Technical Data 10351
Effective September 2018
Supersedes July 2018
BUSSMANN
SERIES
5.5kV E-Rated medium voltage fuses for feeder
circuit, switchgear and transformer protection
Features and benefits
Current-limiting E-Rated medium voltage
fuses are defined by their melting time-current
characteristic that permit their electrical
interchangeability with other fuses of the same
E Rating.
E-Rated fuses must have a defined current
response time specified by ANSI C37
.46.
E-Rated fuse of 100 amps and below must
melt in 300 seconds at an RMS current within
the range of 200% to 240% of the fuse’s
nameplate current rating. E-Rated fuses greater
than 100 amps must melt in 600 seconds at an
RMS current within the range of 220% to 264%
of the fuse’s nameplate current rating.
E-Rated fuses are physically dimensioned for
easy installation in existing hardware.
Current-limiting fuses provide positive
interruption even on low fault currents. The
fuse limits the magnitude of electromechanical
stresses in the protected apparatus.
Constructions available in ferrule, bolt-on
and clip-lock, and specialty mount fuses for
AMPGARD motor starters.
Outdoor rating available on select catalog
numbers (requires installation in a suitable
enclosure).
Open fuse indicator easily integrates
into automation schemes and speeds
troubleshooting by providing a positive visual
indication of fuse operation.
Optional remote contact signaling microswitch
available.
50/60Hz operating frequency for worldwide
application.
Mountings are available in disconnect and non-
disconnect versions with porcelain or glass poly-
ester insulators.
Live parts and end fittings available.
Description:
Bussmann™ series E-Rated, current-limiting,
medium voltage fuses for feeder circuit,
switchgear and transformer protection.
Typical applications:
Medium voltage transformer primary
protection
Medium voltage feeder circuit protection
Medium voltage switches
Medium voltage metal-enclosed switchgear
feeder circuit, switchgear and transformer protection
Dimensions (see catalog number tables for values)
E-Rated medium voltage ferrule fuses
Catalog symbols:
General purpose:
5CLE-_E-D (10-25A)
5CLE-_E (10-1350A)
5HLE-_E (10-450A)
JCY-_E (1-25A)
MV055F_ (10-450A)
Full range (per ANSI C37
.40)
3.31
(84.1)
Ratings*:
Volts — 5.5kV
Amps — 1 to 1350A
Interrupting ratings — 40 to 65 kA RMS Sym
* See catalog number tables for voltages, ampacities and interrupting ratings by
catalog number.
Agency information:
E-Rated fuses meet the performance characteristics of
ANSI C37
.46
UL Listed, Guide JEEG, File E240398. See catalog numbers.
Recommended CLE and HLE holders:
Catalog number
Fuse
mounting
type*
Non-disconnect
Disconnect
Disconnect
Approximate dimensions - in (mm)
BIL (kV)
Diameter
Clip center
CLE
Mounting
(including live parts, end fittings)**
Porcelain insulator
5CLE-PNM-D
5CLE-PDM-D
5CLE-PNM-C
5CLE-PDM-C
5CLE-PNM-E
5CLE-PDM-E
Glass-polyester
insulator
5CLE-GNM-D
5CLE-GDM-D
5CLE-GNM-C
5CLE-GDM-C
5CLE-GNM-E
5CLE-GDM-E
Amp rating
10E-D–25E-D
30E–250E
Single barrel
15E–25E
Single barrel
300E–450E
Double barrel
600E and 750E
Double barrel
1100E and 1350E
Four barrel
10E-D–250E
Single barrel
300E–450E
Double barrel
Live parts
(including
end fittings)
CLE-NL-D
CLE-DL-D
CLE-NL-C
CLE-DL-C
CLE-NL-E
CLE-DL-E
End fittings
(disconnect
only)
CLE-DF-D
CLE-DF-C
CLE-DF-E
3.0 (76.2)
2.0 (50.8)
3.0 (76.2)
4.0 (101.6)
4.0 (101.6)
14.0 (355.6)
11.5 (292.1)
14.0 (355.6)
N/A
N/A
17 (454.7)
.9
12.9 (327
.7)
17 (454.7)
.9
N/A
N/A
Non-disconnect
Non-disconnect
Disconnect
Consult factory
Consult factory
HLE
Non-disconnect
Disconnect
Non-disconnect
Disconnect
3.0 (76.2)
12.0 (304.8)
12.0 (304.8)
15.9 (403.9)
15.9 (403.9)
5HLE-PNM-D
5HLE-PDM-D
5HLE-PNM-E
5HLE-PDM-E
5HLE-GNM-D
5HLE-GDM-D
5HLE-GNM-E
5HLE-GDM-E
CLE-NL-D
CLE-DL-D
CLE-NL-E
CLE-DL-E
CLE-DF-D
CLE-DF-E
* See page 12 for illustrations and dimensions
** End fittings supplied only when required.
† Disconnect mountings provide a means for fuse extraction only. Do not use a disconnect mounting for load switching or fuse removal while energized.
www.bussmann.com