Print
Create PDF
Create EXCEL file
21.04.2011
09:38:58h
Datasheet - SRB 207AN-230V
Guard door monitors and Safety control modules for
Emergency Stop applications / Monitoring of
electromechanical switchgear / SRB 207AN
• Fit for signal evaluation of outputs of safety magnetic switches
• 2 safety contacts, STOP 0
• 6 Signalling outputs
• Multi-evaluation of up to 6 safety guards
• Suitable for signal processing of potential-free outputs, e.g. emergency stop
command devices, position switches and solenoid interlocks
(Minor differences between the printed image and the original
product may exist!)
Ordering details
Product type description
Article number
EAN code
SRB 207AN-230V
1196817
4030661365022
Approval
Approval
USA/CAN
BG
Classification
Standards
PL
Control category
DC
CCF
PFH value
- notice
SIL
Mission time
- notice
EN ISO 13849-1, IEC 61508, EN 60947-5-1
up d (STOP 0)
up 3 (STOP 0)
> 60% (STOP 0)
> 65 points
≤ 2 x 10
-7
/h (STOP 0)
up to max. 36500 switching cycles/year and at max. 60% contact load
up 2 (STOP 0)
20 Years
Global Properties
Product name
Standards
Compliance with the Directives (Y/N)
Climatic stress
Mounting
Terminal designations
Materials
- Material of the housings
- Material of the contacts
Weight
Start conditions
Start input (Y/N)
Feedback circuit (Y/N)
Start-up test (Y/N)
Reset after disconnection of supply voltage (Y/N)
Automatic reset function (Y/N)
Reset with edge detection (Y/N)
Pull-in delay
- ON delay with automatic start
- ON delay with reset button
Drop-out delay
- Drop-out delay in case of emergency stop
≤ 20 ms
120 ms
30 ms
Plastic, glass-fibre reinforced thermoplastic, ventilated
, self-cleaning, positive action
400 g
Automatic or Start button (Optional monitored)
Yes
Yes
No
No
Yes
Yes
SRB 207AN
IEC/EN 60204-1, EN 60947-5-1, EN ISO 13849-1, IEC 61508
Yes
EN 60068-2-78
snaps onto standard DIN rail to EN 60715
IEC/EN 60947-1
Mechanical data
Connection type
Cable section
- Min. Cable section
- Max. Cable section
Pre-wired cable
Tightening torque for the terminals
Detachable terminals (Y/N)
Mechanical life
Electrical lifetime
restistance to shock
Resistance to vibration To EN 60068-2-6
0,25 mm²
2.5 mm²
rigid or flexible
0,6 Nm
Yes
10.000.000 operations
Derating curve available on request
10 g / 11 ms
10...55 Hz, Amplitude 0,35 mm, ± 15 %
Screw connection
Ambient conditions
Ambient temperature
- Min. environmental temperature
- Max. environmental temperature
Storage and transport temperature
- Min. Storage and transport temperature
- Max. Storage and transport temperature
Protection class
−40 °C
+85 °C
−25 °C
+45 °C
- Protection class-Enclosure
- Protection class-Terminals
- Protection class-Clearance
Air clearances and creepage distances To IEC/EN 60664-1
- Rated impulse withstand voltage U
imp
- Overvoltage category
- Degree of pollution
IP40
IP20
IP54
4 kV
II To VDE 0110
2 To VDE 0110
Electromagnetic compatibility (EMC)
EMC rating
conforming to EMC Directive
Electrical data
Rated DC voltage for controls
- Min. rated DC voltage for controls
- Max. rated DC voltage for controls
Rated AC voltage for controls, 50 Hz
- Min. rated AC voltage for controls, 50 Hz
- Max. rated AC voltage for controls, 50 Hz
Rated AC voltage for controls, 60 Hz
- Min. rated AC voltage for controls, 60 Hz
- Max. rated AC voltage for controls, 60 Hz
Contact resistance
Power consumption
Type of actuation
Switch frequency
Rated operating voltage U
e
Operating current I
e
Frequency range
Electronic protection (Y/N)
Fuse rating for the operating voltage
48 V
240 V
max. 100 mΩ
6.8 VA, plus signalling outputs Y1-Y6
AC
max. 3 Hz
48 … 240 VAC
0,11 A
50 / 60 Hz
Yes
secondary side: Internal electronic trip, tripping current > 0,12 A
primary side: Safety fuse, tripping current > 1 A
48 V
240 V
Inputs
Monitored inputs
- Short-circuit recognition (Y/N)
- Wire breakage detection (Y/N)
- Earth connection detection (Y/N)
Number of shutters
Number of openers
Cable length
Conduction resistance
Yes
Yes
Yes
6 piece
6 piece
1500 m with 1.5 mm²;
2500 m with 2.5 mm²
max. 40 Ω
Outputs
Stop category
Number of safety contacts
Number of auxiliary contacts
Number of signalling outputs
Switching capacity
- Switching capacity of the safety contacts
max. 230 VAC, 6 A ohmic ( inductive in case of appropriate protective wiring)
2 piece
1 piece
6 piece
- Switching capacity of the auxiliary contacts
- Switching capacity of the signaling/diagnostic outputs
Fuse rating
- Protection of the safety contacts
- Fuse rating for the auxiliary contacts
- Fuse rating for the signaling/diagnostic outputs
Utilisation category To EN 60947-5-1
Number of undelayed semi-conductor outputs with signaling
function
Number of undelayed outputs with signaling function (with
contact)
Number of delayed semi-conductor outputs with signaling
function.
Number of delayed outputs with signalling function (with
contact).
Number of secure undelayed semi-conductor outputs with
signaling function
24 VDC; 2 A
Y1-Y6: 24 VDC 20, mA
6.3 A slow blow
2 A slow blow
Internal electronic trip, tripping current > 0,2 A
AC-15: 230 V / 6 A
DC-13: 24 V / 6 A
0 piece
7 piece
0 piece
0 piece
0 piece
Number of secure, undelayed outputs with signaling function,
with contact.
2 piece
Number of secure, delayed semi-conductor outputs with
signaling function
Number of secure, delayed outputs with signaling function
(with contact).
0 piece
0 piece
LED switching conditions display
LED switching conditions display (Y/N)
Number of LED´s
- The integrated LEDs indicate the following operating states.
- Position relay K1
- Position relay K2
- Internal operating voltage U
i
Yes
3 piece
Miscellaneous data
Emergency-Stop button
Pull-wire emergency stop switches
Guard system
Safety sensor
Dimensions
Dimensions
- Width
- Height
- Depth
45 mm
100 mm
121 mm
notice
Inductive loads (e.g. contactors, relays, etc.) are to be suppressed by means of a suitable circuit.
notice - Wiring example
To secure 6 guard doors up to PL d and Category 3
Monitoring 6 guard door(s), each with a magnetic safety sensor of the BNS range
Start button (S) with edge detection
The feedback circuit monitors the position of the contactors K3 and K4.
Automatic start:
The automatic start is programmed by connecting the feedback circuit to the terminals X1/X3. If the feedback circuit is not
required, establish a bridge
The wiring diagram is shown with guard doors closed and in de-energised condition.
Documents
Operating instructions and Declaration of conformity
(en) 847 kB, 22.02.2010
http://127.0.0.1/Bilddata/Si_baust/Pdf/srb207an230v/bedien/en/mrl_srb207an-230v_en.pdf
(fr) 457 kB, 20.01.2011
http://127.0.0.1/Bilddata/Si_baust/Pdf/srb207an230v/bedien/fr/mrl_srb207an-230v_fr.pdf
(it) 455 kB, 20.01.2011
http://127.0.0.1/Bilddata/Si_baust/Pdf/srb207an230v/bedien/it/mrl_srb207an-230v_it.pdf
(jp) 533 kB, 26.01.2011
http://127.0.0.1/Bilddata/Si_baust/Pdf/srb207an230v/bedien/jp/mrl_srb207an-230v_jp.pdf
(nl) 458 kB, 20.01.2011
http://127.0.0.1/Bilddata/Si_baust/Pdf/srb207an230v/bedien/nl/mrl_srb207an-230v_nl.pdf
(es) 455 kB, 20.01.2011
http://127.0.0.1/Bilddata/Si_baust/Pdf/srb207an230v/bedien/es/mrl_srb207an-230v_es.pdf
(de) 903 kB, 25.06.2010
http://127.0.0.1/Bilddata/Si_baust/Pdf/srb207an230v/bedien/de/mrl_srb207an-230v_de.pdf
Wiring example
(99) 18 kB, 04.08.2008
http://127.0.0.1/Bilddata/Si_baust/srb207an/schaltun/ksrb2l14.pdf
Images
Wiring example
K.A. Schmersal GmbH, Möddinghofe 30, D-42279 Wuppertal
The data and values have been checked throroughly. Technical modifications and errors excepted.
Generiert am 21.04.2011 - 09:38:58h Kasbase 1.4.7 DBI