Embedded Power for
Business-Critical Continuity
NFS40 Series
SIngle and
triple output
Rev.12.12.08_118
NFS40 Series
1 of 4
Total Power:
40 - 50W
Input Voltage:
85 - 264VAC
120 - 370VDC
# of Outputs:
Single, triple
Electrical Specifications
Special Features
• 5.0 x 3.0 x 1.2 inch package
(1U applications)
• Industry standard package
• Overvoltage and
short circuit protection
• 40 W with free air convection
• 50 W with 20 CFM forced air
• EN55022, EN55011
conducted noise level A
• UL, VDE and CSA
safety approvals
• Available RoHS compliant
• 2 year warranty
Input
Voltage adjustability:
Line regulation:
LL to HL, FL
Load regulation:
FL to NL
Transient response:
Temperature coefficient:
Overvoltage protection:
Output power limit:
Short circuit protection:
+5 V output on triples
Vout on singles
Main output
Auxiliary outputs
Main output
Auxiliary outputs
+5 V (1.5 - 3 A)
All outputs
+5 V output
Primary power limited
Single outputs
Multiple outputs
Universal input
±5.0%
±5.0%
±0.2%
±1.0%
±2.0%
±5.0%
± 120 mV max. dev.
500 µs recovery
±0.02%/°C
S3.15 A, 250 Vac In live and neutral
90 W input power limit
Continuous
Short term
85-264 Vac
120-370 Vdc
47-440 Hz
132 Vac, cold start
264 Vac, cold star
110 Vac, 60 Hz
230 Vac, 50 Hz
12 A max.
24 A max.
0.13 mA, max.
0.32 mA, max.
Output
Input voltage range:
Input frequency range:
Safety
• VDE0805/EN60950/
• IEC950/IEC1010
• File No. 10401-3336-0044
• License No. 2559
• UL1950 File No. E136005
• CSA C22.2 No. 950
• File No. LR41062C
Max. input surge current:
Safety ground leakage current:
Embedded Power for
All specifications are typical at nominal input, full load at 25
C unless otherwise stated
Rev.12.12.08_118
NFS40 Series
2 of 4
EMC Charateristics
(11, 12)
Conducted emissions:
Radiated emissions:
ESD air:
ESD contact:
Surge:
Fast transients:
Radiated immunity:
Conducted immunity:
EN55022, FCC part 15
EN55022
EN61000-4-2, level 3
EN61000-4-2, level 4
EN61000-4-4, level 3
EN61000-4-3, level 3
EN61000-4-6, level 3
110 Vac, 40 W
230 Vac, 40 W
Input/output
Input/chassis
Variable
Level B
Level A
Perf. criteria 1
Perf. criteria 1
Perf. criteria 1
Perf. criteria 1
Perf. criteria 2
Perf. criteria 2
14 ms
110 ms
70% typical
3000 Vac
1500 Vac
General Specifications
Hold-up time:
Efficiency:
Isolation voltage:
Switching frequency:
Approvals and standards: (see VDE0805, EN60950, IEC950, IEC1010,
Notes 9, 13)
UL1950, CSA C22.2 No. 950
Weight:
280 g (9.88 oz)
MTBF demonstrated:
MIL-HDBK-217E
170,000 hours
Environmental Specifications
Thermal performance:
(See notes 8, 10)
Operating
Non-operating
50 °C ambient temp.,
convection cooled
Forced air cooling
+50 °C to +70 °C ambient
Peak (60 seconds)
Relative humidity:
Altitude:
Vibration (See Note 11):
Non-condensing
Operating
Non-operating
5-500 Hz
0° C to +70 °C
-40 °C to +85 °C
40 W
50 W @ 20 CFM
Derate linearly to 50% load
60W
5 to 80% RH
10,000 feet max.
40,000 feet max.
2.4 G rms peak
Embedded Power for
Ordering Information
Output
+5.1 V (A)
+12 V (B)
–12 V (C)
+5.1 V (A)
+12 V (B)
-12 V (C)
+5.1 V (A)
+12 V (B)
-5.0 V (C)
+5.1 V (A)
+15 V (B)
–15 V (C)
3.3 V
+5.1 V
+12.0 V
+15.0 V
+24.0 V
Output Currents
3A
2A
0.35 A
4A
0.35 A
0.35 A
3A
2A
0.35 A
3A
2A
0.35 A
6A
6A
3.3 A
2.6 A
1.6 A
Peak
(2)
7A
3A
1A
7A
1A
1A
7A
3A
1A
7A
2.5 A
1A
12 A
12 A
5A
4A
2.5 A
Fan
(3)
5A
2A
0.5 A
5A
0.5 A
0.5 A
5A
2A
0.5 A
5A
2A
0.5 A
8A
8A
4A
3.3 A
2A
Ripple
(4)
50 mV
120 mV
120 mV
50 mV
120 mV
120 mV
50 mV
120 mV
50 mV
50 mV
150 mV
150 mV
100 mV
100 mV
120 mV
150 mV
240 mV
Total
Regulation
(5)
±2.0%
±5.0%
±5.0%
±2.0%
±5.0%
+5.0%
±2.0%
±5.0%
±5.0%
±2.0%
±10.0%/-3.0%
±5.0%
±2.0%
±2.0%
±2.0%
±2.0%
±2.0%
Model Numbers
(13, 14, F)
NFS40-7608J
(5,6)
Rev.12.12.08_118
NFS40 Series
of 4
NFS40-7628J
(12)
NFS40-7607J
(5,6)
NFS40-7610J
(5,6)
NFS40-76S3J
NFS40-7605J
NFS40-7612J
NFS40-7615J
NFS40-7624J
Natural convection cooled, 40 W maximum.
Peak output current lasting less than 30 seconds with duty cycle less than 10%.
During peak loading, outputs may go outside of total regulation limits. Peak
total power must not exceed 60 W.
Forced air, 20 CFM at 1 atmosphere, 50 W maximum.
Figure is peak-to-peak. Output noise is measured across a 50 MHz bandwidth
using a 12 inch twisted pair, terminated with a 47 µF capacitor.
Total regulation is defined as the static output regulation at 25
C, including
initial tolerance, line voltage within stated limits, load currents within stated
limits, and output voltages adjusted to their factory settings. Also, 0.25<I(A)/
I(B)<5.0 to maintain stated regulation. This does not apply to the NFS40-7628J
power supply as it has regulated auxiliary outputs.
A minimum load of 0.5 A is required on the +5 V output to obtain full current
from the negative output.
The NFS40 offers the possibility of power sharing between outputs. Consult
factory for details.
Derating curve is application specific for ambient temperatures >50
C, for
optimum reliability no part of the heatsink should exceed 110
o
C and no
semiconductor case temperature should exceed 115
o
C.
A 4 W minimum load is recommended to achieve the design MTBF.
Caution: Allow a minimum of 1 second after disconnecting the power when
making thermal measurements.
Three orthogonal axes, sweep at 1 octave/minute, 5 minute dwell at four major
resonances.
The NFS40-7628J has separately linear regulated +12 V and -12 V outputs. The
loading conditions in Notes 5 and 6 do not apply.
This product is only for inclusion by professional installers within other
equipment and must not be operated as a stand alone product.
The ‘J’ suffix indicates that these parts are Pb-free (RoHS 6/6) compliant.
NOTICE: Some models do not support all options. Please contact your local
Emerson Network Power representative or use the on-line model number
search tool at http://www.powerconversion.com to find a suitable alternative.
Pin Connections
J1
Pin 1
Pin 2
J2
Pin 1
Pin 2
Pin 3
Pin 4
Pin 5
Pin 6
P1
(c)
Pin 1
DERATING CURVE
Output Power (Watts)
50W
20 CFM FORCED AIR COOLING
40W
-7608J, -7628J
AC Live
AC Neutral
+12 V
+5.1 V
+5.1 V
Return
Return
-12 V
-7607J
AC Live
AC Neutral
+12 V
+5.1 V
+5.1 V
Return
Return
-5 V
-7610J
AC Live
AC Neutral
+15 V
+5.1 V
+5.1 V
Return
Return
-15 V
SINGLES
AC Line
AC Neutral
+Vout
+Vout
+Vout
Return
Return
Return
Safety Ground
NATURAL
CONVECTION
COOLING
25W
20W
0C
10C
20C
30C
40C
50C
60C
70C
Embedded Power for
Mechanical Drawing
0.156 (3.96) Dia.
(4 Places)
5.00
(127.00)
Americas
5810 Van Allen Way
Carlsbad, CA 92008
USA
Telephone: +1 760 930 4600
Facsimile: +1 760 930 0698
Rev.12.12.08_118
NFS40 Series
4 of 4
NON-METALLIC
STAND-OFF
(SEE NOTE A)
C5
Q1
MAXIMUM
COMPONENT
HEIGHT 1.2 inches
Europe (UK)
J1
3.00
(76.2)
F1
F 3.15A, H 250VAC
P1 (SEE NOTE C)
T1
J2
2.550
(64.8)
Waterfront Business Park
Merry Hill, Dudley
West Midlands, DY5 1LX
United Kingdom
Telephone: +44 (0) 1384 842 211
Facsimile: +44 (0) 1384 843 355
Asia (HK)
0.22 (5.59)
4.55
(115.8)
14/F, Lu Plaza
2 Wing Yip Street
Kwun Tong, Kowloon
Hong Kong
Telephone: +852 2176 3333
Facsimile: +852 2176 3888
0.22
(5.59)
For global contact, visit:
techsupport.embeddedpower
@emerson.com
While every precaution has been taken to ensure
accuracy and completeness in this literature, Emerson
Network Power assumes no responsibility, and disclaims
all liability for damages resulting from use of this
information or for any errors or omissions.
ALL DIMENSIONS IN INCHES (mm)
Mechanical Notes
In order to meet safety requirements, a non-metallic stand-off is mandatory for one hole as specified in the mechanical
drawing above.
The ground pad of the mounting hole near P1 allows system grounding through a metal stand-off.
To improve conducted noise, the ground pad of the mounting hole near the output connector should be connected with
the ground pad of the mounting hole near P1. Use metal stand-offs attached to a common metal chassis. This connection
also significantly attenuates common mode noise.
A standard L-bracket and cover is available for mounting which contains all screws, connectors and necessary mounting
hardware. Order part number ‘NFS40 COVER KIT’.
Emerson Network Power.
The global leader in enabling
business-critical continuity.
AC Power
Connectivity
DC Power
Embedded Computing
Embedded Power
Monitoring
Outside Plant
Power Switching & Controls
Precision Cooling
Racks & Integrated Cabinets
Services
Surge Protection
EmersonNetworkPower.com
Emerson Network Power and the Emerson
Network Power logo are trademarks and
service marks of Emerson Electric Co.
©2008 Emerson Electric Co.