PSR-SCP- 24DC/SDC4/2X1/B
PSR-SPP- 24DC/SDC4/2X1/B
Safety Relay for Emergency Stop and
Safety Door Circuits
INTERFACE
Data Sheet
102858_02_en
The
PSR-...- 24DC/SDC4/2X1/B
safety relay can be used
in safety circuits according to DIN EN 60204-1/VDE 0113-1
and EN 954-1.
Control is implemented via single or two-channel switches
with N/O/N/C or N/C/N/C contacts (mechanical or elec-
tronic) or via light grids. The device has an interface for the
T-BUS DIN rail connector. This interface can be used for
single-channel control and monitoring of extension units.
For this function, a T-BUS connector with switchable con-
tacts is required.
Depending on the external wiring, the maximum safety cat-
egory that can be achieved is safety category 2 or 4.
The device has two enable current paths and a 24 V alarm
output (N/O contact function) with stop category 0 accord-
ing to EN 60204-1/VDE 0113-1.
© PHOENIX CONTACT - 12/2006
Observe the safety instructions on page 4.
Make sure you always use the latest documentation.
It can be downloaded at
www.download.phoenixcontact.com.
A conversion table is available on the Internet at
http://www.download.phoenixcontact.com/general/7000_en_00.pdf.
This data sheet is valid for all products listed on the following page:
Ordering Data
Safety Relays
Safety relay for emergency stop and safety door circuits,
with screw connection
with spring-cage connection
Order No.
2981486
2981499
Pcs./Pkt.
Accessories
DIN rail connector, yellow, for PSR applications
Dummy plug
PSR-TBUS
PSR-TBUS-TP
Order No.
2890425
2981716
Pcs./Pkt.
Documentation
Application manual for PSR safety relays
Order No.
Pcs./Pkt.
UM EN SAFETY RELAY APPLICATION 2888712
Technical Data
Input Data
Nominal input voltage U
Permissible range
Typical current consumption at U
Typical response time
Monitored/manual start
Automatic start
Typical release time
Simultaneity between channel 1 and channel 2 when using the restart inhibit
in the event of a mains failure
Status indicators
20 ms
150 ms
10 ms
3 seconds, approximately
Green LED
24 V DC
0.85 - 1.1 x U
70 mA
Alarm Output Y30
Switching voltage
Limiting continuous current
24 V DC
100 mA
Output Data
Contact type
Contact material
Maximum switching voltage
Minimum switching voltage
Limiting continuous current (N/O contact)
Maximum inrush current (N/O contact)
Minimum switching current
Maximum shutdown power
2 enable current paths
Silver tin oxide (AgSnO
250 V AC/DC
15 V AC/DC
6A
6A
25 mA
Ohmic load
τ
= 0 ms
24 V DC 144 W
48 V DC 288 W
110 V DC 77 W
220 V DC 88 W
250 V AC 1500 VA
Minimum switching power
Mechanical service life
0.4 W
cycles, approximately
Inductive load
τ
= 40 ms
48 W
40 W
35 W
33 W
102858en_02_
PHOENIX CONTACT
Output Data (Continued)
Switching capacity according to DIN EN 60947-5-1/VDE 0660-200
Cycles
360/h:
3600/h:
Short-circuit protection of the output circuits, external
24 V:
230 V:
24 V:
230 V:
NEOZED 10 A gL/gG
DC13
6A
3A
AC15
5A
3A
General Data
Permissible ambient operating temperature
Nominal operating mode
Degree of protection according to VDE 0470-1
Housing
Connection terminal blocks
Installation location
Mounting position
Air and creepage distances between circuits
Basic insulation
Impulse voltage withstand level
Pollution degree
Surge voltage category
Dimensions (W x H x D)
Conductor cross section
Housing material
-20°C to +55°C
100% operating factor
IP20
IP20
IP54, minimum
Any
According to DIN EN 50178:1998-04
4 kV
III
22.5 mm x 99 mm x 114.5 mm
22.5 mm x 112 mm x 114.5 mm
0.2 mm
... 2.5 mm
0.2 mm
... 1.5 mm
Polyamide PA, not reinforced
Safe isolation, reinforced insulation, and 6 kV between the input circuit/N/C contacts and the enable contact current paths.
Tests/Approvals
BG/GS
UL
applied for
102858en_02_
PHOENIX CONTACT
Safety Instructions
During operation, parts of electrical switching devices carry hazardous voltages.
Before working on the device, disconnect the power.
Please observe the safety regulations of electrical engineering and industrial safety and liability
associations.
Disregarding these safety regulations may result in death, serious personal injury or damage to
equipment.
Startup, assembly, modifications, and upgrades may only be carried out by a skilled electrical
engineer.
For emergency stop applications, the machine must be prevented from restarting automatically by
a higher-level control system.
Protective covers must not be removed when operating electrical switching devices.
In the event of an error, replace the device immediately.
Repairs, especially if the housing must be opened, may only be carried out by the manufacturer or
authorized persons. Otherwise the warranty is invalidated.
When operating relay modules the operator must meet the requirements for noise emission for electrical and
electronic equipment (EN 61000-6-4) on the contact side and, if required, take appropriate measures.
102858en_02_
PHOENIX CONTACT
Structure
R-
PS
R-
PS
SD
C4
IN
SD
C4
IN
r
e
w
o
r
e
w
o
IN
IN
APPROVAL
S3
4S
33
APPROVAL
S3
Y1
Order No.: 29 81 48 6
Order No.: 29 81 49 9
24
23
23
24
24
Serial No.
Serial No.
13 23
13 23
Figure 1
Structure
Metal lock for mounting on the DIN rail
Plug-in COMBICON screw terminal blocks
Plug-in COMBICON spring-cage terminal blocks
13-14, 23-24: Enable current paths
S33, S34, S35: Start circuit (activating circuit)
Y1: Activating circuit
A1, A2: Supply voltage connection
Y30: 24 V alarm output
S10, S11, S12, S13: Input circuits
Y30
T-BUS
S11
S12
A1
T-BUS
T-BUS
Y1
T-BUS
S33
S34
S35
S10
S13
S22
Figure 2
A2
Block diagram
23
14 24
14 24
Block Diagram
+24V
24VDC
LOGIC
RESET
FEEDBACK
POWER
24VDC
IN1
K1
K2
IN2
T-BUS
K1/K2
102858en_02_
PHOENIX CONTACT