AC-DC
400 Watts
SMM Series
xppower.com
Industrial, IT & Medical Approvals
Low Profile for 1U Applications
Optional Current Share & AC Fail
Output Voltages from 3.3 V to 54 V
Enclosed with Internal Fan & U-Channel Versions
Class B Conducted Emissions
Optional Molex Connectors
Specification
Input
Input Voltage
Input Frequency
Input Current
Inrush Current
90-264 VAC (120-370 VDC)
47-63 Hz
6.35 A at 90 VAC, full load
35 A peak max (cold start at 240 VAC
& full load)
Meets EN61000-3-2
<300 µA max at 264 VAC/60 Hz
Shut down when 75 VAC <Vin <85 VAC
& turns on when Vin >86 VAC
Internal 8 A fuse in line and neutral
General
Efficiency
• 3.3 & 5.0 V single output: 70% min,
All other single output: 80% min, Dual
outputs: 75% min at 230 VAC, full load
• 4000 VAC Input to Output, 1500 VAC Input
to Ground, 250 VDC Output to Ground
• 25 kHz for PWM stage,
60 kHz for PFC stage
• 6.25 W/In
based on unit without cover/fan
• Current Share, Power Good, Current
Monitor & optional AC Fail (see note 5 -
available on single output models only)
• 140 kHrs at +25 °C per MIL-HDBK-217F
Isolation
Switching Frequency
Power Density
Signals
Power Factor
Earth Leakage Current
UVLO
Input Protection
Output
Output Voltage
Output Voltage Trim
Initial Set Accuracy
Minimum Load
Start Up Delay
Hold Up Time
Line Regulation
Load Regulation
Over/Undershoot
Transient Response
Ripple & Noise
Overvoltage Protection
Overtemperature
Protection
Overload Protection
Short Circuit Protection
Remote Sense
Remote On/Off
Current Share
Fan Drive
3.3 to 54 VDC - see tables
±5% on V1, adjustable by user
Within 1% of stated output voltage
Single output: 1%, Dual output (V1): 10%
2 s max at 120 VAC
20 ms min at 80% full load
0.5%
±1% (single outputs),
±3% V1, ±7% V2 (dual outputs)
Not to exceed 5% of nominal voltage
5% max deviation, recovery to within 1%
in 500 µs for a 50% load change
<1% of nominal output voltage
>130% Vnom, recycle input to reset
Shuts down at +85 °C, measured internally
with auto recovery
110-140%
Constant current, auto recovery
Compensates for up to 0.5 V drop
(not available with current share)
MTBF
Environmental
• -0 °C to +70 °C, derate linearly from
+50 °C to+ 70 °C at 2.5%/°C
Cooling
• Minimum 23 CFM airflow required for
maximum power output. ‘-C’ version has
built-in fan, others require 23 CFM air flow
to meet fan-cooled ratings
Operating Humidity
• 5-90% RH, non-condensing
Storage Temperature
• -20 °C to +85 °C
Vibration
• 5-50 Hz, acceleration 2 g, 3 minute
sweep, 60 mins in 3 axes
Shock
• 15 g 11 ms 1/2 sine wave, 3 times in 6
axes
Bump
• 15 g 6 ms 1/2 sine 4000 bumps in 3 axes
EMC & Safety
Emissions
Harmonic Currents
ESD Immunity
Radiated Immunity
EFT/Burst
Surge
Conducted Immunity
Dips & Interruptions
EN55011/22 Level B conducted & radiated
EN61000-3-2
EN61000-4-2, level 3 Perf Criteria A
EN61000-4-3, 3 V/m Perf Criteria A
EN61000-4-4, level 2 Perf Criteria A
EN61000-4-5, level 3 Perf Criteria A
EN61000-4-6, 3 V, Perf Criteria A
EN61000-4-11 70% U
for 10 ms,
40% U
for 100 ms, <5% U
for 5000 ms
Perf Crit A, B, B (Perf Crit A, A, B with
85% load)
• UL60601-1, EN60601-1, EN60950-1:2001,
UL60950, CSA C22.2 No. 60950-1-03,
CSA C22.2 No. 601.1-M90
• On = TTL Logic High or Open
Off = TTL Logic Low or Short
• Option ‘-I’ available on single output
models only - see note 4
• 12 V at 500 mA
Safety Approvals
AC-DC
Models and Ratings
Output
5.0
12.0
15.0
18.0
24.0
27.0
36.0
48.0
54.0
3.3 V/12.0
3.3 V/24.0
5.0 V/12.0
5.0 V/24.0
12.0 V/24.0
Total
Output Power
198 W
300 W
400 W
400 W
400 W
400 W
400 W
400 W
400 W
400 W
300 W
300 W
300 W
300 W
400 W
Maximum Output Current
V1
60.00
60.00
33.34
26.60
22.20
16.70
14.80
11.10
8.30
7.40
40.00
40.00
40.00
40.00
25.00
V2
SMM-C
Model
Number
(2,3,4,5)
SMM400PS03-C
SMM400PS05-C
SMM400PS12-C
SMM400PS15-C
SMM400PS18-C
SMM400PS24-C
SMM400PS27-C
SMM400PS36-C
SMM400PS48-C
SMM400PS54-C
SMM400PD21-C
SMM400PD22-C
SMM400PD23-C
SMM400PD24-C
SMM400PD25-C
25.00
12.50
25.00
12.50
12.50
1. Other output voltages available. Contact sales.
2. Standard input is screw terminal. For optional IEC320 input and on/off switch, add suffix ‘-D’ to model number.
3. Standard output is screw terminal. For optional Molex output connector, add suffix ‘-G’ to model number.
4. For current share option, add suffix ‘-I’ to model number (remote sense not available). This option also adds internal block diodes.
5. For AC fail option, add suffix ‘-L’ to model number (single output only). UVLO function is disabled. Output is low when input is <80 VAC, high (5 V) if input is >86 VAC.
6. When ordering place option suffixes in alphabetical order, e.g. SMM400PS24-CDI.
Available from Farnell. See pages 204-206.
Mechanical Details
All dimensions in inches (mm).
Weight: 2.20 lbs (1.0 kg).
Max Screw Penetration: 0.15 (3.81) on bottom, 0.25 (6.35) on sides.
0.80 (20.3)
1.25 (31.8)
Single
Dual
1.50 (38.1)
STANDARD
‘-D’ OPTION
FAN
4.00 (101.6)
5.00 (127.0)
0.50 (12.7)
0.88 (22.2)
3.25 (82.6)
‘-G’
OPTION
VO -
VO -
‘-G’
OPTION
V2
V2
RTN
FAN
RS+
RS-
REM ON/OFF
PG
RTN
AC Inlet
RS+
RS-
REM ON/OFF
PG
ACF*
RTN
CSH
CMN
RTN
VO +
VO +
1.60 (40.6)
1.60 (40.6)
TERMINAL BLOCK
M3 SCREW
3PINS 8.25mm CENTER
Mating Connectors
Signal Connector (Single): JST XHP-9
Signal Connector (Dual): JST XHP-5
Fan Connector: JST XHP-2
Crimp Terminals: SXH-002-P0.6
‘-G’ Optional Output: Molex No. 09-91-1600
Crimps: Molex Series 6838
L N
V1
V1
7.01 (177.8)
1.25 (31.8)
TERMINAL BLOCK
M3.5 SCREW 6PINS
9.5mm CENTER
TERMINAL BLOCK
M3.5 SCREW 6PINS
9.5mm CENTER
1.50 (38.1)
7.01 (177.8)
0.80 (20.3)
AC-DC
Models and Ratings
Output Voltage
Range
5.0
12.0
15.0
18.0
24.0
27.0
36.0
48.0
54.0
V/12.0
V/24.0
V/12.0
V/24.0
V/24.0
Total Output Power
Convection
148.5 W
225.0 W
250.0 W
250.0 W
250.0 W
250.0 W
250.0 W
250.0 W
250.0 W
250.0 W
200.0 W
200.0 W
200.0 W
200.0 W
250.0 W
Fan-Cooled
198 W
300 W
400 W
400 W
400 W
400 W
400 W
400 W
400 W
400 W
300 W
300 W
300 W
300 W
400 W
Output 1
Output 2
Convection
Fan-Cooled
Convection
Fan-Cooled
45.00 A
60.00 A
45.00 A
60.00 A
20.80 A
33.34 A
16.60 A
26.60 A
13.90 A
22.20 A
10.40 A
16.70 A
9.20 A
14.80 A
6.90 A
11.10 A
5.20 A
8.30 A
4.60 A
7.40 A
30.00 A
40.00 A
16.70 A
25.00 A
30.00 A
40.00 A
8.30 A
12.50 A
30.00 A
40.00 A
16.70 A
25.00 A
30.00 A
40.00 A
8.30 A
12.50 A
16.70 A
25.00 A
8.30 A
12.50 A
SMM
Model
Number
(2,3,4,5,6)
SMM400PS03
SMM400PS05
SMM400PS12
SMM400PS15
SMM400PS18
SMM400PS24
SMM400PS27
SMM400PS36
SMM400PS48
SMM400PS54
SMM400PD21
SMM400PD22
SMM400PD23
SMM400PD24
SMM400PD25
5.0
5.0
12.0
2. For optional solid cover, add suffix ‘-A’ to the model number (external dimensions remain the same).
3. Standard input is screw terminal. For optional Molex input connector, add suffix ‘-F’ to model number.
4. Standard output is screw terminal. For optional Molex output connector, add suffix ‘-G’ to model number.
5. For current share option, add suffix ‘-I’ to model number (remote sense not available). This option also adds internal block diodes.
6. For AC fail option, add suffix ‘-L’ to model number (single output only). UVLO function is disabled. Output is low when input is <80 VAC, high (5 V) if input is >86 VAC.
7. When ordering place option suffixes in alphabetical order, e.g. SMM400PS24-GI.
Mechanical Details
0.80
1.25 (20.3)
(31.8)
Single
Dual
7.00 (177.8)
0.50
(12.7)
0.50
(12.7)
FAN
RS+
RS-
REM ON/OFF
PG
ACF*
RTN
CSH
CMN
‘-G’
OPTION
VO -
VO -
‘-G’
OPTION
V2
V2
5.00 ±0.012
(127.0 ±0.3)
4.00
(101.6)
‘-F’ OPTION
RTN
FAN
RS+
RS-
REM ON/OFF
PG
RTN
RTN
VO +
VO +
3.25
(82.6)
V1
V1
C:M O U
TERMINAL BLOCK
M3.5 SCREW 6PINS
9.5mm CENTER
TERMINAL BLOCK
M3.5 SCREW 6PINS
9.5mm CENTER
8.00 (203.2)
Mounting holes B: 6-32
Mounting holes C: M4
1.60
(40.6) 1.25
(31.8) 0.80
(20.3)
Mating Connectors
‘-F’ optional input: Molex No. 09-91-0700
‘-G’ optional output: Molex No. 09-91-1600
AC-DC
Application Notes
Remote On/Off
Current Monitor
SMM
Single Output Only
ON/OFF
CN3 Pin 3, control connector
CMN
CN3 Pin 8, control connector
PSU
Return
CN3 Pin 6, control connector (single output)
CN3 Pin 5, control connector (dual output)
PSU
Return
1. Applying <0.3 V or short between
pins 5(6) and 3 turns the output OFF.
2. Applying >4.5 V or open circuit between
pins 5(6) and 3 turns output ON.
1. 0.5 V to 3.0 V represents 0% to 100% full load.
Remote Sense
CD
CN3 Pin 1 Sense
Optional AC Fail
Single Output Only
Output
+12 V
1K
CL
AC Fail
LOAD
Twisted Pair
Supply
CN3 Pin 2 Sense
CD
Output
5V
Return
1. CL is 47 µF electrolytic capacitor.
2. CD is 0.1 µF ceramic capacitor.
Parallel Connection with Current Share Option
Single Output Only
Output
Supply 1
Return
CN3 Pin 7 Current Share
V1
AC GOOD
LOAD
Comm
Supply 2
Output
Return
AC FAIL
Current share option includes internal blocking diodes.
Power Good
Sink current = 250 mA
Source current = 7 mA
+5 V
1K
CN3 Pin 4, control connector
PG
POWER GOOD
Sink current = 5 mA
Source current = 1 mA
POWER NOT GOOD
Return
18-Dec-07