3000VA on-line, double-conversion UPS system for critical server, network and telecommunications equipment.
3U rackmount form factor with an installed depth of 26 inches. Expandable battery runtime with optional
BP72V15-2U (limit 1), BP72V28RT-3U (multi-pack compatible) and BP72V18-2US (multi-pack compatible)
external battery packs. Full time sine wave 110 or 120V output with +/-2% voltage regulation. Online,
double-conversion Uninterruptible Power Supply (UPS) actively converts raw incoming AC power to DC, then
re-converts output back to completely regulated, filtered AC output. Operates continuously without using battery
power during brownouts to 65V and overvoltages to 150V. Highly efficient operation in optional economy mode
saves BTU heat output and energy costs. NEMA L5-30P input plug. NEMA 5-15, NEMA 5-15/20R and NEMA
L5-30R output receptacles. Network-grade AC surge and noise suppression. Zero transfer time between AC and
battery operation. Network management interfaces support simultaneous communications via USB port, DB9
serial port and SNMPWEBCARD slot. Built-in DB9 port offers both enhanced RS-232 enabled monitoring data,
plus contact closure monitoring ability. HID-compliant USB interface enables integration with built-in power
management and auto shutdown features of Windows and Mac OS X. Supports simultaneous detailed
Distributed Server Rooms
Network Closets
Small Business Networks
Voice over IP (VoIP) Phone
Systems
Package Includes
SU3000RTXL3U UPS System
PowerAlert Software and Cabling
Mounting hardware for 4 post
rack enclosures
Instruction manual
monitoring of equipment load levels, self-test data and utility power conditions via all 3 network interfaces. Includes PowerAlert monitoring software and
complete cabling. Emergency Power Off (EPO) interface. Integrated two-bank PDU switching supports load shedding and remote reboot of connected
equipment. 3-stage metered current monitoring and battery charge status LEDs. LED display panel easily rotates for viewing in rackmount or tower
configurations. Dataline surge suppression for dialup, DSL or network Ethernet connection. Utility power and voltage regulation LEDs. Audible alarm. Self-test.
capacity, AC line frequency, timed inverter shutoff, activate self-test, load bank output power control and remote reboot, UPS nominal voltage adjustment
and UPS line to battery power voltage setpoints
Built-in Emergency Power Off (EPO) interface with cable
NEMA L5-30P input plug; NEMA 5-15/20R & L5-30R output receptacles
Integrated 2 bank switched PDU enables remote outlet management for load shedding or remote reboot of individual load banks (each bank has four
outlets)
Front panel LEDs offer current monitoring and battery charge level information
UPS ships fully assembled in full compliance with DOT regulations; no time consuming connection of internal batteries by user required
Single line TEL/DSL or network ethernet line surge suppression
$250,000 Ultimate Lifetime Insurance (U.S., Canada, and Puerto Rico only)
OUTPUT
Output Capacity Details
Output Volt Amp Capacity (VA)
Output kVA Capacity (kVA)
Output Watt Capacity (Watts)
Output kW Capacity (kW)
Power Factor
Crest Factor
Nominal Output Voltage(s)
Supported
Supports up to 105% load continuously in double conversion mode, 106 to 125% for 1 minute, 126% to 150% for 30
seconds
3000
2.4
0.8
3:1
110V; 120V
2/6
Nominal Voltage Details
Frequency Compatibility
Frequency Compatibility Details
Output Voltage Regulation (Line
Mode)
(Economy Line Mode)
Output Voltage Regulation (Battery
Mode)
Output Receptacles
Load Management Receptacles
Output Circuit Breakers
Output AC Waveform (AC Mode)
Output AC Waveform (Battery Mode)
120V default
50 / 60 Hz
Output frequency matches input nominal on startup, defaults to 60 Hz on cold-start
+/- 2%
+/- 10%
+/- 2%
(4) 5-15R; (4) 5-15/20R; (1) L5-30R
Two switchable four-outlet load banks, (bank 1 - four 5-15/20R, bank 2 - four 5-15R outlets)
15A branch rated (x2) - each breaker protects 4 outlets, L5-30R is unbreakered
Pure Sine wave
Pure Sine wave
INPUT
Rated input current (Maximum Load)
Nominal Input Voltage(s) Supported
UPS Input Connection Type
Input Circuit Breakers
UPS Input Cord Length (ft.)
UPS Input Cord Length (m)
Recommended Electrical Service
Input Phase
24A
110V AC; 120V AC
L5-30P
40A
30A 120V
Single-Phase
BATTERY
Full Load Runtime (min.)
Half Load Runtime (min.)
Expandable Battery Runtime
External Battery Pack Compatibility
DC System Voltage (VDC)
Battery Recharge Rate (Included
Batteries)
Internal UPS Replacement Battery
Cartridge
Battery Access
Battery Replacement Description
5 min. (2400w)
14 min. (1200w)
Supports extended runtime with optional external battery packs
BP72V15-2U
(limit 1);
BP72V28RT-3U
(multi-pack compatible);
BP72V18-2US
72
Less than 6 hours from 10% to 80% (typical, full load discharge)
RBC96-3U
(quantity 1)
Front panel battery access door
Hot-swappable, user replaceable batteries
3/6
VOLTAGE REGULATION
Voltage Regulation Description
Overvoltage Correction
Undervoltage Correction
Severe Undervoltage Correction
Online, double-conversion power conditioning
2% output voltage regulation during overvoltages to 150
2% output voltage regulation during undervoltages to 80
2% output voltage regulation during undervoltages to 65 (under 70% load only)
USER INTERFACE, ALERTS & CONTROLS
Switches
Alarm Cancel Operation
Audible Alarm
LED Indicators
2 switches control off/on power status and alarm-cancel/self-test operation
Power-fail alarm can be silenced using alarm-cancel switch