UL, CUL and CSFM Listed, FM Approved, LPCB Approved, For
CE Marked (EN12259-5) / VdS Approved model use VSR-EU
Service Pressure:
450 PSI (31 BAR) - UL
Flow Sensitivity Range for Signal:
4-10 GPM (15-38 LPM) - UL
Maximum Surge:
18 FPS (5.5 m/s)
Contact Ratings:
Two sets of SPDT (Form C)
10.0 Amps at 125/250VAC
2.0 Amps at 30VDC Resistive
10 mAmps min. at 24VDC
Conduit Entrances:
Two knockouts provided for 1/2" conduit.
Individual switch compartments suitable
for dissimilar voltages.
Environmental Specifications:
• NEMA 4/IP54 Rated Enclosure suitable for indoor or
outdoor use with factory installed gasket and die-cast housing
when used with appropriate conduit fitting.
• Temperature Range: 40°F - 120°F, (4.5°C - 49°C) - UL
• Non-corrosive sleeve factory installed in saddle.
Service Use:
Automatic Sprinkler
NFPA-13
One or two family dwelling
NFPA-13D
Residential occupancy up to four stories
NFPA-13R
National Fire Alarm Code
NFPA-72
Specifications subject to change without notice.
Ordering Information
Nominal Pipe Size
2"
2 1/2"
3"
3 1/2"
4"
5"
6"
8"
DN50
DN65
DN80
DN100
DN150
DN200
Model
VSR-2
VSR-2 1/2
VSR-3
VSR-3 1/2
VSR-4
VSR-5
VSR-6
VSR-8
1144425
1144403
1144435
1144404
1144405
1144406
1144408
• Installation must be performed by qualified personnel and in
accordance with all national and local codes and ordinances.
• Shock hazard. Disconnect power source before servicing. Serious
injury or death could result.
• Risk of explosion. Not for use in hazardous locations. Serious
Optional:
Cover Tamper Switch Kit, stock no. 0090148
Replaceable Components:
Retard/Switch Assembly, stock no. 1029030
Waterflow switches that are monitoring wet pipe sprinkler systems shall
not be used as the sole initiating device to discharge AFFF, deluge,
or chemical suppression systems. Waterflow switches used for this
application may result in unintended discharges caused by surges,
trapped air, or short retard times.
General Information
The Model VSR is a vane type waterflow switch for use on wet sprinkler
systems. It is UL Listed and FM Approved for use on steel pipe;
schedules 10 through 40, sizes 2" thru 8" (50 mm thru 200 mm). LPC
approved sizes are 2" thru 8" (50 mm thru 200 mm). See Ordering
Information chart.
The VSR may also be used as a sectional waterflow detector on large
systems. The VSR contains two single pole, double throw, snap action
switches and an adjustable, instantly recycling pneumatic retard. The
switches are actuated when a flow of 10 GPM (38 LPM) or more occurs
downstream of the device. The flow condition must exist for a period
of time necessary to overcome the selected retard period.
Enclosure
The VSR switches and retard device are enclosed in a general purpose,
die-cast housing. The cover is held in place with two tamper resistant
screws which require a special key for removal. A field installable
cover tamper switch is available as an option which may be used
to indicate unauthorized removal of the cover. See bulletin number
5401103 for installation instructions of this switch.
Potter Electric Signal Company, LLC • St. Louis, MO • Phone: 866-956-1211/Canada 888-882-1833 • www.pottersignal.com
PRINTED IN USA
MFG. #5401146 - REV L
3/09
PAGE 1 OF 4
VSR
VANE TYPE WATERFLOW
ALARM SWITCH WITH RETARD
Installation (see
Fig. 1)
These devices may be mounted on horizontal or vertical pipe. On horizontal pipe they shall be installed on the top side of the pipe where they
will be accessible. The device should not be installed within 6" (15 cm) of a fitting which changes the direction of the waterflow or within 24"
(60 cm) of a valve or drain.
NOTE:
Do not leave cover off for an extended period of time.
Drain the system and drill a hole in the pipe using a hole saw in a slow speed drill (see Fig. 1). Clean the inside pipe of all growth or other
material for a distance equal to the pipe diameter on either side of the hole. Roll the vane so that it may be inserted into the hole; do not bend
or crease it. Insert the vane so that the arrow on the saddle points in the direction of the waterflow. Take care not to damage the non-corrosive
bushing in the saddle. The bushing should fit inside the hole in the pipe. Install the saddle strap and tighten nuts alternately to required torque
(see the chart in Fig. 1). The vane must not rub the inside of the pipe or bind in any way.
Do not trim the paddle. Failure to follow these instructions may prevent the
device from operating and will void the warranty.
Fig. 1
DO NOT LEAVE COVER OFF FOR
AN EXTENDED PERIOD OF TIME
Retard Adjustment
The delay can be adjusted by rotating the retard adjustment knob from
0 to the max setting (60-90 seconds). The time delay should be set at
the minimum required to prevent false alarms
TIGHTEN NUTS
ALTERNATELY
Hole must be drilled perpendicular to the pipe and vertically centered.
Refer to the Compatible Pipe/Installation Requirements chart for size.
MOUNT ON PIPE SO
ARROW ON SADDLE
POINTS IN DIRECTION
OF WATERFLOW
Correct
Incorrect
DIRECTION OF
WATERFLOW
ROLL PADDLE IN
OPPOSITE DIRECTION
OF WATERFLOW
50mm
ADAPTER
ADAPTER
(Flowing water activates
device in one direction only.)
20mm ±2mm MAX.
DN50 ONLY
USE (2) 5180162 ADAPTERS AS SHOWN ABOVE
DWG# 1146-1F
Compatible Pipe/ Installation Requirements
Model
Nominal Pipe
inch
VSR-2
VSR-2 1/2
VSR-2 1/2
VSR-3
VSR-3 1/2
VSR-4
VSR-5
VSR-6
VSR-8
mm
DN50
DN65
DN80
DN100
DN150
DN200
Nominal Pipe
O.D.
inch
2.375
2.875
3.000
3.500
4.000
4.500
5.563
6.625
8.625
mm
60.3
73.0
76.1
88.9
101.6
114.3
141.3
168.3
219.1
Pipe Wall Thickness
Schedule 10 (UL)
inch
0.109
0.120
0.120
0.120
0.120
0.134
0.134
0.148
mm
2.77
3.05
3.05
3.05
3.05
3.40
3.40
3.76
Schedule 40 (UL)
inch
0.154
0.203
0.216
0.226
0.237
0.258
0.280
0.322
mm
3.91
5.16
5.49
5.74
6.02
6.55
7.11
8.18
BS-1387 (LPC)
inch
0.142
0.142
0.157
0.177
0.197
0.248
mm
3.6
3.6
4.0
4.5
5.0
6.3
DN (VDS)
inch
0.091
0.102
0.114
0.126
0.157
0.177
mm
2.3
2.6
2.9
3.2
2.00 ± .125
4.0
4.5
50.8 ± 2.0
1.25 + .125/-.062
33.0 ± 2.0
inch
mm
Hole Size
U-Bolt Nuts
Torque
ft-lb
n-m
NOTE:
For copper or plastic pipe use Model VSR-CF.
PRINTED IN USA
3/09
PAGE 2 OF 4
VSR
VANE TYPE WATERFLOW
Fig. 2
To remove knockouts: Place screwdriver at
inside edge of knockouts, not in the center.
Fig. 3
Break out thin section of cover when
wiring both switches from one conduit
entrance.
Fig. 4
Switch Terminal Connections Clamping
Plate Terminal
DWG 1146-4
Do not drill into the base as this creates
metal shavings which can create
electrical hazards and damage the
device. Drilling voids the warranty.
Fig. 5
Typical Electrical Connections
An uninsulated section of a single conductor should not be looped
around the terminal and serve as two separate connections. The
wire must be severed, thereby providing supervision of the
connection in the event that the wire become dislodged from under
the terminal. Failure to sever the wire may render the device
inoperable risking severe property damage and loss of life.
Do not strip wire beyond 3/8" of length or expose an uninsulated
conductor beyond the edge of the terminal block. When using
stranded wire, capture all strands under the clamping plate.
BELL
Notes:
1. The Model VSR has two switches, one can be used to operate a central
station, proprietary or remote signaling unit, while the other contact
is used to operate a local audible or visual annunciator.
2. A condition of LPC Approval of this product is that the electrical
entry must be sealed to exclude moisture.
3. For supervised circuits, see “Switch Terminal Connections”
drawing and warning note (Fig. 4).
DWG. 1146-12
POWER SOURCE
SUITABLE FOR BELL
WATERFLOW ZONE
EOLR ON FIRE PANEL
Testing
The frequency of inspection and testing for the Model VSR and its associated protective monitoring system shall be in accordance with applicable
NFPA Codes and Standards and/or the authority having jurisdiction (manufacturer recommends quarterly or more frequently).
If provided, the inspector’s test valve shall always be used for test purposes. If there are no provisions for testing the operation of the flow detection
device on the system, application of the VSR is not recommended or advisable.
A minimum flow of 10 GPM (38 LPM) is required to activate this device.
Advise the person responsible for testing of the fire protection system that this system must be tested in accordance
with the testing instructions.
Fig. 7 Mounting Dimensions
3.50 in
(89.0 mm)
2.34 in
(59.4 mm)
PIPE DIA.
+ 5.25 in
(+ 133.4 mm)
2.00 in
(50.8 mm)
5.56 in
(141.2 mm)
Fig. 8
GREEN GROUND
SCREWS
U-BOLT NUT
U-BOLT WASHER
PIPE SADDLE
PIPE
PLASTIC PADDLE
U-BOLT
NOMINAL PIPE DIA. +1.75 in (+44.5 MM) FOR DN 50 – DN 65 2–2.5 in
NOMINAL PIPE DIA. +2.125 in (+54.0 MM) FOR DN 80 – DN 200 3–8 in
PRINTED IN USA
3/09
PAGE 3 OF 4
VSR
VANE TYPE WATERFLOW
Maintenance
Inspect detectors monthly. If leaks are found, replace the detector. The VSR waterflow switch should provide years of trouble-free service.
The retard and switch assembly are easily field replaceable. In the unlikely event that either component does not perform properly, please order
replacement retard switch assembly stock #1029030 (see Fig. 6). There is no maintenance required, only periodic testing and inspection.
Retard/Switch Assembly Replacement
(See Fig. 6)
The Retard/Switch Assembly is field-replaceable without draining the system or removing the waterflow switch from the
pipe
1.
2.
3.
4.
5.
6.
7.
8.
Make sure the fire alarm zone or circuit connected to the waterflow switch is bypassed or otherwise taken out of service.
Disconnect the power source for local bell (if applicable).
Identify and remove all wires from the waterflow switch.
Remove the (2) mounting screws holding retard/switch assembly to the base.
Do not
remove the (2) retard housing screws.
Remove the retard assembly by lifting it straight up over the tripstem.
Install the new retard assembly. Make sure the locating pins on the retard/switch assembly fit into the locating pin bosses on the base.
Re-install the (2) original mounting screws.
Reconnect all wires. Perform a flow test and place the system back in service.
REMOVE (2) ORIGINAL MOUNTING
SCREWS HOLDING RETARD/SWITCH
ASSEMBLY TO BASE
BREAK OUT THIN SECTION OF COVER
WHEN WIRING BOTH SWITCHES
FROM ONE CONDUIT ENTRANCE.
RETARD/SWITCH ASSEMBLY
Fig. 6
SCREWS
(2) LOCATING PINS
(2) LOCATING PIN
BOSSES IN BASE
DO NOT
REMOVE
(2) RETARD HOUSING
SCREWS
BASE
DWG# 1146-10
Removal of Waterflow Switch
To prevent accidental water damage, all control valves should be shut tight and the system completely drained before waterflow detectors are
removed or replaced.
• Turn off electrical power to the detector, then disconnect wiring.
• Loosen nuts and remove U-bolts.
• Gently lift the saddle far enough to get your fingers under it. With your fingers, roll the vane so it will fit through the hole while continuing