Hz
*2
• 12 VDC
*2
• 24 to 240 VAC/DC: 85% to 110% of rated voltage
• 12 VDC: 90% to 110% of rated voltage
Minimum power-OFF time: 0.1 s
• 24 to 240 VAC/DC
High level: 20.4 to 264 VAC/DC, Low level: 0 to 2.4 VAC/DC
• 12 VDC
High level: 10.8 to 13.2 VDC, Low level: 0 to 1.2 VDC
At 240 VAC: 6.6 VA max.
*4
At 240 VAC: 4.5 VA max.
*4
At 12 VDC: 0.9 W max.
At 12 VDC: 0.6 W max.
Contact output, 5 A at 250 VAC with resistive load (cosφ = 1),
5 A at 30 VDC with resistive load
*4, *5
−20
to 55°C (with no icing)
−40
to 70°C (with no icing)
25% to 85%
*1.
*2.
*3.
*4.
*5.
*6.
When using a 24-VDC power supply voltage, there will
be an inrush current of approximately 0.25 A. Allow for
this inrush current when turning ON and OFF the
power supply to the Timer with device with a solid-
state output, such as a sensor.
DC ripple: 20% max.
The power consumption is for mode A after the Timer
times out.
For the H3DK-M@, the maximum power consumption
is given, including the current consumed by the input
circuit.
Refer to
DC Power Consumptions (Reference Infor-
mation)
on page 27 for DC power consumptions.
The control output ratings are for one H3DK operating
alone. If you operate two or more Timers side by side,
refer to
Installation Pitch and Output Switching Capac-
ity (Reference Values)
on the next page.
125 VDC: 0.15 A max. with resistive load, 125 VDC:
0.1 A with L/R of 7 ms.
Minimum load: 10 mA at 5 VDC (P level, reference
value)
H3DK-M/H3DK-S
Characteristics
Accuracy of operating
time
Setting error
Minimum input signal
width
Influence of voltage
Influence of tempera-
ture
Insulation resistance
±1%
of FS max. (±1%
±10
ms max. at 1.2-s range)*
±10%
of FS
±0.05
s max.*
50 ms* (start input)
±0.5%
of FS max. (±0.5%
±10
±2%
of FS max. (±2%
±10
100 MΩ min. at 500 VDC
Between current-carrying metal parts and exposed non-current-carrying metal
parts: 2,000 VAC 50/60 Hz for 1 min.
Between control output terminals and operating circuit: 2,000 VAC 50/60 Hz for
1 min.
Between contacts not located next to each other: 1,000 VAC 50/60 Hz for
1 min.
24 to 240 VAC/VDC: 3 kV between power terminals, 4.5 kV between current-
carrying metal parts and exposed non-current-carrying metal parts
12 VDC: 1 kV between power terminals, 1.5 kV between current-carrying metal
Square-wave noise generated by noise simulator (pulse width: 100 ns/1
µs,
1-ns rise):
±1.5
kV
Malfunction: 4 kV, Destruction: 8 kV
Switching Capacity (Reference Val-
ues)
The relation between the installation pitch
and the load current is shown in the follow-
ing graph. (Except for the H3DK-GE)
If Timer is used under load conditions that
exceed the specified values, the tempera-
ture inside the Timer will increase, reducing
the life expectancy of internal parts.
Ambient temperature (°C)
Dielectric strength
Impulse withstand volt-
age
d = 50 mm
d = 10 mm
d = 5 mm
Maximum ambient operating
temperature in specifications
Noise immunity
Static immunity
d=0 A
Vibration
resistance Malfunction 0.5-mm single amplitude at 10 to 55 Hz for 10 min each in 3 directions
Shock re-
sistance
Life ex-
pectancy
Destruction 1,000 m/s
3 times each in 6 directions
Malfunction 100 m/s
Mechanical 10 million operations min. (under no load at 1,800 operations/h)
Electrical
100,000 operations min. (5 A at 250 VAC, resistive load at 360 operations/h)
IP30 (Terminal block: IP20)
Approx. 120 g
Destruction 0.75-mm single amplitude at 10 to 55 Hz for 2 h each in 3 directions
Load current (A)
Testing Method
Tested Timer: H3DK-M/-S
Applied voltage: 240 VAC
Installation pitch: 0, 5, 10, and 50 mm
Test
timer
Test
timer
Test
timer
Test
timer
Test
timer
Degree of protection
Weight
* With the H3DK-M@, if the voltage exceeds 26.4 VAC/DC in mode C, D, or G, the OFF trigger signal char-
acteristics are as follows:
Accuracy of operating time:
±1% ±50
ms max.
+100
ms
Setting error:
±10%
−50
ms
max.
Minimum input signal width: 100 ms
DIN Track
Timer installation pitch: d
Applicable standards
Safety standards
cURus: UL 508/CSA C22.2 No. 14
EN 50274: Finger protection, back-of-hand proof
EN 61812-1: Pollution degree 2, Overvoltage category III
CCC: Pollution degree 2, Overvoltage category II, section DB14048.5-2008 part 5-1
LR: Test Specification No. 1-2002 Category ENV 1.2
(EMI)
Radiated Emissions:
Emission AC Mains:
Harmonic Current:
Voltage Fluctuations and Flicker:
(EMS)
ESD Immunity:
EN61812-1
EN 55011 class B
EN 55011 class B
EN 61000-3-2
EN61000-3-3
EN61812-1
EN 61000-4-2: 6 kV contact discharge,
8 kV air discharge
Radiated Radio-Frequency Electromagnetic Field Immunity (AM Radio Waves):
EN 61000-4-3: 10 V/m (80 MHz to 1 GHz)
Burst Immunity:
EN 61000-4-4: 2 kV power line,
1 kV I/O signal line
Surge Immunity:
EN 61000-4-5: 2 kV common mode,
1 kV differential mode
EMC
I/O
Item
Input
Output
Model
Start
Control
output
H3DK-M1/-M2
Functions to start timing.
H3DK-S1/-S2
There is no start input.
The output is turned ON/OFF according to the operating mode when the value
that is set on the dial is reached. *
* If the INST/TIME switch on the front of the Timer is set to INST on the H3DK-M2/-S2, relay R2 will
operate as instantaneous contacts and will turn ON/OFF in synchronization with the power supply.
H3DK-M/H3DK-S
Connections
■Block
Diagrams
H3DK-M1/-M2
AC (DC) input
Time setting
detection circuit
Time specification
switches
Operating mode
switch
ROM
Power supply circuit
RAM
Clock
Output circuit
One-chip microcomputer
Start input
Input circuit
Indicator circuit
Power
indicator
Output
indicator
H3DK-S1/-S2
AC (DC) input
Time setting
detection circuit
Time specification
switches
Operating
mode switch
ROM
RAM
Clock
Output circuit
Indicator circuit
Power
indicator
Output
indicator