100% system availability with N+1 modular architecture and 1+1 parallel capability. In an N+1 configuration, the
SU80KTV features four self-contained, redundant 20kVA power modules that can be hot-swapped (with the load
powered) if maintenance is required. Connect two SU80KTV models in parallel (1+1 configuration) to provide
fail-safe redundancy (two 80kVA models supporting a 80kVA load) or to increase capacity (two 80kVA models
supporting a 160kVA load).
IGBT technology; extremely
efficient operation (up to 96%)
Runtime is expandable via
external battery cabinet options
Package Includes
SU80KTV UPS System
PowerAlert Software and cabling
Parallel cable (for 1+1 operation)
The SU80KTV provides mission-critical equipment with the highest level of power protection available. Large
capacity 80,000VA/64,000W UPS continually converts incoming AC power into filtered DC power, and then
resynthesizes it back into AC power with a pure sine wave. Perfectly regulated, continuous sine wave output with
zero transfer time offers compatibility with all equipment types. The SU80KTV's high input power factor,
Instruction manual and startup
checklist
Warranty information
advanced IGBT inverter technology and Digital Signal Processor (DSP) technology create less than 3% input Total Harmonic Distortion (THDi). With
SU80KTV's low THDi, generators run cooler and last longer, allowing managers to save installation costs by installing a generator with a capacity equal to
their equipment load (a 1:1 ratio). Extremely efficient operation (up to 96%) saves money by lowering electricity consumption. Hardwire input and output
connections support a variety of permanent or PDU style power connections. The SU80KTV features 277/480VAC, 3-phase, 4-wire (plus ground), wye input
and output. It also features a wide input voltage correction range (218-348/378-603VAC at full load). Frequency is 50 or 60 Hz (auto-selectable). The
SU80KTV features a single small-footprint tower power module. A stand-alone hardwired external battery module (Models BP480V26B or BP480V40C with
matching battery cabinets, available separately) is required for operation and to provide battery backup support. Additional external BP480V26B or
BP480V40C battery modules can be connected for extended runtime. Other battery cabinets for extended runtime solutions also available; contact Tripp Lite
for more information. A manual bypass breaker as well as an automatic bypass function ensure 100% availability of connected equipment by safely passing
through AC power if the UPS requires maintenance. A built-in RS-232 communication port works with included PowerAlert Software to provide shutdown
commands and reporting on a single server. An accessory slot accepts an optional internal SNMP card (Model SNMPWEBCARD) for remote shutdowns,
reboots and more. Front panel combination LCD/LED display alerts users to a variety of UPS operational modes and conditions. The LCD display includes a
real-time event log screen with up to 500 events listed. A dynamic battery management screen optimizes battery function to lengthen service life and allows
1/5
cold restart of UPS during a prolonged blackout to utilize its batteries for periodic system access or data retrieval. An Emergency Power Off button turns UPS
output OFF and disables Bypass output. Built-in Emergency Power Off (EPO) dry-contact interface supports remote emergency shutdown in large facilities. A
start-up service program is recommended to enhance the reliability of the installation.
N+1 configuration: four self-contained, redundant 20kVA power modules can be hot-swapped (with the load powered) if maintenance is required
1+1 configuration: connect two SU80KTV models in parallel to provide fail-safe redundancy or to increase capacity
High input power factor, advanced IGBT inverter technology and Digital Signal Processor (DSP) technology create low input Total Harmonic Distortion
(THDi)
True on-line, double conversion UPS with IGBT technology provides pure, sine wave AC output at all times
Maintains continuous operation through blackouts, voltage fluctuations and surges with zero transfer time
Removes harmonic distortion, electrical impulses, frequency variations and other hard-to-solve power problems
80,000VA/64,000W power capacity with 3-phase, hardwire 277/480VAC input/output connections
Features a wide input voltage correction range (218-348/378-603VAC at full load)
Precision +/-1% output voltage regulation
A stand-alone hardwired external battery module (Models BP480V26B and BP480V40C, available separately from Tripp Lite) is required for operation
and to provide battery backup support. Additional external battery modules can be connected for extended runtime.
Front panel combination LCD/LED display includes a real-time event log screen with up to 500 events listed
Dynamic battery management screen optimizes battery function to lengthen service life and allows cold restart of UPS
Built-in RS-232 communication port works with included PowerAlert Software to provide shutdown commands and reporting on a single server
Accessory slot accepts an optional internal SNMP card (model # SNMPWEBCARD) for remote shutdowns, reboots and more
Emergency Power Off button turns UPS output OFF and disables Bypass output
Start-up service program is recommended to enhance the reliability of the installation
OUTPUT
Output Volt Amp Capacity (VA)
Output kVA Capacity (kVA)
Output Watt Capacity (Watts)
Output kW Capacity (kW)
Power Factor
Crest Factor
Nominal Output Voltage(s)
Supported
Frequency Compatibility
Output Voltage Regulation (Line
Mode)
Output Voltage Regulation (Battery
Mode)
80000
64
0.8
3:1
277/480V; 3-Phase Wye
50 / 60 Hz
+/-1%
+/-1%
2/5
Output Receptacles
Output AC Waveform (AC Mode)
Output AC Waveform (Battery Mode)
Hardwire
Sine wave
Pure Sine wave
INPUT
Rated input current (Maximum Load)
Nominal Input Voltage(s) Supported
UPS Input Connection Type
UPS Input Connection Description
Input Phase
97A (per phase, online)
277/480V (3ph wye)
Hardwire
277/480V (3-Phase, 4 Wire, wye)
3-Phase
BATTERY
Expandable Battery Runtime
External Battery Pack Compatibility
Expandable Runtime Description
DC System Voltage (VDC)
Battery Recharge Rate (Included
Batteries)
Battery Replacement Description
Battery set sold separate
BP480V103
BP480V140
BP480V26B
BP480V40C
BP480V55
BP480V78
BP480V200
BP480V300
BP480V400
BP480V500
External battery pack wiring is contractor supplied
+/- 240VDC
2 - 4 hours from 10% to 90%
Hot-swappable, replaceable batteries
VOLTAGE REGULATION
Voltage Regulation Description
Overvoltage Correction
Undervoltage Correction
Online, double-conversion power conditioning
Maintains continuous operation without using battery power during overvoltages to 348/603 (3-Phase, 4-Wire, wye)
Maintains continuous operation without using battery power during brownout / undervoltage conditions to 218/378
USER INTERFACE, ALERTS & CONTROLS
Switches
Alarm Cancel Operation
Audible Alarm
LED Indicators
ON button turns UPS's inverter ON. OFF button turns UPS's inverter OFF. LCD Display Control Buttons browses
through and selects items displayed on LCD screen. Emergency Power Off button turns UPS output OFF and
disables Bypass output. Manual Bypass breaker bypasses the UPS's inverter during maintenance.
Power-fail alarm can be silenced using alarm-cancel switch
Alarms warn against a variety of operational conditions: low-battery, overload, shutdown, bypass and more
4-LED Display: Displays normal AC input, on battery power, bypass input and fault conditions
SURGE / NOISE SUPPRESSION
EMI / RFI AC Noise Suppression
AC Suppression Joule Rating
AC Suppression Response Time
Yes
4675
Instantaneous
3/5
PHYSICAL
Installation Form Factors Supported
with Included Accessories
Primary Form Factor
UPS Power Module Dimensions
(hwd, in.)
(hwd, cm)
UPS Power Module Weight (lbs.)
UPS Power Module Weight (kg)
UPS Shipping Dimensions (hwd / in.)
cm)
Shipping Weight (kg)
Cooling Method
UPS Housing Material
Tower
Tower
66.9 x 20.5 x 37.7
169.9 x 52.1 x 95.8
1286
583.8
76.2 x 28.8 x 45.5
193.7 x 73 x 115.6
Fans
Steel
ENVIRONMENTAL
Storage Temperature Range
Relative Humidity
AC Mode BTU / Hr. (Full Load)
+32 to +104 degrees Fahrenheit / 0 to +40 degrees Celsius
+5 to +122 degrees Fahrenheit / -15 to +50 degrees Celsius
0 to 90%, non-condensing
18665
COMMUNICATIONS
Communications Interface
PowerAlert Software
Communications Cable
DB9 Serial; Slot for SNMP/Web interface
Included
DB9 cabling included
LINE / BATTERY TRANSFER
Transfer Time
No transfer time (0 ms.) in online, double-conversion mode
SPECIAL FEATURES
Cold Start (Startup in Battery Mode
During a Power Failure)
High Availability UPS Features
Green Energy-Saving Features
Cold-start operation supported
Automatic inverter bypass; Hot swappable batteries
High efficiency economy mode operation; Schedulable daily hours of economy mode operation
CERTIFICATIONS
4/5
UPS Certifications
Tested to UL1778 (USA); Tested to CSA (Canada); Tested to NOM (Mexico); Meets FCC Part 15 Category A