FireForce 8
The FireForce 8 (FF8) from Gamewell-FCI is a Notification
Appliance Circuit (NAC) extender panel designed to extend
the power capabilities of existing NACs and provide power
(1.5 A) for other ancillary devices. The FF8 will connect to
any brand of a UL-Listed Fire Alarm Control Panel (FACP)
to provide Notification Appliance Circuit expansion.
Designed with advanced switch-mode power-supply tech-
nology, the FireForce 8 provides filtered and electronically-
regulated power distributed to four (4) NACs. Each NAC is
rated at 3.0 Amp. maximum, with a total output capacity of
8.0 Amp. The outputs may be configured as the following:
Four (4), Class B (Style W, X, Y)
Two (2), Class A (Style Z)
Two (2), Class B and one Class A
Four (4), Class A (Style Z) with the optional Class A
adaptor installed
The FF8 includes an internal battery charger.
Gamewell-FCI’s FF8 provides independent output circuit
supervision. In the event of a NAC fault, the FF8 can be
configured to notify the FACP. The FF8 has field-select-
able, built-in strobe and horn sync protocols. Protocols
support Faraday, Gentex, System Sensor, Amseco, and
Cooper-Wheelock devices; or pass through a pre-gener-
ated sync protocol from a single synchronization source.
This eliminates the need for additional individual sync mod-
ules. Independent horn silencing via sync protocol allows
synchronized horns and strobes to operate on a single cir-
cuit.
One of the most challenging aspects of a retrofit application
is locating the existing EOL resistor. In retrofit applications
that have EOL values other than the 3.9K ohm EOL resis-
tor normally used with the FF8, a single resistor matching
the existing EOL can be used as a reference EOL for all
outputs. This feature speeds installation and system check-
out. The reference resistor must be within a range of 2K
ohm to 25K ohm.
“FireForce 8” labeling is placed on the cabinet front, mak-
ing the FF8 ideal for all retrofit applications.
For enhanced notification appliance circuit survivability, the
FF8 can utilize its dual-activation inputs for redundant trip
operation.
NAC Expander/Power Supply
FireForce 8
Provides two fully-supervised input/control circuits
Redundant activation option for survivability
Multiple sync protocols, compatible with the following
appliances: Cooper-Wheelock, Faraday, System Sen-
sor, Amseco, and Gentex-as field-selectable options
Four (4) configurable supervised NAC outputs
8.0 Amp., 24 VDC, fully regulated full-load output
(power-limited)
Output fault notification to FACP
1.5 A auxiliary power output
Eight trouble and status LEDs
Common trouble Form-C relay
Isolated AC Fail Form-C relay, immediate or delayed
six hours
Ground fault detection
26 AH battery charger capability
Selectable temporal coding
Facilitates multiple NAC synchronization for large
areas
Optional multipack for up to four FF8s in a single lock-
able enclosure
Optional Class A adaptor
An ISO 9000-2000 Company
SIGNALING
MEA
Approve
d
S521
206-01-E 7300-1288:162
GAMEWELL-FCI
Specifications are for information only, are not intended for installation purposes, and are subject to change without notice. No responsibility is assumed by Gamewell-FCI for their use.
www.gamewell-fci.com
CS-2282 Rev. a page 1 of 2
©2007 by Honeywell International Inc. All rights reserved.
12 Clintonville Road, Northford, CT 06472-1610 USA • Tel: (203) 484-7161 • Fax: (203) 484-7118
Engineer’s Specifications
The Fire Alarm System shall be designed with remotely
located Notification Appliance Circuit (NAC) Expander/
Power Supplies for the support of notification appliances.
The remote Power Supplies shall be fully supervised and
shall provide 8.0 Amps. of notification appliance power and
1.5 Amps. of auxiliary power output. The NAC Extender
Panel shall be able to select strobe synchronization proto-
col via an internal dip switch. There shall be five selectable
protocols available. The NAC Extender Panel shall syn-
chronize all outputs simultaneously. The NAC Extender
Panel shall be able to use existing notification appliance
circuit’s end-of-line resistors in the range of 2K – 25K ohms
for retrofit applications. The internal battery charging circuit
shall charge up to 26 AH batteries. The NAC Expander/
Power Supply shall be a Gamewell-FCI FireForce 8.
Specifications (Continued)
Input Control Circuit:
Temperature Rating:
Relative Humidity:
Dimensions:
16 – 30 VDC @ 5 mA minimum
32°F to 120°F (0°C to 49°C)
10 - 93%, non-condensing
FF8 Cabinet:
18.0" H x 12.5" W x 4.5" D
(45.72 H x 31.75 W x 11.43 D cm)
FF8-MP Cabinet:
37.2" H x 24.0" W x 6.0" D
(94.49 H x 60.96 W x 15.24 D cm)
Field Selectable NAC Signaling
INPUT
Steady
Steady
Steady
Sync
OUTPUT (Follows Input)
Temporal
Steady - SYNC
Steady with Noise Eliminated
Sync
Options
31081
SCE-95 mounting plate provides a means to install two (2)
SCE-95 modules. The addition of SCE-95s provides a
means to run on FF8 outputs via a panel command on an
SLC. The 31081 mounts over the main PCB and is hinged
for access to FF8 terminal.
FF8-MP
Multipack FF8 option provides a means to place up to four
(4) FF8s or 31085s (XP95 device mounting plates) in a sin-
gle lockable enclosure. UL approved.
31076
Class A adaptor converts the four (4) Class B outputs to
four (4) Class A outputs.
Ordering Information
Model
FF8
FF8-MP
FF8-CM
31076
31081
24 VDC, 8.0 Amp., fire alarm NAC
expander/ power supply with integral
battery charger
Multipack cabinet with one FF8 and
space for up to three additional FF8-CMs
or 31085s (See Options Section).
Chassis assembly version of FF8, for
mounting in FF8-MP spaces
Class A adaptor, converts signal circuits
to Class A wiring (See Options Section).
Mounting plate for placing up to two
SCE-95 modules into the FF8
(FF8 and FF8-MP compatible, See
Options Section).
Mounting plate for placing XP95 devices
into the FF8-MP; includes standoffs for
eight devices
Battery, 12 VDC, 7 AH
(two required for 24 V operation)
Battery, 12 VDC, 12 AH
Primary Input Power:
120 VAC, 60 Hz, 3.0 A
or 220 V, 1.5 A; jumper selectable
Secondary Power:
24-volt operation: two 7 – 24 AH
batteries
Battery Charging
Up to 26 AH batteries
Capacity:
Battery Space:
Up to two 12 AH batteries maxi-
mum inside the FF8 cabinet.
Larger batteries require a separate
battery cabinet
Total Output Power:
8.0 A maximum
Standby Current:
0.030 A
Auxiliary Power
0.15 A under all conditions
Output:
1.5 A, if load is removed during
operation (external relay or AC
Fail relay use required).
NAC Output Ratings:
24 VDC fully regulated, 3.0 A
maximum per circuit (8.0 A total)
End-of-Line Resistor
2K to 25K, 1/2 watt
Range:
Common Trouble
Relay, AC Fail Relay:
2.0 A/28 VDC or 120 VAC
31085
BAT-1270
BAT-12120
GAMEWELL-FCI