PLC-OS…/SEN
PLC INTERFACE With Solid-State Relay,
Sensor Version
INTERFACE
Data Sheet
103152_en_01
© PHOENIX CONTACT - 03/2008
1.2
Optimum Use of Plug-In Bridges
In applications as the interface between the PLC and
sensors (e.g.,
proximity switches, limit switches or auxiliary
contacts),
as a rule only one N/O contact is required. In this
case, the
PLC-OS…/SEN
input module can be used, which
is specially optimized for these applications and consists of
a 6.2 mm basic terminal block and plug-in miniature solid-
state relay with screw or spring-cage connection.
1.1
No Need for Power Terminal Blocks
Unlike conventional input relays, all sensor connections,
including the supply voltage for the sensors and switches,
are connected directly to the PLC INTERFACE module. The
PLC-OS…/SEN can thus be used directly as a terminal strip
with integrated interface function for the incoming sensor
cables, without the need for additional modular terminal
blocks (see also INTERFACE catalog).
– Elimination of the need for modular terminal blocks for
the
sensor/switch
supply, signal, and sensor ground
– Space savings of around 80%
– Time saving of around 60%
– Reduction in wiring due to plug-in bridges
The PLC INTERFACE module achieves maximum
efficiency with the user-friendly FBST plug-in bridge system.
The PLC-OS…/SEN makes effective use of the bridging
options for the power supply for sensors/switches, for the
supply/sensor ground at the A2 connection, and for the
common supply potential of the PLC at connection 13.
Especially effective here are the 500 mm long color-
insulated continuous plug-in bridges that can easily be cut to
the required length and quickly inserted in the bridge shafts.
They eliminate the need for complicated and time-
consuming loop bridges – the reduction in wiring by
eliminating the need for modular terminal blocks and the use
of all bridging options is around 60%.
1.3
Additional Advantages
Switching power of up to 24 V DC/3 A, depending on
the type
IP67-protected fully encapsulated optical electronics
Available with input or power solid-state relays as an
option
Integrated input circuit
Solid-state relay can be replaced using an engagement
lever
Wear-resistant switching
Resistant to vibrations and shocks
Inflammability class V0 according to UL94
Make sure you always use the latest documentation.
It can be downloaded at
www.download.phoenixcontact.com.
A conversion table is available on the Internet at
www.download.phoenixcontact.com/general/7000_en_00.pdf.
This data sheet is valid for all products listed on the following page:
PLC-OS…/SEN
Ordering Data
Order No.
2966773
2966799
2966809
2967578
2967581
2967594
PLC INTERFACE With Solid-State Relay, Sensor Version
PLC INTERFACE, comprising PLC-BSC...SEN
basic terminal block and plug-in solid-state relay
(see INTERFACE catalog), with screw
connection, for mounting on
PLC INTERFACE, comprising PLC-BSP...SEN
(see INTERFACE catalog), with spring-cage
Pcs./Pck.
24 V DC PLCOSC- 24DC/48DC/100/SEN
120 V AC/110 V DC PLCOSC-120UC/48DC/100/SEN
230 V AC/220 V DC
PLCOSC-230UC/48DC/100/SEN
24 V DC PLCOSP- 24DC/48DC/100/SEN
120 V AC/110 V DC PLCOSP-120UC/48DC/100/SEN
230 V AC/220 V
DC
PLCOSP-230UC/48DC/100/SEN
The PLC-ATP BK insulating plate must be installed for voltages greater than 250 V (L1, L2, L3) between the same terminal points on adjacent modules
(see "Accessories"). FBST 8-PLC... or FBST 500... is then used for potential bridging.
With the 120 V and 230 V modules, an OPT-60DC/... 60 V solid-state relay is normally used due to the input circuit integrated in the basic terminal
block.
For the protection of input and output, inductive loads must be dampened with an effective protective circuit.
Accessories
Insulating plate
PLC-ATP BK
Order No.
2966841
Pcs./Pck.
The PLC-ATP BK insulating plate should be used in the following cases: always fit at the start and end of a PLC terminal strip for voltages
greater than 250 V (L1, L2, L3) between the same terminal points on adjacent modules (FBST 8-PLC... or FBST 500... can be used for
potential bridging) and for safe isolation between adjacent modules.
For additional accessories such as power terminal blocks and plug-in bridges, please refer to the INTERFACE catalog or
www.phoenixcontact.com.
Technical Data
...24DC...
24 V DC
0.8 ... 1.2 x U
0.8 x U
0.4 x U
8 mA
μs
μs
300 Hz
Yellow LED, protection
against polarity
reversal, free-wheeling
diode
6 ms
10 ms
10 Hz
Yellow LED, bridge rectifier
Input Data
Nominal input voltage
Permissible range (with reference to U
Switching level
1 signal ("H")
0 signal ("L")
Typical input current at U
Typical response time at U
Typical release time at U
Transmission frequency f
limit
Input circuit
...120UC...
120 V AC/110 V DC
...230UC...
230 V AC/220 V DC
0.8 ... 1.1 x U
0.8 x U
0.3 x U
4 mA
3 ms
5 ms
Output Data
Maximum switching voltage
Minimum switching voltage
Limiting continuous current
Output configuration
Output circuit
Voltage drop at maximum limiting continuous current
48 V DC
3 V DC
100 mA
2-wire floating
Protection against polarity reversal, surge protection
1V
103152_en_01
PHOENIX CONTACT
PLC-OS…/SEN
General Data
Impulse voltage withstand level
Ambient temperature range
Operation
Storage/transport
Nominal operating mode
Inflammability class according to UL 94 (housing)
Standards/specifications
Pollution degree
Surge voltage category
Mounting position
Mounting
Conductor cross-section
Solid, with screw connection
Stranded, with screw connection
Solid, with spring-cage connection
Stranded, with spring-cage connection
Stripping length
Screw connection
Spring-cage connection
Dimensions (W x H x D)
Housing material
2.5 kV, 50 Hz, 1 min.
-25°C ... 60°C (230 V type 20°C ... 55°C)
-40°C ... 85°C
100% operating factor
V0
IEC 60664, IEC 60664 A, DIN VDE 0110 (basic insulation)
III
Any
Can be aligned without spacing
0.14 mm
... 2.5 mm
(26 - 14 AWG)
0.14 mm
... 1.5 mm
(26 - 14 AWG)
0.2 mm
... 2.5 mm
(24 - 14 AWG)
0.2 mm
... 1.5 mm
(24 - 14 AWG)
10 mm
8 mm
6.2 mm x 94 mm x 80 mm
Polyamide PA, green
The PLC-ATP BK insulating plate must be installed for safe isolation between adjacent modules (see "Accessories"). FBST 8-PLC... or FBST 500... is
Tests/Approvals
CE
UL
GL
c
Uu
Block Diagram
Load current [A]
Derating Curve
Ambient temperature [°C]
13+
A2
BB
A1
1)
The input circuit
depends on the type
103152_en_01
PHOENIX CONTACT GmbH & Co. KG • 32823 Blomberg • Germany • Phone: +49 - 52 35 - 30 0