NLP65 Series
Single, dual and triple output
LOW TO MEDIUM POWER AC/DC POWER SUPPLIES
65-75W AC/DC Universal Input Switch Mode Power Supplies
5.0 x 3.0 inch card and 1.26 inch package (1U applications)
Smallest industry standard package
EN61000-3-2 compliance option (HCC)
Overvoltage and short circuit protection
65W with free air convection cooling
EN55022, EN55011 conducted emissions level B
EN61000-4-2,-3,-4, -5, -6 immunity compliant
Enclosure and cover kit options
The NLP65 series is a 65W universal input AC/DC power supply on a 5 x 3 inch card with a
maximum component height of 1.26 inches for use in 1U applications. Each model has the option
of input harmonic current correction in the same package size making the series ideal for product
designs that will need to comply with EN61000-3-2 legislation. The NLP65 provides 65W of
output power with free air convection cooling which can be boosted to 75W with 20CFM of air.
The NLP65, with full international safety approval and the CE mark, meets conducted emissions
EN55022 level B and has immunity compliance to EN61000-4-2,-3,-4, -5, -6. The series is
available in a factory installed enclosure with an IEC connector and output connector on flying
leads plus a cover kit for self-installation is also available as an accessory. The NLP65 series is
designed for use in low power data networking, computer and telecom applications such as hubs,
routers, POS terminals, internet servers, cable modems and PABX’s. This list is not exclusive as
the generic feature set of the NLP65 series with industry standard output configurations provides
a solution for most low power applications including many industrial applications.
All specifications are typical at nominal input, full load at 25°C unless otherwise stated
2 YEAR WARRANTY
(11,12)
OUTPUT SPECIFICATIONS
Total regulation
(Line and load)
Rise time
Transient response
Main output
Auxiliary outputs
At turn-on
Main output
25% step
at 0.1A/µs
±2.0%
±5.0%
1.0s, max.
5.0% or 250mV
max. dev., 1ms max.
recovery to 1%
±0.02%/°C
Main outputs
Cyclic operation
Single and multiple
125%, ±10%
Continuous
(See Note 6)
EMC CHARACTERISTICS (continued)
Surge
Fast transients
Radiated immunity
Conducted immunity
EN61000-4-5,
EN61000-4-4,
EN61000-4-3,
EN61000-4-6,
level
level
level
level
Perf.
Perf.
Perf.
Perf.
criteria
criteria
criteria
criteria
GENERAL SPECIFICATIONS
Hold-up time
Efficiency
Isolation voltage
Switching frequency
Approvals and
standards
(See Notes 9, 13)
Weight
120VAC, 60Hz
230VAC, 50Hz
120VAC, 65W
Input/output
Input/chassis
Fixed
16ms @ 65W
78ms @ 65W
72% typical
3000VAC
1500VAC
100kHz, ±5kHz
EN60950, VDE0805
IEC950, UL1950, BABT
CSA C22.2 No. 950
283g (10 oz)
MIL-HDBK-217F
150,000 hours min.
Temperature coefficient
Overvoltage protection
Short circuit protection
Minimum output current
INPUT SPECIFICATIONS
Input voltage range
Universal input,
(See Note 2)
NLP65-76xx
version only
85 to 264VAC
120 to 370VDC
47Hz to 63Hz
MTBF
Input frequency range
Input surge current
(cold start)
Safety ground
leakage current
Input current
120VAC
230VAC
120VAC, 60Hz
230VAC, 50Hz
120VAC,
230VAC,
120VAC,
230VAC,
with PFC
with PFC
without PFC
without PFC
Thermal performance
(See Notes 1, 3, 10)
Operating ambient,
0°C to +70°C
(See derating curve)
Non-operating
-40°C to +85°C
50°C to 70°C ambient,
Derate to
convection cooled
50% load
0°C to 50°C, ambient,
65W
convection cooled
0°C to 50°C ambient,
75W
20CFM forced air (See Note 10)
Peak (0°C to +50°C, 60s)
See table
Non-condensing
Operating
Non-operating
5Hz to 500Hz
per MIL-STD-810E
5% to 95% RH
10,000 feet max.
30,000 feet max.
2.4G rms peak
516.4 Part IV
17A max.
32A max.
0.7mA
1.4mA
1.05A
0.51A
1.40A
0.80A
rms
rms
rms
rms
Input fuse
UL/IEC127
(11,12)
250VAC S 3.15A
Relative humidity
Altitude
Level B
Level A
Perf. criteria 1
Perf. criteria 1
Vibration (See Note 5)
Shock
EMC CHARACTERISTICS
Conducted emissions
Radiated emissions
ESD air
ESD contact
EN55022, FCC part 15
EN61000-4-2, level 3
EN61000-4-2, level 4
File Name: NLP65.PDF Rev: 15 Jan 2002
NLP65 Series
OUTPUT
VOLTAGE
+5V (I
+12V (I
–12V
+5V (I
+15V (I
–15V
+5V (I
+24V (I
+5V (I
+12V (I
+5V
+12V
+15V
+24V
For the most current data and application support visit www.artesyn.com/powergroup/products.htm
OUTPUT CURRENT
RIPPLE
MAX
(4)
TOTAL
REGULATION
(6)
NON-HARMONIC
CORRECTED
NLP65-7608
HARMONIC
CORRECTED
NLP65-9608
GROUND
PIN
(12, 14)
PEAK
9.1A
3.3A
(3)
FAN
(10)
7.5A
2.5A
0.65A
7.5A
2.2A
0.65A
7.0A
2.0A
7.0A
2.5A
10.0A
5.4A
4.4A
2.7A
8.0A
3.0A
0.8A
8.0A
2.5A
0.8A
8.0A
2.0A
8.0A
3.0A
12.0A
6.5A
5.3A
3.5A
50mV
150mV
120mV
50mV
150mV
150mV
50mV
240mV
50mV
150mV
50mV
120mV
150mV
240mV
±2.0%
±5.0%
±5.0%
±2.0%
±5.0%
±5.0%
±2.0%
±5.0%
±2.0%
±5.0%
±2.0%
±2.0%
±2.0%
±2.0%
NLP65-X608G
0.81A
9.1A
2.9A
0.85A
9.1A
2.6A
9.1A
3.3A
13.0A
7.0A
5.7A
3.5A
NLP65-7610
NLP65-9610
NLP65-X610G
NLP65-7620
NLP65-9620
NLP65-X620G
NLP65-7629
NLP65-9629
NLP65-X629G
NLP65-7605
NLP65-7612
NLP65-7615
NLP65-7624
NLP65-9605
NLP65-9612
NLP65-9615
NLP65-9624
NLP65-X605G
NLP65-X612G
NLP65-X615G
NLP65-X624G
Natural convection cooling. Models NLP65-X629, NLP65-X608, NLP65-
X610 must not exceed 62.5 Watts continuous output power with natural
convection. Model NLP65-X620 not to exceed 65 Watts continuous output
power with natural convection. Model NLP65-763V3 must not exceed 33
Watts continuous output power.
When the input voltage is less than 90VAC the operating temperature
range is 0
C to +40
C. The ripple and regulation specifications may not be
met.
Peak output current lasting less than 60 seconds with duty cycle less than
5%. During peak loading, output voltage may exceed total regulation limits.
Figure is peak-to-peak for convection power rating. Output noise
measurements are made across a 20MHz bandwidth using a 6 inch twisted
pair, terminated with a 10µF electrolytic capacitor and a 0.1µF ceramic
capacitor.
Three orthogonal axes, random vibration 10 minutes for each axes, 2.4G
rms 5Hz to 500Hz.
A minimum load on the main output is required for proper start up. For
multiple outputs and single +5V output, the minimum load on the +5V is
0.2A. For single outputs greater than +5V the minimum load is 0.1A. To
maintain stated regulation then:
for single output units
0.2A
for multiple output units
0.25
I(A)/I(B)
5, for I(A)
0.2A.
For optimum reliability, no part of the heatsink should exceed 120
o
C, and
no semiconductor case temperature should exceed 130
o
C.
CAUTION: Allow a minimum of 1 second after disconnecting line power
when making thermal measurements.
This product is only for inclusion by professional installers within other
equipment and must not be operated as a stand alone product.
Maximum continuous output power for all multiple output models must not
exceed 75 Watts with 20CFM forced air cooling.
Conducted and radiated emissions testing were performed using the
standard EN55022 set-up with a stand alone NLP65 unit placed on a
grounded metal plate with a line choke on the AC input and ground wires
(i.e. the wires are looped through an EMI suppression toroid).
For system compliance it is usually necessary to install an ‘off-the-shelf’
AC inlet with an integral line filter in the system chassis or to install a line
choke on the input wires as close as possible to AC entry point of the
system chasssis. Please contact the applications group at Artesyn for
assistance with EMI compliance.
The NLP65 units with the suffix ‘G’ is the ground pin and ground choke
option. J2, L6 and JP10 are included. J2 is a safety agency approved
grounding pin, L6 is a ground choke and JP10 is a jumper. This option is
intended for use in non-metallic chassis applications where grounding is
not possible via the mounting screws. The ground choke is provided to
assist system EMC compliance. When performing conducted emissions
testing on stand alone units, the ‘G’ option is required to meet level B. To
order simply add the suffix ‘G’ to the standard model number, e.g. NLP65-
7608G, NLP65-9608G. This option is available for both the PFC and non-
PFC versions.
All models require a minimum mounting stand-off of 0.25 inches (6.35mm)
in the end use product.
These standard models are available with an enclosure. To order an
enclosed version, see model numbering options below.
No PFC version, EN61000-3-2 is not applicable to this model.
International Safety Standard Approvals
VDE0805/EN60950/IEC950 File No. 10401-3336-1096
Licence No. 93678
UL1950 File No. E136005
CSA C22.2 No. 950 File No. LR41062C
Approval No. 606975
Model Numbering Options
The enclosure version includes: IEC connector, on/off switch, wire harness
output connector and fitted cover. To order, please add the suffix ‘E’ to the
end of the model number, e.g. NLP65-X608E. See NLP65 enclosure for
details.
A Safety earth ground pin and ground choke are available as an option.
To order, please add the suffix ‘G’ to the end of the model number, e.g.
NLP65-X608G.
To order a snap-on cover (unfitted), order the part number NLP65C.
To order a mounting bracket (unfitted), order the part number NLP65MB.
www.artesyn.com
NLP65 Series
Mechanical Notes
All dimensions are in inches (mm).
5.00
(127.00)
4.550
(115.57)
0.225
(5.715)
J1
J3
(76.20)
J2
C19
T1
(64.770)
Mounting
Hole Diameter
0.156 (4.00)
MAXIMUM COMPONENT
HEIGHT 1.26 (32.00)
TOLERANCE: .xxx
0.005"
.xx
0.02"
ALL DIMENSIONS IN INCHES (mm)
INPUT
PIN CONNECTIONS
J1
Pin 1
AC Line
Pin 2
No Pin
Pin 3
AC Neutral
J2 (ON ‘G’ SUFFIX ONLY)
Pin 1
Safety Ground
J3
Pin 1
Pin 2
Pin 3
Pin 4
Pin 5
Pin 6
OUTPUT PIN CONNECTIONS
SINGLE -XX05 ONLY
V (A)
V (A)
V (A)
Return
Return
Return
SINGLE
No Connection
V (A)
V (A)
Return
Return
No Connection
DUAL
V (B)
V (A)
V (A)
Return
Return
N/C
TRIPLE
V (B)
V (A)
V (A)
Return
Return
V (C)
Input and output connectors
AC (J1) connector type
Molex 26-60-4030 type.
Mating connectors
AC (J1) mating connector type
Molex 09-50-3031 or equivalent with Molex
08-50-0105 or equivalent crimp terminals.
DC (J3) mating connector type
Molex 09-50-3061 with Molex 2478 phosphor
bronze crimp terminals or equivalent.
DERATING CURVE
Output Power (Watts)
75W
20 CFM FORCED AIR COOLING
65W
DC (J3) connector type
Molex 26-60-4060 type.
The input and output connectors are the same as those used on NFS40,
NFN40, NAL40, NAN40 and NLP40.
NATURAL
CONVECTION
COOLING
38W
32W
0˚C
10˚C 20˚C 30˚C 40˚C 50˚C 60˚C
70˚C
Data Sheet © Artesyn Technologies® 2002
The information and specifications contained in this data sheet are believed to be correct at time of publication. However, Artesyn Technologies accepts no responsibility for consequences arising
from printing errors or inaccuracies. Specifications are subject to change without notice. No rights under any patent accompany the sale of any such product(s) or information contained herein.
www.artesyn.com