Product Data Sheet
HOUR
UP
TO
Fire Protection
Meets Air Leakage
Requirements
1. Product Description
ELASTOMERIC
3M Fire Barrier Silicone Sealant 2000+ is a ready-to-use,
gun-grade, one-component silicone elastomer that cures upon exposure to atmospheric humidity to form
a flexible firestop seal. 3M Fire Barrier Silicone Sealant 2000+ helps control the spread of fire, smoke
and noxious gasses before, during and after exposure to a fire when installed in accordance with a listed
through penetration or fire-resistive joint assembly.
Movement
Capability
3M Fire Barrier Silicone Sealant 2000+ firestops dynamic construction joints, blank openings and
penetrations passing through fire-rated floor, floor/ceiling or wall assemblies and other fire-rated interior
building construction. The sealant remains elastomeric, bonds to most common construction materials
and exhibits excellent weatherability during construction. No mixing is required.
Available in:
Light Gray
FILL, VOID OR CAVITY MATERIAL
FOR USE IN JOINT SYSTEMS AND
THROUGH-PENETRATION FIRESTOP SYSTEMS
SEE UL FIRE RESISTANCE DIRECTORY
90G9
Product Features
• Firestop tested up to 4 hours in
accordance with ASTM E 814 (UL
1479) & CAN/ULC S115
• Fire Resistance tested for construction
joint systems in accordance with
ASTM E 1966 (UL 2079)
• Class 25 sealant, per ASTM C 920
• Compression/extension
capability of ± 13%
• Applied with conventional caulking
equipment — excellent caulk rate
• Excellent weatherability upon cure
• Excellent adhesion
• Re-enterable/repairable
FIRESTOP SYSTEMS
SEE INTERTEK DIRECTORY
MATERIALS
90G9
Compression/extension capabilities
for dynamic joint applications
Meets the intent of LEED VOC environmental quality requirements—helps reduce the quantity of indoor air
contaminants that may be odorous, irritating and harmful to the comfort and well-being of the installers and occupants.
Minimizes noise transfer — STC-Rating of 56 when tested in STC 56-rated wall assembly.
2. Applications
3M Fire Barrier Silicone Sealant 2000+ is a flexible firestop ideal for sealing dynamic joints in fire-rated
construction. In addition, 3M Fire Barrier Silicone Sealant 2000+ is used in mechanical, electrical and plumbing applications to firestop openings
and penetrations through fire-rated floor or wall assemblies. Typical penetrants include: metallic pipe, conduit, power and communication cable
and telephone or electrical wiring. 3M Fire Barrier Silicone Sealant 2000+ is also used to firestop blank openings and static construction joints.
2000+ shall be a one-component, ready-to-use, gun-grade silicone
elastomer. The sealant shall be listed by independent test agencies such as
Intertek or UL. 3M Fire Barrier Sealant 2000+ shall be tested to and pass
the criteria of ASTM E 814 (UL 1479) Standard Test Method for Fire Tests
of Penetration Firestop Systems, ASTM E 1966 (UL 2079) Standard Test
Method for Fire Resistive Joint Systems and CAN/ULC S115 Standard
Method of Fire Tests of Firestop Systems. 3M Fire Barrier Sealant 2000+
shall meet the requirements of the IBC, IRC, IFC, IPC, IMC, NFPA 5000,
NEC (NFPA 70) and NFPA 101.
3. Specifications
Typically Specified Divisions
Division 7
Section 07 84 00 – Firestopping
Related Sections
Section 07 84 16 — Annular Space Protection
Section 07 84 43 — Fire-Resistant Joint Sealants
Section 07 86 00 — Smoke Seals
Section 07 87 00 — Smoke Containment Barriers
Section 07 92 13 — Elastomeric Joint Sealants
Section 07 92 19 — Acoustical Joint Sealants
Section 07 27 00 — Thermal and Moisture Protection Firestopping
Section 21 00 00 — Air Barriers
Section 22 00 00 — Plumbing
Section 26 00 00 — Electrical
For technical support relating to 3M Fire Protection Products and Systems, call: 1-800-328-1687
For more information on 3M Fire Protection Products, visit: www.3M.com/firestop
RATED
3M
FIRE BARRIER
SMOKE SEAL
4. Performance & Typical Physical Properties
Colors Available:
Application Temperature Range:
Service Temperature Range:
STC
(ASTM E 90 and ASTM E 413)
Surface Burning
(ASTM E 84)
Light Gray
-20° to 122°F (-29° to 50°C)
-40° to 302°F (-40° to 150°C)
56 when tested in STC 56 rated
wall assembly
Flame Spread 0, Smoke Development 0
Extension/compression capability:
Hardness
(ASTM D 2240 Shore A)
Tensile Strength:
VOC Less H
O and Exempt Solvents
Elongation at Break
(ASTM D 412):
± 13%
350 psi (0.59 MPa)
<32 g/L
500%
Volume: 10.3 fl. oz tube (304.8cc, 18.6 in. ), 4.5 gal. pail (17,034.4cc, 1,039.5 in. )
Cure:
Under typical cure rate conditions of 75°F (23°C) and 50% R.H., sealant
becomes tack-free in about 90 minutes. Full cure depends upon ambient conditions
and volume of sealant. Typical cure rate is approximately 1/8 inch (3.18mm) per day.
5. Packaging, Storage, Shelf Life
Packaging:
Storage:
Shelf Life:
Product packaged in cartridge or pail is enclosed in HDPE plastic containers.
3M Fire Barrier Silicone Sealant 2000+ should be stored indoors in dry conditions between 40°F and 90°F (4°C and 32°C).
Avoid repeated freeze / thaw exposures of the 3M Fire Barrier Silicone Sealant 2000+ while still in the packaging.
Shelf life of 18 months from date of packaging when stored below 90°F (32°C) in original, unopened containers.
Consult a 3M Authorized Fire Protection Products Distributor / Dealer or Sales Representative
for Applicable UL, Intertek or other third-party drawings and system details.
6. Installation Techniques
Preparatory Work:
The surface of the opening and any penetrating items should be cleaned to allow for the proper adhesion of the 3M Fire Barrier
Silicone Sealant 2000+. Do not use alcohol to clean surfaces (recommended cleaning solvents are mineral spirits, xylene, toluene
or methyl ethyl ketone (MEK). Ensure that the surface of the substrates are not wet and are frost free. Sealant can be installed with
a standard caulking gun, pneumatic pumping equipment or it can be easily applied with a putty knife or trowel.
Installation Details:
Install the applicable depth of backing material, if required, as detailed within the applicable UL, Intertek or other third-party
listed system. Cut the end of the tube spout to achieve the desired bead width when applying. Install the applicable depth of
3M Fire Barrier Silicone Sealant 2000+ into the opening flush with the surface of the substrate, or as detailed within the
applicable listed system, at the depth for the assembly and rating that is required. Tool within 5 minutes. Clean all tools
immediately after use with mineral spirits, xylene, toluene or methyl ethyl ketone (MEK).
Limitations:
Do not apply 3M Fire Barrier Silicone Sealant 2000+ under the following conditions: when surrounding temperature is greater
than 122°F (50°C), when surfaces are wet or frost-coated, in unvented spaces where sealant is not exposed to atmospheric
moisture, in areas where abrasion or physical abuse of the sealant are likely and/or where painting of sealant is required (Note:
once applied, sealant may be exposed to intermittent water — exhibits excellent weatherability when fully cured). Do not apply
3M Fire Barrier Silicone Sealant 2000+ to polycarbonates or to building materials that bleed oil, plasticizers or solvent (e.g.
impregnated wood, oil-based sealants, or green or partially vulcanized rubber).
In confined cure conditions, there may be discoloration of brass, copper or other sensitive metals.
No maintenance is expected when installed in accordance with the applicable third-party listed system. Once installed,
if any section of the 3M Fire Barrier Silicone Sealant 2000+ is damaged, the following procedure will apply: remove and reinstall the damaged section
in accordance with the applicable listed system, with a minimum 1/2 in. (12.7mm) overlap onto the adjacent material.
7. Maintenance
8. Availability
3M Fire Barrier Silicone Sealant 2000+ is available from 3M Authorized Fire Protection Products Distributors and
Dealers in the following sizes: 10.3 fl. oz. cartridges (12/case) and 4.5 gallon pails (1/case). For additional technical and purchasing information regarding
this and other 3M Fire Protection Products, please call: 1-800-328-1687 or visit www.3M.com/firestop.
9. Safe Handling Information
Consult product Material Safety Data Sheet (MSDS) prior to handling and disposal.
Building and Commercial
Services Division
3M Center, Building 223-2N-21
St. Paul, MN 55144-1000 USA
1-800-328-1687
www.3M.com/firestop
Important Notice to User:
Technical Information:
The technical information, recommendations and other statements contained in this document are based upon tests or experience that 3M believes are
reliable, but the accuracy or completeness of such information is not guaranteed.
Product Use:
Many factors beyond 3M’s control and uniquely within user’s knowledge and
control can affect the use and performance of a 3M product in a particular application. Given the variety of factors that can affect the use and performance of a 3M product,
user is solely responsible for evaluating the 3M product and determining whether it is fit for a particular purpose and suitable for user’s method of application.
Warranty
and Limited Remedy:
3M warrants that each 3M Fire Protection Product will be free from defects in material and manufacture for 90 days from the date of purchase from
3M’s authorized distributor. 3M MAKES NO OTHER EXPRESS OR IMPLIED WARRANTIES, INCLUDING ANY IMPLIED WARRANTY OF MERCHANTABILITY OR FITNESS FOR A
PARTICULAR PURPOSE. If a 3M product does not conform to this warranty, the sole and exclusive remedy is, at 3M’s option, replacement of the 3M product or refund of the
purchase price.
Limitation of Liability:
Except where prohibited by law, 3M will not be liable for any loss or damage arising from the 3M product, whether direct, indirect, special,
incidental or consequential, regardless of the legal theory asserted.
Please Recycle. Printed in U.S.A. © 3M 2014. All rights reserved.
Reference Number 98-0400-3266-0
3M is a trademark of 3M. Used under license in Canada. LEED is
a trademark of U.S. Green Building Council Non-Profit Corporation.
All other trademarks are the property of their respective owners.