Single-Phase Power Supply Unit, Primary Switched
for Universal Use
QUINT-PS-100-240AC/48DC/20
QUINT POWER provides:
Preventive function monitoring
through
professional signaling
Global use
due to a wide-range input
A high level of operational safety
even in complex
global networks
Reliable startup of heavy loads
due to
POWER BOOST
The reliability of a power supply unit determines the
availability of individual components in a system and
whether complex systems can function safely.
The globalization of markets increases the demands
placed on the power supply unit. A wide-range input
and a high level of availability are required.
These requirements are met by Generation
2 QUINT POWER.
1. Short Description
The QUINT POWER product range offers universal
DC power supplies from 60 - 960 W. Depending on the
type, regulated and adjustable output voltages of
12 V DC, 24 V DC or 48 V DC are available for output
currents of 2.5 A, 5 A, 10 A, 20 A, 30 A, and 40 A.
These devices, which are designed as primary
switched-mode regulators, operate with a high level of
efficiency so that heat loss is kept to a minimum.
The high level of operational safety is also ensured in
complex global networks. QUINT POWER also
operates in applications where static voltage dips,
transient power supply failures or phase failure are
common.
Powerful capacitors ensure mains buffering of more
than 20 ms at full load. All 3-phase QUINT POWER
units provide the complete output power even in the
event of a continuous phase failure.
Reliable startup of heavy loads is ensured by a
power reserve of up to 50% – the POWER BOOST.
Preventive function monitoring diagnoses an
impermissible operating state and minimizes
downtimes in your system. An active transistor output
and a
floating
relay contact are provided for remote
monitoring of this state.
This signal not only provides information on the
device function, but also indicates a system overload at
an early stage.
2. Area of Application
QUINT POWER can be used globally due to the
consistent provision of a wide-range input.
In this way, your entire system can be tested at any
production location in the world and can be delivered to
any location in the world without faulty switching of the
input voltage. This reduces storage costs and logistical
effort.
An international approval package including CB
Scheme, UL 60950 for IT equipment, and UL 508 for
industrial control equipment enables the device to be
used globally.
Safe operation in adverse conditions is emphasized
by the approval of all QUINT POWER units with
24 V output voltage by Germanischer Lloyd.
Headquarters: © Phoenix Contact GmbH & Co. KG • Flachsmarktstraße 8 • 32825 Blomberg • Germany
Phone +49 - 52 35 - 30 0 • Fax +49 - 52 35 - 34 12 00 • www.phoenixcontact.com
Local contact: www.phoenixcontact.com/salesnetwork
Single-Phase Primary-Switched Power Supply Unit for Universal Use – QUINT 48 V DC/20 A
3. Technical Data
125 mm
L (+ )
P F C
P E
D C
1 3
1 4
O K
130 mm
a c tiv e
240 mm
QUINT 48 V DC/20 A
1 AC
Solid
Input
Output
Signal
Stranded
[mm
AWG
0.2 - 4 25 - 10
0.5 - 10 20 - 6
0.2 - 4 25 - 10
Torque
Nm]
[Ib in.]
0.5 - 0.6
1.2 - 1.5
0.5 - 0.6
5-7
8 mm
10 mm
8 mm
Pcs.
Pkt.
CB
U
Scheme
uB
0.2 - 6
0.5 - 16
0.2 - 6
Power supply unit
primary switched for universal use
Technical Data
Input Data
Nominal input voltage
Input voltage range
Current consumption (for nominal values)
Inrush current limiting/I
t (+25°C)
Mains buffering for a nominal load (typical)
Switch-on time after applying the mains voltage
Transient surge protection
Input fuse, internal
Recommended backup fuse
Discharge current for PE
Output Data
Nominal output voltage U
/tolerance
Setting range for the output voltage
Output current (continuous) during convection cooling
and nominal values
Nominal output current I
-25°C to +60°C
BOOST
Derating
Short-circuit current limit
Startup of capacitive loads
System deviation on:
Static load change 10 - 90%
Dynamic load change 10 - 90%
Input voltage change ±10%
Maximum power dissipation
No load/nominal load
Efficiency
Response time U
OUT
(10% - 90%)
Residual ripple/switching peaks (20 MHz)
Can be connected in parallel
Internal surge protection
Resistance to return supply
Signal Output Data
DC OK (active)
(U
out
> 0.9 x U
high signal)
DC OK (electrically isolated)
(U
out
> 0.9 x U
contact closed)
LED
(U
out
< 0.9 x U
LED
flashing)
Order No.
29 38 97 6
110 - 240 V AC (wide-range input)
85 - 264 V AC
120 - 350 V DC
45 - 65 Hz
0 Hz
11 A (120 V AC)/5 A (230 V AC)
15 A, approximately/3.2 A
s, approximately
> 20 ms
<1s
Varistor
20 AF (device protection)
16 A or 25 A circuit breaker,
characteristic B (EN 60 898)
< 3.5 mA
48 V DC ±1%
30 - 56 V DC
20 A (U
out
= 48 V DC)
22.5
From +60°C 2.5% per Kelvin/below 100 V AC: 2.5%/V
27.5 A, approximately
Unlimited
< 1%, typical
< 5%, typical
< 0.1%, typical
20 W/80 W, approximately
> 92% (for 230 V AC and nominal values)
< 2 ms
< 100 mV
pp
To increase redundancy and power
Yes, limited to 60 V DC, approximately
60 V DC
+24 V DC signal (with regard to the device weight)
20 mA, maximum
60 V AC/DC, maximum; 0.5 A, maximum
Green LED
PHOENIX CONTACT page 2 of 10
General Data
Insulation voltage:
Input/output
Input/PE
Output/PE
Approval package
Electrical equipment of machines
Safety transformers for switched-mode power supply units
Electrical safety
(of IT equipment)
Industrial control equipment
Electronic equipment for use in electrical
power installations
Safety extra-low voltage
Safe isolation
Protection against electric shock
Protection against electric shock,
basic requirements for safe isolation
in electrical equipment
Limitation of harmonic line currents
Mounting position
Degree of protection
Class of protection
MTBF
Housing version
Dimensions (W x H x D) + DIN rail
Weight
Climatic Data
Ambient temperature
Humidity
Vibration
Shock
Pollution degree
Climatic category
3 kV AC (type test)/2 kV AC (routine test)
3 kV AC (type test)/1.5 kV AC (routine test)
500 V DC (routine test)
CB
Scheme
EN 60 204 (Surge Voltage Category III)
EN 61 558-2-17
EN 60950/VDE 0805,
UL/C-UL Recognized UL 60 950
u
UL/C-UL Listed UL 508
U
LISTED
EN 50 178 (VDE 0160)
PELV (EN 60 204)
SELV (EN 60 950)
VDE 0100-410
DIN 57100-410
DIN VDE 0106-101
According to EN 61000-3-2
On horizontal NS 35 DIN rail according to EN 60715
IP20
Ι
, with PE connection
> 500,000 h according to IEC 1709 (SN 29 500)
AluNox (AlMg1), closed
Default upon delivery:
Rotated 90°:
(240 x 130 x 125) mm
(122 x 130 x 243) mm
2.5 kg, approximately
Operation
Storage
According to IEC 68-2-6
According to IEC 68-2-27
-25°C to +70°C (> +60°C derating)
-40°C to +85°C
Up to 95% at +25°C, no condensation
< 15 Hz, amplitude ±2.5 mm/15 Hz - 150 Hz, 2.3g, 90 minutes
30g in all space directions
(according to EN 50 178)
3K3 (according to EN 60 721)
c
Conformance With EMC Directive 89/336/EEC and
Low Voltage Directive 73/23/EEC
EMC (Electromagnetic Compatibility)
Noise Immunity According to EN 61000-6-2:
Electrostatic discharge
(ESD)
Electromagnetic
HF
field
Fast transients
(burst)
Surge current loads
(surge)
EN 61000-4-2
3)
Housing
Contact discharge:
Air discharge:
Housing
Frequency:
Field strength:
Input:
Output:
Signal:
Input:
Output:
Signal:
Conducted
interference
Voltage dips
EN 61000-4-6
2)
I/O/S:
Frequency:
U
Input:
Requirements
EN 61 000-6-2
4 kV
8 kV
80 - 1000 MHz
10 V/m
2 kV
2 kV
1 kV
2 kV
1 kV
0.5 kV
0.5 kV
1 kV
0.15 - 80 MHz
10 V
30% reduction of the input voltage
for 0.5 periods
asymmetrical
5)
asymmetrical
5)
asymmetrical
5)
asymmetrical
5)
symmetrical
4)
asymmetrical
5)
symmetrical
4)
asymmetrical
5)
asymmetrical
5)
Level 4
8 kV
15 kV
Level 3
80 - 1000 MHz/1.4 - 2.0 GHz
10 V/m
4 kV (Level 4)
2 kV (Level 3)
1 kV (Level 2)
4 kV (Inst. Class 4)
2 kV (Inst. Class 4)
0.5 kV (Level 1)
0.5 kV (Level 1)
1 kV (Level 2)
Level 3
0.15 - 80 MHz
10 V
See Input Data:
Mains buffering
> 20 ms
EN 55011 (EN 55022) Class B
7)
7)
EN 61000-4-3
2)
EN 61000-4-4
3)
EN 61000-4-5
3)
EN 61000-4-11
3)
Noise Emission According to EN 61000-6-3:
Radio interference
Radio interference
EN 55011
EN 55011
Class A
6)
Class A
6)
EN 55011 corresponds to CISPR11/EN 55022 corresponds to
CISPR22
EN 61000 corresponds to IEC 1000
2)
Criterion A: Normal operating characteristics within the specified
limits.
3)
Criterion B: Temporary adverse effects on the operating
characteristics which the device corrects automatically.
4)
5)
Symmetrical: Cable to cable
Asymmetrical: Cable to ground
A:
Class B:
Industrial applications
Industrial and domestic applications
6)
Class
7)
PHOENIX CONTACT page 3 of 10
4. Device View, Connections, and Control Elements
DC
DC
DC
QUINT POWER
u
tput
DC
48
In
pu
tA
Ad
j
30 ust
-5
6V
DC
DC
60 F
5…+1
-2 …
95
DC
OK
–2
RO
PP
LS
TRIA
VA
DUS OL T
R N
IN NT ME
COUIP
EQ A
43
EN 602 8-2
EN 615
EN
-2
-6
00
10 1-1
6 8
EN 500
EN
U
LIS
TE
tput D
C 48V
20A
u
ns
io s
ct
ru a i n
st
in o m
n
tio g
la i n
al e c t
st
in n n
d co
ea r e
R fo
be
www.interface.phoenixcontact.com
100-
24
0V
8D
0/4
24
0- 7 6
10 8 9
PS 29 3
T-
IN o.:
QU er-N
d
Or
C/
Figure 04
AC input:
85 - 264 V AC input voltage
Frequency 45 - 65 Hz
(0.2 mm
to 6 mm
solid)
(0.2 mm
to 4 mm
stranded) (25 - 10 AWG)
Internal fuse 20 AF
16 A or 25 A LS/characteristic B
DC output:
48 V DC output voltage (default),
can be set from 30 - 56 V DC using
a potentiometer
(0.5 mm
to 16 mm
solid)
(0.5 mm
to 10 mm
stranded) (20 - 6 AWG)
The device is idling-proof and short-circuit-proof.
DC OK output active
DC OK output electrically isolated
Potentiometer (covered) 40 - 56 V DC
DC OK LED
Universal DIN rail adapter UTA 107
QUINT POWER is a built-in device.
Installation and
startup
must only be carried out by qualified
personnel. The relevant country-specific regulations
(e.g., VDE, DIN) must also be observed.
Before startup it is particularly important to ensure
that:
• The mains has been connected correctly and
protection is provided against electric shock.
• The device can be switched off outside the power
supply according to EN 60950 regulations (e.g., by
the mains protection on the primary side).
• The protective conductor is connected.
• All supply lines have sufficient fuse protection and
are the correct size.
• All output cables are the correct size for the maximum
device output current or have separate fuse
protection.
• Sufficient convection is ensured.
The housing temperature can reach high values
depending on the ambient operating temperature
and the load of the device.
The device contains dangerous live components
and high levels of stored energy.
5. Safety Notes and Warning
Instructions
To ensure that the device can be operated safely
and all functions can be used, please read these
instructions carefully.
Caution: Never carry out work when the
power is turned on, this is highly
dangerous.
PHOENIX CONTACT page 4 of 10
6. Installation
6.1. Mounting
The power supply unit can be snapped onto all DIN
rails according to EN 60715 and should be mounted
horizontally (input terminal blocks facing downwards).
Installation Dimensions
To ensure sufficient convection, we
recommend the following minimum
spacing be used between modules:
8.0 cm for vertical installation
0.0 cm for horizontal installation
QUINT POWER
In
pu
tA
100-2
0V
/4
00
-1 8 9
PS 29 3
T-
IN o.:
QU er-N
d
Or
8D
C/2
DC
30 djus
.0-5 t
6.0
–2
60 F
5…+1
-2 …
95
60 04 -17
EN 02 -2
DC
AP
LS
TRIA
VA
US OL T
R N
RO
IND T E
COUIP
EQ A
43
EN 615
EN
-2
0-6
00
61 81-1
EN 500
EN
U
LI
STE
ut
put
DC
24
ns
ti o s
u c in
s tr m a
in
to
n
ti o g
ll a c ti n
s ta n e
in o n
ad c
R efo r e
be
Figure 05
Flat mounting position:
Installation depth: 125 mm (+ DIN rail)
Narrow mounting position:
Installation depth: 243 mm (+ DIN rail)
240 mm
122 mm
145 mm
80 mm
QUINT POWER
DC OK
Input AC 100-240V
Adjust
30.0-56.0 V 13
DC
OK
Output DC 24V 20A
PHOENIX CONTACT page 5 of 10
130 mm
290 mm
Figure 06