7100 Series
The Gamewell-FCI 7100 Series fire alarm control panel is a
multi processor-based, analog addressable system. The
control panel is a compact, yet expandable, platform.
Intended for commercial, industrial and institutional instal-
lations, the 7100 Series is ideal for life safety and property
protection fire alarm applications.
The basic 7100 Series control panel provides one (1) or
two (2), analog addressable Signaling Line Circuits (SLCs).
Each SLC supports up to ninety-eight (98) analog address-
able sensors, as well as up to ninety-nine (99) addressable
monitor modules and/or control points. With 197 addresses
available on the 7100-1 and 394 addresses available on
the 7100-2. The 7100 uses an advanced protocol that
ensures an almost instant response to events while at the
same time suppressing nuisance alarms.
The system may be programmed with either the
Windows
-based Field Configuration Program (FCP-7100)
or configured through a comprehensive set of intuitive,
secure password protected front-panel programming
options. This important feature allows the system to quickly
adapt to any future requirements due to changes in occu-
pancies, building remodels, or other contingencies.
The sophisticated circuitry and powerful analog software
enables the 7100 Series fire alarm control panel to read the
specific sensitivity level of each sensor and compensate for
changes due to age, dust accumulation or other environ-
mental factors. The 7100 incorporates the Gamewell-FCI
Listed Integrated Sensitivity Testing (LIST) which meets
NFPA 72 sensitivity testing and maintenance requirements.
The LIST testing allows substantial savings in both mainte-
nance and service while eliminating nuisance alarms.
The Model 7100-1D and 2D features an integral Digital
Alarm Communicator Transmitter (DACT) with all popular
transmission formats and a 16-digit telephone number
field. It is 8-digit Carrier Information Code (CIC) compliant
and also prevents “dialer-runaway” in the event of intermit-
tent system faults. The 7100-1D and 2D are UL Listed for
Microsoft Word is a registered trademark of Microsoft Corporation.
Compact Analog Addressable
Fire Alarm Control Panel
7100 Series
• Listed per ANSI/UL 864 9th Edition
• 120 or 240 VAC (optional) input line voltage
• Front panel programming with day/night sensitivity
adjustments
• 80-character alpha-numeric display
• One or two Style 4 (Class “B”) signaling line circuits.
Style 6 (Class “A”) with optional CAOM Module
• Two Style Y (Class “B”) regulated notification appliance
circuits rated for 1.5 amp. each. Style Z (Class “A”) with
• Suitable for pre-action deluge applications with optional
MCOM Module
• Periodic trouble reminder
• Individual sensor drift compensation
• Dual-stage maintenance alerts (“dirty” and “very dirty”)
• Multilevel sensor sensitivity adjustments (front panel
programmable)
continued on the next page
An ISO 9000-2000 Company
SIGNALING
FM
APPROVED
MEA
S1869 3003549
Approved
7165-0694:219 (7100)
307-99-E
7300-0694:231 (LCD-7100)
307-99-E Vol. II
7300-0694:241 (LDM-7100)
Specifications are for information only, are not intended for installation purposes, and are subject to change without notice. No responsibility is assumed by Gamewell-FCI for their use.
www.gamewell-fci.com
9020-0466 Rev. E2 page 1 of 3
©2008 by Honeywell International Inc. All rights reserved.
12 Clintonville Road, Northford, CT 06472-1610 USA • Tel: (203) 484-7161 • Fax: (203) 484-7118
GAMEWELL-FCI
Description (Continued)
Remote Station, Proprietary, and Central Station fire alarm
systems. It allows ample space for wiring and room for bat-
teries up to 7 A/H capacity.
LDM-7100
Features (Continued)
• Alarm verification per individual sensor
• Positive alarm sequence for sensors or monitor
modules
• Four levels of system access using six (6), digit pass-
words with up to five (5), user passwords per Level
• Duplicate and extra address indications
• March time (60 or 120 BPM)/temporal pattern/coded
fours/California Code/user-defined zone coding
• Cross zoning
• System configuration programming and 280 event log
stored in non-volatile memory
• Fan restart with sequential restart delay
• Upload/download of panel configuration between panel
and FCP-7100 program (password protected feature)
• Up to sixty-four (64), 7100 panels in the E3 Broadband
network with an optional INI-7100 Module
The LED Driver Module (LDM-7100) is designed to mount
in a UL Listed remote annunciator and provides outputs for
remote panel switches and thirty-three (33), remote LEDs.
Three (3), LDM-7100 modules may be installed in a single
annunciator for a total of ninety-nine (99), LEDs per annun-
ciator. This combination may be repeated up to five times
for a total of fifteen (15), LDM-7100 panels installed at up to
five (5), different locations. Maximum distances of up to
4,000 feet (1,219 m) can be achieved using one pair of
twisted, non-shielded wire for serial communication and
using another pair of straight-lay wire for operating voltage.
(For additional information, refer to the LDM-7100 data
sheet, Part Number: 9020-0519).
CAOM
The Class “A” Optional Module (CAOM) allows Style Y and
Z (Class “B” and “A”) operation for both Notification Appli-
ance Circuits and allows Style 4 and 6 (Class “B” and “A”)
for both Signaling Line Circuits. It also provides disconnect
switches for each signaling line circuit and a common dis-
connect switch for both notification appliance circuits.
MCOM
Optional Accessories
LCD-7100
The LCD-7100 remote serial display offers an 80-character
alphanumeric readout for the remote display of all system
events. It duplicates all the information on the 7100 Series
panel display and provides key switch protected functions
such as System Reset, Alarm Acknowledge, Trouble
Acknowledge, Signal Silence, and Drill Test.
LEDs on the LCD-7100 indicate Alarm, Supervisory, Sys-
tem Trouble, Power Fault, Systems Silenced, NAC#1, and
NAC#2 Silenced conditions.
The LCD-7100 can be surface or semi-flush mounted on a
standard four-gang electrical box. It can be installed up to
4,000 feet (1,219 m) from the main control panel. The 7100
Series fire alarm control panel supports up to five (5),
remote LCD-7100 annunciators using one pair of twisted,
non-shielded 18 AWG min. wire or serial communication
and uses another pair of 16 AWG min. for operating volt-
age.
(For additional information, refer to the LCD-7100 data
sheet, Part Number: 9020-0486).
The Municipal Connection Option Module (MCOM) pro-
vides three (3) choices of outputs. It can be configured as a
Municipal Circuit (City Box) output. It may also be set to
serve as a Reverse Polarity output with a nominal voltage
output of 24 VDC at 0.012 amp. maximum alarm and
supervisory current. The MCOM’s third option provides a
releasing solenoid output rated at:
• 24 VDC nominal voltage.
• 0.005 amp. supervisory current.
• 0.710 amp. maximum alarm current.
• 2 ohms maximum line resistance.
PTRM
The Printer Transient Module (PTRM) provides RS-232
Isolator/Transient protection for the 7100’s RS-232 port
(BSM connector J2). It is used in conjunction with a serial
printer applied to the RS-232 port for permanent record
keeping.
INI-7100
The Intelligent Network Interface Module allows the 7100
Series fire alarm control panel to become the platform of a
peer-to-peer, token ring, self-regenerative network com-
prised of up to sixty-four (64), 7100 panels.
9020-0466 Rev. E2 page 2 of 3
GAMEWELL-FCI
Primary Input Power
120 VAC, 50/60 Hz @ 2.0 amps.
or 240 VAC, 50/60 Hz @ 1.0 amp.
Output Power
4 amps. @ 24 VDC (total)
Non-resettable Power:
1.0 amp. max.
1.0 amp. max. from both circuits
Resettable Power:
1.0 amp. max.
Two (2) Notification
1.5 amp. each @ 24 VDC
Appliance Circuits:
Current:
Supervisory
Alarm
7100-1 (One SLC)
0.065 amp.
0.085
amp.
7100-1D
0.085 amp.
0.105
amp.
(One SLC w/DACT)
7100-2 (Two SLC)
0.065 amp.
0.085
amp.
7100-2D
0.105
amp.
(Two SLC w/DACT)
0.085 amp.
LCD-7100
.012 amp.
.023
amp.
LDM-7100
.012 amp.
.023
amp.
(All LEDs lit)
INI-7100-UTP,-FO
0.040 amp.
0.040
amp.
Operating
32° - 120° F (0° - 49° C)
Temperature:
Relative Humidity:
85 % (non-condensing)
Battery Charger
Capacity:
31 A/H (Cabinet accommodates
12 A/H size batteries)
Alarm & Trouble
Relay Contacts:
Form “C”, 2 amps. @ 24 VDC
(resistive)
Ordering Information
(Continued)
Optional Modules
LCD-7100
Dimensions:
LDM-7100
Dimensions:
CAOM
Remote Serial Annunciator, LCD
Display (80-character)
4.25” H x 8.25” W x 1.90”
(43 H x 37 W x 7.7 D cm)
Remote LED Driver Module
6” W x 4.50”
(15.2 x 11.4 cm)
Class A Option Combination Module
with disconnect switches for both
signaling line circuits and notification
appliance circuits
for local energy city box reverse polar-
ity signaling, or releasing solenoid
Intelligent Network Interface Module,
Fiber-Optic
Unshielded, Twisted-Pair
Transformer, 120 VAC input
(replace-
ment)
Transformer, 240 VAC input
(replace-
ment)
Replacement board for 7100-1
Replacement board for 7100-1D
MCOM
PTRM
INI-7100-FO
INI-7100-UTP
Replacement Parts
T-7100
T-7100-240
BSM-7100-1
BSM-7100-1D
Systems
Model
7100-1
Dimensions:
7100-1D
Dimensions:
7100 Addressable System, 1 SLC
mounted in enclosure
19 3/8” x 19 3/8”
(49 x 49 cm)
Enclosure
7100 Addressable FACP w/DACT,
1 SLC mounted in enclosure
19 3/8” x 19 3/8”
(49 x 49 cm)
Enclosure
Basic Kits
BK-7100-2
Basic System Kit, 2 SLC
(BSM, Keypad Display, Transformer)
BK-7100-2D
Basic System Kit w/DACT, 2 SLC
BK-7100-2-240V
Basic System Kit, 2 SLC, 240 VAC
BK-7100-2D-240V
Cabinets
EN-7100
CS-7100M
7100-ENCL-M
Dimensions:
NS-7100B
NS-7100R
Dimensions:
Enclosure (replacement)
Metal Door (replacement)
7100 Enclosure
16.9” H x 14.4” W x 3” D l
Enclosure, E3 Series Broadband,
black Enclosure,
E3 Series Broadband, red
19 3/8” H x 19 3/8” W x 4” D
(49 H x 49 W x 10 D cm)
GAMEWELL-FCI
9020-0466 Rev. E2 page 3 of 3