INNOVATION and EXCELLENCE
Dual Output
BWR Models
Miniature, 1" x 1"
5 Watt, DC/DC Converters
Small size, 1" x 1" x 0.45"
Full 5 Watts output power
No external components required
Drop-in replacements for many
standard, 2" x 1" DC/DC’s
Wide input voltage ranges:
18-36V or 36-72V
Standard output voltages:
±5, ±12, ±15 Volts
Guaranteed efficiencies to 80%
Fully regulated and isolated
(1000Vdc guaranteed)
Output overvoltage protection and
current limiting
–25 to +95
o
C operating temperature
Shielded cases (5 sides)
UL1950, CSA 22.2 No. 234, and IEC950
Modifications and customs for OEM's
The migration to distributed power is accelerating. The critical need for accurate
voltages, tight regulation and rapid transient response is propelling the move to
power processing at the "point-of-use" with low-power DC/DC converters physically
located right at their loads.
DATEL’s miniature, full featured, 5 Watt BWR Models were specifically designed
for today’s demanding distributed power architectures in aerospace, marine,
telecom and computer applications. The converters’ small size (1" x 1" x 0.45"),
full 5 Watt output capability and low cost give system architects unprecedented
design and layout flexibility.
Occupying less than 0.5in
total volume, these extremely compact, fully regulated
and isolated (1000Vdc) modules are available with ±5, ±12 or ±15 Volt outputs.
Input voltage ranges are either 18-36 Volts ("D24" models) or 36-72 Volts ("D48"
models).
Although their overall size is 50-75% smaller than many similarly rated power
modules, these 1" x 1" BWR Models are exact, drop-in, pin-for-pin replacements for
many standard 2" x 1" and 2" x 2", 5 Watt modules. They achieve their small size
and low cost by exploiting a novel feedback approach that does not depend upon
traditional optocoupler techniques.
All models are 5-side shielded and have a non-conductive baseplate that permits
pc-card runs to be placed beneath the package. Units are assembled using
high-speed automated SMT techniques and are fully encapsulated with thermally
conductive potting compound. Every unit is electrically tested before and after
encapsulation, 100% burned-in under full load, hi-pot tested, and final-electrical
tested prior to shipment. Every unit meets DATEL’s traditional high standards for
quality and long-term reliability.
+V
IN
PWM
+V
OUT
(3)
COMMON
(4)
–V
OUT
(6)
–V
IN
(2)
* "D24" models only
Figure 1. Simplified Schematic
DATEL, Inc., 11 Cabot Boulevard, Mansfield, MA 02048 (U.S.A.)
Tel: (508)339-3000, (800)233-2765 Fax: (508)339-6356
Email: datellit@mcimail.com
XWR Series
M I N I AT U R E , 5 WAT T D C / D C C O N V E R T E R S
Performance Specifications and Ordering Guide
Output
Model
BWR-5/500-D24
BWR-5/500-D48
BWR-12/210-D24
BWR-12/210-D48
BWR-15/165-D24
BWR-15/165-D48
➀
➁
➂
➃
➀
Input
Regulation (Max.)
Line
±2%
±2%
±2%
±2%
±2%
±2%
OUT
(Volts)
±5
±5
±12
±12
±15
±15
OUT
(mA, Max.)
±500
±500
±210
±210
±165
±165
R/N (mVp-p)
➁
Typ.
Load
➂
±2%
±2%
±2%
±2%
±2%
±2%
IN
Nom.
(Volts)
24
48
24
24
24
24
Range
(Volts)
18-36
36-72
18-36
18-36
18-36
18-36
IN
➃
(mA, Max.)
25/282
25/141
25/264
25/133
25/260
25/130
Efficiency
Min.
75%
75%
80%
80%
80%
80%
Typ.
78%
78%
82%
82%
83%
82%
Package
(Case,
Pinout)
C7, P4
C7, P4
C7, P4
C7, P4
C7, P4
C7, P4
Typical at T
= +25°C under nominal line voltage and full-load conditions unless otherwise noted.
Ripple/Noise (R/N) measured over a 20MHz bandwidth.
Balanced loads, 20% to 100% load.
Nominal line voltage, no-load/full-load conditions.
P A R T
N U M B E R
S T R U C T U R E
M E C H A N I C A L
S P E C I F I C A T I O N S
B WR
D24
Output Configuration:
= Bipolar
Wide Range Input
Input Voltage Range:
D24
= 18-36 Volts (24V nominal)
D48
= 36-72 Volts (48V nominal)
0.45
(11.43)
Case C7
1.00
(25.40)
METAL CASE
INSULATED BASE
Nominal Output Voltages:
±5, ±12 or ±15 Volts
Maximum Output Current
in mA from each output
0.20 MIN
(5.08)
0.040 ±0.002 DIA.
(1.016 ±0.051)
0.800
(20.32)
0.10
(2.54)
0.100
(2.54)
(10.16)
1.00
(20.32) (25.40)
TEMPERATURE DERATING
(5.08)
BOTTOM VIEW
0.200
(5.08)
0.10
(2.54)
DIMENSIONS ARE IN INCHES (MM)
Output Power (Watts)
3.5
–25
90
95
I/O Connections
Pin Function P4
+Input
–Input
+Output
Common
No Pin
–Output
Notes:
For "D24" models, the case
is connected to pin 2 (–V
IN
For "D48" models, the case
is connected to pin 1 (+V
IN
Ambient Temperature (°C)
BWR Models
Performance/Functional Specifications
Typical @ T
= +25°C under nominal line voltage and full-load conditions, unless noted.
➀
Input
"D24" Models
"D48" Models
Input Current
Input Filter Type
➁
Reverse-Polarity Protection
OUT
Accuracy
(50% load):
±5V Outputs
±12/±15V Outputs
Temperature Coefficient
Ripple/Noise
(20MHz BW)
➁
Line Regulation
Load Regulation
Efficiency
Isolation Voltage
➂
Current Limiting
Overvoltage Protection
Transient Response (50% load step)
Switching Frequency
(ambient):
➃
Without Derating
With Derating
Storage Temperature
Dimensions
Shielding
Case Connection:
"D24" Models
"D48" Models
Case Material
Pin Material
Weight
See Ordering Guide
LC on "D24" models
C on "D48" models
Yes (Instantaneous, 6A maximum)
Input Voltage:
"D24" Models
"D48" Models
Absolute Maximum Ratings
44 Volts
88 Volts
Current must be <6A. Brief
duration only. Fusing recommended.
6.8 Volts, limited duration
15 Volts, limited duration
18 Volts, limited duration
Current limited. Max. current and
short-circuit duration are model
dependent.
–55 to +125°C
+300°C
Input Reverse-Polarity Protection
Output Overvoltage Protection
±5V Outputs
±12V Outputs
±15V Outputs
Output Current
Output
±1.5%, maximum
±1%, maximum
±0.02% per °C
See Ordering Guide
See Ordering Guide
See Ordering Guide
See Ordering Guide
1000Vdc, minimum
Auto-recovery
Zener/transorb clamps
Storage Temperature
Lead Temperature
(soldering, 10 sec.)
These are stress ratings. Exposure of devices to any of these conditions may adversely
affect long-term reliability. Proper operation under conditions other than those listed in the
Performance/Functional Specifications Table is not implied.
TECHNICAL NOTES
Dynamic Characteristics
500µsec max. to ±1.5% of final value
170kHz (±10kHz)
Environmental
–25 to +60°C
to +95°C (See Derating Curve)
–55 to +125°C
Floating Outputs
Since these are isolated DC/DC converters, their outputs are "floating." Any
BWR model may be configured to produce an output of 10V, 24V or 30V
(for ±5V, ±12V or ±15V models, respectively) by applying the load across
the +Output and –Output (pins 3 and 6), with either output grounded. The
Common (pin 4) should be left open. Minimum 20% loading is recommended
under these conditions.
Filtering and Noise Reduction
All BWR 5 Watt DC/DC Converters achieve their rated ripple and noise
specifications without the use of external input/output capacitors. In critical
applications, input/output ripple and noise may be further reduced by install-
ing low-ESR, tantalum or electrolytic capacitors across the input
and/or output terminals. Output capacitors should be connected between
their respective output pin (pin 3 or 6) and Common (pin 4) as shown in
Figure 2. The capacitors should be located as close to the power converters
as possible. Typical values are listed below. In many applications, using
values greater than those listed will yield better results.
To Reduce Input Ripple
"D24" Models
"D48" Models
To Reduce Output Ripple
±5V Outputs
±12/15V Outputs
20µF, 50V
10µF, 100V
47µF, 10V, Low ESR
33µF, 20V, Low ESR
Physical
1" x 1" x 0.45" (25.4 x 25.4 x 11.4mm)
5-sided
Pin 2 (–V
IN
Pin 1 (+V
IN
Corrosion resistant steel with
epoxy-based enamel finish
Brass, solder coated
0.7 ounces (20 grams)
➀
These power converters require a minimum 20% loading to maintain specified regulation.
Operation under no-load conditions will not damage these devices, however they may not
meet all listed specifications.
➁
Application-specific internal input/output filtering can be recommended and perhaps added
internally on request. Contact DATEL Applications Engineering for details.
➂
Units can be screened or modified for higher guaranteed isolation voltages.
➃
Units can be screened for lower-temperature operation.
In critical, space-sensitive applications, DATEL may be able to tailor the
internal input/output filtering of these units to meet your specific require-
ments. Contact our Applications Engineering Group for additional details.
XWR Series
Typical Performance Curves
(T
= +25°C)
The performance curves below were derived from actual test data for a single model number (BWR-15/165-D24).
Since all devices in this series have the same circuit topology, the performance curves are representative of all devices.
E F F I C I E N C Y V S . I N P U T VO LTAG E A N D O U T P U T L OA D
Efficiency vs. Input Voltage
(Full-load conditions. Guaranteed efficiency = 80%
at V
IN
= 48V
85
84
Efficiency (%)
83
82
81
36
42
48
54
72
Efficiency (%)
84
82
76
74
72
Efficiency vs. Output Load
(V
IN
= nominal = 48V. Guaranteed efficiency at full load = 80%)
33
66
99
Output Currents (±mA)
132
165
Input Voltage (Volts)
L OA D R E G U L AT I O N
Output Voltage vs. Load (Balanced)
(V
IN
= nominal = 48V. Nominal V
OUT
span = 30V)
30.3
Output Voltage Span (Volts)
30.2
30.1
30.0
29.9
29.8
29.7
55
65
75
85
95
105 115 125 135 145 155 165
Output Voltage (±Volts)
15.20
15.15
15.10
15.05
15.00
14.95
14.90
14.85
14.80
Output Voltage vs. Load (Unbalanced)
(V
IN
= nominal = 24V. Load on +V
OUT
fixed at 165mA)
+V
OUT
–V
OUT
75
95
115
135
155
175
–V
OUT
Output Current (mA)
L I N E R E G U L AT I O N
Output Voltage vs. Input Voltage
(Full-load conditions. Nominal V
OUT
span = 30V)
30.3
30.2
30.1
30.0
29.9
29.8
29.7
36
48
52
56
68
72
BWR Models
E M I R A D I AT E D E M I S S I O N S
+OUTPUT
+INPUT
IN
–INPUT
COMMON
OUT
OUT
–OUTPUT
If you’re designing with EMC in mind, please note that all of DATEL’s BWR 5
Watt DC/DC Converters have been characterized for radiated and conducted
emissions in our new EMI/EMC laboratory. Testing is conducted in an
EMCO 5305 GTEM test cell utilizing EMCO automated EMC test software.
Radiated emissions are tested to the limits of FCC Part 15, Class B and
CISPR 22 (EN 55022) Class B. Correlation to other specifications can
be supplied upon request. Radiated emissions plots to FCC and CISPR 22
appear below. Its performance is typical of all models in the Family.
Published EMC test reports are available for each model number. Contact
DATEL’s Applications Engineering Department for details.
Radiated Emissions
FCC Part 15 Class B, 3 Meters
Converter Output = ±15Vdc @ ±132mA
Figure 2. Using External Capacitors to Reduce
Input/Output Ripple/Noise
Radiated Emissions (dBµV/M)
FCC Class B Limit
Input Fusing
Certain applications and/or safety agencies may require the installation of
fuses at the inputs of power conversion components. For DATEL BWR
5 Watt DC/DC Converters, you should use slow-blow type fuses with values
no greater than 0.5A.
Radiated Emissions
C U S T O M
C A P A B I L I T I E S
–10
–20
DATEL’s world-class design, development and manufacturing team stands
ready to work with you to deliver the exact power converter you need for
your demanding, large volume, OEM applications. And . . . we’ll do it on
time and within budget!
Our experienced applications and design staffs; quick-turn prototype capa-
bility; highly automated, SMT assembly facilities; and in-line SPC quality-
control techniques combine to give us the unique ability to design and
deliver any quantity of power converters to the highest standards of quality
and reliability.
We have compiled a large library of DC/DC designs that are currently used
in a variety of telecom, medical, computer, railway, aerospace and industrial
applications. We may already have the converter you need.
Contact us. Our goal is to provide you the highest-quality, most cost-effective
power converters available.
Frequency (MHz)
Radiated Emissions
EN 55022 Class B, 10 Meters
EN 55022 Class B Limit
Radiated Emissions
–10
–20
Frequency (MHz)
ISO-9001 REGISTERED
DS0318
5/02
DATEL, Inc. 11 Cabot Boulevard, Mansfield, MA 02048-1151
Tel: (508) 339-3000 (800) 233-2765 Fax: (508) 339-6356
Internet: www.datel.com
Email: sales@datel.com
Data Sheet Fax Back: (508) 261-2857
DATEL (UK) LTD. Tadley, England Tel: (01256)-880444
DATEL S.A.R.L. Montigny Le Bretonneux, France Tel: 01-34-60-01-01
DATEL GmbH München, Germany Tel: 89-544334-0
DATEL KK Tokyo, Japan Tel: 3-3779-1031, Osaka Tel: 6-6354-2025
DATEL makes no representation that the use of its products in the circuits described herein, or the use of other technical information contained herein, will not infringe upon existing or future patent rights. The descriptions contained herein do
not imply the granting of licenses to make, use, or sell equipment constructed in accordance therewith. Specifications are subject to change without notice. The DATEL logo is a registered DATEL, Inc. trademark.