Flex Series
GWF402 and
GWF404
The Flex 402 is a two zone fire alarm control panel (FACP)
and the Flex 404 is a four zone FACP. These control pan-
els provide reliable fire signaling protection for small to
medium sized retail, office, multi-family, or other similar
commercial or institutional building.
Initiating device circuits (IDCs) for Flex Series panels are
power limited and operate in Style B (Class B). Each panel
is compatible with conventional input devices such as two-
wire smoke detectors, four-wire smoke detectors, pull sta-
tions, water flow devices, tamper switches and other nor-
mally-open contact devices. This includes System Sensor
2 and 4 Zone Conventional
Fire Alarm Control Panels
GWF402 (left) and GWF404 (right)
i
3™
Series microprocessor-based detectors with advanced
features like drift compensation, maintenance alert and
freeze warning. (See Device Compatibility Document PN
52195 for a listing of compatible devices.)
Outputs include one notification appliance circuit (NAC) on
the Flex 402 and two NACs on the Flex 404. NACs are
power limited and operate in Style Y (Class B). Each FACP
has a Form-C Alarm and Trouble relay and 24 VDC special
applications resettable power. In addition, the Flex 404 has
a Form-C Supervisory relay and a special application non-
resettable power output. The FACP supervises wiring, AC
voltage and battery level.
Activation of a compatible smoke detector or any normally-
open fire alarm initiating device will activate audible and
visual signaling devices, illuminate an indicating LED,
sound the piezo sounder at the FACP, activate the FACP
alarm relay and operate and optional modules used to
notify a remote station or initiate an auxiliary control
function.
Both the Flex 402 and Flex 404 fire alarm control panels
are listed to UL
Standard 864, 9th Edition.
• Flex 402: Two Style B (Class B) IDC zones, one Style Y
(Class B) NAC
• Flex 404: Four Style B (Class B) IDC zones, two Style Y
(Class B) NACs
• Optional NAC Class A converter module (Flex 404)
• NAC synchronization and programmability features:
- ADA compliant strobe synchronization
- ANSI audible signals as required by NFPA 72
- Silence inhibit, auto-silence, non-silenceable
- Selective Silence: mute horns, keep strobes lit
- Temporal or steady signal
• Silent or audible walk test from front keypad
• Zone disable, alarm verification selectable per zone
• Controls: Acknowledge, Alarm, Silence, Reset,
Walktest, Zone enable/disable
• LED indicators: Alarm, Supervisory, Maintenance,
Trouble (one per zone): AC, NAC / Zone disable, NAC
fault, System / Power Trouble, Walktest, Alarm Silence,
Charger / Battery / Earth Fault (on pcb)
• Alarm verification
• Low AC voltage sense, automatic battery charger
• Piezo sounder for alarm, trouble, and supervisory
An ISO 9000-2000 Company
SIGNALING
i
3™
is a trademark of Honeywell International Inc.
UL
is a registered trademark of Underwriter’s Laboratories Inc.
MEA
Approve
d
S521 366-04-E 7165-1288:180
GAMEWELL-FCI
Specifications are for information only, are not intended for installation purposes, and are subject to change without notice. No responsibility is assumed by Gamewell-FCI for their use.
©2007 by Honeywell International Inc. All rights reserved.
www.gamewell-fci.com
9021-60292 Rev. A page 1 of 2
12 Clintonville Road, Northford, CT 06472-1610 USA • Tel: (203) 484-7161 • Fax: (203) 484-7118
Options
Used to convert Style B (Class B) IDCs to
Style D (Class A) and Style Y (Class B)
NACs to Style Z (Class A). Mounts in
FACP. Flex 404 only.
XRM-24
Second 100VA transformer for maximum
accessory power. Mounts in FACP. Flex
404 only.
4XTMF
Transmitter module provides output for
local energy municipal box transmitter and
alarm and trouble reverse polarity. Mounts
in FACP. Flex 402 & Flex 404.
4XZMF
Zone relay module provides Form-C relays:
Alarm Zones 1, 2, 3, 4, System Alarm,
Trouble. Mounts in FACP. Flex 404 only.
4XLMF
LED interface module supports the
GWSAN-404 remote annunciator,
supervises annunciator wiring for open
conditions. Mounts in FACP. Flex 404 only.
411UD
Four input/channel, dual line, digital alarm
communicator/transmitter(DACT). Input/
channels are compatible with normally
open relay contacts, are supervised and
fully programmable. Interfaces with public
switched telephone networks and
compatible with most central station receiv-
ers. Flex 404 only.
GWSAN-404
Remote annunciator mounts in single-gang
electrical box, provides LED indication of
Alarm Zones 1, 2, 3, 4; and System
Trouble. Flex 404 only.
CAC-4
Specifications (Continued)
Circuits (NAC)
Operation: Style Y (Class B)
Power limited circuitry
Operating voltage: nominal 24 VDC
Maximum signaling current: 2.5 A total
(5.0 A Flex 404 with optional
transformer)
Maximum line impedance: 1.5 volt drop
Form-C Relays
Trouble, Alarm (Supervisory, Flex 404)
Contact ratings 2 A @ 30 VAC
(resistive)
Resettable
power
Maximum available current: 500 mA
Maximum Available current: 500 mA
Door: 15.3" x 14.7" x 0.3"
(39 x 37 x 1 cm)
Backbox: 15.0" x 14.5" x 3.0"
(38
x 37 x 8 cm)
Nonresettable
power
Cabinet
Ordering Information
GWF402
GWF404
71252
52194
Flex 402 conventional FACP, 2 zones,
120 VAC, red
Flex 404 conventional FACP, 4 zones,
120 VAC, red
EOL resistor, 4.7K ohm, ½ watt
Flex 402 and Flex 404 Installation &
Operation Manual
AC Power
Battery
120 VAC, 50/60Hz, 2.3 A
Max. charging circuit: 27.6 VDC@ 0.8A
Max. charger capacity: 18 Ah (two 7Ah
batteries fit inside FACP)
Options:
CAC-4
Class A converter for initiating device
circuits and notification appliance cir-
cuits (cannot be used on Flex 402)
Transformer, expands NAC circuit
power from 3 to 5 amps
Transmitter module for remote station
output or municipal box connection
Relay module, four relays-by-zone,
alarm and trouble contacts, 24VDC
Remote annunciator driver, 24 VDC,
supports GWSAN-404
Four channel dual slave programmer
DACT, Form C relay and upload/down-
load capability; with enclosure, requires
PRO-411
Programmer, use with 411UD,
411UDAC
LED remote annunciator for Flex 404,
4 alarms, 1 trouble (requires 4XLMF)
Battery box, houses 2 batteries
(7-18 Ah max)
XRM-24
4XTMF
4XZMF
4XLMF
411UD
Initiating Device
Alarm zones 1 & 2 (Flex 402 / Flex 404)
Circuits (IDC)
Alarm zones 3 & 4 (Flex 404 only)
Operation: All zones Style B (Class B)
Operating voltage: nominal 20 VDC
Alarm current: 15 mA minimum
Short circuit current: 40 mA maximum
Standby current: 4 mA
Maximum loop resistance: 100 ohms
Notification
One NAC: Flex 402; two NACs:Flex 404
PRO-411
GWSAN-404
BB-17F
GAMEWELL-FCI
9021-60292 Rev. A page 2 of 2