5349
AC SMOKE DETECTOR
WITH INTERCONNECT AND TIMER
The A5349CA is a low-current, CMOS circuit providing all of the
required features for an ionization-type smoke detector. A networking
capability allows as many as 125 units to be interconnected so that if
any unit senses smoke, all units will sound an alarm. In addition,
special features are incorporated to facilitate alignment and test of the
finished smoke detector. This device is designed to comply with
Underwriters Laboratories Specification UL217.
The internal oscillator and timing circuitry keeps standby power to
a minimum by powering down the device for 1.66 seconds and sensing
smoke for only 10 ms. Every 24 on/off cycles, a check is made for low
battery condition. By substituting other types of sensors, or a switch for
the ionization detector, this very-low power device can be used in
numerous other safety or security applications.
The A5349CA is supplied in a low-cost, 16-pin dual in-line plastic
package. It is rated for continuous operation over the temperature
range of 0°C to +50°C.
Data Sheet
26110.4
TIMER START
I/O
LOW-V SET
TIMER OUT
LED
+ SUPPLY
TIMING RES.
FEEDBACK
SS
DD
LOGIC
GUARD 2
DETECT. IN
GUARD 1
SENSITIVITY
SET
OSC. CAP.
HORN 2
HORN 1
– SUPPLY
OSC. &
TIMING
HORN
DRIVER
Dwg. PC-004
s
s
s
s
s
s
s
Interconnect Up to 125 Detectors
Piezoelectric Horn Driver
Guard Outputs for Detector Input
Low Supply Detection
Power-ON Reset
Internal Timer & Control for Reduced Sensitivity
Built-In Hysteresis Reduces False Triggering
ABSOLUTE MAXIMUM RATINGS
(Voltages are referenced to V
SS
Supply Voltage Range,
DD
-0.5 V to +15 V
Input Voltage Range,
IN
-0.3 V to V
DD
+ 0.3 V
Input Current, I
IN
10 mA
Operating Temperature Range,
C to +50
Storage Temperature Range,
C to +125
CAUTION: CMOS devices have input static
protection but are susceptible to damage when
exposed to extremely high static electrical
charges.
Always order by complete part number:
A5349CA
5349
AC SMOKE DETECTOR
with INTERCONNECT
and TIMER
FUNCTIONAL BLOCK DIAGRAM AND TYPICAL APPLICATION
+ SUPPLY V DD
I/O
DD
FEEDBACK
HORN
LOW-V
SET
LOGIC
HORN 1
LED
+V
SENSITIVITY
SET
– SUPPLY
VSS
GUARD 1
+V
DETECT. 15
IN
GUARD 2
TIMER
START
POWER-ON
RESET
TIMING RES.
OSCILLATOR
& TIMING
OSC. CAP.
TIMER OUT
+V
Dwg. FC-005A
115 Northeast Cutoff, Box 15036
Worcester, Massachusetts 01615-0036 (508) 853-5000
Copyright © 1995, Allegro MicroSystems, Inc.
5349
AC SMOKE DETECTOR
with INTERCONNECT
and TIMER
ELECTRICAL CHARACTERISTICS at T
= +25
C, V
DD
= 9.0 V, V
SS
= 0 V, C
= 0.1
µ
F,
= 8.2 M
(unless otherwise noted).
Characteristic
Detector Input Current
Input Offset Voltage
Test
Pin
16-15
15-13
Hysteresis
Common Mode Range
13-15
Active Guard Impedance
Oscillator Period
Limits
Test Conditions
Operating
0 to 40% RH, V
IN
= 0 to 9.0 V
Active Guard
Active Guard
Detect Comparator
No Alarm to Alarm
Guard Amplifier
Smoke Comparator
to V
SS
to V
SS
No Alarm
Alarm
Oscillator Pulse Width
Timer Period
Low Voltage Threshold
Sensitivity Adj. Voltage
Horn Output Voltage
After Pin 1 High-to-Low, No Smoke
= 0 to 50°C
/ V
DD
, pin 13 open circuit
OUT
= 16 mA, V
DD
= 9.0 V
OUT
= 16 mA, V
DD
= 7.2 V
OUT
= -16 mA, V
DD
= 9.0 V
OUT
= -16 mA, V
DD
= 7.2 V
Horn Output ON Time
10-11
Alarm
Low Battery
Horn Output OFF Time
10-11
Alarm
Low Battery
Timer Start Logic Levels
IH
IL
Timer Start Input Current
Timer Out Output Current
IN
= 9.0 V
OUT
= 0.5 V
Min.
6.0
90
2.0
32
8.0
8.0
7.2
48.5
8.5
6.3
3.5
Typ.
9.0
130
8.8
160
±1.0
±100
±100
±50
170
DD
- 0.5
DD
- 2.0
2.00
48
51.5
208
48
Units
pA
mV
mV
mV
mV
kΩ
kΩ
s
ms
ms
min
ms
ms
ms
s
µA
µA
NOTE 1: Negative current is defined as coming out of (sourcing) the specified device pin.
NOTE 2: Alarm (Smoke) Condition is defined as V
< V
; No Alarm (No Smoke) Condition as V
> V
Continued next page . . .
5349
AC SMOKE DETECTOR
with INTERCONNECT
and TIMER
ELECTRICAL CHARACTERISTICS continued
Test
Pin
Limits
Test Conditions
DD
= 7.2 V, V
OUT
= 1.0 V
Local Alarm
Timer Mode, No Alarm
LED Output OFF Time
No Alarm, In Standby
No Alarm, Timer Mode After Pin 1
High-to-Low
I/O Current
No Alarm, V
I/O
= V
DD
– 2.0 V
Alarm, V
I/O
= V
DD
– 2.0 V
I/O Alarm Voltage
I/O Delay
Supply Current
External “Alarm” In
“Alarm” Out
DD
= 9.0 V, No Alarm, No Loads
DD
= 12 V, No Alarm, No Loads
< V
> V
Characteristic
LED Output ON Current
LED Output ON Time
Min.
Typ.
constant OFF
Units
constant ON
s
3.0
1.67
3.0
5.0
s
µA
s
µA
µA
CIRCUIT DESCRIPTION
The A5349CA is a low-current CMOS circuit providing all of the
Oscillator.
An internal oscillator operates with a period of 1.67
seconds during no-smoke conditions. Every 1.67 seconds, internal
power is applied to the entire circuit and a check is made for smoke.
Every 24 clock cycles (40 seconds), a check is made for low supply by
comparing V
DD
to an internal reference. Since very-low currents are
used in the device, the oscillator capacitor at pin 12 should be a low-
leakage type (PTFE, polystyrene, or polypropylene).
Detector Circuitry.
When smoke is detected, the resistor divider
network that sets the sensitivity (smoke trip point) is altered to in-
crease the sensitivity set voltage (pin 13) by typically 130 mV with no
external connections to pins 3 or 13. This provides hysteresis and
reduces false triggering. An active guard is provided on both pins
adjacent to the detector input (pin 15). The voltage at pins 14 and 16
will be within 100 mV of the input. This will keep surface leakage
currents to a minimum and provide a method of measuring the input
voltage without loading the ionization chamber. The active-guard
amplifier is not power strobed and thus provides constant protection
from surface leakage currents. The detector input has internal diode
protection against static damage.
5349
AC SMOKE DETECTOR
with INTERCONNECT
and TIMER
Alarm Circuitry.
If smoke is detected, the
oscillator period changes to 40 ms and the
horn is enabled. The horn output is typically
160 ms ON, 80 ms OFF. During the OFF
time, smoke is again checked and will inhibit
further alarm output if smoke is not sensed.
During smoke conditions the low-supply
alarm is inhibited.
LED.
The LED is continuously ON during the
standby mode indicating the unit is receiving
power. During a remote alarm condition the
LED remains ON. The LED is OFF during a
local alarm condition.
Sensitivity Adjust.
The detector sensitivity
to smoke is set internally by a voltage divider
connected between V
DD
and V
SS
. The
sensitivity can be externally adjusted to the
individual characteristics of the ionization
chamber by connecting a resistor between
pin 13 and V
DD
, or between pin 13 and V
SS
Low Supply.
The low supply threshold is set
internally by a voltage divider connected
between V
DD
and V
SS
. The threshold can be
increased by connecting a resistor between
pin 3 and V
DD
. The threshold can be de-
creased by connecting a resistor between pin
3 and V
SS
. The supply voltage level is
checked every 40 seconds.
Timer.
An internal timer is provided that can
be used in various configurations to allow for
a period of reduced smoke detector sensitiv-
ity (“hush”). When a high-to-low transition
occurs at pin 1, the internal timer is reset, the
timer mode enabled, and the circuit reset to a
no-alarm condition (the LED will flash at a 10
second rate). If the level of smoke is in-
creased such that the reduced sensitivity
level is reached, the device will go into the
alarm condition. The timer, however, will
continue to completion of the nominal 10-1/4
minute period (368 clock cycles). If the timer
mode is not used, pin 1 should be tied low.
I/O.
A connection is provided at pin 2 to
allow multiple smoke detectors to be
commoned. If any single unit detects smoke
(I/O is driven high), all connected units will
TYPICAL APPLICATION
50 kΩ
+ SUPPLY
TIMER
MODE
200 kΩ
200 kΩ
NOTE
8.2 MΩ
µF
SS
DD
LOGIC
µF
NOTE
PUSH
TO
TEST
OSC. &
TIMING
HORN
DRIVER
1 MΩ
200 kΩ
TO
OTHER
UNITS
0.001
µF
NOTE 2
Dwg. EC-005-1A
NOTE 1: Use an external resistor to adjust sensitivity for a particular
smoke chamber.
NOTE 2: Select resistor to reduce sensitivity during timer mode.
NOTE 3: A resistor to ground or V
DD
may be added to this pin to modify low battery
voltage threshold.
NOTE 4: Reverse supply protection must be supplied externally.
sound their associated horns after a nominal 3 second delay. The LED
remains ON when an alarm is signaled from an interconnected unit
and a local smoke condition does not exist.
Testing.
On power up, all internal counters are reset. Internal test
circuitry allows for low-battery check by holding pins 8 and 12 low
during power up, then reducing V
DD
and monitoring HORN
(pin 10).
All functional tests can be accelerated by driving pin 12 with a 2 kHz
square wave. The 10 ms strobe period must be maintained for proper
operation of the comparator circuitry.