GE Energy
CAR2024FP series rectifier
Input: 90Vac to 264Vac; Output: 24Vdc @ 83A; 3.3Vdc or 5 Vdc @ 1A
Data Sheet
Universal input with PFC
Constant power characteristic
3 front panel LEDs: input, output, fault
Remote ON/OFF control of the 24Vdc output
Remote sense on the 24Vdc output
No minimum load requirements
Redundant parallel operation
Active load sharing (single wire)
Hot Plug-ability
Efficiency: typically 90% @ 50% load
Standby orderable either as 3.3Vdc or 5Vdc
Auto recoverable OC & OT protection
Operating temperature: -10 - 70C (de-rated above
50C)
Digital status & control: I
C and PMBus serial bus
EN/IEC/UL60950-1 2
nd
edition; UL, CSA and VDE
EMI: class A FCC docket 20780 part 15, EN55022
Meets EN6100 immunity and transient standards
Shock & vibration: NEBS GR-63-CORE, level 3
24Vdc distributed power architectures
Telecom Base Stations
Mid to high-end Servers
Enterprise Networking
Network Attached Storage
Telecom Access Nodes
Routers/Switches
Broadband Switches
ATE Equipment
The CAR2024FP series of Front-End rectifiers provide highly efficient isolated 2000 watts @ 24Vdc power from
worldwide input mains in a compact 1U industry standard form factor in an unprecedented power density of 21W/in
These rectifiers are ideal for either datacom or telecom applications such as enterprise networking, remote base
stations, mid to high-end servers, and storage equipment, where mid to light load efficiency is of key importance
given the nature of the power consumption of the end application.
The high-density, front-to-back airflow is designed for minimal space utilization and is highly expandable for future
growth. The industry standard PMBus compliant I
C communications buss offers a full range of control and
monitoring capabilities. The SMBAlert signal pin alerts customers automatically of any state change within the power
supply.
March 28, 2013
©2012 General Electric Company. All rights reserved.
GE Energy
Absolute Maximum Ratings
Stresses in excess of the absolute maximum ratings can cause permanent damage to the device. These are absolute stress ratings only, functional
operation of the device is not implied at these or any other conditions in excess of those given in the operations sections of the data sheet.
Exposure to absolute maximum ratings for extended periods can adversely affect the device reliability.
Input: 90Vac to 264Vac; Output: 24 Vdc @ 83A; 3.3Vdc or 5 Vdc @ 1A
Input Voltage: Continuous
Operating Ambient Temperature
Storage Temperature
I/O Isolation voltage to Frame (100% factory Hi-Pot tested)
Device
All
All
All
All
VIN
TA
Tstg
Min
-40
ac
ac
85
1500
Electrical Specifications
Unless otherwise indicated, specifications apply over all operating input voltage, load, and temperature conditions.
INPUT
Operational Range
Frequency Range
Main Output Turn_OFF
Maximum Input Current
(V
= V
O, set
, I
=I
O, max
Cold Start Inrush Current
(Excluding x-caps, 25C, <10ms, per ETSI 300-132)
Efficiency
(T
amb
=25C, V
in
= 230V
ac
, V
out
= 24Vdc, I
=I
O, max
100% load
All
All
All
All
All
(Vin= 250Vac, Fin = 60Hz)
Input/Output
Input/Frame
Output/Frame
All
All
IN
3000
1500
PF
50% load
20% load
Power Factor
(Vin=230Vac, I
=I
O, max
Holdup time
in
= 220V
ac
(Vout= 24V
dc
, Tamb 25C, I
=I
O, max
in
= 100V
ac
Early warning prior to loss of DC output below regulation
Ride through
Leakage Current
Isolation
IN
= 100V
ac
IN
= 180V
ac
(ETSI 300-132-1 recommendation)
Device
All
All
All
All
All
IN
IN
IN
IN
IN
Min
90
47
Typ
110/230
50/60
63
85
14.3
12.6
ac
Hz
ac
ac
peak
90
90
84
0.99
ms
ms
ms
mArms
ac
ac
dc
24V
dc
MAIN OUTPUT
Output Power
HL / LL [180 – 264 / 90-132 Vac] V
dc
24V
dc
dc
= 21V
dc
Set point
Overall regulation (load, temperature, aging)
Ripple and noise
Turn-ON overshoot
Turn-ON delay
Device
All
All
All
All
All
All
Min
-3
Typ
24.00
1743/1050
24.024
+3
240
+3
dc
mV
p-p
sec
out
Derated above 50C at 2.5%/C
24V output can decay down to 20V
Measured across a 10µf electrolytic and a 0.1µf ceramic capacitors in parallel. 20MHz bandwidth
Page 2
GE Energy
24V
dc
MAIN OUTPUT (continued)
Remote ON/OFF delay time
Turn-ON rise time (10 – 90% of V
out
Transient response 50% step [10%-60%, 50% - 100%]
(dI/dt – 1A/
out
µs, recovery 300µs)
Programmable range (hardware & software)
Overvoltage protection, latched
(recovery by cycling OFF/ON via hardware or software)
Output current
Current limit, Hiccup (programmable level)
Active current share
Device
All
All
All
All
All
in
= HL
in
= LL
All
All
All
Min
Typ
ms
ms
%V
out
dc
dc
dc
% of FL
% of FL
-5
out
21
out
110
-5
31
+5
29
32
83
+5
AUXILIARY OUTPUT
Set point
Ripple and noise
Output current
Overload protection -
Isolation
Output/Frame
All
dc
Device
All
All
All
All
out
out
out
Min
-5
Typ
3.3 / 5.0
dc
mVp-p
dc
Environmental, Reliability
Ambient Temperature
Operating
Altitude Operating
Power Derating
Storage
Altitude non-operating
Acoustic noise
Over-temperature Protection
Humidity
Operating
Storage
95
95
2250/7.4k
2.0
85
8200/30k
55
m / ft
%/°C
C/1000
ft
m / ft
dbA
Grms
Zone
Hrs
Yrs
Full load
Shutdown / restart
Relative humidity, non-condensing
NEBS GR-63-CORE, Level 3, 20 -2000Hz, min 30 minutes
NEBS GR-63-CORE, all floors, Seismic Zone 4 Designed
and tested to meet NEBS specifications.
Full load, 25C ; MTBF per SR232 Reliability protection
for electronic equipment, method I, case III,
Full load, excluding fans
Air inlet from sea level to 5,000 feet.
51°C to 70C
Above 5,000 ft
Min
Typ
Units
-40
Shock and Vibration acceleration
Earthquake Rating
Reliability
Service Life
Designed to start at an ambient down to -40°C; meet spec after
30 min warm up period, may not meet operational limits below -10°C.
March 28, 2013
Page 3
GE Energy
EMC
AC input
Criteria
Conducted emissions
Radiated emissions
Voltage dips
Standard
EN55022, FCC Docket 20780 part 15, subpart J
EN61000-3-2
EN55022
EN61000-4-11
Level
Test
0.15 – 30MHz
0 – 2 KHz
30 – 10000MHz
-30%, 10ms
-60%, 100ms
-100%, 5sec
4kV, 1.2/50µs, common mode
2kV, 1.2/50µs, differential mode
5/50ns, 2kV (common mode)
130dBµV, 0.15-80MHz, 80% AM
10V/m, 80-1000MHz, 80% AM
4kV contact, 8kV air
Voltage surge
immunity
Enclosure
immunity
Fast transients
Conducted RF fields
Radiated RF fields
ESD
EN61000-4-5
EN61000-4-4
EN61000-4-6
EN61000-4-3
ENV 50140
EN61000-4-2
Status and Control
Some functions have two means of monitor/control; A
signal level that represents the analog value being
measured or controlled, or, reading/writing via the i
port the measured value or the control command.
Unless otherwise noted, control via the signals pins is
‘active’ so long that a firmware based command is not
initiated. Once firmware initiates a command that is also
represented on a signal pin, the firmware takes over and
replaces the hardware based control signal. Firmware
control is maintained until bias power to the processor is
interrupted. Once bias power is removed the processor
resets and the analog signal pin control is ‘active’ until
firmware takes over control.
Details of analog controls are provided in this data sheet
under Signal Definitions. GE Energy will provide separate
application notes on the I2C protocol. Contact your local
GE Energy representative for details.
Load share (Ishare):
This is a single wire analog signal
that is generated and acted upon automatically by power
supplies connected in parallel. The Ishare pins should be
tied together for power supplies if active current share
among the power supplies is desired. No resistors or
capacitors should get connected to this pin.
Remote ON/OFF:
Controls the presence of the main
24Vdc output voltage. This is an open collector, TTL level
control signal. This signal needs to be pulled HI
externally through a resistor. Maximum collector voltage
is 12Vdc and the maximum sink current is 1mA. A Logic
1 (TTL HI level) turns ON the 24Vdc output, while a Logic
0 (TTL LO level) turns OFF the 24Vdc output.
A turn OFF command either through this signal (Remote
ON/OFF) or firmware commanded would turn OFF the
24V output.
Enable:
This is a short signal pin that controls the
presence of the 24Vdc main output. This pin should be
connected to ‘output return’ on the system side of the
output connector. The purpose of this pin is to ensure
that the output turns ON after engagement of the power
blades and turns OFF prior to disengagement of the
power blades.
Write protect (WP):
This signal protects the contents of
the EEPROM from accidental over writing. When left
open the EEPROM is write protected. A LO (TTL
compatible) permits writing to the EEPROM. This signal
is pulled HI internally by the power supply.
Signal Definitions
All signals and outputs are referenced to Output return.
These include ‘Vstb return’ and ‘Signal return’.
Input Signals
Voltage programming (V
prog
An analog voltage on this
signal can vary the output voltage ± 10% from 21Vdc to
29Vdc. The equation of this signal is:
out
= 21 + (V
prog
* 3.2) 0 < V
prog
< 2.5
If 2.5 < Vprog < 3, the output is 29V. If Vprog is > 3V or
left open the programming signal is ignored and the unit
output is set at the setpoint of 24Vdc.
Output signals
Output current monitor (Imon):
A voltage level of
0.1V/Amp proportional to the delivered output current is
present on this pin. Accuracy: ± 500mV for loads > 25%
FL.
March 28, 2013
Page 4
GE Energy
AC OK:
A TTL compatible status signal representing
whether the input voltage is within the anticipated range.
This signal needs to be pulled HI externally through a
resistor. Maximum sink current
4mA and the max
voltage is 12Vdc. Open collector (HI) on this signal
indicates that the input voltage is applied within the
specified input range.
DC OK:
whether the output voltage is present. This signal needs
to be pulled HI externally through a resistor. Maximum
sink current
4mA and the max voltage is 12Vdc. Open
collector (HI) on this signal indicates that the output
voltage is present.
Over temp warning:
representing whether an over temperature exists. This
signal needs to be pulled HI externally through a resistor.
12Vdc. Open collector (HI) on this signal indicates that
temperatures are normal.
If an over temperature should occur, this signal would
pull LO for approximately 10 seconds prior to shutting
down the power supply. The unit would restart if internal
temperatures recover within normal operational levels. At
that time the signal reverts back to its open collector (HI)
state.
Fault:
whether a Fault occurred. This signal needs to be pulled
HI externally through a resistor. Maximum sink current
4mA and the max voltage is 12Vdc. Open collector (HI)
on this signal indicates that no Fault is present.
This signal activates for OTP, OVP, OCP, AC fault or No
output.
PS Present:
This pin is connected to ‘output return’ within
the power supply. Its intent is to indicate to the system
that a power supply is present. This signal may need to
Interrupt (SMBAlert):
A TTL compatible status signal,
representing the SMBusAlert# feature of the PMBus
compatible i C protocol in the power supply. This signal
4mA and the pull up resistor
should be tied to 3.3Vdc. Open collector (HI) on this
signal indicates that no Interrupt has been triggered.
Address lines (A2, A1, A0):
These signal pins allow up to
eight (8) modules to be addressed on a single I²C bus.
The pins are pulled HI internal to the power supply. For a
logic LO these pins should be connected to ‘Output
Return’
Serial Clock (SCL):
The clock pulses on this line are
generated by the host that initiates communications
across the I²C Serial bus. This signal is pulled up
internally to 3.3V by a 10kΩ resistor. The end user
should add additional pull up resistance as necessary to
ensure that rise and fall time timing and the maximum
sink current is in compliance to the I²C specifications.
Serial Data (SDA):
This line is a bi-directional data line. .
This signal is pulled up internally to 3.3V by a 10kΩ
resistor. The end user should add additional pull up
resistance as necessary to ensure that rise and fall time
timing and the maximum sink current is in compliance to
EEPROM
The microcontroller has 96 bytes of EEPROM memory
available for the system host.
Another separate EEPROM IC will provide another 128
bytes of memory with write protect feature. Minimum
information to be included in this separate EEPROM:
model number, revision, date code, serial number etc.
See the communications protocol for further information.
Communications Protocol
The I²C protocol is described in detail by the
I C and
PMBus Serial Communications Protocol for the CAR
Family of Power Supplies
application note.
The following I²C protocol commands are not supported:
FAN1_SPEED_ I²C, FAN2_SPEED_ I²C
VIN_ I²C, IIN_ I²C, PIN_ I²C
The following PMBus protocol commands are not
supported:
FAN_COMMAND_1
STATUS_FAN_1_2
READ_VIN
READ_IIN
READ_FAN_SPEED_1
READ_FAN_SPEED_2
READ_PIN
0 x 21
0 x 81
0 x 88
0 x 89
0 x 90
0 x 91
0 x A3
Serial Bus Communications
The I²C interface facilitates the monitoring and control of
various operating parameters within the unit and
transmits these on demand over an industry standard I²C
Serial bus.
All signals are referenced to ‘Signal Return’.
Device addressing:
The microcontroller (MCU) and the
EEPROM have the following addresses:
Device
MCU
EEPROM
Address
0xBx
0xAx
Address Bit Assignments
(Most to Least Significant)
1 A2 A1 A0
0 A2 A1 A0
The STAUS_MFR_SPECIFIC (Register 0 x 80) has a bit
changed;
Bit 5
0 = interrupt, 1 = no interrupt
R/W
R/W
March 28, 2013
Page 5