AC-DC
250 Watts
JPS250 Series
xppower.com
200 W with Convection Cooling
High Efficiency - up to 88%
Meets 1U, Low Profile Requirements
AC OK & DC OK Signals
Zero Voltage Switching Technology
Remote On/Off & Remote Sense
Current Share
Specification
Input
Input Voltage
Input Frequency
Input Current
Inrush Current
Power Factor
Earth Leakage Current
Input Protection
90-264 VAC (170-370 VDC)
47-63 Hz
2.75 A/1.40 A max at 115 VAC/230 VAC
30 A at 115 VAC, 60 A at 230 VAC
0.99 typical
2.0 mA max 264 VAC/60 Hz
Internal 5 A, 250 V fuse
General
Efficiency
Isolation
• Up to 88%
• 3000 VAC Input to Output
1500 VAC Input to Ground
500 VAC Output to Ground
• 120 kHz typical for PFC and PWM
• 4.96 W/In
• AC OK, DC OK, Remote On/Off
(see control and supervisory signals)
• 255 kHrs per MIL-HDBK-217F at +25 °C
Switching Frequency
Power Density
Signals
MTBF
Output
• See tables
• ±10% on output 1 only
• At 60% rated load ±1% on V1 & V2,
±5% on V3 & V4
Minimum Load
• Single output models: No minimum load
required. Multi-output models, see note 4
Start Up Delay
• 2 s typical
Start Up Rise Time
• 80 ms typical
Hold Up Time
• 20 ms min at low line & rated load
Line Regulation
• ±0.5% at rated load across input
voltage range
Load Regulation
• ±1% for single output models & V1 & V2
of multi-output models, ±5% for V3 & V4
Transient Response
• 4% max deviation, recovery to within
1% in 500 µs for a 25% load change
Ripple & Noise
• ±1% max pk-pk, 20 MHz BW
Overvoltage Protection
• 115-140% on single outputs & V1 of quad
output models, recycle input to reset
Overtemperature
• Shuts down at +110 °C, auto recovery
Protection
measured internally
Overload Protection
• 110-130% of max rated load on all O/Ps,
trip & restart (Hiccup mode), auto recovery
Short Circuit Protection
• Trip and restart (Hiccup mode)
Temperature
• ±0.05%/°C
Coefficient
Remote Sense
• Compensates for up to 0.5 V drop
Remote On/Off
Current Share
• On = Logic Low or Open, Off = Logic High
• Single wire current sharing on single
output models & V1 & V2 of multi-output
models (4 supplies can be paralleled)
• 5 V model: 5 V at 390 mA,
24 V model: 24 V at 80 mA,
all other models: 12 V at 112 mA
Output Voltage
Output Voltage Trim
Initial Set Accuracy
Environmental
• 0 °C to +70 °C, (see derating curve)
Full power to +50 °C
• 250 W with 18 CFM airflow
Cooling
200 W convection cooling
Operating Humidity
• 5-95% RH, non-condensing
Storage Temperature
• -20 °C to +85 °C
Operating Altitude
• 3000 m
Vibration
• 2 g, 10 Hz to 55 Hz,
3 mins/cycle for 30 mins each axis
EMC & Safety
Emissions
Harmonic Currents
Voltage Flicker
ESD Immunity
Radiated Immunity
EFT/Burst
Surge
Safety Approvals
• EN55022, level B conducted
FCC 20780, level B conducted
• EN61000-3-2
• EN61000-3-3
• EN61000-4-2, level 3 Perf Criteria A
• EN61000-4-3, 10 V/m Perf Criteria A
• EN61000-4-4, level 3 Perf Criteria A
• EN61000-4-5, level 3 Perf Criteria A
• EN60950-1:2001, UL60950-1,
CSA C22.2 No. 60950-1-03,
CE Mark LVD
Fan Output
AC-DC
Models and Ratings
Output
Power
225 W
Output
5V
12 V
15 V
24 V
48 V
Output Current
Convection-cooled
18 CFM
36.0 A
45.0 A
17.0 A
21.0 A
13.5 A
17.0 A
8.5 A
10.4 A
4.3 A
5.2 A
JPS250 - Single Output
Ripple & Noise
Pk-Pk
50 mV
120 mV
120 mV
200 mV
200 mV
Efficiency
83%
86%
87%
88%
88%
Model
Number
(2)
JPS250PS05C
JPS250PS12C
JPS250PS15C
JPS250PS24C
JPS250PS48C
250 W
1. Maximum power with 18 CFM forced air is 250 W, or 200 W with convection cooling.
2. For non-current share version delete suffix ‘C’ from model number.
Available from Farnell. See pages 204-206.
Available from Newark. See pages 207-208.
Mechanical Details
All dimensions are in inches (mm)
Tolerance:
± 0.03 (0.8) max
Weight:
1.65 lbs (750 g) approx.
All models (except JPS250PS05)
8.00 (203.2)
TB1
3.75
(95.3)
TRANSFORMER
TB2
TB3
TB4
Pin
PIN CONNECTIONS
TB2
JPS250PS05 All other models
+5 V
+5 V
0V
0V
0V
0V
+5 V
+5 V
+V
+V
+V
0V
0V
0V
TB4
All models
Signal 0 V
DC OK
AC OK
Remote On/Off
+Sense
-Sense
Current Share
(6)
N/C
N/C
N/C
4.20
(106.7)
(38.3)
5.50 (139.0)
6.50 (165.1)
0.30
(7.6)
(19.1)
0.36
(9.1)
JPS250PS05
8.00 (203.2)
(95.3)
TB1
TB2
TRANSFORMER
TB3
(106.7)
TB4
Notes:
1. TB3 is for fan, with Molex 5045-02A or equivalent.
2. TB1 (AC input) and TB2 (DC output) are terminal blocks.
3. TB4 signal connector is Molex 70246-10 or equivalent.
4. Maximum mounting screw penetration is 0.16 (4.0) from chassis
outer surface.
5. Fan/Cover option available, order part number:
5 V models: JPS250 F/CVR 5
12, 15 & 48 V models: JPS250 F/CVR
24 V models: JPS250 F/CVR 24
Or add suffix ‘-E’ to model number to receive unit with cover fitted.
6. For current share operation connect signal 0 V (pin 1) between
units and current share (pin 7) between units. For non ‘C’ models
pin 7 (single wire parallel) is not used.
Fixing Holes:
A = #6-32 screw mounting holes
B = M3 x 0.5 screw mounting holes
0.70 (19.1)
5.50 (139.0)
6.50 (165.1)
Application Notes
Derating Curve
A 60
D 50
%) 30
JPS250PS with 18 CFM Fan
JPS250PS Convection-cooled
Signals
1. To turn off the output, apply 5 V to the remote On/Off.
2. AC OK is a TTL signal which goes LOW when input falls below
60 VAC at rated load.
3. DC OK is a TTL signal which goes LOW when PSU is in an
overcurrent condition, overvoltage condition, disabled or when
output falls out of regulation.
4. For AC OK and DC OK signals, source current is 1 mA, sink
current is 6 mA.
Ambient Temperature (˚C)
AC-DC
Models and Ratings
Output 1
Output
Conv.
V1
Cooled 18 CFM
3.3 V
16.0 A
20 A
5.0 V
17.5 A
30 A
5.0 V
20.0 A
25 A
5.0 V
20.0 A
25 A
Output 2
Output
Conv.
V2
Cooled 18 CFM
5V
12 A
20 A
12 V
7A
8A
12 V
4A
6A
15 V
3A
5A
JPS250 - Multi Output
Output 3
Output
Conv.
V3
Cooled 18 CFM
12 V
5A
6A
-12 V
2A
3A
24 V
2A
3A
24 V
2A
3A
Output
V4
-12 V
-5 V
-12 V
-15 V
Output 4
Conv.
Cooled 18 CFM
1A
2A
1A
2A
1A
2A
1A
2A
Model
Number
(2,3)
JPS250PQ46
JPS250PQ41
JPS250PQ47
JPS250PQ48
2. For current share option add suffix ‘C’ to model number.
3. Current share models are built to order.
4. All models require 2 A minimum load on V1. On V2, JPS250PQ46 requires 1 A and JPS250PQ41 requires 0.5 A.
Mechanical Details
All dimensions are in inches (mm).
Tolerance:
± 0.03 (0.8) max.
Weight:
PIN CONNECTIONS - TB2
PQ46
PQ47
+3.3 V +S
+5 V -S
+3.3 V PS
(6)
DC OK
+5 V +S
+3.3 V -S
+5 V PS
(6)
Remote On/Off
AC OK
0V
+5 V +S
+5 V PS
(6)
+12 V +S
DC OK
+12 V -S
+5 V -S
+12 V PS
(6)
Remote On/Off
AC OK
0V
8.00 (203.2)
Pin
PQ41
+5 V +S
+5 V PS
(6)
+12 V +S
DC OK
+12 V -S
+5 V -S
+12 V PS
(6)
Remote On/Off
AC OK
0V
PQ48
+5 V +S
+5 V PS
(6)
+15 V +S
DC OK
+15 V -S
+5 V -S
+15 V PS
(6)
Remote On/Off
AC OK
0V
TB1
TRANSFORMER
TB3
TB2
(106.7)
TB5
(7.6)
(19.1)
0.36
(9.1)
0.16 (4.0)
(33.1) (38.1)
Pin
PQ41
+5 V
+5 V
0V
0V
0V
-5 V
-12 V
+12 V
PIN CONNECTIONS - TB3
PQ46
PQ47
+12 V
-12 V
+5 V
+5 V
0V
0V
0V
0V
+3.3 V
+3.3 V
+5 V
+5 V
0V
0V
0V
-12 V
+24 V
+12 V
PQ48
+5 V
+5 V
0V
0V
0V
-15 V
+24 V
+15 V
8.00 (203.2)
(95.3)
1.30 (32.1)
0.70
(19.1)
(5.7)
5.50 (139.0)
6.50 (165.1)
Fixing Holes:
Notes:
1. TB5 is for fan with Molex 5045-02A or equivalent.
2. TB1 (AC input) and TB3 (DC output) are terminal blocks.
3. TB2 signal connector is Molex 70246-10 or equivalent.
outer surface.
PQ41, PQ46 & PQ47: JPS250 F/CVR
PQ48: JPS250 F/CVR 24
or add suffix ‘-E’ to model number to receive unit with cover fitted.
6. PS - Single wire parallel on ‘C’ models only.
No connection on standard models.
Application Notes
Derating Curve
A 60
D 50
(%) 30
JPS250PQ with 18 CFM Fan
JPS250PQ Convection-cooled
Signals
current is 6 mA.
AC-DC
Control & Supervisory Signals
AC OK Signal
+5 V
330 R
AC OK (HIGH)
JPS250
DC OK Signal
+5 V
330 R
DC OK (HIGH)
AC OK
DC OK
AC NOT OK (LOW)
DC NOT OK (LOW)
Remote On/Off Control (Inhibit)
Parallel Connection Utilizing Optional Current Share
Supply 1
Output
Return
OUTPUTS OFF (5V)
Remote On/Off
Single Wire Parallel
V1
LOAD
Comm
Ground
OUTPUTS ON (0 V or open circuit)
Supply 2
Output
Return
Remote Sense Connection
Output
CD
Sense
Twisted Pair
LOAD
CL
Supply
Sense
CD
Output
Notes:
1. CD is 0.1 µF ceramic capacitor.
2. CL i s 47 µF electrolytic capacitor.
JPS250 Fan/Cover Option
See mechanical details notes for information on how to order.
Typical internal clearance
0.15 (3.8)
2.48 (62.9)
1.70 (43.2)
4 x M3 x 6 C/S head fixing screws
in existing countersunk holes
04-June-07