AC-DC
800 Watts
SMR Series
xppower.com
Up to 900 W Peak Output Power
Single Outputs from 12 V to 60 V
Active PFC
Remote On/Off
Semi F47 Compliant
Optional Current Share
Optional Input & Output Connectors
Specification
Input
Input Voltage
Input Frequency
Input Current
Inrush Current
Power Factor
Earth Leakage Current
Input Protection
90-264 VAC (120-370 VDC)
47-63 Hz
12 A at 90 VAC, 6 A at 230 VAC
70 A at 230 VAC
0.99 typical
<2.4 mA max at 264 VAC
Fitted with a T12 A/250 V fuse
General
Efficiency
Isolation
• 80% min for 12 V model
82% min for others models at 230 VAC
• 3000 VAC Input to Output
1500 VAC Input to Ground
250 VDC Output to Ground
• 25 kHz PWM, 60 kHz PFC
• 8.2 W/In
• Green LED for Power On, Power Good
TTL HIGH within 100-500 ms and LOW
≤1
ms before loss of regulation
• 0.5 V to 3 V output denoting
0-100% output current
• 150 kHrs min per MIL-HDBK-217F
Switching Frequency
Power Density
Signals
Output
Output Voltage
Output Voltage Trim
Initial Set Accuracy
Minimum Load
Start Up Delay
Start Up Rise Time
Hold Up Time
Line Regulation
Load Regulation
Over/Undershoot
Transient Response
See tables
±5%
±1%
1% to meet ripple & noise spec
1.0 s at 230 VAC
40 ms typical
16 ms min at 120 VAC
±0.5%, low line to high line
±1%, 1-100% load (see note 4)
5% max
5% max deviation, 500 µs recovery to
within 1% for a 50% load change
Ripple & Noise
• 50 mV (Vo
5 V), 1% (Vo
12 V)
(see note 2)
Overvoltage Protection
• 110-130% recycle input to reset
Overtemperature
• Measured internally with auto recovery
Protection
Overload Protection
• 110-140% with auto recovery
Short Circuit Protection
• Trip and restart (Hiccup mode)
Remote Sense
• Compensates for up to 0.5 V line drop
Remote On/Off
• On = TTL Logic HIGH, or open circuit
Off = TTL Logic LOW or short circuit
Current Share
• Optional single wire current share
within 10% for up to 4 units
(add suffix ‘-I’ to model number)
Note that this option includes output
blocking diodes. Remote sense is not
available with current share.
Current Monitor
MTBF
Environmental
• 0 to +70 ˚C, derates from 100% load at
+50 ˚C to 50% load at +70 ˚C
Cooling
• Internal fan
Operating Humidity
• 5-90%, non-condensing
Storage Temperature
• -20 ˚C to +85 ˚C
Operating Altitude
• 3000 m
Vibration
• 5-50 Hz, acceleration 7.35 ms
on
X, Y and Z axis
EMC & Safety
Emissions
Harmonic Currents
ESD Immunity
Radiated Immunity
EFT/Burst
Surge
Conducted Immunity
Dips & Interruptions
• FCC Part 15 & EN55022
Level B conducted
• EN61000-3-2-3-3
• EN61000-4-2, level 3 Perf Criteria A
• EN61000-4-3, 3 V/m Perf Criteria A
• EN61000-4-4, level 2 Perf Criteria A
• EN61000-4-5, level 3 Perf Criteria A
• EN61000-4-6, 3V Perf Criteria A
• EN61000-4-11 70% U
for 10 ms, 40% U
for 100 ms, <5% U
for 5000 ms
Perf Criteria A, B, B
• UL60950, CSA C22.2 No. 950,
EN60950-1:2001, CE Mark LVD,
SEMI F47 compliant (high line only) at
100% rated power output
Safety Approvals
AC-DC
Models and Ratings
Output
Power
750 W
Output
(3,4)
12 V
15 V
18 V
24 V
27 V
36 V
48 V
54 V
60 V
Output Current
Maximum
Peak
62.50 A
75.00 A
50.00 A
56.00 A
41.67 A
50.00 A
33.39 A
37.50 A
29.62 A
33.33 A
25.00 A
29.60 A
16.67 A
18.75 A
14.81 A
16.67 A
13.33 A
15.00 A
240
270
360
480
540
SMR Series
Ripple & Noise
(2)
mV
mV
mV
mV
mV
mV
mV
mV
mV
Model
Number
SMR800PS12
SMR800PS15
SMR800PS18
SMR800PS24
SMR800PS27
SMR800PS36
SMR800PS48
SMR800PS54
SMR800PS60
800 W
1. This peak can be taken for 500 µs only, average power should not exceed the maximum power.
2. Ripple & Noise is measured using 0.1 µF ceramic and 22 µF electrolytic capacitor, 20 MHz bandwidth.
3. Alternative output voltages available. Consult sales.
4. Load regulation increases to 2% for 0-100% load change.
Mechanical Details
B Mounting Hole 8 Places
A Mounting Hole 8 Places
0.22 (5.6)
0.25 (6.4)
0.07 (1.9)
0.02 (0.6)
0.22 (5.6)
0.25 (6.4)
UNC6-32
(Zn-plated)
(50.8) 2.50
(63.5)
M4
(Zn (yellow) -plated)
2.09
(53.0)
5.00 (127.0)
1.59
(40.4)
CN3
Pin 7
Pin
2*
6*
7*
2.50 (63.5)
CN3 (Signals)
Function
Current monitor
Current share
Return
Power good
Remote On/Off
-Remote sense
+Remote sense
0.07 (1.9)
0.02 (0.6)
FAN
2.50 (63.5)
2.50 (63.5)
1.59
(40.3)
6.00 (152.4)
Pin 1
(44.45)
0.32 (8.25)
(41.25)
2.50
(63.6)
For SMS
Version
only
*If optional current share if
fitted then remote sense
function is excluded.
0.59
(15.0)
VO-
VO+
4.25
(108.0)
L N
0.88 (22.25)
OPTION ‘-D’
IEC320 or equivalent
STANDARD
Terminal Block
M3 Screw
3 Pins 8.25 mm center
Terminal Blocks
M3.5 Screw 8 Pins 9.5 mm center
(50.8)
2.50
(63.5)
9.17 (233.0)
All dimensions are in inches (mm).
Weight: 3.30 lbs (1.5 kg) approx.
Logic connector CN3 mates with:
JST XHP-7 or equivalent &
JST SXH-002T-P0.6 crimp terminals.
Maximum mounting screw penetration:
0.12 (3.0) on base & 0.25 (6.3) on each side.
Options
• Current share and internal oring diode add suffix ‘-I’ to model number. Note that this option includes output blocking diodes.
Remote sense is not available with current share.
• Optional IEC320 inlet add suffix‘-D’ to model number.
• Optional Molex output connector add suffix ‘-E’ to model number.
• For U-Channel version replace ‘SMR’ in the model number with ‘SMS’ e.g. SMS800PS12 (note that 25 CFM cooling air is required).
Dimensions are 8.00(l) x 4.33(w) x 2.56(h) (203.2 x 110.0 x 65.0).
• For top mounting fan version replace ‘SMR’ in the model number with ‘SMT’ e;g; SMT800PS12.
Dimensions are 8.00(l) x 4.33(w) x 3.40(h) (203.2 x 110.0 x 86.4).
• For multiple option codes place codes in alphabetical order. e.g. SMR800PS12-DI.
Application Notes
Parallel Connect with
Current Share Option
Supply 1
Output
Return
CN3 Pin 2 Current Share
V1
Remote On/Off
Power Good
+5 V
CN3 Pin 5,
control connector
ON/OFF
1K
PSU
LOAD
CN3 Pin 4,
control connector
Power Good
POWER GOOD
Comm
Supply 2
Output
Return
CN3 Pin 3,
control connector
Return
CN3 Pin 3,
control connector
Return
POWER NOT GOOD
Applying <0.3 V or short between pins 5 and 3 turns
the output OFF. Applying >4.5 V or open circuit
between pins 5 and 3 turns output ON.
Sink current = 6 mA
Source current = 4 mA
17-Apr-07