SM SERIES INPUT MODULES
• Plug into mounting boards for SM Series modules
• AC Inputs (Yellow Case) for 24 V, 120 V, 240 V
• DC Inputs (White Case) for 3.3 to 32 V, 10 to 48 V
• 4kV Optical isolation
• Open-collector Output
• Industry standard packaging
SPECIFICATIONS (1)
Input
Voltage Range
Maximum Current [mA](4)
Resistance [Ohms](2)(3)
Drop-out Current [mA](5)
Voltage for No Output [VAC/VDC](6)
Allowable Current [mA]
SM-IAC5
90-140 VAC/DC
28 k
SM- IAC5A
180-280 VAC/DC
75 k
SM- IAC24
90-140 VAC/DC
28 k
SM- IAC24A
180-280 VAC/DC
75 k
SM-IDC5
3.3-32 VDC/AC
34
Output
Maximum Voltage[VDC](9)
Maximum Voltage Drop [VDC](12)
Nominal Logic Supply Voltage [VDC]
Logic Supply Voltage Range [VDC]
Maximum Current [mA](10)
Maximum Logic Supply Current [mA](7)
Maximum Logic Supply Leakage Current [µA](8)
Maximum Leakage Current [µA](11)
Maximum Turn-On Time [msec] (13)
Maximum Turn-Off Time [msec] (13)
5.0
3.0-6.0
10.0
10.0
5.0
3.0-6.0
10.0
10.0
5.0
20-30
10.0
10.0
5.0
20-30
10.0
10.0
5.0
3.0-6.0
10.0
10.0
SPECIFICATIONS (1)
Input
Voltage Range
SM-IDC24
3.3-32 VDC/AC
34
1k
SM-IDC5F
4-32 V
68
SM-IDC24F
4-32 V
68
SM-IDC5N
10-48 VDC/AC
34
1k
SM-IDC24N
10-48 VDC/AC
34
1k
Output
5.0
3.0-6.0
10.0
10.0
5.0
3.0-6.0
10.0
10.0
0.05
0.10
5.0
20-30
10.0
10.0
0.05
0.10
5.0
3.0-6.0
10.0
10.0
8.0
7.0
5.0
20-30
10.0
10.0
8.0
7.0
For Contact information visit our web
site.
www.crydom.com
©2008 Crydom, Inc.
Specifications subject to change without notice.
GENERAL SPECIFICATIONS
Input/Output Isolation Voltage (14)
Input/Output Capacitance
Storage Temperature Range
Line Frequency Range
Weight
4000
-30 to 80°C
-40 to 80°C
47 to 63
1.1 oz. (31.2g)
GENERAL NOTES:
(2)
(3)
(4)
(5)
Specifications apply to an ambient temperature of -30 t o 80 °C unl ess otherwise noted.
Resistance v alues for I AC modules are effectiv e impedance v alues at 25 °C.
Resistance v alues are +/-10% at 25 °C.
Measured at maximum s pecif ied input voltage, 25°C.
Defined as the maximum current allowed through the module's input to guarantee that
the output will switc h from "on" to "off". Higher c urrents may result in the out put remaining
in the "on" s tate.
Defined as the maximum current allowed through the module's input that will not s witch
the module's output state f rom "off: t o "on".
With ext ernal LED status indicator at maximum specified logic supply vol tage and 25°C.
18mA without external LED.
At maximum specif ied logic voltage and 25°C.
Applied acros s open collector output trans istor.
Sinking c urrent through the open c ollector output transistor.
At maximum output voltage and 25°C.
At maximum output current and 25°C .
At nominal logic supply voltage, 25mA output sinking current, nominal input vol tage
and 25°C
At 25°C for 1 second maxi mum duration.
(6)
(7)
(8)
(9)
(10)
(11)
(12)
(13)
(14)
MECHANICAL SPECIFICATIONS
AGENCY APPROVALS
UL E46203
CSA 38595
Rev. 072808
site.
www.crydom.com
©2008 Crydom, Inc.
site.
www.crydom.com
©2008 Crydom, Inc.
ANNEX - ENVIROMENTAL INFORMATION
site.
www.crydom.com
©2008 Crydom, Inc.