https://www.phoenixcontact.com/us/products/2692076
I/O module - ILB S3 AI4 AO2-2TX - 2692076
Inline Block IO Analog I/O module, Sercos III, inputs: 0-20 mA, 4-20 mA, ±20 mA, 0-5 V, ±5 V, 0-10 V, ±10
V, Pt 100, Pt 1000, Ni 1000..., outputs: 0-5 V, ±5 V, 0-10 V, ±10 V, 0-20 mA, ±20 mA, 4-20 mA, 2-, 3-, 4-wire
connection
Product description
The multifunctional, analog Inline Block I/O modules can be used universally. The four inputs either offer the difference measured between analog
current / voltage signals or the option of connecting resistance thermometers (RTDs). Furthermore, the current or voltage actuators can be connected at
the two outputs. In addition, all channels are equipped with shield connections as a standard and are provided with the 2, 3 or 4-conductor system. The
analog signals are made available with a resolution of 16 bits.
The plugs can be labeled using hinged labeling fields. The fields have insert cards that can be labeled individually to suit the application. Additionally,
there is the proven ZBFM-6... Zack marker strip for labeling the terminal points.
Product Features
Short-circuit-proof outputs
2 shielded analog signal outputs with 4 voltage and 3 current ranges
Sensor supply with channel-specific integrated short-circuit and overload protection
Adjustable filter times
4 voltage measuring ranges and 3 current measuring ranges
4 shielded analog differential signal inputs or 4 universal RTD inputs
Connection of actuators in 2-wire technology
Connection of sensors in 2, 3, and 4-wire technology
Packing unit
Custom tariff number
Country of origin
1 pc
85176200
Germany
Key commercial data
Technical data
Utilization restriction
EMC: class A product, see manufacturer's declaration in the download
area
09/03/2014 Page 1 / 6
Technical data
Dimensions
Width
Height
Depth
156 mm
136.8 mm
57 mm
Ambient conditions
Ambient temperature (operation)
Ambient temperature (storage/transport)
Permissible humidity (operation)
Permissible humidity (storage/transport)
Air pressure (operation)
Air pressure (storage/transport)
Degree of protection
-25 °C ... 60 °C
-25 °C ... 85 °C
10 % ... 85 % (non-condensing)
10 % ... 95 % (non-condensing)
70 kPa ... 108 kPa (up to 3500 m above mean sea level)
IP20
General
Weight
Mounting type
Protection class
Test section
465 g
DIN rail
III, IEC 61140, EN 61140, VDE 0140-1
Sercos III/logic area 500 V AC 50 Hz 1 min
Sercos III/analog I/O 500 V AC 50 Hz 1 min
Sercos III/communications power 500 V AC 50 Hz 1 min
Sercos III/initiator supply 500 V AC 50 Hz 1 min
Sercos III/functional earth ground 500 V AC 50 Hz 1 min
Logic/analog I/O 500 V AC 50 Hz 1 min
Logic area/initiator supply 500 V AC 50 Hz 1 min
Logic area/functional earth ground 500 V AC 50 Hz 1 min
Analog I/O/communications power 500 V AC 50 Hz 1 min
Analog I/O/initiator supply 500 V AC 50 Hz 1 min
Functional earth ground/analog I/O (isolating distance) 500 V AC 50 Hz 1
min
Functional earth ground/communications power 500 V AC 50 Hz 1 min
Functional earth ground/initiator supply 500 V AC 50 Hz 1 min
Mechanical tests
Vibration resistance in acc. with EN 60068-2-6/IEC 60068-2-6 5g
Shock in acc. with EN 60068-2-27/IEC 60068-2-27 30g
Interfaces
Fieldbus system
Designation
Connection method
Transmission speed
Sercos
Inline local bus
RJ45 socket, shielded
100 MBit/s
09/03/2014 Page 2 / 6
Technical data
Interfaces
Transmission physics
Copper
Inline potentials
Communications power U
Power supply at U
Current consumption from U
Segment supply voltage U
Power supply at U
24 V DC
max. 8 A
max. 220 mA (AO-I nominal load)
24 V DC
max. 8 A
max. 220 mA (Maximum full load)
Axioline potentials
Analog inputs
Number of inputs
Connection method
Input name
A/D conversion time
Resolution A/D
Limit frequency (3 dB)
Data formats
Measured value resolution
Current input signal
max. 4 (Differential inputs, voltage or current can be chosen separately)
Spring-cage connection
2, 3, 4-wire (shielded)
Analog inputs
typ. 180 µs
16 bit
120 Hz (default for 4.5 ms filter)
450 Hz (for 1.1 ms filter)
IB IL, S7-compatible
16 bits (15 bits + sign bit)
0 mA ... 20 mA
4 mA ... 20 mA
-20 mA ... 20 mA
Input resistance current input
Voltage input signal
typ. 107 Ω
0 V ... 5 V
-5 V ... 5 V
0 V ... 10 V
-10 V ... 10 V
Input resistance of voltage input
Number of inputs
Type of protection
Open circuit response
typ. 276 kΩ
4 (differential inputs, voltage)
Overload protection, short-circuit protection of sensor supply
Goes to 0 V
0 V ... 5 V
-5 V ... 5 V
0 V ... 10 V
-10 V ... 10 V
09/03/2014 Page 3 / 6
Technical data
Analog inputs
Number of inputs
Type of protection
typ. 276 kΩ
4 (differential inputs, current)
Short-circuit protection for the sensor supply
Going to 0 mA; open-circuit detection from 4 mA ... 20 mA
0 mA ... 20 mA
4 mA ... 20 mA
-20 mA ... 20 mA
Number of inputs
Input name
Sensor types (RTD) that can be used
Linear resistance measuring range
Protective circuit
typ. 107 Ω
Analog RTD inputs
Pt100, Pt500, Pt1000, Ni100, Ni1000, Ni1000 L&G
0 Ω ... 3200 Ω
0 Ω ... 9500 Ω
Analog outputs
Number of outputs
Connection method
Output name
D/A conversion time
D/A resolution
Type of protection
Process data update
Current output signal
2-wire (shielded)
Analog outputs
typ. 70 µs
16 bit
Short-circuit protection of outputs
17 ms
0 mA ... 20 mA
4 mA ... 20 mA
-20 mA ... 20 mA
Voltage output signal
0 V ... 5 V
-5 V ... 5 V
0 V ... 10 V
-10 V ... 10 V
Load/output load voltage output
> 2 kΩ
Classifications
eCl@ss
eCl@ss 4.0
eCl@ss 4.1
27250303
27250303
09/03/2014 Page 4 / 6
Classifications
eCl@ss
eCl@ss 5.0
eCl@ss 5.1
eCl@ss 6.0
eCl@ss 7.0
eCl@ss 8.0
27250303
27250303
27242601
27242601
27242601
ETIM
ETIM 2.0
ETIM 3.0
ETIM 4.0
ETIM 5.0
EC001431
EC001596
EC001596
EC001596
UNSPSC
UNSPSC 6.01
UNSPSC 7.0901
UNSPSC 11
UNSPSC 12.01
UNSPSC 13.2
43172015
43201404
43172015
43201404
43201404
Approvals
Approvals
Approvals
UL Listed / cUL Listed / UL Listed / cUL Listed / cULus Listed
Ex Approvals
Approvals submitted
Approval details
UL Listed