QUINT-PS/ 1AC/48DC/10
Primary-switched power supply with SFB
technology, 1 AC, output current 10 A
INTERFACE
Data Sheet
103381_en_02
© PHOENIX CONTACT - 03/2009
Quick tripping of standard power circuit breakers with
dynamic SFB technology power reserve
Reliable starting of difficult loads with static POWER
BOOST power reserve
Preventive function monitoring
Can be used worldwide
High degree of operational safety due to high MTBF >
500 000 h, long mains buffering times > 20 ms, high
dielectric strength up to 300 V AC
QUINT POWER power supply units – highest system
availability due to SFB technology
Compact power supply units of the new QUINT POWER
generation maximize the availability of your system. Even the
standard power circuit-breakers can be tripped reliably and
quickly with the SFB technology (Selective Fusebreaking
Technology) and six times the nominal current for 12 ms.
Defective current paths are disconnected selectively, the
defect is limited and the important system parts remain in
operation. A comprehensive diagnostics is carried out by
continuously monitoring the output voltage and current. This
preventive function monitoring visualizes the critical
operating modes and reports them to the control unit before
an error occurs.
DANGER OF EXPLOSION!
Only remove equipment when it is disconnected and not in the potentially explosive area.
DANGER
The device contains dangerous live elements and high levels of stored energy.
Never carry out work when the power is turned on.
Make sure you always use the latest documentation.
It can be downloaded at
www.phoenixcontact.net/download
Table of contents
Description ..................................................................................................................................
Table of contents.........................................................................................................................
Ordering data ..............................................................................................................................
Technical data.............................................................................................................................
Structure......................................................................................................................................
Block diagram .............................................................................................................................
Safety notes ................................................................................................................................
Installation ...................................................................................................................................
Installation position......................................................................................................................
Slim-style installation .................................................................................................................................................9
Low-profile installation ...............................................................................................................................................9
10 Mounting on DIN rails ..................................................................................................................
11 Connection to various systems..................................................................................................
12 Input ..........................................................................................................................................
Protection of the primary side...................................................................................................................................10
Recommended backup fuse for mains protection ....................................................................................................10
13 Output .......................................................................................................................................
Protection of the secondary side ..............................................................................................................................11
14 Signaling ...................................................................................................................................
Floating contact........................................................................................................................................................12
Active signal outputs ................................................................................................................................................12
Signal loop ...............................................................................................................................................................12
15 Function ....................................................................................................................................
Output characteristic curve ......................................................................................................................................13
Thermal behavior .....................................................................................................................................................13
Parallel operation .....................................................................................................................................................14
Redundant operation ...............................................................................................................................................14
Increased performance ............................................................................................................................................14
103381_en_02
PHOENIX CONTACT
Ordering data
Primary-switched power supply with SFB technology, 1 AC, output current
10 A
Order No.
2866682
Pcs. / Pkt.
Accessories
Universal wall adapter
UWA 182/52
Order No.
2938235
Pcs. / Pkt.
Technical data
Input data
Input nominal voltage range
AC input voltage range
Short-term input voltage
DC input voltage range
AC frequency range
DC frequency range
Current consumption
Inrush current limitation
Power failure bypass
Typical response time
Protective circuitry
Input fuse, integrated
Discharge current to PE
100 V AC ... 240 V AC
85 V AC ... 264 V AC
300 V AC
90 V DC ... 350 V DC
45 Hz ... 65 Hz
0 Hz
Approx. 5.1 A (120 V AC)
Approx. 2.3 A (230 V AC)
< 20 A (typical)
< 3.2 A
s
> 20 ms (120 V AC)
> 20 ms (230 V AC)
<1s
Transient surge protection Varistor
12 A (slow-blow, internal)
10 A
16 A (characteristic B)
< 3.5 mA
Output data
Nominal output voltage
Setting range of the output voltage
Output current
48 V DC ±1%
30 V DC ... 56 V DC (> 48 V constant capacity)
10 A (-25°C ... 70°C)
13 A (with POWER BOOST, -25°C ... 40°C permanent)
60 A (with SFB technology, 12 ms)
From +60°C 2.5% per Kelvin
BOOST
= 13 A (for short circuit), approximately
< 1 % (change in load, static 10% ... 90%)
< 2 % (change in load, dynamic 10% ... 90%)
< 0.1 % (change in input voltage ±10%)
41 W
16 W
> 93 % (for 230 V AC and nominal values)
< 0.5 ms (U
OUT
(10% ... 90%))
< 80 mV
PP
(with nominal values)
Yes, for redundancy and increased capacity
Yes
yes, limited to approx. 60 V DC
Max. 60 V DC
Derating
Current limitation
Control deviation
Power loss nominal load max.
Maximum power dissipation idling
Efficiency
Ascent time
Residual ripple
Connection in parallel
Connection in series
Surge protection against internal surge voltages
Resistance to reverse feed
103381_en_02
PHOENIX CONTACT
DC OK active
Output description
Current
Status display
U
OUT
> 0.9 x U
: High signal
+ 24 V DC
20 mA (short circuit resistant)
"DC OK" LED green / U
OUT
< 0.9 x U
: LED flashing
DC OK floating
Output description
Current
Status display
Relay contact, U
OUT
> 0.9 x U
: Contact closed
30 V AC/DC (≤ 0.5 A / at 60 V AC/DC)
1A
OUT
< 0.9 x U
: LED flashing
POWER BOOST, active
Output description
Current
Status display
OUT
< I
: High signal
+ 24 V DC
LED "BOOST", yellow / I
OUT
> I
: LED on
General data
Insulation voltage input/output
Insulation voltage input / PE
Insulation voltage output / PE
Degree of protection
Class of protection
MTBF
Housing material
Dimensions W / H / D (state of delivery)
Dimensions W / H / D (90° turned)
Weight
4 kV AC (type test)
2 kV AC (routine test)
3.5 kV AC (type test)
500 V DC (routine test)
IP20
I, with PE connection
> 500 000 h in acc. with IEC 61709 (SN 29500)
Steel sheet, zinc-plated
90 mm / 130 mm / 125 mm
122 mm / 130 mm / 93 mm
1.7 kg
Ambient conditions
Ambient temperature (operation)
Ambient temperature (storage/transport)
Max. permissible relative humidity (operation)
Vibration (operation)
Shock
Pollution degree in acc. with EN 50178
Climatic class
-25 °C ... 70 °C (> 60°C derating)
-40 °C ... 85 °C
95 % (at 25°C, no condensation)
< 15 Hz, amplitude ±2.5 mm in acc. with IEC 60068-2-6
15 Hz ... 150 Hz, 2.3g, 90 min.
30g in all directions in acc. with IEC 60068-2-27
3K3 (in acc. with EN 60721)
Standards
Electrical Equipment for Machinery
Safety transformers for power supply units
Electrical safety (of information technology equipment)
Electronic equipment for use in electrical power installations
SELV
Safe isolation
Protection against electric shock
Protection against electric shock, basic requirements for safe isolation in
electrical equipment
EN 60204
IEC 61558-2-17
IEC 60950/VDE 0805 (SELV)
EN 50178/VDE 0160 (PELV)
IEC 60950 (SELV) and EN 60204 (PELV)
DIN VDE 0100-410
DIN VDE 0106-1010
DIN 57100-410
DIN VDE 0106-101
103381_en_02
PHOENIX CONTACT
Standards (Continued)
Limitation of mains harmonic currents
Device safety
Network variants (undervoltage)
Certificate
EN 61000-3-2
GS (tested safety)
Semi F47-200
CB Scheme
Approvals
UL approvals
UL applied for
Conformance with EMC guideline 2004/108/EC and for low-voltage guideline 2006/95/EC
Noise immunity according to EN 61000-6-2
Electrostatic discharge
EN 61000-4-2
Housing
Contact discharge
Discharge in air
Comments
Electromagnetic HF field
EN 61000-4-3
Housing
Frequency range
Field intensity
Comments
Fast transients (burst)
EN 61000-4-4
Input
Output
Signal
Comments
Surge current loads (surge)
EN 61000-4-5
Input
Output
Signal
Comments
Conducted interference
EN 61000-4-6
Input/Output/Signal
Frequency range
Comments
Voltage dips
EN 61000-4-11
Input
Comments
(mains buffering > 20 ms)
Criterion B
Level 3 - asymmetrical
0.15 MHz ... 80 MHz
10 V
Criterion A
4 kV (inst. class 4 - asymmetrical: conductor to ground)
2 kV (inst. class 4 -symmetrical: conductor to conductor)
2 kV (level 3 - asymmetrical: conductor to ground)
1 kV (level 1 - symmetrical: conductor to conductor)
1 kV (level 3 - asymmetrical: conductor to ground)
Criterion B
4 kV (level 4 - asymmetrical)
2 kV (level 1 - asymmetrical)
1 kV (level 1 - asymmetrical)
Criterion B
Level 4
80 MHz ... 1000 MHz
20 V/m
Criterion A
Level 4
8 kV
15 kV
Criterion B
Emitted interference in acc. with EN 61000-6-3
Radio interference voltage in acc. with EN 55011
Emitted radio interference in acc. with EN 55011
EN 55011 (EN 55022) Class B, area of application: Industry and residential
103381_en_02
PHOENIX CONTACT