https://www.phoenixcontact.com/hq/products/2702383
Extension module - PSR-MC82-5NO-1NC-1DO-24DC-SP - 2702383
Contact extension up to SILCL 3, Cat. 4, PL e in conjunction with suitable evaluation device, 5 enabling
current paths, U
= 24 V DC, plug-in spring-cage terminal block
The figure shows a version with a
screw connection
Why buy this product
Up to Cat. 4/PL e according to ISO 13849-1, SILCL 3 according to IEC 62061 in conjunction with suitable evaluation device
Low housing width of just 17.5 mm
One or two-channel activation
5 enabling current paths, 1 confirmation current path, 1 digital signal output
Automatic activation
Key Commercial Data
Packing unit
GTIN
GTIN
Custom tariff number
4055626145488
85371099
Made to Order (non-returnable)
1 STK
Technical data
Utilization restriction
EMC: class A product, see manufacturer's declaration in the download
area
Dimensions
Width
Height
Depth
17.5 mm
116.6 mm
114.5 mm
11/15/2016 Page 1 / 5
Technical data
Ambient conditions
Ambient temperature (operation)
Ambient temperature (storage/transport)
Max. permissible relative humidity (operation)
Max. permissible humidity (storage/transport)
Shock
Maximum altitude
-20 °C ... 60 °C (observe derating)
-40 °C ... 80 °C
75 % (on average, 85% infrequently, non-condensing)
15g
max. 2000 m (Above sea level)
Input data
Rated control circuit supply voltage U
Power consumption at U
Rated control supply current I
Inrush current
Typical response time
Typ. starting time with U
s
Typical release time
Recovery time
Status display
Maximum switching frequency
Filter time
24 V DC -20 % / +25 %
typ. 1.92 W
typ. 80 mA
30 mA (Δt = 7 ms at U
s
< 50 ms
< 50 ms (when controlled via A1/A2)
< 25 ms (when controlled via A1/A2)
< 100 ms
2 x green LEDs
0.5 Hz
4 ms (at A1/A2 in the event of voltage dips at U
s
max. 1 ms (at A1/A2, test pulse width, blanking pulses/dark test)
5 ms (at A1/A2, test pulse rate, blanking pulses/dark test)
Where test pulse width < 1 ms: test pulse rate = 5 x test pulse width
max. 1 ms (at A1/A2, test pulse width, switch-on pulses/light test)
10 ms (at A1/A2; test pulse rate; switch-on pulses/light test)
Deactivate switch-on pulses/light tests for safety applications.
Output data
Contact type
Contact material
Minimum switching voltage
Maximum switching voltage
Limiting continuous current
Inrush current, minimum
Maximum inrush current
Sq. Total current
Switching capacity
Output fuse
5 enabling current paths via N/O contacts
1 enabling current path via N/C contacts
AgSnO
5 V AC/DC
250 V AC/DC (Observe the load curve)
6 A (observe derating)
10 mA
6A
64 A (observe derating)
min. 50 mW
10 A gL/gG (N/O contact)
6 A gL/gG (N/C contact)
6 A gL/gG (N/O contact, for low-demand applications)
4 A gL/gG (N/C contact, for low-demand applications)
11/15/2016 Page 2 / 5
Technical data
Alarm outputs
Number of outputs
Current
Short-circuit protection
1 (digital, PNP)
typ. 23 V DC (U
- 1 V)
max. 100 mA
500 mA (Δt = 1 ms at U
s
Yes
General
Relay type
Mechanical service life
Nominal operating mode
Net weight
Mounting type
Assembly instructions
Mounting position
Degree of protection
Min. degree of protection of inst. location
Control
Housing color
Electromechanical relay with forcibly guided contacts in accordance with
EN 50205
10 x 10 cycles
100% operating factor
178.12 g
DIN rail mounting
See derating curve
horizontal
IP20
IP54
one and two channel
yellow
Connection data
Connection method
pluggable
Conductor cross section solid min.
Conductor cross section solid max.
Conductor cross section flexible min.
Conductor cross section flexible max.
Conductor cross section AWG min.
Conductor cross section AWG max.
Stripping length
Spring-cage connection
Yes
0.2 mm²
1.5 mm²
0.2 mm²
1.5 mm²
24
8 mm
Safety-related characteristic data
Stop category
Designation
Safety Integrity Level (SIL)
Designation
Designation
Performance level (PL)
Category
Designation
Safety Integrity Level Claim Limit (SIL CL)
IEC 61508 - High demand
3 (In conjunction with suitable evaluating device)
IEC 61508 - Low demand
EN ISO 13849
e (In conjunction with suitable evaluating device)
4 (In conjunction with suitable evaluating device)
EN 62061
11/15/2016 Page 3 / 5
Technical data
Standards and Regulations
Shock
Designation
Standards/regulations
Rated insulation voltage
15g
Air clearances and creepage distances between the power circuits
DIN EN 50178
250 V AC
250 V AC
Rated surge voltage/insulation
Safe isolation, reinforced insulation 6 kV between the input circuit and
the enabling current paths.
4 kV basic insulation between enabling current paths
Basic insulation 4 kV between all current paths and housing
Degree of pollution
Overvoltage category
Vibration (operation)
Conformance
III
10 Hz ...150 Hz, 2g (In the event of stress caused by vibration, contact
reactions are possible for up to 10 ms.)
CE-compliant
Environmental Product Compliance
China RoHS
Environmentally friendly use period: unlimited = EFUP-e
No hazardous substances above threshold values
Drawings
Block diagram
A1
24V
K1
24V DC
PSR-MC82
K2
A2
M1
11/15/2016 Page 4 / 5
Circuit diagram
24V DC
K1
K2
S2
K3
K4
S1
K5
K6
K7
K8
A1
S34 S11
K1
K3
K2
K4
S12
S21
(GND)
S22
A1 24V
33
43
53
63
PSR-MC30
PSR-MC82
A2
M1
A2
M1
24
34
44
54
64
K5
K7
K6
K1
K2
K3
K4
K6
K5
K8
K7
K8
0V
Approvals
Approvals
Approvals
UL Listed / cUL Listed / Functional Safety / cULus Listed
Ex Approvals
Approval details
UL Listed
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/index.htm FILE E 140324
cUL Listed
Functional Safety 44-205-15124303
cULus Listed
Phoenix Contact 2016 © - all rights reserved
http://www.phoenixcontact.com
11/15/2016 Page 5 / 5