MDLA
产品描述MDL, MDLW Sync Modules for SpectrAlert Series
文件大小239KB,共4页
制造商Gamewell-FCI ( Honeywell )
官网地址http://www.gamewell-fci.com
下载文档 选型对比 全文预览
MDLA概述
The Sync•Circuit
TM
module
synchronizes SpectrAlert®
strobes at 1 Hz and horns
at temporal 3 over a single
pair of wires. Patented mod-
ule technology also allows
the silencing of horns on
horn/strobe models over a
single pair of wires.
Application Flexibility.
The Sync•Circuit
TM
module
is designed to power and
synchronize either two 3-
amp circuits wired in Class
B or one 3-amp circuit pow-
ered as Class A. Should
more than two zones require
synchronization, additional
modules can be added by
interconnecting the “slave”
input and output terminals
between modules.
Voltage range:
DC or full-wave-
rectified; 11 to 30 volts.
NOTE:
Supply voltage range at 12 volts, 11
to 17 VDC; at 24 volts, 21 to 30 VDC.
Maximum load on loop:
3 amps.
Current:
See table below.
Average
Current
(ma)
Peak
Current
(mA)
DC FWR DC FWR DC FWR
37 198 262
Operating temperature:
0°C to
49°C (32°F to 120°F).
Listings
Listings and approvals below apply to
the MDL(W) Sync Modules for
SpectrAlert® Series. In some cases,
certain modules may not be listed by
certain approval agencies, or listing
may be in process. Consult factory for
latest listing status.
UL Listed: files S5512, S4011.
ULC Listed: files CS548, CS549.
MEA approved: file 257-97-M.
FM approved.
CSFM approved:
file 7300-1209:179.
The MDL Module
Additional Capabilities.
The Sync•Circuit
TM
module is also designed to gener-
ate temporal 3 tone for System Sensor’s Multi-Alert
TM
and PA400 Mini-Alert
TM
sounders. Existing installations can be upgraded to comply with NFPA 72.
Module Configuration
Each MDL module has the capability of connecting two Style Y (Class B) cir-
cuits or one Style Z (Class A) circuit.
The NAC output(s) from the panel are connected to the zone inputs of the MDL
module and the zone output(s) from the MDL module are connected to the noti-
fication loop(s). Supervision is accomplished in the module by a direct connec-
tion between the zone input and the zone output of each of the two zone circuits
connected to the normal end-of-line device. The FACP “sees” the EOL device
through the MDL module. When either or both outputs (zones 1 & 2) from the
module are wired to the SpectrAlert products, the horns and strobes in both
zones will be synchronized.
The MDL module can be configured so that more than two zones can be syn-
chronized by the interconnection of the slave input and output
(see
Application
Examples).
Product Line Information
MDL
MDLA
Sync module for use with
SpectrAlert Series,
red.
SpectrAlert Series, red,
for Canada.
Same as above,
white.
MDLW
MDLWA
Same as above, white,
for Canada.
Special Considerations
NOTE:
The MDL Module is factory-set with the trouble contacts in the open
state. These contacts may close during shipping. Approximately two sec-
onds after power-up, these contacts will open.
MDL and MDLW Sync Modules
CS-2456
10/21/04
Page 1 of 4