economical solution to the challenge of load-applied
harmonics mitigation in three-phase power systems.
With a plug-and-play approach and more compact
dimensions than comparable products, they can be
quickly installed and easily commissioned. They
increase the reliability and service life of electric
installations, help utilize electric sytem capacity
better, and are the key to meet Power Quality
standards such as IEEE 519. Ecosine filters reshape
your distorted current back to the desired sinusoidal
waveform. Schaffner ecosine filters can be applied to
virtually any kind of power electronics with front-end
six-pulse rectifiers, 3-phase diode or thyristor bridges,
where harmonic current distortion needs to be
reduced to defined limits.
Technical specifications
Nominal operating voltage
Operating frequency
Nominal motor drive input power rating
Total harmonic current distortion THDi*
Efficiency
Overload capability
SCCR**
High potential test voltage
Overvoltage category
Earthing System
Protection category
Cooling
Ambient temperature range
3 x 440 VAC to 500 VAC ±10%
50 Hz ±1 Hz
1.1 to 315 kW
<5% at rated power
>98% for rated voltage and power
1.6x rated current for 1 minute, once per hour
100 kA
P –> E 2160 VAC (1 s)
OV III (IEC 60664-1 / UL 61800-5-1)
TN, TT, IT
IP 00, IP 20
Internal fan cooling or external cooling***
–25°C to +45°C fully operational
+45°C to +70°C derated operation****
–25°C to +85°C transport and storage
Filter: UL 61800-5-1, EN 61800-5-1
Chokes: EN 61558-2-20 or EN 60076-6
UL 94 V-2
>200,000 hours
Typical applications
Equipment with front-end six-pulse rectifier
Motor drives
Factory automation equipment
Water/wastewater treatment facilities
Fan and pump applications
HVAC installations
Mission-critical processes
DC fast chargers
Design corresponding to
Flammability corresponding to
MTBF @ 45°C/480 V (Mil-HB-217F)
Typical electrical schematic
*****System requirements: THDv <2%, line voltage unbalance <1%
*****Note:
performance specifications in this brochure refer to six-pulse diode rectifiers.
*****SCR
rectifier front-ends will produce different results, dependent upon the firing angle of the thyristors.
*****THDi
~5% at rated power for filter <6 kW/HP
*****External UL-rated fuses required. Please consult the user manual.
*****Please check the inlet air flow required for cooling table further in this document and the user manual.
*****I
derated
= I
nominal
*√((T
max-
amb
)/(T
max-
nominal
)) = I
nom
*√((70°C-T
amb
)/25°C)
(all configurable optional functionalities shown)
Ecosine passive
Schaffner Group
Datasheets
23 Oct 2020
Filter selection table – IP 00 enclosure
Filter
Rated load power
@ 480 VAC/50 Hz
[kW]
1.1
2.2
4.0
5.5
7.5
22
45
55
75
90
110
132
160
315
Motor drive
input current
[Arms]***
5.5
32
38
45
90
110
210
260
320
Rated filter
input current
[Arms]
1.35
2.75
4.99
6.77
9.24
13.6
18.5
23.3
27.0
36.9
45.4
55.2
67.5
92.5
111
135
163
198
248
310
392
Weight
Typical
losses
Terminal
Frame
size
[kg]
21
28
32
36
48
54
63
67
88
161
181
217
244
331
[W]****
49
76
132
135
183
256
287
376
374
460
546
598
784
1036
1016
1083
1440
1412
1597
1745
2025
110
110
112
112
112
112
113
113
113
115
115
115
115
115
116
116
118
118
118
118
119
FN 3450-1-110-E0_ _ _ _ _*
FN 3450-2-110-E0_ _ _ _ _*
FN 3450-4-112-E0_ _ _ _ _*
FN 3450-6-112-E0_ _ _ _ _*
FN 3450-8-112-E0_ _ _ _ _*
FN 3450-11-112-E0_ _ _ _ _*
FN 3450-15-113-E0_ _ _ _ _
FN 3450-19-113-E0_ _ _ _ _
FN 3450-22-113-E0_ _ _ _ _
FN 3450-30-115-E0_ _ _ _ _
FN 3450-37-115-E0_ _ _ _ _
FN 3450-45-115-E0_ _ _ _ _
FN 3450-55-115-E0_ _ _ _ _
FN 3450-75-115-E0_ _ _ _ _
FN 3450-90-116-E0_ _ _ _ _
FN 3450-110-116-E0_ _ _ _ _
FN 3450-132-118-E0_ _ _ _ _
FN 3450-160-118-E0_ _ _ _ _**
FN 3450-200-118-E0_ _ _ _ _**
FN 3450-250-118-E0_ _ _ _ _**
FN 3450-315-119-E0XXSXX
* Filter rating which does not require forced cooling or fan module
** Filter rating which does not require RC damping module for rectifiers with EMI filter
*** Motor drive input current without harmonic filter
**** Typical losses @ 45°C, 480V, 50Hz and rated load power
Filter power terminals
Terminal designation*
Screw thread
Flex wire AWG
Flex wire
Screw torque value
Max width**
cable lug
[mm
112
113
115
116
118
119
M3
M4
M6
M8
M8
M10
M16
14-22
10-22
6-18
1/0-8
3/0-8
3/0-500 kcmil
350-750 kcmil
0.4-2.5
0.4-6
0.75-16
10-50
10-95
95-240
185-400
[Nm]
[mm]
B, C
E, F
Frame size
* Recommended connector type: wire or cable lug for 110 to 113, only cable lug for 115 to 119
** To fulfill creepage/clearance acc. UL 61800-5-1 without additional protection (insulation). Creepage/clearance can vary depending on applicable standard and must
be reviewed by customer. Creepage/clearance may be reduced when additional protection (insulation) is provided.
Filter signal and earth terminals
Terminal type
Screw thread
Screw torque value
[Nm]
Signal
Earth (PE)
Earth (PE)
Earth (PE)
Earth (PE)
Earth (PE)
M3*
M5
M6
M8
M10
M12
All
B, C
D, E
F, G, H
Frame size
* Max width cable lug = 7 mm
Ecosine passive
Schaffner Group
Datasheets
23 Oct 2020
Filter selection table – IP 20 enclosure
Filter
Rated load power
@ 480 VAC/50 Hz
[kW]
1.1
2.2
4.0
5.5
7.5
22
45
55
75
90
110
132
160
315
Motor drive
input current
[Arms]***
5.5
32
38
45
90
110
210
260
320
Rated filter
input current
[Arms]
1.35
2.75
4.99
6.77
9.24
13.6
18.5
23.3
27.0
36.9
45.4
55.2
67.5
92.5
111
135
163
198
248
310
392
Weight
Typical
losses
Terminal
Frame
size
[kg]
23
32
36
74
95
129
149
178
198
234
261
357
[W]****
49
76
132
135
183
256
287
376
374
460
546
598
784
1036
1016
1083
1440
1412
1597
1745
2025
110
110
112
112
112
112
113
113
113
115
115
115
115
115
116
116
118
118
118
118
119
FN 3450-1-110-E2_ _ _ _ _*
FN 3450-2-110-E2_ _ _ _ _*
FN 3450-4-112-E2_ _ _ _ _*
FN 3450-6-112-E2_ _ _ _ _*
FN 3450-8-112-E2_ _ _ _ _*
FN 3450-11-112-E2_ _ _ _ _*
FN 3450-15-113-E2_ _ _ _ _
FN 3450-19-113-E2_ _ _ _ _
FN 3450-22-113-E2_ _ _ _ _
FN 3450-30-115-E2_ _ _ _ _
FN 3450-37-115-E2_ _ _ _ _
FN 3450-45-115-E2_ _ _ _ _
FN 3450-55-115-E2_ _ _ _ _
FN 3450-75-115-E2_ _ _ _ _
FN 3450-90-116-E2_ _ _ _ _
FN 3450-110-116-E2_ _ _ _ _
FN 3450-132-118-E2_ _ _ _ _
FN 3450-160-118-E2_ _ _ _ _**
FN 3450-200-118-E2_ _ _ _ _**
FN 3450-250-118-E2_ _ _ _ _**
FN 3450-315-119-E2FASXX
Screw thread
Flex wire AWG
Flex wire
Screw torque value
Max width**
cable lug
[mm
112
113
115
116
118
119
M3
M4
M6
M8
M8
M10
M16
14-22
10-22
6-18
1/0-8
3/0-8
3/0-500 kcmil
350-750 kcmil
0.4-2.5
0.4-6
0.75-16
10-50
10-95
95-240
185-400
[Nm]
[mm]
B, C
E, F
Frame size
Terminal type
Screw thread
Screw torque value
[Nm]
Signal
Earth (PE)
Earth (PE)
Earth (PE)
Earth (PE)
Earth (PE)
M3*
M5
M6
M8
M10
M12
All
B, C
D, E
F, G, H
Frame size
Ecosine passive
Schaffner Group
Datasheets
23 Oct 2020
Product selector
Table 1: Filter configurations if external air flow is available for cooling
(Filters do
not contain fan
and do
not contain aux. power supply)
E0XXXXX
- For rectifiers without DC-link
choke
E0XXJXX
choke
- Filters contain trap disconnect
jumper
E0XXXRX
choke and with EMI filter
- Filters contain RC damper
module
E0XXJRX
- Contain RC damper module
and trap disconnect jumper
Ecosine passive
Schaffner Group
Datasheets
23 Oct 2020
Table 2: Filter configurations with embedded ventilation
(Filters
contain fan
and
aux. power supply)
E0FAXXX and E2FAXXX
choke
- Filters contain fan, aux. power
supply
E0FAJXX and E2FAJXX
choke
supply and trap disconnect
jumper
E0FAXRX and E2FAXRX
supply and RC damper module
E0FAJRX and E2FAJRX
supply, RC damper module and
Table 3: Filter configurations if external aux. power supply for the fan is available