Switched mode power supply for DIN rail mounting type SMP21 DC24V/10A
Switched mode power supply for rail mounting, with independent
change-over of input voltages (AC 115/230 V), integral passive power
factor compensation (PFC), high power reserve and optional parallel
mode.
Features and Benefits
l
The
l
l
l
l
devices switches over automatically when connected to
AC 115 V AC and 230 V
ide range inputs from AC 90 to 132 V at rated input voltage 115
V, and AC 180 to 264 V at rated input voltage 230 V
Efficiency up to 89 %
Integral passive power factor compensation
Parallel mode for performance improvement (selectable by switch)
SMP21-DC24V-10A
Version L20
Technical data (T
U
= 25°C, U
= AC 115 / 230 V, I
= 10A)
Typical applications
Process control, industrial switch- and controlgear, machine
construction, telecommunication systems
Operating data
Input voltage ranges U
Operating voltage range
U
Effective output
Output voltage U
Output current rating I
Efficiency
General data
Switching frequency
Insulation voltage
between
input and output
input and
protective conductor
output and
Insulation resistance
Ambient temperature
Derating factor (see
curve)
Storage temperature
Relative humidity
MTBF to Bellcore, ed. 6
Max. altitude in
operation to IEC
60068-2-13
Cooling
Mounting direction
Pollution degree
Input circuit
Input rated voltage
Input current
Max. input current
Supply frequency
AC 115 V / AC 230 V
AC 90…132 V / DC 180…264 V
1.55 A typically at U
B =
AC 230 V
4.0 A typically at U
B =
AC 115 V
2.2 A at U
= AC 180 V
5.4 A at U
= AC 88 V
47...63 Hz
40 kHz
AC 90…132 V / AC 180…264 V
AC 115 / 230 V
240 W
24 V SELV
10 A
87 % min. / 89 % typically
Order numbering code
Type No.
SMP21
Single phase switch-mode power supply for rail mounting
Connector design
pcb mounting (preferred type)
plug-in type
Terminal design
screw terminals
Output voltage
DC24V
DC 24 V
Output current
10 A
SMP21-L 20-DC24V-10A
ordering example
AC 3000 V, DC 4242 V
AC 1500 V, DC 2121 V
AC 500 V, DC 710 V
100 MΩ (DC 500 V) between
input and output
-40 °C…+71°C
2.5 % / °C
-40 °C…+85 °C
20…90 % RH
481,000 hours at 40°C, GB
5000 m above sea level
Approvals and standards
Approval
authority
UL
TÜV
Rheinland
Standards
UL508, CSA C22.2 No. 107.1 (listed)
UL 60950-1, CSAC22.2 No. 60950-1 (recognized)
EN 60950-1 / EN61558-1 / EN61558-2-16
by convection
wall-mounted (see dimensions)
EMC
EN 61000-6-3, EN 61000-6-2, EN 61204-3
1646
www.e-t-a.de
Technical data (T
U
= 25°C, U
= AC 115 / 230 V, I
= 10A)
Inrush current
at AC 115 V
at AC 230 V
Power loss
(at U
230 V, I
10 A)
Power factor
Compensation (passive)
Output circuit
Rated voltage U
Current rating I
Output voltage accuracy
Min. load
Supply regulation
Load regulation
Single mode
Parallel mode
Voltage adjustment
range
Continuous load
Power boost factor
DC 24 V SELV
10 A
0…+1 %
0%
± 0.5 % at U
min. … U
max.
± 1%
± 5%
DC 22.5…28.5 V at 0.8 x I
10 A at U
= DC 24 V, 8.4 A at
U
= DC 28.5 V
typically 130 % (120%...145% see
output curve)
U/I trip curve
25 / 20 ms
1s
1.5 s
30 A max.
60 A max.
35 W typically
typically 0.75
Technical data (T
U
= 25°C, U
= AC 115 / 230 V, I
= 10A)
Control and protection circuit
input protection
Recommended back-up
fuse
Current rating
Characteristic curve
Internal overvoltage
protection
available power
(output RDY)
Insulation voltage
Contact load at
Overvoltage protection
Degree of protection
Physical data
Dimensions (h x w x d)
version L20 with
screw terminals:
Version S20 with
removeable plug
Housing material:
Mass
Vibration (random
vibration to IEC
60068-2-6)
Shock
(to IEC 60068-2-27,)
124.5 x 83.5 x 123.6 mm
(4,9 x 3,29 x 4,87 inches)
143.5 x 83.5 x 123.6 mm
(5.65 x 3.29 x 4.87 inches)
metal
approx. 1380 g
mounted on symmetrical rail, 10 - 500 Hz,
2 g, on X, Y & Z axis, 60 minutes per axis
15 g (11 ms), 3 axes,
6 sides, 3 times per side
internal blade fuse
T6.3A / AC 250 V
1-pole MCB, e.g. E-T-A type 4230
10 A / 16 A
max. 20 A
B/C/D
varistor
Contact closed at:
DC 17.6...19.4 V
DC 500 V (to output)
DC 60 V / 0.3 A
30…33 V at 0.8 x I
IP20
Short circuit behaviour
Exposure time
ON delay at:
resistive load
capacitive load of
7,000 µF
Rise time at:
resistive load
capacitive load of
7,000 µF
Release time
Residual ripple
Power back immunity
Capacitive load
Parallel mode
150 ms
0.5 s
150 ms
100 mV, spectrum = 20 MHz
DC 35 V min.
7,000 µF max.
3 power supplies max. at
0.1 x I
… 0.9 x I
Dimensions
L20
83.05 (3.29)
S20
83.05 (3.29)
24 V DC/ 10 A
24 V DC/10 A
SMP21
115/230 V AC
5.4/2.2 A
47-63Hz
SMP21
115/230 V AC
5.4/2.2 A
47-63Hz
7.0 (0.3)
0.00 (0.00) - 30.00 (1.18)
30.00 (1.18) - 120.00 (4.72)
120.00 (4.72) - 400.00 (15.75)
124.50 (4.9)
143.50 (5.65)
GENERAL TOLERANCE
±0.30 (0.01)
±1.50 (0.06)
±1.50 (0.06)
www.e-t-a.de
124.50 (4.9)
1646
Mounting and Installation
Mounting
Ventilation / cooling
Mounting position
snap onto DIN rail (TS35/7.5 or
TS35/15)
normal air convection, recommended
distance on each side 25 mm
wall-mounted with the input terminals
pointing downwards (see dimensions)
input terminal
AWG24-10 (0.2 mm² – 4 mm²) flexible/rigid
output terminal
input connector 1 Nm max.
Output terminal 0.6 Nm max.
8 mm
input terminal
output terminal
input connector 0.5 Nm max.
Output connector 0.8 Nm max.
4…5 mm
pin no.
5.6
RDY
V+
V-
PE
DC ON
DC LO
Vout Adj
S/P
limit value DC ON, relay contact (make
contact)
output voltage +
output voltage -
earth conductor
Input voltage, neutral conductor
(not polarised with DC input voltage)
Input voltage, phase conductor
visual status indication with LED
DC LOW output voltage LED indication
potentiometer for adjustment of output
voltage U
change-over switch single / parallel mode
name
V+
V+
V-
V-
RDY
RDY
No
10 A
Pin assignment – Display - Controls
L1
PE
Version L20 with screw terminals:
Screw terminals
Tightening torque
Wire stripping length
Screw terminals
Version S20 with removeable plug
Tightening torque
Schematic diagram
Fuse
Filter
Inrush Current
Limiter&Rectifier
and Auto Select
115/230 V
Vo+
P.F.C
Circuit
Smoothing
Circuit
Switching
Device
Rectifier
Current
Detection
Vo-
Single/Parallel
select
Vout
ADJ.
PWM
Controller
Opto-
Isolation
Reference &
Error Amp.
Opto-
Isolation
Over Voltage
Level
Detection
Output
Level
Detection
DC ON
(Green LED)
DC LOW
(Red LED)
RDY
(Relay Contact)
1646
www.e-t-a.de
Typical output trip curve
Output Voltage (%)
140
Output Current (%)
230 Vac
115 Vac
Derating curve
Typical efficiency curve
Efficiency (%)
Leistung (%)
89
88
87
86
85
84
83
82
81
230 Vac
115 Vac
Safe Operating Area
Temperature (°C)
61
71
Power out (%)
Current-voltage curve
current-voltage-curve
➞ short
circuit
current-voltage-curve short circuit
➞ output
REF16-S101-DC24V-6A
current:
10 A / Div
voltage:
10 V / Div
time 20 ms / Div.
current:
2 A / Div
voltage:
10 V / Div
time 20 ms / Div.
www.e-t-a.de
1646
Application example with protection by 4230-T and REF16-S
L1
PE
L1.1
N.1
4230-T110-K0CE-16A
F1
(see catalog Circuit
Breaker Thermal
Magnetic Datasheet
4230-T)
PE
SMP21
V1
10 A
L1
V+
V+
V-
V-
RDY RDY
NO
X11
X1
12 (b)
LINE+
X2
X3
12 (b)
LINE+
X4
12 (b)
LINE+
X5
12 (b)
LINE+
X6
12 (b)
LINE+
LINE+
12 (b)
ETA.REF16-S100-DC24V-0,5A
ETA.REF16-S101-DC24V-2A
ETA.80PLUS-PT01
ETA.80PLUS-PT01
ETA.REF16-S101-DC24V-1A
ETA.80PLUS-PT01
ETA.80PLUS-PT01
ETA.80PLUS-PT01
RE
0,5 A
LOAD+
2 1114
2A
2 11 14
LOAD+
Si
Si
2 1114
2A
2 11 14
LOAD+
Si
Si
2 1114
1A
2 11 14
LOAD+
Si
Si
2 11 14
1A
2 11 14
LOAD+
Si
Si
2 11 14
SF +24V
LOAD+
4A
2 11 14
RE
(see catalog
electronic
overcurrent
protection
Chapter 6)
ETA.REF16-S124-DC24V-4A
ETA.80PLUS-PT01
SF +24V
M1
2.1/2.2
2.1/2.2
2.1/2.2
2.1/2.2
2.1/2.2
11(a)
14(c)
11(a)
14(c)
11(a)
14(c)
11(a)
14(c)
11(a)
14(c)
11(a)
2.1 2.2 11 14
2.1 2.2 11 14
2.1 2.2 11 14
2.12.2 11 14
2.1 2.2 11 14
2.1 2.2 11 14
X8
X7
X9
X10
E0.0
E0.1
E0.3
14(c)
Status OUT
F2
F3
F4
F5
F6
F7
Reset IN
Notes for installation
The power distribution system must only be installed by qualified
personnel.
l
Only after expert installation must the device be supplied with
power.
l
The user has to ensure that the cable cross section complies with
the applicable current rating.
l
The national standards (e.g. for Germany DIN VDE 0100) have to
be observed for installation and selection of feed and return cables.
l
Recommended circuit breaker for the primary input cable protection:
E-T-A type 4230 IN max. 20 A
l
Recommended selective overcurrent protection for the secondary
output protection: E-T-A types ESS.., ESX.., und REF…
l
In addition special precautions must be taken in the system or
machine (e.g. use of a safety PLC) which reliably prevent an
automatic re-start of parts of the system (cf. Machinery Directive
2006/42/EU and EN 60204-1, Safety of Machinery). In the event of
a failure (short circuit/overload) the load circuit will be disconnected
by the circuit breaker/protector or the switched mode power supply.
l
1646
www.e-t-a.de