TMX-350
Multiple Output, 48 Vdc Hot Swap
FEATURES:
Diode isolated outputs for hot swap
“Zero wire” slope program current sharing
Self-aligning connector with solid metal, machined contacts
Identical output performance as RMX-350 Series
• Dual converter design eliminates interaction between logic
and auxiliary outputs
• Low ripple and noise on all outputs
• Dc power good signal
True remote inhibit
Monotonic turn-on and turn-off
SPECIFICATIONS:
INPUT
Dc Input:
40-60 Vdc. Internally fused for 13 A.
Efficiency:
75% typical.
Low Input
Provides TTL “0” when input is below 40 Vdc.
ENVIRONMENTAL
Thermal Protection:
Shuts down power supply if overheated.
Automatic recovery.
Holdup Time:
20 ms minimum after removal of power at full load.
Temperature Range:
0° to 50°C at full ratings.
Safety Agencies:
Most models are approved to UL1950; CSA
22.2 #234; IEC 950 and TÜV EN60950, Class 1 SELV., CE 72/23/
EEC/93/68EEC (low voltage directive).
Conducted RFI:
Meets FCC Part 15, Subpart J, Class A;
EN55022 Class B and CISPR 22 Class B.
Cooling:
Self-cooled by internal ball-bearing fan.
Output Isolation:
Isolated from ground 50 Vdc.
DC INPUT
FUNCTION
J1-22
J1-24
J1-11
48 VDC
+48 Vdc
-48 Vdc
Safety Ground
CONNECTOR
See below
OUTPUT
Adjustability:
Outputs #1 and 2, and 4 factory adjusted to
nominal ±0.2%. Output #3 tracks #2; initial accuracy ±3%.
Line & Load Reg:
Outputs #1, 2, and 4 hold ±2% (with local
sense) over dc input range and 0 to 100% load change
(preprogrammed slope). Output #3 requires 20% minimum load
on outputs #2 and 3 to hold ±5%.
Ripple & Noise:
1% p-p or 100 mV, whichever is greater.
Remote Sense (Output #1):
Compensates for 250 mV total line
drop. Preprogrammed slope remains under ±3% worst case.
Open sense lead protection.
Temperature Coefficient (Outputs #1, 2, and 4):
0.03% per
degree C.
Stability:
0.1% over 8 hours after 30 minutes warm-up.
Transient Response (Outputs #1, 2, and 4):
Output voltage
returns to within 1% in less than 500 µs for a 50% load change
(measured with rise time and fall time of 200 µs). Peak transient
does not exceed 5%.
Overload Protection:
All outputs are protected against overload
and short circuit. Automatic recovery upon removal of fault.
Overvoltage Protection (Outputs #1 and 2):
Protects load
against power supply induced over voltage. Trip point is factory
set so that output voltage cannot exceed 136% of nominal.
Peak Output Current:
Dual current ratings define continuous
and peak currents. The peak current shown can be delivered for
a maximum period of 30 seconds.
Remote Inhibit:
Contact closure to the negative sense line or a
TTL level “0” turns off dc outputs.
Redundancy:
Built-in OR-ing diodes, slope program current
sharing on all outputs, and self aligning connector provide “hot
swap” and “N+1” capabilities. Current sharing remains within 10%
of the unit’s full output rating while units are in thermal equilibrium.
Remote Enable:
Contact closure to common turns on dc
outputs (recessed pin for “make last, break first” connection).
Dc Power Good:
Provides a TTL “1” open collector when
output #1 is above 4.6 V nominal.
Reverse Voltage:
Protected against reverse voltage up to
supply current rating.
DC OUTPUT
FUNCTION
Output #1
LOCATION
J1-10,20,30
J1-9,19,29
Output #2
J1-2
J1-3
Output #3
J1-4
J1-3
Output #4
J1-5
J1-6
Rtn (common)
(+) Floating Output
(-) Floating Output
Rtn (common)
NOTES
Main Output
Rtn (common)
CONNECTOR
Positronics #
PLC30M400A1-168.3
Mates with panel
mounted
PLC30F1000
connector using
crimp contacts
FC114N2 (14 to 16 AWG)
STATUS AND CONTROL
FUNCTION
Remote Sense
J1-18
J1-8
Dc Power Good
J1-7
LOCATION
NOTES
Output #1 Sense
Output #1 Sense Rtn
Reference to common
when #1 Sense Rtn is
terminated
Enable
Inhibit
Ac Power Fail
Aux Fan (+)
J1-16
J1-27
J1-17
J3-1
Reference to common
CONNECTOR
See above
Condor D.C. Power Supplies, Inc., 2311 Statham Parkway, Oxnard, CA 93033
800-235-5929 • 805-486-4565 • FAX 805-487-8911 • www.condorpower.com