IB IL 24 DO 8 ...
Inline terminal with eight digital outputs
4 x
AUTOMATION
Data sheet
5558_en_08
© PHOENIX CONTACT 2010-11-23
This terminal is designed for use within an Inline station. It is
used to output digital signals.
Connections for eight digital actuators
Connection of actuators in 2, 3, and 4-wire technology
Nominal current of each output: 0.5 A
Total current of the terminal: 4 A
Short-circuit and overload protected outputs
Diagnostic and status indicators
Approved for use within a safety-related segment circuit
(observe the notes on page 8)
This data sheet is only valid in association with the IL SYS INST UM E user manual.
Make sure you always use the latest documentation.
It can be downloaded at
www.phoenixcontact.net/catalog.
This data sheet is valid for all products listed on the following page:
IB IL 24 DO 8 ...
Ordering data
IB IL 24 DO 8-PAC
Products
Terminal with eight digital outputs;
complete with accessories (connectors consecutively numbered and labeling
fields);
transmission speed of 500 kbps
complete with accessories (connectors not consecutively numbered and la-
beling fields);
Terminal with eight digital outputs; without accessories;
fields);
transmission speed of 2 Mbps
beling fields);
Order No.
2861289
Pcs./Pkt.
IB IL 24 DO 8-PAC/SN
2862945
IB IL 24 DO 8
IB IL 24 DO 8-2MBD-PAC
2726269
2861687
IB IL 24 DO 8-2MBD-PAC/SN
2878227
IB IL 24 DO 8-2MBD
2819037
One of the listed connectors is needed for the complete fitting of the
IB IL 24 DO 8
and IB IL 24 DO 8-2MBD terminals.
Accessories
Connector with eight spring-cage connections (green, w/o color print)
Connector with eight spring-cage connections (green, with color print)
Connector set with 32 spring-cage connections (green, w/o color print)
Connector set with 32 spring-cage connections (green, with color print)
IB IL SCN-8
IB IL SCN-8-CP
IB IL DI/DO 8-PLSET
IB IL DI/DO 8-PLSET/CP
Order No.
2726337
2727608
2860950
2860963
Pcs./Pkt.
Documentation
"Configuring and installing the INTERBUS Inline product range" user manual
"Automation terminals of the Inline product range" user manual
"INTERBUS addressing" data sheet
"Safety-related segment circuit" application note
IB IL SYS PRO UM E
IL SYS INST UM E
DB GB IBS SYS ADDRESS
AH EN IL SAFE
Order No.
2743048
2698737
Pcs./Pkt.
_en_08
PHOENIX CONTACT
IB IL 24 DO 8 ...
Technical data
48.8 mm x 119.8 mm x 71.5 mm
130 g (without connectors)
Process data mode with 1 byte
-25°C to +55°C
-25°C to +85°C
75% on average, 85% occasionally
10% to 95% according to DIN EN 61131-2
70 kPa to 106 kPa (up to 3000 m above sea level)
IP20 according to IEC 60529
Class 3, according to EN 61131-2, IEC 61131-2
Spring-cage terminals
0.08 mm
to 1.5 mm
(solid or stranded), 28 - 16 AWG
General data
Housing dimensions (width x height x depth)
Weight
Operating mode
Connection method for actuators
Permissible temperature (operation)
Permissible temperature (storage/transport)
Permissible humidity (operation)
Permissible humidity (operation/storage/transport)
Permissible air pressure (operation/storage/transport)
Degree of protection
Protection class
Connection data for connectors
Connection method
Conductor cross-section
Interface
Local bus
Transmission speed
IB IL 24 DO 8
IB IL 24 DO 8-PAC
IB IL DO 8-2MBD
Via data routing
500 kbps
500 kbps
500 kbps
2 Mbps
2 Mbps
2 Mbps
Supply of the module electronics and I/O through the bus terminal/power terminal
Connection method
Via potential routing
Power consumption
Communications power
Current consumption from the local bus
Power consumption from the local bus
Segment supply voltage U
Nominal current consumption at Us
500 kbps
7.5 V
60 mA, maximum
0.45 W, maximum
24 V DC (nominal value)
4 A (8 x 0.5 A), maximum
2 Mbps
7.5 V
85 mA, maximum
0.64 W, maximum
Digital outputs
Number
Nominal output voltage U
OUT
Differential voltage for I
nom
Nominal current I
nom
per channel
Tolerance of the nominal current
Total current
Protection
24 V DC
1V
0.5 A
+10%
4A
Short circuit; overload
Channels are thermally coupled in groups of four, i.e., an error in one channel can affect the other channels.
Nominal load
Ohmic
Lamp
Inductive
48
/ 12 W
12 W
12 VA (1.2 H, 50
Ω)
5558
_en_08
PHOENIX CONTACT
IB IL 24 DO 8 ...
Digital outputs (continued)
Signal delay upon power up of:
Nominal ohmic load
Nominal lamp load
Nominal inductive load
Signal delay upon power down of:
Nominal ohmic load
Nominal lamp load
1 ms, typical
1 ms, typical
50 ms, typical (1.2 H, 50
Ω)
100 µs, typical
100 ms, typical (with switching frequencies up to 8Hz; above this frequency
the lamp load responds like an ohmic load)
100 ms, typical (1.2 H, 50
Ω)
Switching frequency with:
Nominal ohmic load
300 Hz, maximum
This switching frequency is limited by the selected data rate, the number of bus devices, the bus structure, the software and the control or
computer system used.
Nominal lamp load
300 Hz, maximum
Overload response:
Response time with ohmic overload (12
Ω)
Restart frequency with ohmic overload
Restart frequency with lamp overload
Response with inductive overload
Response time in the event of a short circuit
Reverse voltage protection against short pulses
Resistance to permanently applied reverse voltages
Resistance to polarity reversal of the supply voltage
Resistance to permanently applied surge voltage
Validity of output data after connecting the 24 V voltage supply (power up)
Response upon power down
Limitation of the voltage induced on circuit interruption
Single maximum energy in free running
Protective circuit type
Overcurrent shutdown
Output current when switched off
Output voltage when switched off
Output current with ground connection interrupt
Switching power with ground connection interrupt
Inrush current with lamp load
0.5 Hz, maximum (1.2 H, 48
Ω)
Auto restart
3 s, approximately
400 Hz, approximately
Output may be damaged
400 ms, approximately
Protected against reverse voltages
Up to 2 A DC
Protective elements in the bus terminal or power terminal
No
5 ms, typical
The output follows the supply voltage without delay.
-15 V
U
demag
-46 V (U
demag
= demagnetization voltage)
400 mJ, maximum
Integrated 45 V Zener diode in the output chip
0.7 A, minimum
300 µA, maximum
2 V, maximum
25 mA, maximum
100 mW at 1 kΩ load resistance, typical
1.5 A for 20 ms, maximum
Output characteristic curve when switched on (typical)
Output current (A)
0.2
0.3
0.4
Differential output voltage (V)
0.08
0.12
0.16
0.20
5558
_en_08
PHOENIX CONTACT
IB IL 24 DO 8 ...
Power dissipation
Formula to calculate the power dissipation of the electronics
500 kbps
EL
= 0.19 W +
(0.10 W + I
Ln2
x 0.40
n=1
2 Mbps
Where:
EL
n
Ln
Total power dissipation in the terminal
Index of the number of set outputs n = 1 to 8
load current of output n
E L
= 0 .4 6 W
n = 1
(0 .1 0 W
+ I
n
x 0 .4 0
Power dissipation of the housing P
HOU
Limitation of simultaneity, derating
Derating
2.7 W, maximum
(within the permissible operating temperature)
No limitation of simultaneity, no derating
Protective equipment
Overload/short circuit in the segment circuit
Surge voltage
Polarity reversal of the supply voltage
Electronic; with two 4-channel drivers
Protective elements of the power terminal
Protection up to 33 V DC
The supply voltage must be protected. The power supply unit should be able
to supply four times (400%) the nominal current of the fuse.
Reverse voltage
Protected against reverse voltages up to 2 A DC
Electrical isolation/isolation of the voltage areas
To provide electrical isolation between the logic level and the I/O area it is necessary to supply the station bus coupler and the digital output
terminal described here via the bus coupler or a power terminal from separate power supply units. Interconnection of the power supply units
in the 24 V area is not permitted. (See also user manual.)
Common potentials
The 24 V main voltage, 24 V segment voltage, and GND have the same potential. FE is a separate potential area.
Separate potentials in the system consisting of bus terminal/power terminal and I/O terminal
Test distance
Test voltage
5 V supply incoming remote bus/7.5 V supply (bus logic)
5 V supply outgoing remote bus/7.5 V supply (bus logic)
7.5 V supply (bus logic) / 24 V supply (I/O)
24 V supply (I/O) / functional earth ground
500 V AC, 50 Hz, 1 min.
Error messages to the higher-level control or computer system
Short circuit/overload of an output
Yes
An error message is generated when an output is shorted and switched on. In addition, the diagnostic LED (D) flashes on the terminal at 2Hz
(medium) under these conditions.
Operating voltage out of range
No
Approvals
For the latest approvals, please visit
5558
_en_08
PHOENIX CONTACT