17.5mm INPUT MODULES
• DIN-Rail Mountable Single Point Input Modules
• AC Inputs (Yellow Top), DC Inputs (White Top)
• UL, cUL Recognized, CE Compliant
• 4kV Optical isolation
• Input and Output Barrier Strips Accept 14 to 28
AWG Wire
• Open-Collector Output, with LED Status Indicator
SPECIFICATIONS (1)
Input
Voltage Range
Maximum Current [mA](2)
Minimum Current [mA](2)
Drop-out Current [mA](3)
Voltage for No Output (4)
Allowable Current [mA] (4)
84115501
90-140 VAC/DC
28 k
50 VAC/DC
84115502
180-280 VAC/DC
75 k
50 VAC/DC
0.7
84115503
4-32 VDC
27
28 k
2.2 VDC
Output
Logic Supply Voltage Range [VDC]
Maximum Logic Supply Voltage [VDC]
Maximum Logic Supply Current [mA](5)
Maximum Supply Idle Current (5)
Maximum Current [mA](6)
Maximum Logic Leakage Current [µA]
Maximum Voltage Drop [VDC]
Maximum Turn-On Time [msec] (7)
Maximum Turn-Off Time [msec] (7)
4.5 to 30
0.2
4.5 to 30
0.2
4.5 to 30
0.2
GENERAL SPECIFICATIONS
Input/Output Isolation Voltage (8)
Input/Output Capacitance
Storage Temperature Range
Line Frequency Range
Weight
4000
-30 to 80°C
-40 to 100°C
47 to 63
1.1 oz. (31.2g)
GENERAL NOTES:
(1) Specificat ions apply t o an ambient temperature of -30 to 80 °C unless otherwise noted.
(2) Measured at maximum specifi ed input voltage, 25° C.
(3) Defined as the maximum current allowed through the module's input t o guarantee that
the out put will switch from "on" to "of f". Higher current s may result in t he output remaining
i n the "on" s tate.
(4) Defined as the maximum current allowed through the module's input t hat will not switc h
the module's output state f rom "off: to "on".
(5) At maximum specified logic voltage and 25° C.
(6) Maximum allowable sink ing c urrent through the open c ollector output transistor.
(7) At 15 VDC logic, 30 VDC output, 50 mA, 25° C and nominal input voltage.
(8) At 25°C for 1 second maximum durat ion.