60W Single Output Industrial DIN Rail Power Supply
Features :
Universal AC input/Full range
MDR-60
series
Protections: Short circuit / Overload / Over voltage
Cooling by free air convection
Can be installed on DIN rail TS-35/7.5 or 15
NEC class 2 / LPS compliant (24V,48V only)
LED indicator for power on
DC OK relay contact
No load power consumption<0.75W
100% full load burn-in test
3 years warranty
SPECIFICATION
MODEL
DC VOLTAGE
RATED CURRENT
CURRENT RANGE
RATED POWER
OUTPUT
VOLTAGE ADJ. RANGE
VOLTAGE TOLERANCE
Note.3
LINE REGULATION
LOAD REGULATION
SETUP, RISE TIME
HOLD UP TIME (Typ.)
VOLTAGE RANGE
FREQUENCY RANGE
INPUT
EFFICIENCY (Typ.)
AC CURRENT (Typ.)
INRUSH CURRENT (Typ.)
LEAKAGE CURRENT
OVERLOAD
PROTECTION
OVER VOLTAGE
FUNCTION DC OK SIGNAL
WORKING TEMP.
WORKING HUMIDITY
ENVIRONMENT STORAGE TEMP., HUMIDITY
TEMP. COEFFICIENT
VIBRATION
SAFETY STANDARDS
WITHSTAND VOLTAGE
ISOLATION RESISTANCE
EMC EMISSION
EMC IMMUNITY
MTBF
DIMENSION
PACKING
NOTE
MDR-60-5
5V
10A
0 ~ 10A
50W
5 ~ 6V
2.0%
1.0%
1.5%
Note.5
500ms, 30ms/230VAC
MDR-60-12
12V
5A
0 ~ 5A
60W
120mVp-p
12 ~ 15V
1.0%
1.0%
1.0%
500ms, 30ms/115VAC at full load
20ms/115VAC at full load
120 ~ 370VDC
86%
MDR-60-24
24V
2.5A
0 ~ 2.5A
60W
150mVp-p
24 ~ 30V
1.0%
1.0%
1.0%
MDR-60-48
48V
1.25A
0 ~ 1.25A
60W
200mVp-p
48 ~ 56V
1.0%
1.0%
1.0%
RIPPLE & NOISE (max.)
Note.2
80mVp-p
50ms/230VAC
85 ~ 264VAC
47 ~ 63Hz
78%
88%
87%
1.8A/115VAC
1A/230VAC
COLD START 30A/115VAC
60A/230VAC
<1mA / 240VAC
105 ~ 150% rated output power
Protection type : Constant current limiting, recovers automatically after fault condition is removed
6.25 ~ 7.25V
15.6 ~ 18V
31.2 ~ 36V
57.6 ~ 64.8V
Protection type : Shut down o/p voltage, re-power on to recover
Relay contact rating(max.): 30V/1A resistive
-20 ~ +70 (Refer to "Derating Curve")
20 ~ 90% RH non-condensing
-40 ~ +85
, 10 ~ 95% RH
0.03%/ (0 ~ 50
Component : 10 ~ 500Hz, 2G 10min./1cycle, period for 60min. each along X, Y, Z axes ; Mounting : Compliance to IEC60068-2-6
UL508, UL60950-1, TUV EN60950-1 approved, NEC class 2 / LPS compliant (24V,48V only)
I/P-O/P:3KVAC I/P-FG:1.5KVAC O/P-FG:0.5KVAC
I/P-O/P, I/P-FG, O/P-FG:>100M Ohms / 500VDC / 25 / 70% RH
Compliance to EN55011, EN55022 (CISPR22), EN61204-3 Class B, EN61000-3-2,-3
Compliance to EN61000-4-2, 3, 4, 5, 6, 8, 11, EN55024, EN61000-6-2, EN61204-3, heavy industry level, criteria A
299.2K hrs min. MIL-HDBK-217F (25
40*90*100mm (W*H*D)
0.33Kg; 42pcs/14.8Kg/0.82CUFT
SAFETY &
EMC
(Note 4)
OTHERS
1. All parameters NOT specially mentioned are measured at 230VAC input, rated load and 25 of ambient temperature.
2. Ripple & noise are measured at 20MHz of bandwidth by using a 12" twisted pair-wire terminated with a 0.1uf & 47uf parallel capacitor.
3. Tolerance : includes set up tolerance, line regulation and load regulation.
4. The power supply is considered a component which will be installed into a final equipment. The final equipment must be re-confirmed that it still meets
EMC directives.
5. Length of set up time is measured at first cold start. Turning ON/OFF the power supply may lead to increase of the set up time.
File Name:MDR-60-SPEC 2011-05-24