Thermal-Magnetic Overcurrent Circuit Breaker 3200
Single pole thermal-magnetic circuit breaker with tease-free, trip-free,
press-to-reset, snap action mechanism and additional manual release
(M-type TM CBE to EN 60934). Designed for plug-in mounting with E-T-A
sockets 10 and 16.
Approved to CBE standard EN 60934 (IEC 60934).
Typical applications
Control equipment, extra-low voltage wiring systems and components.
Ordering information
Type No.
3200
plug-in
Current ratings
0.05...25 A
3200 - 5 A
ordering example
3200-...
Technical data
For further details please see chapter: Technical Information
Voltage rating
AC 240 V, 50/60 Hz; DC 28 V
Current ratings
0.05...25 A
Typical life
500 operations at 1 x I
, inductive
4,000 operations at 1 x I
, resistive
Ambient temperature
-30...+60 °C (-22...+140 °F)
Insulation co-ordination
rated impulse
pollution
(IEC 60664 and 60664 A) withstand voltage
degree
2.5 kV
reinforced insulation in operating area
Dielectric strength
(IEC 60664 and 60664A) test voltage
operating area
AC 3,000 V double insulation
Insulation resistance
> 100 MΩ (DC 500 V)
Interrupting capacity I
cn
0.05...0.8 A
self-limiting
1...2 A
200 A
2.5...25 A
400 A
Degree of protection
operating area IP40
(IEC 60529/DIN 40050)
terminal area IP00
Vibration
5 g (57-500 Hz), ± 0.38 mm (10-57 Hz)
to IEC 60068-2-6, test Fc
10 frequency cycles/axis
Shock
25 g (11 ms)
to IEC 60068-2-27, test Ea
Corrosion
96 hours at 5 % salt mist
to IEC 60068-2-11, test Ka
Humidity
240 hours at 95 % RH
to IEC 60068-2-78, test Cab
Mass
approx. 50 g
Standard current ratings and typical internal resistances
Current
rating (A)
0.05
0.1
0.2
0.3
0.4
0.8
Internal
resistance (Ω)
534
149
56
24.2
13.6
8.1
5.25
3.55
2.02
0.90
0.51
0.36
0.23
Current
rating (A)
Internal
resistance (Ω)
0.141
0.107
0.060
0.049
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
Approvals
Authority
VDE
Standard
IEC/EN 60934
Rated voltage
AC 240 V
DC 28 V
Current ratings
0.05...25 A
0.05...25 A
2015/16
www.e-t-a.de
Dimensions
Internal connection diagram
line 1
ø9.5
.374
ø13
.512
OFF
15.5
.610
ON
I >
1.91
9.6
.378
19
.748
43
1.69
current rating in A
Installation drawing
operating area
(reinforced insulation)
1.36
Typical time/current characteristics
0.05…7 A
10000
AC/DC
1)
8…16 A
10000
AC/DC
1)
18…25 A
10000
43
1.69
19
.748
AC/DC
1)
Trip time in seconds
… times rated current
0.1
0.1
0.01
0.01
0.01
0.001
+23 °C
+73.4 °F
-30 °C
-22 °F
0.001
0.001
+60 °C
+140 °F
1)
Magnetic tripping currents are inceased by 20 % on DC supplies.
Ambient °F
temp.
Derating factor
-22
-30
-4
-20
+14
-10
0.83
+32 +73.4 +86
0.88
+104 +122 +140 The time/current characteristic curve depends on the ambient temperature
+40 +50 +60 prevailing. In order to eliminate nuisance tripping, please multiply the circuit
breaker current ratings by the derating factor shown below. See also section
1.04 1.11 1.19 1.29 Technical information.
This is a metric design and millimeter dimensions take precedence ( mm )
inch
www.e-t-a.de
2015/16
Accessories
Sockets 10R-K10
10R-P10
wire cross sectional areas
2 x max. 2.5 mm
(AWG 14) stranded
2 x max. 4 mm
(AWG 12) solid
.039
.472
Blanking plug
Y 301 477 01
for sockets 10R-P10/K10/A10
42
1.65
Terminal for mounting rack
(DIN/EN 50 035-G32)
X 200 800 01
for sockets 10R
27.5
1.08
5.6
.220
68
2.68
.374
21
22
10R-A10
blade terminal
DIN 46244-A6.3-0.8
(QC .250)
blade terminal
DIN 46244-A6.3-0.8
(QC .250)
14.5
.571
7.5
.295
45
1.77
75
2.95
19
.748
9.5
.374
M5 x 12
ø4
.157
27
1.06
Connector bus links -K10
X 210 589 01/
2.5 mm
, (AWG 14) (black) up to 20 A max. load
X 210 589 02/
1.5 mm
, (AWG 16) (brown) up to 13 A max. load
for sockets 10R-P10, 10R-A10 and 16
ø2.5
.099
50 pin lugs to
DIN 46230
tinned copper
59
2.32
9.5
.374
Bus bars for sockets 10…
(up to 20 A max. load)
Y 301 166 02,
2-way
Y 301 166 01,
4-way
2.9
.114
7.9
.311
4.2
.165
22.9
.902
thickness = 0.8 mm
.031 in.
52.9
2.08
Connector bus links -P10
X 210 588 01/
1.5 mm
X 210 588 02/
2.5 mm
X 210 588 03/
2.5 mm
, (AWG 14) (red) up to 20 A max. load
X 210 588 04/
2.5 mm
, (AWG 14) (blue) up to 20 A max. load
100 quick-connect tabs 6.3 (.250)
DIN 46247 tinned brass,
insulated
~70
~2.76
Socket 16
(up to 16 A max. load)
52
2.05
39.5
1.56
32
1.26
38.5
1.52
12.5
.492
8.5
.335
Adapter
for socket 16
X 200 409 01
for track mounting
to EN 50035-G32
(G profile)
on request
symmetrical rail
EN 50022-35x7.5
sockets individually
(de)mountable
inch
All dimensions without tolerances are for reference only. In the interest of improved design,
performance and cost effectiveness the right to make changes in these specifications
without notice is reserved.Product markings may not be exactly as the ordering codes.
Errors and omissions excepted.
2015/16
www.e-t-a.de
~70
~2.76
2 x max. 2.5 mm
(AWG 14) stranded
2 x max. 4 mm
(AWG 12) solid
www.e-t-a.de
2015/16