MAP130 AC-DC Series Data Sheet
Automatic 115/230 input voltage selection
All outputs fully regulated
Remote sense, overvoltage protection, and
overtemperature protection
Power Fail signal included
Greater than 100,000 Hour MTBF
U-Channel chassis: 8.50" x 4.50" x 2.00"
(215.9mm x 114.3mm x 50.8mm)
Optional cover
Metric and SAE mounting inserts
Power-One’s MAP130 Series of single and multiple output power supplies provide fully-regulated outputs with high
peak current capabilities in a compact 4.50" x 8.50" x 2.00" U-channel chassis. Other standard features include
autoselect AC input, EMI level B filtering, power fail, thermal shutdown (with warning), remote sense, and metric and
SAE mounting inserts.
This convection-cooled series is designed for use in commercial and industrial environments in temperatures up to
50°C. All products are approved to the latest international regulatory standards and display the CE Mark.
Single Output Model Selection
MODEL
OUTPUT
VOLTAGE
ADJUSTMENT
RANGE
CONTINUOUS
CURRENT
PEAK
CURRENT (NOTE 3)
LINE
REGULATION
LOAD
REGULATION
TYPICAL RIPPLE &
INITIAL SETTING
NOISE %p-p (NOTE 1)
ACCURACY
MAP130-1005
MAP130-1012
MAP130-1024
5V
12V/15V
24V/28V
4.75V to 5.50V
11.4V to 15.75V
22.5V to 30.0V
26A
12A/10A (Note 2)
6.2A/5.4A (Note 2)
30A
13.8A/11A
6.8A/5.9A
0.2%
0.2%
0.2%
1%
1%
1%
1%
1%
1%
5.1V to 5.2V
12.0V to 12.2V
23.9V to 24.1V
NOTES:
1) Typical peak to peak noise expressed as a percentage of output voltage, 20MHz bandwidth.
2) MAP130-1012 output currents are expressed as 12V/15V operation. MAP130-1024 output currents are expressed as 24V/28V operation.
3) Peak load for 60 seconds or less are acceptable, 10% duty cycle, maximum.
Multiple Output Model Selection
130W Continuous Output Power
MODEL
OUTPUT
VOLTAGE
ADJUSTMENT
RANGE
OUTPUT
CURRENT
PEAK CURRENT
(NOTE 1)
LINE
REGULATION
LOAD
REGULATION
TYPICAL RIPPLE &
INITIAL SETTING
NOISE %p-p (NOTE 2)
ACCURACY
MAP130-4000
MAP130-4001
MAP130-4002
MAP130-4003
+5V
+12V
-5V
-12V
+5V
+24V
-12V
+12V
+5V
+12V
-12V
+12V
+5V
+15V
-5V
-15V
4.75V to 5.50V
11.5V to 12.5V
Fixed
Fixed
4.75V to 5.50V
23.0V to 25.0V
Fixed
Fixed
4.75V to 5.50V
11.5V to 12.5V
Fixed
Fixed
4.75V to 5.50V
14.0V to 16.0V
Fixed
Fixed
20A
5A
1A
1A
20A
3.5A
1A
1A
20A
5A
1A
1A
20A
4A
1A
1A
30A
10A
1A
1A
30A
5A
1A
1A
30A
10A
1A
1A
30A
8A
1A
1A
0.2%
0.5%
0.5%
0.5%
0.2%
0.5%
0.5%
0.5%
0.2%
0.5%
0.5%
0.5%
1%
1%
2%
2%
1%
2%
2%
2%
1%
2%
2%
2%
1%
2%
2%
2%
1%
2%
2%
2%
1%
1%
1%
1%
1%
1%
1%
1%
1%
1%
1%
1%
1%
1%
1%
1%
5.1V to 5.2V
11.75V to 12.0V
-4.8V to -5.2V
-11.6V to -12.4V
5.1V to 5.2V
23.9V to 24.1V
-11.6V to -12.4V
-11.6V to -12.4V
5.1V to 5.2V
11.9V to 12.1V
-11.6V to -12.4V
11.6V to 12.4V
5.1V to 5.2V
15.0V to 15.1V
-4.8V to -5.2V
-14.7V to -15.3V
REV. MAY 13, 2005
Page 1 of 4
www.power-one.com
Multiple Output Model Selection (Cont.)
MODEL
OUTPUT
VOLTAGE
ADJUSTMENT
RANGE
OUTPUT
CURRENT
PEAK CURRENT
(NOTE 1)
LINE
REGULATION
LOAD
REGULATION
TYPICAL RIPPLE &
INITIAL SETTING
NOISE %p-p (NOTE 2)
ACCURACY
MAP130-4004
MAP130-4010
MAP130-4020
+5V
+24V
-15V
+15V
+5V
+12V
-5V
-12V
+5V
+12V
-12V
-5V
4.75V to 5.50V
23.0V to 25.0V
Fixed
Fixed
4.75V to 5.50V
11.5V to 12.8V
Fixed
Fixed
4.75V to 5.50V
11.5V to 12.8V
Fixed
Fixed
20A
3.5A
1A
1A
20A
5A
1A
3A
20A
5A
1A
3A
30A
5A
1A
1A
30A
10A
1A
3A
30A
10A
1A
3A
0.2%
0.5%
0.5%
0.5%
0.2%
0.5%
0.5%
0.5%
0.2%
0.5%
0.5%
0.5%
1%
2%
2%
2%
1%
2%
2%
2%
1%
2%
2%
2%
1%
1%
1%
1%
1%
1%
1%
1%
1%
1%
1%
1%
5.15V to 5.2V
23.9V to 24.1V
-14.5V to -15.5V
14.5V to 15.5V
5.1V to 5.25V
11.75V to 12.0V
-4.8V to -5.2V
-11.6V to -12.4V
5.1V to 5.25V
11.75V to 12.0V
-11.6V to -12.4V
-4.8V to -5.2V
NOTES:
1) Peak loads up to 165 Watts, (total of all outputs), for 60 seconds or less are acceptable, (10% duty cycle max.).
2) Maximum peak to peak noise expressed as a percentage of output voltage, 20MHz bandwidth.
Input Specifications
PARAMETER
CONDITIONS/DESCRIPTION
MIN
NOM
MAX
UNITS
Input Voltage- AC
Input Frequency
Brown out Protection
Hold-up Time
Input Current
Input Protection
Inrush Surge Current
Operating Frequency
Auto-ranging.
Low Range
High Range
AC Input.
Lowest AC input voltage that regulation is maintained with full rated loads.
Nominal AC input voltage (115 VAC).
130W load:
90 VAC, 130W load.
Non-user serviceable internally located AC input line fuse.
Internally limited by thermistor. Vin = 264 VAC (one cycle). 25° C.
Switching frequency of main transformer (variable).
Range:
90
175
47
90
230
132
264
63
VAC
Hz
VAC
mS
RMS
PK
kHz
38
Output Specifications
PARAMETER
MIN
NOM
MAX
UNITS
Efficiency
Minimum Loads
Ripple and Noise
Output Power
Overshoot /Undershoot
Regulation
Transient Response
Turn-on Delay
Turn-on Rise Time
Full Load, 115VAC. Varies with distribution of loads among outputs.
MAP130-1012.
MAP130-1024.
MAP130-1005 and all multiple output models, main channel only.
Full load, 20MHz bandwidth.
Continuous output power, all multiple output models.
Peak output power (60s maximum, 10% duty cycle), all multiple output models.
Output voltage overshoot/undershoot at turn-on / turn-off
Varies by output, Total regulation includes: line changes from 90-132 VAC
or 175-264, changes in load starting at 20% load and changing to 100% load.
Recovery time to within 1% of initial set point due to a 50-100% load change,
4% max. deviation. (Main output only on multi-output units)
Time required for initial output voltage stabilization.
Time required for output voltage to rise from 10% to 90%.
71
0.63
3.00
See Model Selection Chart
130
165
Amps
Watts
µS
Sec
mS
REV. MAY 13, 2005
Page 2 of 4
www.power-one.com
Interface Signals and Internal Protection
PARAMETER
MIN
NOM
MAX
UNITS
Overvoltage Protection
Provided on single output units and only
the main output of multiple output units.
Overcurrent Protection
Remote Sense
Power Fail Warning
(Note 1)
Overtemperature Warning
(Note 2)
MAP130-1012
17.0
MAP130-1024
32.0
MAP130-4004
6.2
All other models.
5.5
All models have inherent short circuit protection. Units will automatically restart at the removal of the fault.
Total voltage compensation for main output cable losses.
Logic LO (denotes power fail detected).
Logic HI with internal pull-up to output.
Power Fail trip point, maximum load, decreasing line.
86
Time before regulation dropout, at full load, due to loss of input power.
Warning prior to system shutdown due to excessive internal temperatures.
Shifts Power Fail signal to a logic LO state.
22.0
37.0
7.4
6.8
250
0.7
94
VDC
mV
k
VAC
mS
mS
NOTES:
1) Power Fail not available on MAP130-1012 and MAP130-1024.
2) MAP130-1012 and MAP130-1024 have overtemperature protection, but do not have the warning feature.
Safety, Regulatory, and EMI Specifications
PARAMETER
MIN
NOM
MAX
UNITS
Agency Approvals
Dielectric Withstand Voltage
Electromagnetic
Interference,
ESD Susceptibility
Radiated Susceptibility
EFT/Burst
Input Transient Protection
Leakage Current
UL1950.
CSA 22.2 No. 234/950.
EN60950 (TÜV).
Input to Output, 1 second.
FCC CFR title 47 Part 15 Sub-Part B - Conducted
EN55022 / CISPR 22 Conducted
EN55022 / CISPR 22 Radiated (Note 1)
Per EN61000-4-2, level 4
Per EN61000-4-3, level 3
Per EN61000-4-4, level 3 (Note 2)
Per EN61000-4-5 class 3
Input to output
Per EN60950 (264 VAC)
Approved
2600
±2
Line to Line
Line to Ground 2
VDC
Class
kV
V/M
kV
kV
µA
NOTES:
1) MAP130-1005 meets Class A, radiated.
2) MAP130-1005, MAP130-4003, and MAP130-4010, meet level 2, ±1kV.
Environmental Specifications
PARAMETER
MIN
NOM
MAX
UNITS
Altitude
Operating
Non-Operating
Derate linearly above 50°C by 2.5% per °C
At 100% load:
At 50% load:
0°C to 70°C (after 15 minute warm-up period)
Non-Condensing
Operating, peak acceleration
Random vibration, 10Hz to 2kHz, 3 axis
±0.02
Storage Temperature
Temperature Coefficient
Relative Humidity
Shock
Vibration
10K
40K
±0.05
95
Feet
%/°C
%RH
PK
RMS
Options
NOTES
DIMENSIONS
Cover
Add ‘C’ suffix to model number or order part number 412-59586 separately.
For convection cooled applications with covers, derate output power as follows:
Derate all multiple output models and MAP130-1005 to 120 watts.
Derate MAP130-1012 and MAP130-1024 to 140 watts.
8.50" x 4.50" x 2.40"
(215.9mm x 114.3mm x 61.0mm)
REV. MAY 13, 2005
Page 3 of 4
www.power-one.com
OVERALL SIZE: 8.50" x 4.50" x 2.00" (215.9mm x 114.3mm x 50.8mm)
WEIGHT: 2.5 lb (1.13 kg)
INPUT & OUTPUT CONNECTIONS: 6-32 SCREW WIRE CLAMPS ON 0.312" (7.9mm) CENTERS,
0.045" (1.1mm) SQUARE PINS ON 0.156" (3.96mm) CENTERS;
MATES WITH MOLEX SERIES 2139, 6442, & 41695
POWER FAIL CONNECTIONS, J2:
CHASSIS:
0.035" (0.89mm) SQUARE PINS ON 0.100" (2.54mm) CENTERS;
MATES WITH MOLEX SERIES 2695 & 6471
0.090" (2.286mm) ALUMINUM ALLOY WITH CLEAR FINISH
NUCLEAR AND MEDICAL APPLICATIONS - Power-One products are not designed, intended for use in, or authorized for use as critical components
in life support systems, equipment used in hazardous environments, or nuclear control systems without the express written consent of the respective
divisional president of Power-One, Inc.
TECHNICAL REVISIONS - The appearance of products, including safety agency certifications pictured on labels, may change depending on the date
manufactured. Specifications are subject to change without notice.
REV. MAY 13, 2005
Page 4 of 4
www.power-one.com