PSR-SCP- 24DC/URD3/4X1/2X2/T2
PSR-SPP- 24DC/URD3/4X1/2X2/T2
Safety Relay as a Contact Extension Block
With Off-Delay Contacts
INTERFACE
Data Sheet
102987_01_en
The
PSR-...- 24DC/URD3/4X1/2X2/T2
safety relay can be
used as a contact extension block in safety circuits
according to DIN EN 60204-1/VDE 0113-1.
The device has an interface for the T-BUS DIN rail
connector. This interface can be used for single-channel
control and monitoring. Alternatively, the device can also be
operated in single-channel mode via a contact on the basic
device.
Depending on the external wiring, up to safety category 3
according to EN 954-1 can be achieved.
The relay has four enabling current paths, one signaling
current path, and one confirmation path. The contacts drop
with at least a 2 second delay according to stop category 1
(DIN EN 60204-1/VDE 0113-1).
The extension unit can be used as a contact multiplier for
emergency stop relays and two-hand controls.
© PHOENIX CONTACT - 09/2007
Contact extension block
Safety category 3 according to EN 954-1
Plug-in screw or spring-cage connection terminal
blocks
Single-channel wiring
Safe isolation
Housing width 22.5 mm
Four enable contacts, one alarm contact, and one
confirmation contact
Observe the safety instructions on page 4.
Make sure you always use the latest documentation.
It can be downloaded at
www.download.phoenixcontact.com.
A conversion table is available on the Internet at
www.download.phoenixcontact.com/general/7000_en_00.pdf.
This data sheet is valid for all products listed on the following page:
Ordering Data
Safety Relay
Safety relay as a contact extension block with off-delay contacts, with screw
connection
Order No.
2981703
2981729
Pcs./Pck.
Safety relay as a contact extension block with off-delay contacts, with spring- PSR-SPP- 24DC/URD3/4X1/2X2/T2
cage connection
Accessories
DIN rail connector, yellow, for PSR applications
Terminating connector
PSR-TBUS
PSR-TBUS-TP
Order No.
2890425
2981716
Pcs./Pck.
Documentation
Application manual for PSR safety relays
UM EN SAFETY RELAY APPLICATION
Order No.
2888712
Pcs./Pck.
Technical Data
Input Data
Nominal input voltage U
Permissible range
Typical current consumption at U
Typical response time (K1, K2)
Release time (K1, K2)
Recovery time
Surge protection
Status indicators (K1, K2, Power)
24 V DC
0.85 ... 1.1 x U
84 mA
20 ms
2 s +50%
1 s, approximately
Suppressor diode
Green LED
Output Data
Contact type: Positively driven contact assembly Class A according to
EN 50205
Contact material
Maximum switching voltage
Minimum switching voltage
Limiting continuous current
N/O contact
N/C contact (65-66)
TH2
= I
+ I
22
+ ... I
N2
Maximum inrush current
N/O contact
N/C contact (65-66)
Minimum switching current
Maximum shutdown power
6A
3A
25 mA
Ohmic load
τ
= 0 ms
24 V DC 144 W (72 W)
48 V DC 288 W (144 W)
110 V DC 77 W
220 V DC 88 W
250 V AC 1500 VA (750 VA)
Minimum switching power
0.4 W
4 enabling current paths, 1 signaling current path, 1 confirmation path
Silver tin oxide (AgSnO
250 V AC/DC
15 V AC/DC
6A
3A
50 A
Inductive load
τ
= 40 ms
48 W
40 W
35 W
33 W
102987_01_en
PHOENIX CONTACT
Output Data (Continued)
Mechanical service life
Switching capacity according to DIN EN 60947-5-1/VDE 0660-200
cycles, approximately
Cycles
3600/h:
360/h:
Short-circuit protection of the output circuits, external
Enabling current paths
Signaling current path
DC13
24 V DC
230 V AC
24 V/6 A
230 V/5 A
3A
AC15
3A
NEOZED 10 A gL/gG
NEOZED 4 A gL/gG
The maximum values given in brackets apply to N/C contacts 65-66.
General Data
Permissible ambient operating temperature
Nominal operating mode
Degree of protection according to VDE 0470-1
Housing
Connection terminal blocks
Installation location
Mounting position
Air and creepage distances between the circuits
Basic insulation
Impulse voltage withstand level
Pollution degree
Surge voltage category
Dimensions (W x H x D)
Screw connection
Spring-cage connection
Conductor cross-section
Screw connection
Stripping length
Screw connection
Housing material
-20°C ... +55°C
100% operating factor
IP20
IP20
IP54, minimum
Any
According to DIN EN 50178:1998-04
4 kV
III
22.5 mm x 114.5 mm x 99 mm
22.5 mm x 114.5 mm x 112 mm
0.2 mm
... 2.5 mm
0.2 mm
... 1.5 mm
7 mm
8 mm
Polyamide PA, not reinforced
Safe isolation, reinforced insulation, and 6 kV between the input circuit/N/C contacts and the enable contact current paths.
Tests/Approvals
BG/TÜV
UL/CUL
102987_01_en
PHOENIX CONTACT
Block Diagram
K1
/K2
T-BUS
Y1
T-BUS
37
47
57
65
Derating Curve
TH2
[A]
K1
POWER
K2
A1
T-BUS
A2
T-BUS
T-BUS
20 25 30 35 40 45 50 55 60
28
38
48
58
Figure 1
Block diagram
66
Ambient operating temperature [°C]
Figure 2
Derating curve
Safety Instructions
During operation, parts of electrical switching devices carry hazardous voltages.
Before working on the device, disconnect the power.
Please observe the safety regulations of electrical engineering and industrial safety and liability
associations.
Disregarding these safety regulations may result in death, serious personal injury or damage to
equipment.
Startup, assembly, modifications, and upgrades may only be carried out by a skilled electrical
engineer.
For emergency stop applications, the machine must be prevented from restarting automatically by
a higher-level control system.
Protective covers must not be removed when operating electrical switching devices.
In the event of an error, replace the device immediately.
Repairs, especially if the housing must be opened, may only be carried out by the manufacturer or
authorized persons. Otherwise the warranty is invalidated.
When operating relay modules, the operator must meet the requirements for noise emission for electrical and
electronic equipment (EN 61000-6-4) on the contact side and, if required, take appropriate measures.
102987_01_en
PHOENIX CONTACT
Structure
38
65
PS
RD
-U
(t
(t
T2
o
w
r
e
PS
U
R-
RD
T2
r
e
w
o
(t
(t
K 2
K1
APPROVAL
2 Y1
APPROVAL
Input: 24 V dc
Output: 240 V ac/24 V dc. 6A
B300 Pilot duy
R300 Pilot duty
Order No.: 29 81 70 3
Input: 24 V dc
B300 Pilot duy
R300 Pilot duty
Order No.: 29 81 72 9
47
ET 07036
47
ET 07036
48
48
57
58
23
58
57
24
Serial No.
Serial No.
15 27 37 47 57 65
15 27 37 47 57 65
Figure 3
Structure
Metal lock for mounting on the DIN rail
COMBICON plug-in screw terminal blocks
COMBICON plug-in spring-cage terminal blocks
27-28, 37-38, 47-48, and 57-58: Enabling current paths
K1, K2: Input
16 28 38 48 58 66
16 28 38 48 58 66
Y1: Connection to the DIN rail connector
15-16: Confirmation contacts
A1, A2: Supply voltage connection
65-66: Alarm contacts
Function
When the 24 V DC operating voltage is applied at terminal
blocks A1-A2 or is led via the DIN rail connector, the
"Power" LED lights up.
When a 24 V DC voltage is applied at input K1-K2 (or via
the DIN rail connector), both relays are activated. The LEDs
light up and the contacts for enabling current paths 27-28,
37-38, 47-48, and 57-58 close. Alarm contacts 15-16 and
65-66 open.
If the voltage is switched off at input K1-K2, the enable
contacts open and the alarm contacts close after two
second (2 s).
For additional connection examples, see page 7.
102987_01_en
PHOENIX CONTACT