40W Single Output Switching Power Supply
Features :
HLP-40H
series
Universal AC input / Full range (up to 305VAC)
Built-in active PFC function, PF>0.95
Protections: Short circuit / Over current / Over voltage / Over temperature
Cooling by free air convection
Output constant current level adjustable
100% full load burn-in test
Three in one dimming function (1~10Vdc or PWM signal or resistance)
Suitable for built in LED lighting system
Suitable for dry / damp location
3 years warranty
SELV
( for 48V,54V only)
( except for 48V,54V )
SPECIFICATION
MODEL
DC VOLTAGE
RATED CURRENT
RATED POWER
VOLTAGE ADJ. RANGE
OUTPUT
CURRENT ADJ. RANGE
VOLTAGE TOLERANCE
Note.3
LINE REGULATION
LOAD REGULATION
SETUP, RISE TIME
HOLD UP TIME (Typ.)
VOLTAGE RANGE
FREQUENCY RANGE
POWER FACTOR (Typ.)
INPUT
EFFICIENCY (Typ.)
AC CURRENT (Typ.)
INRUSH CURRENT(Typ.)
LEAKAGE CURRENT
OVER CURRENT
PROTECTION OVER VOLTAGE
OVER TEMPERATURE
WORKING TEMP.
WORKING HUMIDITY
ENVIRONMENT STORAGE TEMP., HUMIDITY
TEMP. COEFFICIENT
VIBRATION
SAFETY STANDARDS
SAFETY & WITHSTAND VOLTAGE
EMC
ISOLATION RESISTANCE
EMC EMISSION
EMC IMMUNITY
MTBF
OTHERS
DIMENSION
PACKING
NOTE
Note.4
HLP-40H-12 HLP-40H-15 HLP-40H-20 HLP-40H-24 HLP-40H-30 HLP-40H-36 HLP-40H-42 HLP-40H-48 HLP-40H-54
12V
3.33A
40W
15V
9 ~ 15V
2.67A
40W
150mVp-p
20V
12 ~ 20V
2A
40W
150mVp-p
17 ~ 22V
1.2 ~ 2A
1.0%
0.5%
24V
14.4 ~ 24V
1.67A
40.1W
150mVp-p
22 ~ 27V
1 ~ 1.67A
1.0%
0.5%
0.5%
30V
18 ~ 30V
1.34A
40.2W
200mVp-p
27 ~ 33V
0.8 ~ 1.34A
1.0%
0.5%
0.5%
36V
21.6 ~ 36V
1.12A
40.3W
200mVp-p
33 ~ 40V
42V
25.2 ~ 42V
0.96A
40.3W
300mVp-p
40 ~ 46V
48V
28.8 ~ 48V
0.84A
40.3W
300mVp-p
44 ~ 53V
54V
32.4 ~ 54V
0.75A
40.5W
300mVp-p
49 ~ 58V
0.45 ~ 0.75A
1.0%
0.5%
0.5%
CONSTANT CURRENT REGION
Note.4
7.2 ~12V
RIPPLE & NOISE (max.)
Note.2
150mVp-p
10.8 ~ 13.5V 13.5 ~ 17V
2 ~ 3.33A
2.5%
0.5%
1.6 ~ 2.67A
2.0%
0.5%
Can be adjusted by internal potentiometer or through output cable
0.67 ~ 1.12A 0.58 ~ 0.96A 0.5 ~ 0.84A
1.0%
1.0%
1.0%
0.5%
0.5%
0.5%
0.5%
0.5%
0.5%
1.5%
1.0%
2.0%
Note.6
1500ms, 80ms / 115VAC at full load
16ms/230VAC
Note.5
90 ~ 305VAC
1000ms, 80ms / 230VAC at full load
16ms/115VAC at full load
127 ~ 431VDC
47 ~ 63Hz
PF>0.97/115VAC, PF>0.95/230VAC, PF>0.92/277VAC at full load (Please refer to "Power Factor Characteristic" curve)
88%
87%
0.43A / 115VAC
0.24A / 230VAC
COLD START 70A/230VAC
<0.75mA / 277VAC
95 ~ 108%
Protection type : Constant current limiting, recovers automatically after fault condition is removed
41 ~ 49V
18 ~ 24V
17.5 ~ 30V
23 ~ 30V
35 ~ 43V
48 ~ 58V
28 ~ 35V
Protection type : Shut down o/p voltage, re-power on to recover
85
10 (RTH2)
-40 ~ +70
-40 ~ +80
0.03%/
(Refer to "Derating Curve")
, 10 ~ 95% RH
(0 ~ 50 )
20 ~ 95% RH non-condensing
54 ~ 63V
59 ~ 68V
87%
88.5%
88%
0.23A / 277VAC
89%
89%
89.5%
89.5%
10 ~ 500Hz, 2G 12min./1cycle, period for 72min. each along X, Y, Z axes
UL8750, CSA C22.2 No. 250.0-08 (except for 48V, 54V), EN61347-1, EN61347-2-13 approved ;
Design refer to UL60950-1, TUV EN60950-1, EN60335-1
I/P-O/P:3.75KVAC
I/P-FG:1.88KVAC
O/P-FG:0.5KVAC
I/P-O/P, I/P-FG, O/P-FG:100M Ohms / 500VDC / 25 / 70% RH
Compliance to EN55015, EN61000-3-2 Class C ( 60% load) ; EN61000-3-3
Compliance to EN61000-4-2,3,4,5,6,8,11; EN61547, EN55024, light industry level (surge 4KV), criteria A
287.9Khrs min. MIL-HDBK-217F (25 )
147*53*27mm (L*W*H)
0.2Kg;72pcs/15.4Kg/1.09CUFT
1. All parameters NOT specially mentioned are measured at 230VAC input, rated load and 25 of ambient temperature.
2. Ripple & noise are measured at 20MHz of bandwidth by using a 12" twisted pair-wire terminated with a 0.1uf & 47uf parallel capacitor.
3. Tolerance : includes set up tolerance, line regulation and load regulation.
4. Constant current operation region is within 60% ~100% rated output voltage. This is the suitable operation region for LED related applications, but please
reconfirm special electrical requirements for some specific system design.
5. Derating may be needed under low input voltages. Please check the static characteristics for more details.
6. Length of set up time is measured at cold first start. Turning ON/OFF the power supply may lead to increase of the set up time.
7. The power supply is considered as a component that will be operated in combination with final equipment. Since EMC performance will be affected by the
complete installation, the final equipment manufacturers must re-qualify EMC Directive on the complete installation again.
File Name:HLP-40H-SPEC 2011-08-31
Constant Current Mode
0 .9 8
0 .9 7
0 .9 6
0 .9 5
0 .9 4
0 .9 3
0 .9 2
0 .9 1
0 .9
0 .8 9
0 .8 8
0 .8 7
0 .8 6
0 .8 5
50%
60%
70%
80%
90%
100%
277VAC
230VAC
115VAC
HLP-40H
series
PF
LOAD
(40W)
EFFICIENCY vs LOAD (48V Model)
HLG-40H series possess superior working efficiency that up to 89.5% can be reached in field applications.
92
90
88
EFFICIENCY (%)
86
84
82
277VAC
76
74
72
10%
20%
30%
40%
50%
60% 70%
80%
90% 100%
230VAC
115VAC
LOAD
DRIVING METHODS OF LED MODULE
There are two major kinds of LED drive method "direct drive" and "with LED driver".
A typical LED power supply may either work in "constant voltage mode (CV) or constant current mode (CC)" to drive the LEDs.
Mean Well's LED power supply with CV+ CC characteristic can be operated at both CV mode (with LED driver, at area (A) and CC mode (direct drive, at area (B).
(B)
Constant
Current area
(A) Constant
Voltage area
(max.)
(C)
Hiccup
Protection
Io (%)
Vo(%)
Typical LED power supply I-V curve
DIMMING OPERATION
HLP-40H
series
FG
AC/N
AC/L
+V
+V
-V
-V
DIM-
DIM+
Output constant current level can be adjusted through output connector by 1~10VDC, PWM signal, or connecting a resistance
between DIM+ and DIM-.
Please DO NOT connect "DIM-" to "-V".
Reference resistance value for output current adjustment (Typical)
20K
10K
30K
40K
50K
70K
80K
90K
Single driver
100K
60K
Resistance
Multiple drivers
value
(N=driver quantity for synchronized
10K
/N 20K /N 30K /N 40K /N 50K /N 60K /N 70K /N 80K /N 90K /N 100K /N
dimming operation)
OPEN
95%~105%
Percentage of rated current
10%
20%
30%
40%
50%
60%
70%
80%
90%
100%
1 ~ 10V dimming function for output current adjustment (Typical)
Dimming value
1V
10%
2V
20%
3V
30%
4V
40%
5V
50%
6V
60%
7V
70%
8V
80%
9V
90%
10V
100%
OPEN
95%~105%
10V PWM signal for output current adjustment (Typical): Frequency range :100Hz ~ 3KHz
Duty value
10%
10%
20%
20%
30%
30%
40%
40%
50%
50%
60%
60%
70%
70%
80%
80%
90%
90%
100%
100%
OPEN
95%~105%
Using the built-in dimming function can't turn the lighting fixture totally dark. Please refer to the connection method below to achieve 0% brightness
of the lighting fixture connecting to the LED power supply unit.
Dimming connection diagram for turning the lighting fixture ON/OFF :
FG
Relay
Switch
Adjuster
0~100K Ohms resistance
1~10V DC Voltage
10V PWM Signal
Green/
Yellow
Brown
Blue
AC/L
AC/N
HLP-40H
DIM+
DIM-
V(-)
V(+)
Blue
White
Black
Red
LED Lighting Fixture
Using a switch and relay can turn ON/OFF the lighting fixture.
1.Output constant current level can be adjusted through output connector by connecting a resistance or 1~10Vdc or 10V PWM signal between DIM+ and DIM-.
2.The LED lighting fixture can be turned ON/OFF by the switch.