https://www.phoenixcontact.com/pi/products/2800186
Lightning/surge arrester type 1/2 - VAL-MS-T1/T2 335/12.5/1+1-
FM - 2800186
Universal varistor-based plug-in lightning/surge arrester for 1-phase power supply networks with separate N
and PE (3-conductor system: L1, N, PE), with remote indication contact.
Your advantages
Plugs can be checked with CHECKMASTER
With floating remote indication contact
Secure hold of plugs in the event of high lightning current loads and strong vibrations thanks to new latching
Thermal disconnect device for each individual plug
Pluggable
Mechanical coding of all slots
Key Commercial Data
Packing unit
GTIN
GTIN
4046356518574
1 pc
Technical data
Dimensions
Height
Width
Depth
Horizontal pitch
96.8 mm
35.6 mm
77.5 mm (incl. DIN rail 7.5 mm)
2 Div.
Ambient conditions
Degree of protection
Ambient temperature (operation)
IP20 (only when all terminal points are used)
-40 °C ... 80 °C
10/28/2018 Page 1 / 7
FM - 2800186
Technical data
Ambient conditions
Ambient temperature (storage/transport)
Altitude
Permissible humidity (operation)
Shock (operation)
Vibration (operation)
-40 °C ... 80 °C
≤ 2000 m (amsl (above mean sea level))
5 % ... 95 %
30g (Half-sine / 11 ms / 3x ±X, ±Y, ±Z)
7.5g (10 ... 500 Hz / 2.5 h / X, Y, Z)
General
IEC test classification
I / II
T1 / T2
T1
EN type
IEC power supply system
Mode of protection
T1 / T2
T1
TT
TN-S
L-N
L-PE
N-PE
Mounting type
Color
Housing material
Degree of pollution
Flammability rating according to UL 94
Surge protection fault message
DIN rail: 35 mm
jet black RAL 9005
PA 6.6
PBT
V-0
DIN rail module, two-section, divisible
Optical, remote indicator contact
Protective circuit
Nominal voltage U
Nominal frequency f
Maximum continuous operating voltage U
(L-N)
(L-PE)
Maximum continuous voltage U
(N-PE)
Rated load current I
Residual current I
PE
Standby power consumption P
Nominal discharge current I
n
(8/20) µs (L-N)
n
(8/20) µs (L-PE)
n
(8/20) µs (N-PE)
Maximum discharge current I
max
(8/20) µs
240 V AC (TN-S)
240 V AC (TT)
50 Hz (60 Hz)
335 V AC
335 V AC
264 V AC
80 A
≤ 5 µA
≤ 270 mVA
12.5 kA
12.5 kA
50 kA
50 kA
10/28/2018 Page 2 / 7
FM - 2800186
Technical data
Protective circuit
Impulse discharge current (10/350) µs (L-N), charge
Impulse discharge current (10/350) µs (L-N), specific energy
Impulse discharge current (10/350) µs (L-N), peak current value I
imp
Impulse discharge current (10/350) µs (L-PE), charge
Impulse discharge current (10/350) µs (L-PE), specific energy
Impulse discharge current (10/350) µs (L-PE), peak current value I
imp
Impulse discharge current (10/350) µs (N-PE), charge
Impulse discharge current (10/350) µs (N-PE), specific energy
Impulse discharge current (10/350) µs (N-PE), peak current value I
imp
Total discharge current I
total
(8/20) µs
total
(10/350) µs
Follow current interrupt rating I
fi
(N-PE)
Short-circuit current rating I
SCCR
Voltage protection level U
p
(L-N)
p
(L-PE)
p
(N-PE)
Residual voltage U
res
(L-N)
6.25 As
39 kJ/Ω
12.5 kA
6.25 As
39 kJ/Ω
12.5 kA
25 As
625 kJ/Ω
50 kA
50 kA
25 kA
100 A
25 kA
≤ 1.2 kV
≤ 1.6 kV (30 kA - 8/20 µs)
≤ 2 kV
≤ 1.7 kV
≤ 1.2 kV (at I
n
≤ 1.1 kV (at 10 kA)
≤ 1 kV (at 5 kA)
≤ 0.9 kV (at 3 kA)
Residual voltage U
res
(L-PE)
≤ 2 kV (at I
n
≤ 1.5 kV (at 10 kA)
≤ 1.2 kV (at 5 kA)
≤ 1.1 kV (at 3 kA)
Residual voltage U
res
(N-PE)
≤ 0.6 kV (at I
n
≤ 0.5 kV (at 10 kA)
≤ 0.5 kV (at 5 kA)
≤ 0.4 kV (at 3 kA)
TOV behavior at U
(L-N)
TOV behavior at U
(N-PE)
Response time t
(L-N)
Response time t
(L-PE)
Response time t
(N-PE)
Max. backup fuse with V-type through wiring
Max. backup fuse with branch wiring
415 V AC (5 s / withstand mode)
457 V AC (120 min / safe failure mode)
1200 V AC (200 ms / withstand mode)
≤ 25 ns
≤ 100 ns
≤ 100 ns
80 A (gG - 16 mm²)
160 A (gG)
Indicator/remote signaling
10/28/2018 Page 3 / 7
FM - 2800186
Technical data
Switching function
Operating voltage
Operating current
Connection method
Screw thread
Tightening torque
Stripping length
Conductor cross section flexible
Conductor cross section solid
Conductor cross section AWG
PDT contact
5 V AC ... 250 V AC
30 V DC
5 mA AC ... 1.5 A AC
1 A DC
Plug-in/screw connection via COMBICON
M2
0.25 Nm
7 mm
0.14 mm² ... 1.5 mm²
28 ... 16
Connection data
Connection method
Screw thread
Tightening torque
Stripping length
Connection method
Screw connection
M5
3 Nm (1,5 mm² ... 16 mm²)
4.5 Nm (25 mm² ... 35 mm²)
16 mm
1.5 mm² ... 25 mm²
1.5 mm² ... 35 mm²
15 ... 2
Fork-type cable lug
1.5 mm² ... 16 mm²
UL specifications
SPD Type
Maximum continuous operating voltage MCOV (L-N)
Maximum continuous operating voltage MCOV (L-G)
Maximum continuous operating voltage MCOV (N-G)
Nom. voltage
Mode of protection
4CA
335 V AC
335 V AC
264 V AC
240 V AC
L-N
L-G
N-G
Power distribution system
Nominal frequency
Measured limiting voltage MLV (L-N)
Measured limiting voltage MLV (L-G)
Measured limiting voltage MLV (N-G)
n
(L-N)
Single phase
50/60 Hz
2630 V
3600 V
2600 V
20 kA
10/28/2018 Page 4 / 7
FM - 2800186
Technical data
UL specifications
n
(L-G)
n
(N-G)
20 kA
20 kA
UL indicator/remote signaling
Operating voltage
Operating current
Tightening torque
125 V AC
1 A AC
4 lb
f
-in.
30 ... 14
UL connection data
Tightening torque
10 ... 2
30 lb
f
-in.
Standards and Regulations
Standards/regulations
IEC 61643-11 2011
EN 61643-11 2012
Environmental Product Compliance
China RoHS
Environmentally Friendly Use Period = 50
For details about hazardous substances go to tab “Downloads”,
Category “Manufacturer's declaration”
Drawings
Dimensional drawing
96,8
89,8
35,6
Circuit diagram
FM
77,5
44
Approvals
Approvals
Approvals
DNV GL / CCA / UL Recognized / KEMA-KEUR / cUL Recognized / IECEE CB Scheme / ÖVE / EAC / EAC / cULus Recognized
Ex Approvals
10/28/2018 Page 5 / 7