600 Series
IdentiFlex 650
The IdentiFlex 650 (IF650) is a full-featured Fire Alarm
Control Panel (FACP) that can be configured to monitor
and control both analog intelligent addressable devices
and conventional hard-wired zones, providing maximum
application flexibility. It is easily adapted to a new or retrofit
installation, providing up to 2016 analog addressable
points plus 96 conventional circuits. With the addition of a
SmartLink™ network, the IdentiFlex 650 system can
include multiple IF650s or other 600 Series fire alarm pan-
els. The interactive operator’s display uses LED prompting
for easy user operation and programming. The alphanu-
meric display and keypad simplify field programming.
Gamewell-FCI’s Smart Program II can be used to program
the IF650 with a PC.
Integration of analog and hard-wired circuits allows the
system engineer to customize the control panel based on
the application. The CPU automatically senses system
configuration to ensure that modules are correctly posi-
tioned to speed installation and maintenance.
IdentiFlex 650 software allows the system to be custom-
ized to specific applications, such as cross-zoning and
alarm verification.
Front-panel construction is designed to allow routine main-
tenance of the system without disturbing the I/O modules.
Multiple levels of password protection prevent unautho-
rized use. The cabinet is designed with terminal strips for
ease of installation and service.
Analog Addressable Control Panel
ID650
Operator’s Display
The IdentiFlex 650 operator’s display supplies all the nec-
essary keys and annunciation points to maintain and moni-
tor the system. Alarm, Supervisory and Trouble conditions
are all indicated on the operator’s display by dedicated
LEDs and the internal sounder. The Acknowledge, Reset,
and Signal Silence keys are easily identified on the display.
Analog/addressable and conventional input circuits.
SmartStart™ self-programming logic.
Fully modular.
160-character, four-line display.
One to 16 Signal Line Circuits (SLC) for up to 2016
analog points.
Polarity-insensitive SLC wiring (XP95 protocol).
Automatic default response for increased survivability.
1000-event history log.
Digital SLC protocol.
PC or front-panel programming.
Password protected.
Serial annunciator, remote display, and remote printer
options.
One-man, selectable-input walk test.
Automatic drift compensation.
Coded signaling.
Day/night mode settings.
Approved for Suppressant Releasing and Supervisory
Service.
UDACT compatible.
Adjustable sensor sensitivity and temperature settings.
SmartLink™ network compatible.
An ISO 9000-2000 Company
SIGNALING
FM
MEA
Approved
SmartStart™ and SmartLink™ are trademarks of Honeywell International Inc.
S521
APPROVED
132-95-E
7165-1288:144
Approved
7170-1288:146
High Rise
City of
Chicago
GAMEWELL-FCI
Specifications are for information only, are not intended for installation purposes, and are subject to change without notice. No responsibility is assumed by Gamewell-FCI for their use.
©2007 Honeywell International Inc. All rights reserved.
www.gamewell-fci.com
CS-2005 Rev. A page 1 of 4
12 Clintonville Road, Northford, CT 06472-1610 USA • Tel: (203) 484-7161 • Fax: (203) 484-7118
The Reset key returns the control panel to idle mode after
an alarm condition has been cleared. Trouble conditions
that have been cleared will automatically return the control
panel to idle mode if the problem has been corrected. Trou-
ble conditions that have been acknowledged will resound
the internal sounder if the condition is not corrected within
a programmed time period.
The Signal Silence key deactivates notification appliances.
This function can be modified by user programming to
operate only after a specified time period.
There are three additional programmable switches avail-
able to control application-specific operations. Keys for
programming and bypass functions, along with LEDs for
active and trouble conditions, are provided for the City
Connection, and two signal circuits which are part of the
Common Control section.
greatly expanding its use in retrofit applications (consult
Gamewell-FCI Technical Support for specific wiring
requirements).
The
CONVENTIONAL INPUT MODULE
(CIM-8) occupies
one bay and provides eight hard-wired input circuits for
monitoring conventional detectors and contact-type
devices. The CIM-8 monitors and reports each circuit’s
analog status to the CPU as it distinguishes between
detectors and contact devices and determines if two or
more detectors are in alarm. Each input module uses one
slot in the MPU bus and is supplied with its own display
module. The display module provides LED annunciation of
alarm and trouble conditions and has a switch (per circuit)
for programming and bypass functions. The display has
space for user-defined custom labels for each circuit.
Beyond normal alarm and supervisory functions, the input
circuits can be programmed for Remote Acknowledge,
Reset, Signal Silence, and Release Abort switches. Cir-
cuits can be wired for Style B, D, and E service and are
capable of monitoring normally-closed devices.
The 600 Series
UNIVERSAL SIGNAL MODULE
(USM-8)
occupies one bay and is a multifunctional eight-circuit out-
put module. USM-8 modules communicate via the MPU
bus and require one expansion slot each. The USM can be
configured as 24 VDC signaling circuits. Modules are pro-
grammed in two-circuit increments, making it possible to
perform all four functions with a single module. Signal cir-
cuits provide steady or coded outputs. All circuits are
power-limited per NEC 760 and UL 864. Signal circuits can
be wired in either Style Y or Z. Signal modules are supplied
with their own display that provides LED annunciation of
activation and trouble conditions and has a switch (per cir-
cuit) for programming and bypass functions. The display
has space for user-defined custom labels for each circuit.
The 600 Series
POWER SUPPLY
(MPS-8) furnishes sys-
tem operating and signaling power. The supply is equipped
with a battery charger for maintaining the secondary power
source. The power supply is monitored by the main CPU to
ensure that adequate power levels are maintained. The
power supply design allows for high efficiency while provid-
ing precise power output. The battery charger is capable of
operating with lead-acid batteries and maintaining up to 50
AH batteries. Multiple auxiliary power supplies (APS-8)
may be added to the system when additional power is
required.
The 600 Series
RELAY MODULE
(RM-8) supplies eight
NO/NC relays for control of auxiliary functions. The relays
are controlled by the main CPU and are fully programma-
ble. Each position on the MPU bus can accommodate a
relay module. The relays are rated at 10 Amps and each is
Other Panel/System Components
The IF650
COMMON CONTROL SECTION
comprises the
heart of the system. The common control section houses
the main CPU and all system memory as well as providing
local and remote communications and supervision. The
common control contains the common system relays, two
signal circuits, city tie, and optional EIA-232 port. All inter-
action with the common control section is through the oper-
ator’s display panel. Four relay circuits control auxiliary
functions. The relays, rated at 10 Amps, are controlled by
the main CPU. Two 24 VDC notification appliance circuits
(NAC) are provided. The NACs can provide a steady or
coded output. All circuits are power-limited per NEC 760
and UL 864.
The IF650
ANALOG INTERFACE MODULE
(AAM95-
1,2,4) occupies one bay and has from one to four circuits
that can monitor and control up to 126 addressable/analog
devices each for a total of 504 points per bay. Gamewell-
FCI IF650 systems can be configured for up to 2016 points.
The analog interface module has a dedicated microproces-
sor which simultaneously communicates with the con-
nected field devices and the main CPU. This feature allows
the IF650 to maintain maximum communications speed
throughout the system. Analog/addressable circuits can be
wired as non-polarized in Style 4, 6, or 7. The communica-
tions protocol provides for alarm verification per detector,
detector adjustability and compensation, adjustable analog
heat detector range (131°F to 194°F/55°C to 90°C), circuit
isolation, and priority interrupts. Priority interrupts allow
contact-type devices such as manual fire alarm stations to
interrupt the polling cycle and transmit their addresses at
any time during a polling sequence. The digital protocol
allows the IF650 to operate on most types of field wiring,
GAMEWELL-FCI
CS-2005 Rev. A page 2 of 4
provided with a feedback point for positive confirmation of
activation. Like all 600 Series expansion modules, the relay
module reports activation.
The 600 Series
BUILDING CONTROL MODULE
(BCM-8)
provides an interface between the fire alarm and HVAC
systems. Relays (rated at 10 A) are accompanied by feed-
back points for positive confirmation of the programmed
action. The BCM is available in eight-circuit modules that
are monitored and controlled by the MPU bus which can
monitor and control one expanded (i.e., eight-circuit) BCM
per position. The display for the BCM provides LEDs for
annunciation of relay state or feedback, and windows for
user-defined custom labeling. In addition, the display for
the BCM comes with a three position ON/OFF/AUTO
switch per circuit for manual override of the programmed
automatic functions.
Although the common control module is equipped with a
city tie circuit which is suitable for most applications, an
optional four-circuit
CITY TIE MODULE
(CTX-4) has been
developed for applications that require multiple connec-
tions. The city tie module connects to the MPU bus and is
supplied with a display module. The CTX-4 can also be
used for applications requiring a polarity-reversal output.
There are two
SYSTEM HOUSING CONFIGURATIONS
available for the IF650 control panel. The four-bay cabinet
(IF654) will accommodate four 600 Series modules in addi-
tion to the common control, power supply, and batteries. An
eight-bay cabinet (IF658) will accommodate eight 600
Series modules in addition to the common control, power
supply and batteries. The housings are designed with
ample wiring space, conduit knockouts, and mounting
options. The unit’s dead-front design allows all operation,
programming, and user interface to take place without
exposing the system modules or field wiring. Field-wiring
terminals are mounted directly to the backbox for ease of
installation and service. Modules can be removed for ser-
vicing without disturbing field wiring.
Addressable input-interface devices provide the means to
communicate with cost-effective conventional devices in
areas that do not require analog sensors.
Addressable control-output devices serve as the interface
between the analog circuits and building functions. The
outputs are controlled via Control-by-Event software and
can be programmed to respond to any event. The control
devices can also be used as supervised remote signal cir-
cuits.
The IF650’s optional EIA-232 output expands the system’s
display and control capability.
Serial annunciators can be added to display system activity
and control. The serial annunciator drivers provide the
interface to graphic annunciators.
An alphanumeric display (RAN2-RCS) can also be used for
remote status and control. The alphanumeric display is
designed to communicate over the serial communications
network. It features a 160-character display and provides
remote reset/acknowledge/silence keys. See RAN/SAN
data sheets CS-2025 and CS-2027 for complete annuncia-
tor details.
The IF650 communicates with an EIA-232 printer either
locally or remotely for documentation of system activity.
The printer interface accepts serial communications from
the control panel and provides a parallel output to the
printer.
The IF650 can provide the required functions to control the
releasing of bulk fire-suppressant materials. The IF650 is
Listed for the following NFPA types of suppressant: 13
Sprinkler, 15 Water Spray, 11 Low-Expansion Foam, 16
Water Foam, 17 Dry Chemical, and 2001 Clean Agent.
The Gamewell-FCI IdentiFlex 650 Analog Addressable
Control Panel is designed for small-to-large projects. The
embedded CPU offers users unrivaled reliability with flexi-
bility and value.
The IF650 control panel is designed to incorporate the
XP95 analog addressable sensors into an integrated life
safety system which will meet today’s most stringent
requirements.
GAMEWELL-FCI
CS-2005 Rev. A page 3 of 4
Common Control
Standby Current:
Alarm Current:
0.275A.
0.407A plus signaling circuit power,
plus 0.002A for master box, or plus
0.022A for reverse-polarity
120 VAC, 2.0A
24 VDC, 2.0A combined maximum
Common Relays:
10A @ 30 VDC or 250 VAC
24 VDC nominal @ 2.0A per circuit
37.14" H x 24.0" W x 6.0" D
(94.3 H x 61 W x 15.2 D cm)
52.5" H x 24.0" W x 6.0" D
(133.4 H x 61 W x 15.2 D cm)
50 AH.
Ordering Information
Model
IF654
IdentiFlex 650 base analog/addressable
system consisting of the following:
• IF650 common control that includes:
- Main CPU
- IF650 front display with LCD
- Bus Driver Module
- Common system relays
• Two NAC circuits and ribbon cables
• MPS-8 main power supply
• Four-bay cabinet assembly
• Supports up to 2016 points
- Main CPU
- Bus Driver Module
• Eight-bay cabinet assembly
MPU bus expander module, complete
with cables. Allows expansion for
additional 600 Series Modules installed
into a second eight-bay cabinet.
Eight-bay cabinet with blank deadfront
(no display windows). For housing auxil-
iary power supplies (APS-8) with lock.
Dimensions: 52.5" H x 24.0" W x 6.0" D
Eight-bay expansion cabinet assembly,
with space for eight (8) MPU bus mod-
ules. Includes backbox, deadfront cover,
inner door assemblies, lock and key.
Four-bay expansion cabinet assembly,
with space for four (4) MPU bus mod-
Dimensions: 37.14" H x 24.0" W x 6.0" D
Eight-amp auxiliary power supply. Fits in
one module expansion slot, includes one
blank dress panel.
IdentiFlex 650 Installation/Operating
Manual.
Input Power:
Auxiliary Output:
S+/S–, A+/A–:
Signaling Circuits:
Panel Dimensions:
Four-bay cabinet:
Eight-bay cabinet:
Battery Capacity:
Battery Storage
Dimensions:
IF658
8.0" H x 14.25" W x 6.0" D
(20.3 H x 36.2 W x 15.2 D cm)
Relative Humidity:
93% non-condensing
Temperature Rating:
32° – 120°F (0° – 49°C)
SYS-EXP8
CAB600-BD8
CAB600-8
CAB600-4
APS-8
72122
GAMEWELL-FCI
CS-2005 Rev. A page 4 of 4