4930-01-20A
产品描述断路器 Single pole remote control circuit breaker, standard, with auxiliary contacts, 20A
产品类别电路保护    断路器与附件    断路器
文件大小202KB,共5页
制造商E-T-A [E-T-A Circuit Breakers]
4930-01-20A在线购买
4930-01-20A - - 点击查看 点击购买
4930-01-20A概述
4930-01-20A规格参数
厂商名称E-T-A [E-T-A Circuit Breakers]
产品种类断路器
发货限制Mouser目前不销售该产品。
系列4930
类型Remote Control
电流额定值20 A
电压额定值 AC125 VAC
电压额定值 DC28 V
极数1 Pole
执行器类型Plunger
最小工作温度- 54 C
最大工作温度+ 71 C
照明Not Illuminated
高度108.2 mm
长度82.55 mm
端接类型Screw
电压额定值115 VAC, 28 VDC
宽度31.9 mm
安装风格Flange
Remote Control Circuit Breaker 4930 (RCCB)
Single pole remote control circuit breaker (RCCB), temperature
compensated, either with or without auxiliary contacts, and featuring
a bimetal actuator which trips the circuit breaker mechanism within
a specified time under overcurrent conditions. The switching contact
latching system is operated by a bi-stable linear motor controlled by
electronic circuitry incorporated within the device. Remote control
is achieved through the use of a conventional single pole manually
operated aircraft style thermal circuit breaker type 4120-0,5 A which
connects the control input of the RCCB to ground.
With the control circuit breaker (ICU) in the ON position, the RCCB will
switch on. When the control circuit breaker is switched off, the RCCB
will change to the OFF condition. If power is applied to a previously
de-energised RCCB, the device will adopt the same switching status
as the control circuit breaker.
If the RCCB trips thermally in the event of a load circuit fault, the
electronic circuitry will also cause the control circuit breaker to trip,
thereby providing a visual indication through the position of the circuit
breaker actuator.
Approved to MIL-PRF-83383.
4930 (RCCB)
Technical data
(T
= 25 °C, U
e
= DC 28 V or AC 115V/400 Hz)
Operating data LINE
Voltage ratings U
e
(operating voltage range)
Current rating range I
Bias current
Switching current/
switching period for
internal linear motor
(see also MIL-PRF-83383)
AC 115 V 400 Hz (AC 104...126 V);
DC 28 V (DC 18...36 V)
5...100 A (see ordering information)
typically 2.5 mA at DC 28 V
typically 25 mA at AC 115 V
Typical applications
Aircraft electrical systems and equipment, and other high performance
applications.
Ordering information
Type No.
4930
single pole remote control circuit breaker (RCCB)
Variation
01
02
with modified terminal barrier and auxiliary contacts
03
standard, without auxiliary contacts
04
with modified terminal barrier but without auxiliary contacts
Current ratings
5...100 A
4930 - 01 - 5 A
/A
ordering example
MIL
part number
M83383/02-01
M83383/02-02
M83383/02-03
M83383/02-04
M83383/02-05
M83383/02-06
M83383/02-07
M83383/02-08
M83383/02-09
M83383/02-10
M83383/02-11
M83383/02-12
M83383/02-13
E-T-A
part number
4930-03-5A
4930-03-7.5A
4930-03-10A
4930-03-15A
4930-03-20A
4930-03-25A
4930-03-35A
4930-03-40A
4930-03-50A
4930-03-60A
4930-03-75A
4930-03-80A
4930-03-100A
MIL
part number
M83383/01-01
M83383/01-02
M83383/01-03
M83383/01-04
M83383/01-05
M83383/01-06
M83383/01-07
M83383/01-08
M83383/01-09
M83383/01-10
M83383/01-11
M83383/01-12
M83383/01-13
E-T-A
part number
4930-01-5A
4930-01-7.5A
4930-01-10A
4930-01-15A
4930-01-20A
4930-01-25A
4930-01-35A
4930-01-40A
4930-01-50A
4930-01-60A
4930-01-75A
4930-01-80A
4930-01-100A
typically 3.4 A / 28 ms at DC
typically 2.8 A / 17 ms at AC
Optical indication ON/OFF status indicator (near terminal A1)
Load circuit LOAD
Interrupting capacity
DC 28 V: 6,000 A
AC 115 V 400 Hz: 3,600 A
Voltage drop at I
see table 1
(standard current ratings and
typical voltage drop values)
Overload disconnection
see table 2
(typical time/current characteristics)
Trip limits
see table 2
Control circuit ICU
ICU
Indicator/Control Unit
thermal circuit breaker 0.5 A
e.g. 4120-G111-K1M1-A1S0ZN-0.5A
Trigger current for ICU
(“TRIP FREE“-mode) /
duration
approx. 3.2 A / 5 s max
Control voltage U
ICU
Limits:
RCCB “OFF”
U
ICU
> 2 V (25 °C)
(ICU open)
(> 1.5 V between -54...+71 °C /
-65...+160 °F)
RCCB “ON”
U
ICU
< 0.6 V (25 °C)
(ICU closed)
(< 0.2 V between -54...+71 °C /
-65...+160 °F)
Control current I
ICU
typically 0.4 mA
Additional control units
ON/OFF-cycling time
(e. g. additional relay
contact in ICU circuit)
Signal output AUX
Auxiliary contacts
one relay contact or one ON/OFF switch
is applicable (see application note ICU)
ON > 80 ms / OFF > 80 ms
change over contacts
S1 - S2 is open, when RCCB main
contact is open
DC 28 V, AC 115 V (400 Hz)
resistive load: 3 A
inductive load 1.5 A
lamp load: 0.5 A
Approvals
Authority
DSCC
Standard
MIL-PRF-83383
Voltage ratings
AC 115 V, 400 Hz
DC 28 V
Current
ratings
5 A…100 A
5 A…100 A
Voltage ratings
Current ratings
1646
www.e-t-a.de
站点相关: 大学堂 TI培训 Datasheet 电子工程 索引文件: 1348  2485  416  786  1383  38  9  8  26  4