CMP350 SERIES
Quad output
10 x 5 inch footprint with 1.75 inch low profile
EN61000-3-2 compliant
Current sharing
Individually protected outputs
Power fail signals
350W with 300LFM
EN55022, EN55011 conducted emissions level B
UL, VDE and CSA safety approvals
[ 2 YEAR WARRANTY ]
The CMP350 series is a 350W universal input AC/DC power supply in a 10 x 5 x
1.75 inch package. The series has the lowest standard 350W profile in the
industry, input harmonic current emission correction as standard, current sharing
and has 3.3V models to support the industry's transition from 5V to lower
operating voltages. The CMP350 provides 350W of output power with 300LFM of
forced air. Standard features include isolated outputs with individual overvoltage
and overload protection on each output. The series has an enclosure with end-
mounted fans option that does not change the overall height. The series, with full
international safety approval and the CE mark, meets conducted emissions
EN55022 level B and has immunity compliance to EN61000-4-2,-3,-4, -5, -6. The
CMP350 series is designed for use in medium power data networking, computer
and telecom applications such as hubs, routers, file servers, graphic workstations
and mass storage peripherals. It is also suitable for industrial, test and office
applications.
SPECIFICATION
OUTPUT SPECIFICATIONS
Output accuracy
Total regulation
(Line and load)
Transient response
All specifications are typical at nominal input, full load at 25°C unless otherwise stated
EMC CHARACTERISTICS
±1.0%
Conducted emissions
Radiated emissions
Harmonic current
emission correction
ESD air
ESD contact
Surge
Fast transients
Radiated immunity
Conducted immunity
EN55022, FCC part 15
EN61000-3-2
EN61000-4-2
EN61000-4-2
EN61000-4-5
EN61000-4-4
EN61000-4-3
EN61000-4-6
Level B
Level A
Compliant
Level
Level
Level
Level
Level
Level
Main and auxiliary V1 output
Auxiliary output (V2)
Auxiliary output (V3)
Main output
25% step load
change at 1A/µs
±1.0%
±6.0%
±5.0%
2.0% max. dev.,
500µs recovery
±0.02%/°C
Temperature coefficient
Ripple and noise
(See Note 3)
Overvoltage protection
Short circuit protection
Overload protection
Thermal protection
Current sharing
Main output and
Aux. 1 (5V and 3V3)
0Hz to 20MHz
Latching
All channels
All channels
50mV pk-pk
or 1.0%
See table
Continuous,
auto recovery
Yes
GENERAL SPECIFICATIONS
Hold-up time
Efficiency
Isolation voltage
Input/output
Input/chassis
Output/output
110VAC, 60Hz, 350W
16ms
75% typical
3000VAC
1500VAC
50VDC
150kHz
EN60950, VDE0805, UL1950,
CSA C22.2 No. 950
2.0kg (4.4Ibs)
Open frame
Enclosed
10.0 x 5 x 1.75 inches
10.5 x 5 x 1.75 inches
212,707 hours
959,870 hours
Switching frequency
Auto shutdown,
auto recovery
±10% of rating
Approvals and
standards
Weight
(See Note C)
MTBF
INPUT SPECIFICATIONS
Input voltage range
Input frequency range
Input surge voltage
Inrush current
Safety ground
leakage current
Input current
Input fuse
Power factor
110VAC, 350W
UL, IEC approved
110/220VAC full load
300VAC
264VAC, cold start
Universal
90 to 264VAC
(30s brown-out at 85VAC)
47Hz to 63Hz
20ms
75A max.
0.72mA
4.2Arms max.
6.3A 250V
0.97 min.
MIL-HDBK-217F
Bellcore TR-NWT-332
ENVIRONMENTAL SPECIFICATIONS
Thermal performance
Operating ambient, FL
0°C to +50°C
Cooling
300LFM airflow required
+50°C to +70°C, Derate to 50% load
ambient
on all channels
Non-operating
-40°C to +85°C
Non-condensing
Operating
Non-operating
5% to 95% RH
10,000 feet max.
30,000 feet max.
2.4G rms peak
Relative humidity
Altitude
Vibration (See Note 15) 5Hz to 500Hz
PAGE 62
LOW TO MEDIUM POWER AC/DC POWER SUPPLIES
350W AC/DC
350 Watt
AC/DC high wattage power supplies with PFC
OUTPUT
VOLTAGE
5V
3.3V
12V
12V
5V
12V
12V
5V
(2)
(2)
(2)
(2)
(2)
(2)
OUTPUT
TYPE
Main
Aux 1
Aux 2
Aux 3
Main
Aux 1
Aux 2
Aux 3
Main
OUTPUT CURRENT
RIPPLE
MIN
0A
1.0A
1.0A
0.5A
0A
1.0A
0.5A
0.5A
0A
1.0A
0.5A
0.2A
0A
0.8A
0.4A
0.2A
0A
1.0A
0.5A
0.3A
0A
1.0A
0.5A
0.5A
0A
1.0A
1.0A
5.0A
(3)
TOTAL
REGULATION
OVP
THRESHOLD
5.75 to 6.75V
4.15 to 4.35V
13.2 to 14.5V
12.6 to 15.2V
(4)
ADJUST
RANGE
+10, -5%
+20, -5%
±5%
(6)
MODEL
NUMBERS
(A)
(8)
MAX
(2)
50A
20A
10A
5.0A
(8)
(8)
(8)
50mV
50mV
120mV
120mV
50mV
120mV
120mV
50mV
50mV
120mV
120mV
240mV
50mV
150mV
150mV
240mV
50mV
120mV
120mV
120mV
50mV
50mV
120mV
120mV
240mV
50mV
120mV
120mV
±1.0%
±1.0%
±1.0%
±5.0%
±1.0%
±1.0%
±5.0%
±1.0%
±1.0%
±1.0%
±5.0%
±1.0%
±1.0%
±1.0%
±5.0%
±1.0%
±1.0%
±1.0%
±5.0%
±1.0%
±1.0%
±1.0%
±1.0%
±5.0%
±1.0%
±1.0%
±1.0%
±5.0%
CMP350-9604
CMP350-9601
CMP350-9602
50A
10A
5.0A
5.0A
50A
10A
5.0A
2.0A
50A
8.0A
4.0A
2.0A
50A
10A
5.0A
3.0A
50A
15A
5.0A
5.0A
(9)
(9)
(9)
5.75 to 6.75V
13.2 to 14.5V
12.6 to 15.2V
(4)
+10, -5%
±5%
(5)
(7)
5.75 to 6.75V
5.75 to 6.75V
13.2 to 14.5V
12.6 to 15.2V
(4)
5V
12V
12V
24V
5V
15V
15V
24V
5V
12V
12V
12V
(2)
(2)
(2)
(2)
(2)
(2)
(2)
(2)
(2)
+10, -5%
±5%
(5)
(7)
Aux 1
Aux 2
Aux 3
Main
Aux 1
Aux 2
Aux 3
Main
Aux 1
Aux 2
Aux 3
Main
Aux 1
Aux 2
Aux 3
Main
Aux 1
Aux 2
Aux 3
26.4 to 28.8V
5.75 to 6.75V
16.5 to 18.0V
15.7 to 19.0V
(4)
+10, -5%
±5%
(5)
(7)
CMP350-9606
26.4 to 28.8V
5.75 to 6.75V
13.2 to 14.5V
12.6 to 15.2V
(4)
+10, -5%
±5%
(5)
(7)
CMP350-9603
13.2 to 14.5V
4.15 to 4.35V
5.75 to 6.75V
13.2 to 14.5V
12.6 to 15.2V
(4)
3.3V
5V
12V
12V
(2)
(2)
(2)
+20, -5%
+10, -5%
±5%
(6)
CMP350-9692
(9)
24V
5V
12V
12V
10A
15A
10A
5.0A
26.4 to 28.8V
5.75 to 6.75V
13.2 to 14.5V
12.6 to 15.2V
(4)
±5%
+10, -5%
±5%
(6)
CMP350-9623
DERATING CURVE
(See Notes 10, 11)
Output Power (Watts)
350W
International Safety Standard Approvals
VDE0805/EN60950/IEC950 Licence No. 96709
UL1950 File No. E136005
CSA C22.2 No. 950 File No. LR41062C
20W
0W
300LFM
FORCED AIR
COOLING
175W
20W MINIMUM LOAD REQUIRED TO MAINTAIN
REGULATION
C 10
http://www.artesyn.com
PAGE 63
350W AC/DC
350 Watt
TB1
VMAIN +
VMAIN -
J1
TOP VIEW
TB2
Notes:
There are three external accessible connectors in the unit besides the main
Busbar. The first one is designated as TB1 which is the input power
connector.
USER INTERFACE PIN (J1)
PIN NO. REFERENCE
J1-3
12CH1
J1-4
12CH2
(B)
Pin assignment (TB1)
Input connector TB1 is a standard
screw type terminal block. An IEC
type connector is provided on
enclosed models (suffix ‘CF’).
Main output connector
Main output Busbar connector
VMAIN+ and VMAIN-.
PIN CONNECTIONS
Input connector TB1
PIN NO.
TB1-1
TB1-2
TB1-3
FUNCTION
Live
Ground
Neutral
PIN CONNECTIONS
Output Busbar connector
PIN NO.
VMAIN+
VMAIN-
FUNCTION
Positive
Negative
FUNCTION
12V Bias Refd. to Main Ch. -ve
12V Bias Refd. to Aux. Ch. #1 -ve,
(-9601, -9602, -9603, -9606)
12V Bias Refd. to Aux. Ch. #2 -ve,
(-9604, -9692)
Main Ch. Positive Remote Sense
(See Note 14)
Ground Refd. to Aux. Ch. #1 -ve,
Ground Refd. to Aux. Ch. #2 -ve,
(-9604, -9692)
J1-5
J1-6 *
J1-7
VSENMAIN+
AUX1SET
GND2
Auxiliary output pin assignment (TB2)
TB2 auxiliary output connector is used on models -9601, -9602, -9603, -9606.
PIN NO.
TB2-1
TB2-2
TB2-3
TB2-4
TB2-5
TB2-6
TB2-7
TB2-8
PIN CONNECTIONS (TB2)
REFERENCE
FUNCTION
AUX CH. 1
Positive
AUX CH. 1
AUX CH. 1
AUX CH. 1
AUX CH. 2
AUX CH. 2
AUX CH. 3
AUX CH. 3
Positive
Negative
Negative
Positive
Negative
Positive
Negative
J1-8
J1-9
J1-10
J1-12
J1A-1 *
J1A-2 *
J1A-3 *
J1A-6 *
J1A-7 *
J1A-8
J1A-9
J1A-10
J1A-11
J1A-12
POK
(13)
GND1
PFD
(13)
Power Good Detect Signal
Ground Refd. to Main Ch. -ve
Power Fail Detect Signal
VSENMAIN-
Main Ch. Negative Remote Sense
VAUXSEN- Auxiliary Channel Negative Remote Sense
VAUXSEN+ Auxiliary Channel Positive Remote Sense
GND3
CSAUX
(12)
TRIMAUX2
CSMAIN
(12)
INHIBIT-
INHIBIT+
TRIMAUX
TRIMAIN
Ground Refd. to Aux. Ch. 1 +ve for
-9604 and -9692 models
Auxiliary Channel Current Share Pin
Tim Pin for 5V or 3.3V Auxiliary Channel
Main Channel Current Share Pin
Inhibit Signal Return
Inhibit Signal
Trim Pin for 12V or 15V Auxiliary Channel
Main Channel Trim Pin
Auxiliary output pin assignment (TB2 and TB3)
TB2 and TB3 auxiliary output connectors are used on models -9604 and
-9692. See page 66 for detail.
PIN NO.
TB2-1
TB2-2
TB2-3
TB2-4
TB2-5
TB2-6
TB3-1
TB3-2
PIN CONNECTIONS (TB2 AND TB3)
REFERENCE
FUNCTION
AUX CH. 2
AUX CH. 2
AUX CH. 2
AUX CH. 2
AUX CH. 3
AUX CH. 3
AUX CH. 1
AUX CH. 1
Positive
Positive
Negative
Negative
Positive
Negative
Positive
Negative
* Applies to -9604, -9692 models only.
PAGE 64
350W AC/DC
350 Watt
Current share
(See Note 12)
Power OK
(See Note 13)
Remote-sense
System inhibit
Power fail detect
(See Note 13)
Forced
Asserted Low
0.4V
Asserted high
Asserted low
Main output and
auxiliary 1 if 5V or 3.3V
Main output >75%
Main output and
Inhibits all outputs
Indicates loss of AC
4ms warning
15A
The unit must be powered up into the recommended minimum loads to
ensure the outputs come up.
Combined maximum output power for Aux. 1, 2 and 3 is 220W.
For models -9604 and -9692, on the aux 1 channel, output ripple and
noise is measured 6 inches down the output cables through a 1 foot long
twisted pair terminated with a parallel combination of a 10µF electrolytic
and a 0.1µF ceramic capacitors. For all other channels on all models,
ripple and noise is measured directly at the output terminals.
No shutdown or latch-up occurs; voltage is internally limited to specified
range.
Aux. 2 tracks Aux. 3, Aux. 4 not adjustable.
Aux. 3 tracks Aux. 2.
Output is not adjustable.
CMP350-9604 rated operation:
Graph 1
8A
10A
AC INPUT
10A
Sum of 12V
Channel
Loads*
5A
RATED
OPERATION
OUTPUT
0A
5A
PFD SIGNAL
POWER GOOD SIGNAL
10A
15A
20A
3.3 V Channel Load
t1
t2
* Max. load for AUX2 is 10A
Max load for AUX3 is 5A
t1 Varies with line and load
t2
4ms
t1 + t2
20ms
The auxiliary channels must share power as indicated by graph 1.
The maximum output power is 220W.
CMP350-9692 rated operation:
Graph 2
15A
8A
EXTERNAL OUTPUT TRIMMING
Main channel trim connections
12CH1
(14)
10A
Sum of 12V
Channel
Loads*
10A
TRIM
UP/DOWN
TRIMAIN
TRIM
DOWN
GND1
TRIM
UP
RATED
OPERATION
5A
0A
5A
10A
15A
5V Channel Load
Aux. 1 channel trim connections. (-9601, -9602, -9603, 9606)
Aux. 2 channel trim connections (-9604, -9692)
12CH2
TRIM
UP/DOWN
TRIMAUX
TRIM
DOWN
GND2
TRIM
UP
The auxiliary channels must share power as indicated by graph 2.
A minimum of 300LFM of forced air cooling is required for proper
operation of the CMP350.
All outputs must be derated linearly from maximum specified loads during
operation above 50
C.
Current share is a single wire share circuit that allows the main output on
multiple CMP350 units to be operated in parallel. Auxiliary channels share
on -9604 and -9692 models by connecting the CSAUX channel.
The power fail detect and power OK signals are open-collector outputs
which will sink 40mA or less in the low state and should be pulled up to a
bias voltage with an appropriately sized resistor.
VOL
IOL
VOH
Min.
0V
0A
4V
0.4V
-40mA
40V
Aux. 1 channel trim connections (-9604, -9692)
AUX1SET
GND3
TRIM
UP/DOWN
TRIMAUX2
TRIMAUX2
The system inhibit and output inhibit signals require a current source to be
asserted high.
Min.
VIH
3.5V
15.0V
IIH
0mA
-10mA
14 Connection from TRIMAUX2 to AUX1SET causes the output for Ch. aux. 1
on models -9604 and -9692 to regulate at its nominal factory set voltage.
15 3 orthogonal axes, random vibration, 10 minute test per axes.
16 This product is only for inclusion by professional installers within other
equipment and must not be operated as a stand alone product.
TRIMAUX2 is connected to
AUX1SET by a factory fitted
jumper to ensure CH. 1
regulates at the nominal
set voltage
To trim CH1, remove the
jumper and connect a resistor
between GND3
and TRIMAUX2
PAGE 65
350W AC/DC
350 Watt
Mechanical notes
A A standard cover and fan assembly can be added during manufacturing.
To order, add suffix 'CF' to the model number. e.g.
CMP350-9601CF.
B Visual arrangement for J1 as seen from the front (output) side of the unit.
C The dimensions of the CMP350-9604 and CMP350-9692 are slightly larger
than shown below. The open frame dimensions are 10.2 x 5 x 1.75 inches
and the enclosed dimensions are 10.7 x 5 x 1.75 inches.
2.250
(57.15)
6.500
(165.1)
0.870
(22.098)
Third Angle
Projection
0.164-32-UNC-2B (6 Places)
(2 On Side, 4 On Bottom)
3/16" (4.76) Max. Thread Penetration - Typ.
9.90
(251.46)
AC Input
Terminal
Block
0.410
(10.414)
1.75
(44.45)
1/4 - 20 UNC Thread
Output Studs
HI
LO
TB1
J1
3.900
(99.06)
TB2
(127.00)
0.125 REF.
(3.175)
(57.150)
6.500
(165.100)
10.000
(254.000)
0.400
(10.160)
See Mechanical Note C
ALL DIMENSIONS IN INCHES (mm)
Tolerances unless otherwise specified
.xx =
0.02
.xxx =
0.010
Mating connectors
(J1) mating connector type
Molex P/N 22-55-2241 or equivalent with Molex
P/N 70058 or equivalent crimp terminals.
J1-1
J1A-12
Detail:
VMAIN +
VMAIN -
J1
Input connector
IEC for all enclosed models (suffix ‘-CF’).
3-way 0.375 inch pitch terminal block for
uncovered models.
Output connectors
(TB2) connector type
For models -9601, -9602, -9603 and -9606
8-way 0.197 inch pitch terminal.
J1-12
J1A-1
TB3
TB2
6-way 0.197 inch pitch terminal block.
(TB3) connector type
For models -9604 and -9692.
2-way 0.375 inch pitch terminal block.
User Interface Connector J1 View
Vertical mount 2 row, 24 position
TB2 is a 6 way connector on models -
9604 and -9692 as shown above.
DS_CMP350_20000101.PDF
Data Sheet © Artesyn Technologies® 2000
The information and specifications contained in this data sheet are believed to be correct at time of publication. However, Artesyn Technologies accepts no responsibility for consequences arising
from printing errors or inaccuracies. Specifications are subject to change without notice. No rights under any patent accompany the sale of any such product(s) or information contained herein.
PAGE 66